The following table lists the specifications for three-phase power distributions units (PDUs) in various countries.
| Three-phase PDUs | North America, South America, Japan, and Taiwan | EMEA | 
|---|---|---|
| Rack location | Vertical rack-mounted PDUs that occupy no rack unit (RU) space. | Vertical rack-mounted PDUs that occupy no RU space. | 
| Inlet circuits | Each PDU has one 60 A inlet circuit. Each phase supplies a maximum of 40 A. Output is 23 A (maximum) for each phase. | Each PDU must have one 60 A inlet circuit. Each phase supplies a maximum of 40 A. Output is 23 A (maximum) for each phase. | 
| AC voltage | The PDU supports AC input voltage levels from 200 to 240 VAC. The domestic PDU is used with 60 A 208 V three-phase Wye service. | The PDU supports AC input voltages from 200 to 240 VAC. The European PDU is used with 25 A 380 VAC three-phase Wye service. | 
| Power | Each PDU can supply 14.4KW of power. The inlet cable has a plug style that is an IEC309 60A 4 Pin. | Each PDU can supply 14.4 KW of power. The inlet cable has a plug style that is an IEC309 32A 5 Pin. | 
| Outlet groups | All PDUs have 42 outlets arranged in six groups of seven. Each phase drives two groups on the PDU. Phase 1 supplies power to group 0 and 3. Phase 2 supplies power to group 1 and 4. Phase 3 supplies power to groups 2 and 5. | All PDUs have 42 outlets arranged in six groups of seven. Each phase drives two groups on the PDU. Phase 1 supplies power to group 0 and 3. Phase 2 supplies power to group 1 and 4. Phase 3 supplies power to groups 2 and 5. | 
| Receptacles | All 42 outlets are IEC60320 C13 style receptacles. The C13 receptacle can supply 10A. Note: If two outlets are configured to draw 10 A each, the remaining five outlets in the group cannot be used. | All 42 outlets are IEC60320 C13 style receptacles. The C13 receptacle can supply 10A. Note: If two outlets are configured to draw 10A each, the remaining five outlets in the group cannot be used. | 
| Circuit breaker | Each group of seven outlets have a 20 A rated circuit breaker that can be re-set. | Each group of seven outlets have a 20 A rated circuit breaker that can be re-set. | 
Figure: 1 Three-phase PDU outlet groups
 
 | 1 AC inlet circuit P1 supplies groups 0 and 3 | 
| 2 AC inlet circuit P2 supplies groups 1 and 4 | 
| 3 AC inlet circuit P3 supplies groups 3 and 5 | 
| 4 Amps are monitored across both AC inputs | 
| 5 Group of seven outlets has its own 20 A circuit breaker that can be re-set |