TCA Reporting of Denied Entries
You can construct a Threshold Crossing Alarm (TCA), which issues minor, major, and critical system alarms when the count of denied entries exceeds pre-configured values. For each issued alarm, the TCA also transmits an SNMP trap that reports the alarm state to remote SNMP agents.
After issuing a system alarm and accompanying SNMP trap, the TCA continues to monitor the number of denied entries. If the number of denied entries rises to the next threshold value, a new, and more severe, system alarm/SNMP trap is generated. If the number of denied entries falls below the current threshold level, and remains there for a period of at least 10 seconds, a new, and less severe system alarm/SNMP trap is generated.
  1. Use the following command sequence to move to media-manager-config Configuration Mode.
    ORACLE# configure terminal
    ORACLE(configure)# system
    ORACLE(system)# system-config
    ORACLE(system-config)# alarm-threshold
    ORACLE(alarm-threshold)#
  2. Use the type attribute to specify the TCS type (deny-allocation for denied entries TCAs), the severity attribute to specify the criticality of the alarm, and the value attribute to specify the alarm threshold.
    The following ACLI sequence defines the minor, major, and critical alarm thresholds. Not that you do not need to configure all three thresholds. Given the static deny allocation value of 32000, you can determine what the percentage value maps to.
    ORACLE(alarm-threshold)# type deny-allocation
    ORACLE(alarm-threshold)# severity minor
    ORACLE(alarm-threshold)# value 80
    ORACLE(alarm-threshold)# done
    ORACLE(alarm-threshold)# severity major
    ORACLE(alarm-threshold)# value 90
    ORACLE(alarm-threshold)# severity critical
    ORACLE(alarm-threshold)# value 95
  3. Use exit and verify-config to complete the configuration.