4 Disaster Recovery Procedure
Call My Oracle Support (MOS) prior to running the procedure to ensure that the proper recovery planning is performed.
Before disaster recovery, users must appropriately evaluate the outage scenario. This check ensures the correct procedures are run for the recovery.
Note:
Disaster recovery is an exercise that requires collaboration of multiple groups and is expected to be coordinated by the Oracle Support prime. Based on the Oracle Support assessment of Disaster, it may require to deviate from the documented process.4.1 Recovering and Restoring System Configuration
Disaster recovery requires configuring the system as it was before the disaster and restoration of operational information. There are 8 distinct procedures to choose from depending on the type of recovery needed. Only one of these must be followed.
WARNING:
- Whenever there is a need to restore the database backup for NOAM and SOAM servers in any of below Recovery Scenarios, the backup directory may not be there in the system as system will be DRed (Demand Response Enabling Device).
- In this case, refer to workarounds for issues not fixed in this release, this will provide steps to check and create the backup directory.
- Following is the standard file format to be used for recovery.
Backup.DSR.HPC02-NO2.FullDBParts.NETWORK_OAMP.20140524_223507.UPG.tar.bz2
4.1.1 Recovery Scenario 1 (Complete Server Outage)
For a complete server outage, NOAM servers are recovered using recovery procedures for software and then executing a database restore to the active NOAM server. All other servers are recovered using recovery procedures for software.
Database replication from the active NOAM server will recover the database on these servers. The major activities are summarized in the list below. This list will help to understand the recovery procedure summary. Do not use this list to run the procedure. The major activities are summarized as follows.
- Recover the Standby NOAM server by recovering base software, for a Non-HA
deployment this can be skipped.
- Reconfigure the DSR Application.
- Recover all SOAM and MP servers by recovering software, In a Non-HA deployment
the Standby/Spare SOAM servers can be skipped.
- Recover the SOAM database.
- Reconfigure the DSR Application.
- Reconfigure the signaling interface and routes on the MPs, the DSR software will automatically reconfigure the signaling interface from the recovered database.
Restart process and re-enable provisioning replication
Note:
Any other applications DR recovery actions (SDS and IDIH) may occur in parallel. These actions can/should be worked simultaneously; doing so would allow faster recovery of the complete solution (i.e. stale DB on DP servers will not receive updates until SDS-SOAM servers are recovered.This procedure performs recovery if both NOAM servers are failed and all SOAM servers are failed. This procedure also covers the C-Level Server failure.
Note:
If this procedure fails, contact My Oracle Support (MOS), and ask for assistance.- Refer to workarounds for issues not fixed in this release to understand or apply any workarounds required during this procedure.
- Gather the documents and required materials listed in the Required Materials section.
- Recover the Failed Software:
For VMware based deployments:
- For NOAMs run the following procedures:
- Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Configure NOAM guests based on resource profile.
- Import DSR OVA
- For SOAMs run the following procedures:
- Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Configure Remaining DSR guests based on resource profile
- Import DSR OVA
- For failed MPs run the following procedures:
- Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Configure Remaining DSR guests based on resource profile.
- Import DSR OVA.
- For KVM or Openstack based deployments:
- Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Configure NOAM guests based on resource profile.
- Import DSR OVA.
- For SOAMs run the following procedures:
- KVM / Openstack Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - KVM / Openstack Configure Remaining DSR guests based on resource profile.
- KVM / Openstack Import DSR OVA.
- For OVM-S / OVM-M based deployments run the following procedures:
- Import DSR OVA and prepare for VM creation.
- Configure each DSR VM.
Note:
While running procedure 8, configure the required failed VMs only (NOAMs/SOAMs/MPs).
- For NOAMs run the following procedures:
- Obtain the most recent database backup file from external backup sources (ex.
file servers) or tape backup sources.
- From Required Materials list, use site survey documents and Network Element report (if available), to determine network configuration data.
- Run DSR installation procedure for the first NOAM:
- Verify the networking data for Network Elements.
Note:
Use the backup copy of network configuration data and site surveys (Step 2). - Run installation procedures for the first NOAM server:
- Configure the First NOAM NE and Server.
- Configure the NOAM Server Group.
- Verify the networking data for Network Elements.
- Log in to the NOAM GUI as the guiadmin user.
- Navigate to Main Menu, and then Status &
Manage, and then Files.
- Select the Active NOAM server and click Upload.
- Select "NO Provisioning and Configuration" file, backed up after initial installation and provisioning.
- Click Browse and locate the backup file.
- Check This is a backup file box and click
Upload.
The file will take a few seconds to upload depending on the size of the backup data. The file will be visible on the list of entries after the upload is complete.
- To disable provisioning:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- click Disable Provisioning. A confirmation window
will appear, press OKto disable.
Note:
The message "warning Code 002" will appear.
- Verify the archive contents and database compatibility:
- Select the Active NOAM server and click
Compare.
Click restored database file that was uploaded as a part of step 13 of this procedure.
- Verify that the output window matches the database.
Note:
- As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS).
- Archive content and database compatibilities must consist
the following:
- Archive Contents: Configuration data
- Database Compatibility: The databases are compatible.
- When restoring from an existing backup database to a
database using a single NOAM, the expected outcome for the
topology compatibility check is as follows:
- Topology compatibility: Topology must be compatible minus the NODEID.
- Attempting to restore a backed-up database onto a NOAM
database which is empty. In the context of Topology
Compatibility, this text is expected.
If the verification is successful, click Back and continue to next step of this procedure.
- Select the Active NOAM server and click
Compare.
- Restore the database:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active NOAM server and click
Restore. Select the appropriate backup
provisioning and configuration file and click OK.
Note:
As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS). - Select the Force checkbox and click
OK to proceed with the database
restore.
Note:
After the restore has started, the user will be logged out of XMI NO GUI since the restored Topology is old data.
- Establish a GUI session on the NOAM server by using the VIP IP address of the
NOAM server. Open the web browser and enter the following URL
http://<Primary_NOAM_VIP_IP_Address>
. - Monitor and Confirm database restoral. Wait for 5 to10 minutes for the System to
stabilize with the new topolog.
Monitor the Info tab for Success. This will indicate that the backup is complete and the system is stabilized.
Following alarms must be ignored for NOAM and MP Servers until all the Servers are configured:
- Alarms with Type Column as “REPL” , “COLL”, “HA” (with mate NOAM), “DB”
(about Provisioning Manually Disabled).
Note:
- Do not pay attention to alarms until all the servers in the system are completely restored.
- The maintenance and configuration data will be in the same state as when it was first backed up.
- Alarms with Type Column as “REPL” , “COLL”, “HA” (with mate NOAM), “DB”
(about Provisioning Manually Disabled).
- Log in to the recovered Active NOAM through SSH terminal as admusr user.
- Recover Standby NOAM:
- Install the second NOAM server by running the following procedures:
- "Configure the Second NOAM server" steps 1, 3, and 7.
- "Complete Configuring the NOAM Server Group " Step 4.
- Install the second NOAM server by running the following procedures:
- Correct the Recognized Authority table:
- Establish an SSH session to the active NOAM, log in as an admusr.
- Run the following
command:
$ sudo top.setPrimary - Using my cluster: A1789 - New Primary Timestamp: 11/09/15 20:21:43.418 - Updating A1789.022: <DSR_NOAM_B_hostname> - Updating A1789.144: <DSR_NOAM_A_hostname>
- Restart DSR application:
- Navigate to Main Menu, and then Status & Manage, and then Server.
- Select the recovered standby NOAM server and click Restart.
- Set HA on Standby NOAM:
- Navigate to Main Menu, and then Status & Manage, and then HA.
- Click Edit, select the standby NOAM server and set it to Active and click OK.
- Perform key exchange with Export Server:
- Navigate to Main Menu, Administration, Remote Servers and then Data Export.
- Click SSH Key Exchange, enter the password and click OK.
- Replication will wipe out the databases on the C level servers when Active SOAM
is recovered, hence prevent replication to the operational C level servers that
are part of the same site as the failed SOAM servers.
WARNING:
- If the spare SOAM is also present in the site and lost: Inhibit A and B level replication on C-Level servers (when Active, Standby, and Spare SOAMs are lost)
- If the spare SOAM is not deployed in the site: Run Inhibit A and B level replication on C-level servers.
- Run the steps 1 and 3 to 7 "Configure the SOAM
Servers" to Install the SOAM servers.
Note:
Before continuing to next step, wait for the server to reboot. - Restart DSR application on recovered Active SOAM Server:
- Navigate to Main Menu, and then Status & Manage, and then Server.
- Select the recovered server and click Restart.
- Upload the backed up SOAM database file:
- Navigate to Main Menu, and then Status & Manage, and then Files.
- Select the Active SOAM server. Click Upload and select the file "SO Provisioning and Configuration" backed up after initial installation and provisioning.
- Click Browse and locate the backup file.
- Check This is a backup file box and click Open.
- Click Upload.
The file will take a few seconds to upload depending on the size of the backup data. The file will be visible on the list of entries after the upload is complete.
- Establish a GUI session on the recovered SOAM server. Open the web browser and
enter the following URL
http://<Recovered_SOAM_IP_Address>
. - Recovered SOAM GUI, verify the archive contents and database compatibility:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active SOAM server and click Compare.
- Click Restored Database file that was uploaded as
a part of Step 13 of this procedure. Verify that the output window
matches the database archive.
Note:
- As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS).
- Archive content and database compatibilities must consist
the following:
- Archive Contents: Configuration data
- Database Compatibility: The databases are compatible.
- When restoring from an existing backup database to a
database using a single NOAM, the expected outcome for the
topology compatibility check is as follows:
- Topology compatibility: Topology must be compatible minus the NODEID.
- Attempting to restore a backed-up database onto a NOAM
database which is empty. In the context of Topology
Compatibility, this text is expected.
If the verification is successful, click Back and continue to next step of this procedure.
- Restore the Database:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active NOAM server and click
Restore. Select the appropriate backup
provisioning and configuration file and click OK.
Note:
As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS). - Select the Force checkbox and click
OK to proceed with the database
restore.
Note:
After the restore has started, the user will be logged out of XMI NO GUI since the restored Topology is old data.
- Monitor and Confirm database restoral, wait for 5-10 minutes for the system to
stabilize with the new topology.
Monitor the Info tab for "Success". This will indicate that the backup is complete and the system is stabilized.
Note:
- Do not pay attention to alarms until all the servers in the system are completely restored.
- The maintenance and configuration data will be in the same state as when it was first backed up.
- Establish a GUI session on the NOAM server by using the VIP IP address of the
NOAM server. Open the web browser and enter the following url
http://<Primary_NOAM_VIP_IP_Address>
. - Recover remaining SOAM Server:
- Install the SOAM servers by running the following procedure:
- Run the steps 1 and 3 to 6 "Configure
the SOAM Servers" to Install the SOAM servers.
Note:
Before continuing to next step, wait for the server to reboot.
- Run the steps 1 and 3 to 6 "Configure
the SOAM Servers" to Install the SOAM servers.
- Install the SOAM servers by running the following procedure:
- Restart DSR application on remaining SOAM Server(s):
- Navigate to Main Menu, and then Status & Manage, and then Server.
- Select the recovered server and click Restart.
- Set HA on recovered standby SOAM server:
Note:
For Non-HA sites, skip this step.- Navigate to Main Menu, and then Status & Manage, and then HA.
- Click Edit and set "Max Allowed HA Role" to Active and click OK.
- Start replication on working C- level servers:
Un-Inhibit (Start) replication to the working C level servers which belong to the same site as of the failed SOAM servers.
If the spare SOAM is also present in the site and lost: rxecute un-inhibit A and B level replication on C-level servers (when Active, Standby and Spare SOAMs are lost).
If the spare SOAM is not deployed in the site: Run un-inhibit A and B Level replication on C-level servers.
Navigate to Main Menu, and then Status & Manage, and then Database.
If the "Repl Status" is set to "Inhibited", click Allow Replication using the following order, otherwise if none of the servers are inhibited, skip this step and continue with the next step:
- Active NOAM Server
- Standby NOAM Server
- Active SOAM Server
- Standby SOAM Server
- Spare SOAM Server (if applicable)
- MP/IPFE Servers
- SBRS (if SBR servers are configured, start with the active SBR, then standby, then spare)
Verify that the replication on all the working servers is allowed.
- Establish a SSH session to the C level server being recovered, login as an
admusr.
- Run the following command to set shared memory to
unlimited
$ sudo shl.set –m 0
- Run the following procedures from each server that has been
recovered:
- Run the steps 1, 11 to 14 (step 15 if required) Configure the MP Virtual Machines.
- Run the following command to set shared memory to
unlimited
- Restart DSR application for Recovered C- level server:
- Navigate to Main Menu, and then Status & Manage, and then Server.
- Select the recovered server and click Restart.
- Start replication on all C-level servers:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- If the "Repl" status is set to "Inhibited", click Allow
Replication by following the order:
- Active NOAM Server
- Standby NOAM Server
- Active SOAM Server
- Standby SOAM Server
- Spare SOAM Server (if applicable)
- MP/IPFE Servers
- Verify that the replication on all the working servers is allowed. This can be done by examining the Repl Status.
- Navigate to Main Menu, and then Status &
Manage, and then HA.
- Click Edit, for each server whose Max Allowed HA Role is set to OOS, set it to Active and click OK.
- Perform key exchange between the Active-NOAM and recovered servers:
- Establish an SSH session to the Active NOAM, log in as an admusr.
- Run the following command to perform a key exchange from the active NOAM
to each recovered
server:
$ keyexchange admusr@<Recovered Server Hostname>
Note:
Perform this step, If an export server is configured.
- Activate Optional Features:
- Establish an SSH session to the active NOAM, log in as
admusr.
Note:
- If you have PCA installed in the system being recovered, run the procedure "PCA Activation on Stand By NOAM server" on recovered Standby NOAM Server and procedure "PCA Activation on Active SOAM server" on recovered Active SOAM Server from [3] to re-activate PCA.
- The same procedure applies to all the application.
Refer to Optional Features to activate any features that were previously activated.
Note:
- While running the activation script, the following error message
(and corresponding messages) output may be seen, the error can be
ignored
iload#31000{S/W Fault}
. - If any of the MPs are failed and recovered, then these MP servers should be restarted after activation of the feature.
- Establish an SSH session to the active NOAM, log in as
admusr.
- Fetch and store the database report for the newly restored data and save it:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active NOAM server and click Report.
- Click Save and save the report to the local machine.
- Verify replication between servers:
- Log in to the Active NOAM through SSH terminal as admusr user.
- Run the following
command:
$ sudo irepstat –m Output like below shall be generated: -- Policy 0 ActStb [DbReplication] --------------------- Oahu-DAMP-1 -- Active BC From Oahu-SOAM-2 Active 0 0.50 ^0.15%cpu 25B/s A=me CC To Oahu-DAMP-2 Active 0 0.10 0.14%cpu 25B/s A=me Oahu-DAMP-2 -- Stby BC From Oahu-SOAM-2 Active 0 0.50 ^0.11%cpu 31B/s A=C3642.212 CC From Oahu-DAMP-1 Active 0 0.10 ^0.14 1.16%cpu 31B/s A=C3642.212 Oahu-IPFE-1 -- Active BC From Oahu-SOAM-2 Active 0 0.50 ^0.03%cpu 24B/s A=C3642.212 Oahu-IPFE-2 -- Active BC From Oahu-SOAM-2 Active 0 0.50 ^0.03%cpu 28B/s A=C3642.212 Oahu-NOAM-1 -- Stby AA From Oahu-NOAM-2 Active 0 0.25 ^0.03%cpu 23B/s Oahu-NOAM-2 -- Active AA To Oahu-NOAM-1 Active 0 0.25 1%R 0.04%cpu 61B/s AB To Oahu-SOAM-2 Active 0 0.50 1%R 0.05%cpu 75B/s Oahu-SOAM-1 -- Stby BB From Oahu-SOAM-2 Active 0 0.50 ^0.03%cpu 27B/s Oahu-SOAM-2 -- Active AB From Oahu-NOAM-2 Active 0 0.50 ^0.03%cpu 24B/s BB To Oahu-SOAM-1 Active 0 0.50 1%R 0.04%cpu 32B/s BC To Oahu-IPFE-1 Active 0 0.50 1%R 0.04%cpu 21B/s irepstat ( 40 lines) (h)elp (m)erged
- Verify the database states:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Verify that the "OAM Max HA Role" is either Active or Standby for NOAM and SOAM and "Application Max HA Role" for MPs is Active, and that the status is Normal.
- Verify the HA Status:
- Navigate to Main Menu, and then Status & Manage, and then HA.
- Select the row for all of the servers, verify that the HA role is either Active or Standby.
- Enable Provisioning:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Click Enable Provisioning. A confirmation window will appear, click OK to enable Provisioning.
- Verify the local Node Info:
- Navigate to Main Menu, Diameter, Configuration, and then Connections.
- Verify that all the connections are shown.
- Verify the Peer Node Info:
- Navigate to Main Menu, Diameter, Configuration, and then Peer Nodes.
- Verify that all the peer nodes are shown.
- Verify the Connections Info:
- Navigate to Main Menu, Diameter, Configuration, and then Connections.
- Verify that all the connections are shown.
- To verify the vSTP MP Local nodes info:
- Log in to the SOAM VIP Server console as admusr.
- Run the following command
[admusr@SOAM1 ~]$ mmiclient.py /vstp/localhosts
- Verify the output similar to the below output.
Figure 4-1 Output
- To verify the vSTP MP Remote nodes info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/remotehosts
- Verify the output similar to the below output:
Figure 4-2 Output
- To verify the vSTP MP Connections info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/connections
- Verify the output similar to the below output:
Figure 4-3 Output
- Disable SCTP Auth Flag:
- For SCTP connections without DTLS enabled, refer to Enable/Disable DTLS Appendix from reference [1].
- Run this procedure on all Failed MP Servers.
- Enable Connections if needed:
- Navigate to Main Menu, Diameter, Maintenance, and then Connections.
- Select each connection and click Enable. Alternatively you can enable all the connections by selecting EnableAll.
- Verify that the "Operational State" is
Available.
Note:
If a disaster recovery was performed on an IPFE server, it may be necessary to disable and re-enable the connections to ensure proper link distribution.
- Enable Optional Features:
- Navigate to Main Menu, Diameter, Maintenance, and then Applications.
- Select the optional feature application configured before and click Enable.
- If required, re-enable transport:
- Navigate to Main Menu, Transport Manager, Maintenance, and then Transport.
- Select each transport and click Enable.
- Verify that the Operational Status for each transport is Up.
- Re-enable MAPIWF application if needed:
- Navigate to Main Menu, Sigtran, Maintenance, and then Local SCCP Users.
- Click Enable corresponding to MAPIWF application Name.
- Verify that the SSN status is Enabled.
- Re-enable links if needed.
- Navigate to Main Menu, Sigtran, Maintenance, and then Links.
- Click Enable for each link.
- Verify that the Operational Status for each link is Up.
- Examine All Alarms:
- Navigate to Main Menu, Alarms & Events and View Active.
- Examine all active alarms and refer to the on-line help on how to address them. For any queries contact My Oracle Support (MOS).
- Restore GUI Usernames and Passwords:
- If applicable, run steps in Section 6.0 to recover the user and group information restored.
- Backup and archive all the databases from the recovered system:
- Run DSR database backup to back up the Configuration databases.
4.1.2 Recovery Scenario 2 Partial Server Outage with One NOAM Server Intact and Both SOAMs Failed
For a partial server outage with NOAM server intact and available, SOAM servers are recovered using recovery procedures for software and then running a database restore to the active SOAM server using a database backup file obtained from the SOAM servers. All other servers are recovered using recovery procedures for software. Database replication from the active NOAM server will recover the database on these servers. The major activities are summarized in the list below. Use this list to understand the recovery procedure summary. Do not use this list to run the procedure. The actual detailed steps are in Procedure 6. The major activities are summarized as follows:
Recover Standby NOAM server (if needed) by recovering software and the database.
- Recover the Database.
- Recover the software.
- The database has already been restored at the active SOAM server and does not require restoration at the SO and MP servers.
Note:
If this procedure fails, contact My Oracle Support (MOS)- Refer to workarounds for issues not fixed in this release to understand or apply any workarounds required during this procedure.
- Gather the documents and required materials listed in the Required Materials section.
- Establish a GUI session on the NOAM server by using the VIP IP address of the NOAM
server. Open the web browser and enter the following URL
http://<Primary_NOAM_VIP_IP_Address>
. - Set failed servers to OOS:
- Navigate to Main Menu, Status & Manage, and then HA.
- Click Edit, set the "Max Allowed HA" role server to OOS for the failed servers and click OK.
- Create VMs recover the failed software:
For VMware based deployments:
- For NOAMs run the following procedures:
- Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Configure NOAM guests based on resource profile.
- Import DSR OVA
- For SOAMs run the following procedures:
- Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Configure Remaining DSR guests based on resource profile
- Import DSR OVA
- For failed MPs run the following procedures:
- Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Configure Remaining DSR guests based on resource profile.
- Import DSR OVA.
- For NOAMs run the following procedures:
- Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Configure NOAM guests based on resource profile.
- Import DSR OVA.
- For SOAMs run the following procedures:
- Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Configure Remaining DSR guests based on resource profile.
- Import DSR OVA.
- For OVM-S / OVM-M based deployments run the following
procedures:
- Import DSR OVA and prepare for VM creation.
- Configure each DSR VM.
Note:
While running procedure 8, configure the required failed VMs only (NOAMs/SOAMs/MPs).
- For NOAMs run the following procedures:
- If required, repeat step 5 for all remaining failed servers.
- Establish a GUI session on the NOAM server by using the VIP IP address of the NOAM
server. Open the web browser and enter the following URL
http://<Primary_NOAM_VIP_IP_Address>
. - Install the second NOAM server by running the following procedures:
- Run step 1 and 3 to 7 of "Configure the Second NOAM Server".
- Run step 4 of "Complete Configuring the NOAM Server".
Note:
If topology or nodeId alarms are persistent after the database restore, refer to workarounds for issues not fixed in this release or the next step. - Restart DSR application
- Navigate to Main Menu, Status & Manage, and then Server.
- Select the recovered standby NOAM server and click Restart.
- Navigate to Main Menu, Status &
Manage, and then HA.
- Click Edit, Select the standby NOAM server, set it to Active and click OK.
- Replication will wipe out the databases on the C level servers when Active SOAM is
recovered, hence prevent replication to the operational C level servers that are
part of the same site as the failed SOAM servers.
WARNING:
- If the spare SOAM is also present in the site and lost: Inhibit A and B level replication on C-Level servers (when Active, Standby, and Spare SOAMs are lost)
- If the spare SOAM is not deployed in the site: Run Inhibit A and B level replication on C-level servers.
- Install the SOAM servers by running the following procedure:
- Run steps 1 and 3 to 7 to Configure the SOAM Servers.
Note:
Before continuing to next step, wait for the server to reboot.
- Run steps 1 and 3 to 7 to Configure the SOAM Servers.
- Navigate to Main Menu, Status &
Manage, and then HA.
- Click Edit, Select the standby NOAM server, set it to Active and click OK.
- Navigate to Main Menu, Status &
Manage, and then Server.
- Select the recovered Active SOAM server and click Restart.
- Upload the backed up SOAM Database file:
- Navigate to Main Menu, Status & Manage, and then Files.
- Select the Active SOAM server and click Upload.
- Select the file "NO Provisioning and Configuration" file backed up
after initial installation and provisioning.
- Click Browse and locate the backup file.
- Check This is a backup file box.
- Click Open and click
Upload.
The file will take a few seconds to upload depending on the size of the backup data. The file will be visible on the list of entries after the upload is complete
- Establish a GUI session on the recovered SOAM server. Open the web browser and enter
the following URL
http://<Recovered_SOAM_IP_Address>
. - Recovered SOAM GUI, verify the archive contents and database
compatibility:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active SOAM server and click Compare.
- Click Restored Database file that was
uploaded as a part of Step 14 of this procedure. Verify that the output
window matches the database archive.
Note:
- As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS).
- Archive content and database compatibilities must
consist the following:
- Archive Contents: Configuration data
- Database Compatibility: The databases are compatible.
- When restoring from an existing backup database to
a database using a single NOAM, the expected outcome for the
topology compatibility check is as follows:
- Topology compatibility: Topology must be compatible minus the NODEID.
- Attempting to restore a backed-up database onto a
NOAM database which is empty. In the context of Topology
Compatibility, this text is expected.
If the verification is successful, click Back and continue to next step of this procedure.
- Restore the Database:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active NOAM server and click
Restore. Select the appropriate backup
provisioning and configuration file and click OK.
Note:
As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS). - Select the Force checkbox and click
OK to proceed with the database restore.
Note:
After the restore has started, the user will be logged out of XMI NO GUI since the restored Topology is old data. The provisioning will be disabled after this step.
- Monitor and Confirm database restoral, wait for 5-10 minutes for the system to
stabilize with the new topology.
Monitor the Info tab for "Success". This will indicate that the backup is complete and the system is stabilized.
Note:
- Do not pay attention to alarms until all the servers in the system are completely restored.
- The maintenance and configuration data will be in the same state as when it was first backed up.
- Install the SOAM servers by running the following procedure:
- Run step 1 and 3 to 6 "Configure the SOAM
Servers" to Install the SOAM servers.
Note:
Before continuing to next step, wait for the server to reboot.
- Run step 1 and 3 to 6 "Configure the SOAM
Servers" to Install the SOAM servers.
- Un-Inhibit (Start) replication to the recovered SOAM servers:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Click Allow Replication on the recovered SOAM servers.
- Verify that the replication on all SOAMs servers is allowed. This can be done by checking "Repl" status column of respective server.
- Navigate to Main Menu, and then Status & Manage, and then Server.
- When prompted with the question "Are you sure you wish to Force an NTP Sync on the following server(s)? SOAM2, click OK.
- Navigate to Main Menu, and then Status &
Manage, and then HA.
- Click Edit, For each SOAM server whose Max Allowed HA Role is set to Standby, set it to Active.
- Navigate to Main Menu, Status & Manage, and then Server. Select the recovered server and click Restart.
- Enable Provisioning:
- Navigate to Main Menu, Status & Manage, and then Database.
- Click Enable Site Provisioning, a confirmation window will appear, click OK to enable Provisioning.
- Un-Inhibit (Start) replication to the working C level servers which belong to the
same site as of the failed SOAM servers.
If the spare SOAM is also present in the site and lost: rxecute un-inhibit A and B level replication on C-level servers (when Active, Standby and Spare SOAMs are lost).
If the spare SOAM is not deployed in the site: Run un-inhibit A and B Level replication on C-level servers.
Navigate to Main Menu, and then Status & Manage, and then Database.
If the "Repl Status" is set to "Inhibited", click Allow Replication using the following order, otherwise if none of the servers are inhibited, skip this step and continue with the next step:
- Active NOAM Server
- Standby NOAM Server
- Active SOAM Server
- Standby SOAM Server
- Spare SOAM Server (if applicable)
- MP/IPFE Servers
- SBRS (if SBR servers are configured, start with the active SBR, then standby, then spare)
Verify that the replication on all the working servers is allowed. This can be done by examining the Repl Status table.
- Establish a SSH session to the C level server being recovered, login as
an admusr.
- Run the following command to set shared memory to
unlimited
$ sudo shl.set –m 0
- Run the following procedures for each server that has been
recovered:
- Run step 1, 8 to 14, (step 15 if required) Configure the MP Virtual Machines.
- Run the following command to set shared memory to
unlimited
- Start replication on all C-level servers:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- If the "Repl" status is set to "Inhibited", click Allow
Replication by following the order:
- Active NOAM Server
- Standby NOAM Server
- Active SOAM Server
- Standby SOAM Server
- Spare SOAM Server (if applicable)
- MP/IPFE Servers
- Verify that the replication on all the working servers is allowed. This can be done by examining the Repl Status table.
- Perform key exchange between the Active-NOAM and recovered servers:
- Establish an SSH session to the Active NOAM, log in as an admusr.
- Run the following command to perform a key exchange from the
active NOAM to each recovered
server:
$ keyexchange admusr@<Recovered Server Hostname>
Note:
Perform this step, If an export server is configured.
- Activate Optional Features:
- Establish an SSH session to the active NOAM, log in as
admusr.
Note:
- If you have PCA installed in the system being recovered, run the procedure "PCA Activation on Stand By NOAM server" on recovered Standby NOAM Server and procedure "PCA Activation on Active SOAM server" on recovered Active SOAM Server from [3] to re-activate PCA.
- The same procedure applies to all the application.
Refer to Optional Features to activate any features that were previously activated.
Note:
- While running the activation script, the following error
message (and corresponding messages) output may be seen, the error can
be ignored
iload#31000{S/W Fault}
. - If any of the MPs are failed and recovered, then these MP servers should be restarted after activation of the feature.
- Establish an SSH session to the active NOAM, log in as
admusr.
- Fetch and store the database report for the newly restored data and save
it:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active NOAM server and click Report.
- Click Save and save the report to the local machine.
- Verify replication between servers:
- Log in to the Active NOAM through SSH terminal as admusr user.
- Run the following
command:
$ sudo irepstat –m Output like below shall be generated: -- Policy 0 ActStb [DbReplication] --------------------- Oahu-DAMP-1 -- Active BC From Oahu-SOAM-2 Active 0 0.50 ^0.15%cpu 25B/s A=me CC To Oahu-DAMP-2 Active 0 0.10 0.14%cpu 25B/s A=me Oahu-DAMP-2 -- Stby BC From Oahu-SOAM-2 Active 0 0.50 ^0.11%cpu 31B/s A=C3642.212 CC From Oahu-DAMP-1 Active 0 0.10 ^0.14 1.16%cpu 31B/s A=C3642.212 Oahu-IPFE-1 -- Active BC From Oahu-SOAM-2 Active 0 0.50 ^0.03%cpu 24B/s A=C3642.212 Oahu-IPFE-2 -- Active BC From Oahu-SOAM-2 Active 0 0.50 ^0.03%cpu 28B/s A=C3642.212 Oahu-NOAM-1 -- Stby AA From Oahu-NOAM-2 Active 0 0.25 ^0.03%cpu 23B/s Oahu-NOAM-2 -- Active AA To Oahu-NOAM-1 Active 0 0.25 1%R 0.04%cpu 61B/s AB To Oahu-SOAM-2 Active 0 0.50 1%R 0.05%cpu 75B/s Oahu-SOAM-1 -- Stby BB From Oahu-SOAM-2 Active 0 0.50 ^0.03%cpu 27B/s Oahu-SOAM-2 -- Active AB From Oahu-NOAM-2 Active 0 0.50 ^0.03%cpu 24B/s BB To Oahu-SOAM-1 Active 0 0.50 1%R 0.04%cpu 32B/s BC To Oahu-IPFE-1 Active 0 0.50 1%R 0.04%cpu 21B/s irepstat ( 40 lines) (h)elp (m)erged
- Verify the database states:
- Navigate to Main Menu, Status & Manage, and then Database.
- Verify that the "OAM Max HA Role" is either Active or Standby for NOAM and SOAM and "Application Max HA Role" for MPs is Active, and that the status is Normal.
- Verify the HA Status:
- Navigate to Main Menu, and then Status & Manage, and then HA.
- Select the row for all of the servers, verify that the HA role is either Active or Standby.
- Verify the local Node Info:
- Navigate to Main Menu, Diameter, Configuration, and then Connections.
- Verify that all the connections are shown.
- Verify the Peer Node Info:
- Navigate to Main Menu, Diameter, Configuration, and then Peer Nodes.
- Verify that all the peer nodes are shown.
- Verify the Connections Info:
- Navigate to Main Menu, Diameter, Configuration, and then Connections.
- Verify that all the connections are shown.
- To verify the vSTP MP Local nodes info:
- Log in to the SOAM VIP Server console as admusr.
- Run the following command
[admusr@SOAM1 ~]$ mmiclient.py /vstp/localhosts
- Verify the output similar to the below output.
Figure 4-4 Output
- To verify the vSTP MP Remote nodes info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/remotehosts
- Verify the output similar to the below output:
Figure 4-5 Output
- To verify the vSTP MP Connections info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/connections
- Verify the output similar to the below output:
Figure 4-6 Output
- Disable SCTP Auth Flag:
- For SCTP connections without DTLS enabled, refer to Enable/Disable DTLS Appendix from reference [1].
- Run this procedure on all failed MP Servers.
- Enable Connections if needed:
- Navigate to Main Menu, Diameter, Maintenance, and then Connections.
- Select each connection and click Enable. Alternatively you can enable all the connections by selecting EnableAll.
- Verify that the "Operational State" is Available.
- Enable Optional Features:
- Navigate to Main Menu, Diameter, Maintenance, and then Applications.
- Select the optional feature application configured in step 29 and click Enable.
- If required, re-enable transport:
- Navigate to Main Menu, Transport Manager, Maintenance, and then Transport.
- Select each transport and click Enable.
- Verify that the Operational Status for each transport is Up.
- Re-enable MAPIWF application if needed:
- Navigate to Main Menu, Sigtran, Maintenance, and then Local SCCP Users.
- Click Enable corresponding to MAPIWF application Name.
- Verify that the SSN status is Enabled.
- Re-enable links if needed.
- Navigate to Main Menu, Sigtran, Maintenance, and then Links.
- Click Enable for each link.
- Verify that the Operational Status for each link is Up.
- Examine All Alarms:
- Navigate to Main Menu, Alarms & Events and View Active.
- Examine all active alarms and refer to the on-line help on how to address them. For any queries contact My Oracle Support (MOS).
- Backup and archive all the databases from the recovered system:
- Run DSR database backup to back up the Configuration databases.
4.1.3 Recovery Scenario 3 (Partial Server Outage with all NOAM servers failed and one SOAM server intact)
For a partial server outage with SOAM server intact and available, NOAM servers are recovered using recovery procedures for software and then running a database restore to the active NOAM server using a NOAM database backup file obtained from external backup sources such as customer servers. All other servers are recovered using recovery procedures for software. Database replication from the Active NOAM or Active SOAM server will recover the database on these servers. The major activities are summarized in the list below. Use this list to understand the recovery procedure summary. Do not use this list to run the procedure. The detailed steps are in Procedure 7. The major activities are summarized as follows:
Recover Active NOAM server by recovering software and the database.
- Recover the software.
- Recover the database
Recover Standby NOAM servers by recovering software.
- Recover the software.
Recover any failed SOAM and MP servers by recovering software.
- Recover the software.
- Database is already intact at one SOAM server and does not require restoration at the other SOAM and MP servers.
Note:
If this procedure fails, contact My Oracle Support (MOS), and ask for assistance.- Refer to workarounds for issues not fixed in this release to understand or apply any workarounds required during this procedure.
- Gather the documents and required materials listed in the Required Materials section.
- For VMware based deployments:
- For NOAMs run the following procedures:
- Procedure 1 (VMware). Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 2 (VMware Only). Configure NOAM guests based on resource profile.
- Procedure 1 (VMware). Import DSR OVA
- For SOAMs run the following procedures:
- Procedure 1 (VMWare). Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 3 (VMWare Only). Configure Remaining DSR guests based on resource profile
- Procedure 1 (VMWare). Import DSR OVA
- For failed MPs run the following procedures:
- Procedure 1 (VMWare). Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Procedure 3 (VMWare Only). Configure Remaining DSR guests based on resource profile.
- Procedure 1 (VMWare). Import DSR OVA.
- For NOAMs run the following procedures:
- Procedure 4 (KVM / Openstack) Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Procedure 5 (KVM / Openstack Only). Configure NOAM guests based on resource profile.
- Procedure 4 (KVM / Openstack) Import DSR OVA.
- For SOAMs run the following procedures:
- Procedure 4 (KVM / Openstack) Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 6 (KVM / Openstack Only). Configure Remaining DSR guests based on resource profile.
- Procedure 4 (KVM / Openstack) Import DSR OVA.
- For OVM-S / OVM-M based deployments run the following
procedures:
- Procedure 7 (OVM-S/OVM-M) Import DSR OVA and prepare for VM creation.
- Procedure 8 (OVM-S/OVM-M) Configure each DSR VM.
Note:
While running procedure 8, configure the required failed VMs only (NOAMs/SOAMs/MPs).
- For NOAMs run the following procedures:
- Obtain the most recent database backup file from external backup
sources (ex. file servers) or tape backup sources.
- From Required Materials list, use site survey documents and Network Element report (if available), to determine network configuration data.
- Run DSR installation procedure for the first NOAM:
- Verify the networking data for Network Elements.
Note:
Use the backup copy of network configuration data and site surveys (Step 2). - Run installation procedures for the first NOAM server:
- Procedure 13 Configure the First NOAM NE and Server.
- Procedure 14 Configure the NOAM Server Group.
- Verify the networking data for Network Elements.
- Log in to the NOAM GUI as the guiadmin user.
- Upload the backed up SOAM database file:
- Navigate to Main Menu, and then Status & Manage, and then Files.
- Select the Active SOAM server. Click Upload and select the file "SO Provisioning and Configuration" backed up after initial installation and provisioning.
- Click Browse and locate the backup file.
- Check This is a backup file box and click Open.
- Click Upload.
The file will take a few seconds to upload depending on the size of the backup data. The file will be visible on the list of entries after the upload is complete.
- To disable provisioning:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- click Disable Provisioning. A
confirmation window will appear, press OKto
disable.
Note:
The message "warning Code 002" will appear.
- Verify the archive contents and database compatibility:
- Select the Active NOAM server and click
Compare.
Click restored database file that was uploaded as a part of step 13 of this procedure.
- Verify that the output window matches the database.
Note:
- As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS).
- Archive content and database compatibilities must
consist the following:
- Archive Contents: Configuration data
- Database Compatibility: The databases are compatible.
- When restoring from an existing backup database to
a database using a single NOAM, the expected outcome for the
topology compatibility check is as follows:
- Topology compatibility: Topology must be compatible minus the NODEID.
- Attempting to restore a backed-up database onto a
NOAM database which is empty. In the context of Topology
Compatibility, this text is expected.
If the verification is successful, click Back and continue to next step of this procedure.
- Select the Active NOAM server and click
Compare.
- Restore the database:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active NOAM server and click
Restore. Select the appropriate backup
provisioning and configuration file and click OK.
Note:
As expected, the user will see a database mismatch with respect to the VM's NodeIDs. Proceed if this is the only differenc, if not, contact My Oracle Support (MOS). - Select the Force checkbox and click
OK to proceed with the database restore.
Note:
After the restore has started, the user will be logged out of XMI NO GUI since the restored Topology is old data.
- Establish a GUI session on the NOAM server by using the VIP IP address
of the NOAM server. Open the web browser and enter the following URL
http://<Primary_NOAM_VIP_IP_Address>
. Login as the guiadmin user. - Monitor and Confirm database restoral. Wait for 5 to10 minutes for the
System to stabilize with the new topolog.
Monitor the Info tab for Success. This will indicate that the backup is complete and the system is stabilized.
Following alarms must be ignored for NOAM and MP Servers until all the Servers are configured:
- Alarms with Type Column as “REPL” , “COLL”, “HA” (with mate
NOAM), “DB” (about Provisioning Manually Disabled).
Note:
- Do not pay attention to alarms until all the servers in the system are completely restored.
- The maintenance and configuration data will be in the same state as when it was first backed up.
- Alarms with Type Column as “REPL” , “COLL”, “HA” (with mate
NOAM), “DB” (about Provisioning Manually Disabled).
- Log in to the recovered Active NOAM through SSH terminal as admusr user.
- Re-enable provisioning:
- Navigate to Main Menu, Status & Manage, and then Database.
- Click Enable Provisioning a pop-up window will appear to confirm and click OK.
- Install the second NOAM server by running the following procedure:
- Procedure 15, 1 and 3 to 7 Configure the Second NOAM Server.
- Navigate to Main Menu, Status &
Manage, and then Server.
- Click Restart and click Ok on the confirmation screen.
Note:
If topology or nodeId alarms are persistent after the database restore, refer to workarounds for Issues not fixed in this release or the next step. - Recover the remaining SOAM servers (standby, spare) by repeating the following steps
for each SOAM server:
- Install the remaining SOAM servers by running procedure 22 step 1 and 3 to 7
Configure the SOAM Servers.
Note:
Before continuing, wait for server to reboot.
- Install the remaining SOAM servers by running procedure 22 step 1 and 3 to 7
Configure the SOAM Servers.
- Restart DSR application:
- Navigate to Main Menu, Status & Manage, and then Server.
- Select the recovered server and click Restart.
- Navigate to Main Menu, Status &
Manage, and then HA.
- Click Edit, for each server whose Max Allowed HA role is not Active, set it to Active and click OK.
- Restart DSR application:
- Navigate to Main Menu, Status & Manage, and then Server.
- Select each recovered server and click Restart.
- Activate Optional Features:
- Establish an SSH session to the active NOAM, log in as
admusr.
Note:
- If you have PCA installed in the system being recovered, run the procedure "PCA Activation on Stand By NOAM server" on recovered Standby NOAM Server and procedure "PCA Activation on Active SOAM server" on recovered Active SOAM Server from [3] to re-activate PCA.
- The same procedure applies to all the application
Refer to Optional Features to activate any features that were previously activated.
Note:
- While running the activation script, the following error
message (and corresponding messages) output may be seen, the error can
be ignored
iload#31000{S/W Fault}
. - If any of the MPs are failed and recovered, then these MP servers should be restarted after activation of the feature.
- Establish an SSH session to the active NOAM, log in as
admusr.
- Fetch and store the database report for the newly restored data and save
it:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Select the Active NOAM server and click Report.
- Click Save and save the report to the local machine.
- Verify replication between servers:
- Log in to the Active NOAM through SSH terminal as admusr user.
- Run the following
command:
$ sudo irepstat –m Output like below shall be generated: -- Policy 0 ActStb [DbReplication] ----------------------------------- ---------------------------------------------------------------------- -------------------------------------- RDU06-MP1 -- Stby BC From RDU06-SO1 Active 0 0.50 ^0.17%cpu 42B/s A=none CC From RDU06-MP2 Active 0 0.10 ^0.17 0.88%cpu 32B/s A=none RDU06-MP2 -- Active BC From RDU06-SO1 Active 0 0.50 ^0.10%cpu 33B/s A=none CC To RDU06-MP1 Active 0 0.10 0.08%cpu 20B/s A=none RDU06-NO1 -- Active AB To RDU06-SO1 Active 0 0.50 1%R 0.03%cpu 21B/s RDU06-SO1 -- Active AB From RDU06-NO1 Active 0 0.50 ^0.04%cpu 24B/s BC To RDU06-MP1 Active 0 0.50 1%R 0.04%cpu 21B/s BC To RDU06-MP2 Active 0 0.50 1%R 0.07%cpu 21B/s
- Verify the database states:
- Navigate to Main Menu, and then Status & Manage, and then Database.
- Verify that the "OAM Max HA Role" is either Active or Standby for NOAM and SOAM and "Application Max HA Role" for MPs is Active, and that the status is Normal.
- Verify the HA Status:
- Navigate to Main Menu, and then Status & Manage, and then HA.
- Select the row for all of the servers, verify that the HA role is either Active or Standby.
- Verify the local Node Info:
- Navigate to Main Menu, Diameter, Configuration, and then Local Node.
- Verify that all the local nodes are shown.
- Verify the Peer Node Info:
- Navigate to Main Menu, Diameter, Configuration, and then Peer Node.
- Verify that all the peer nodes are shown.
- Verify the Connections Info:
- Navigate to Main Menu, Diameter, Configuration, and then Connections.
- Verify that all the connections are shown.
- To verify the vSTP MP Local nodes info:
- Log in to the SOAM VIP Server console as admusr.
- Run the following command
[admusr@SOAM1 ~]$ mmiclient.py /vstp/localhosts
- Verify the output similar to the below output.
Figure 4-7 Output
- To verify the vSTP MP Remote nodes info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/remotehosts
- Verify the output similar to the below output:
Figure 4-8 Output
- To verify the vSTP MP Connections info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/connections
- Verify the output similar to the below output:
Figure 4-9 Output
- Enable Connections if needed:
- Navigate to Main Menu, Diameter, Maintenance, and then Connections.
- Select each connection and click Enable. Alternatively you can enable all the connections by selecting EnableAll.
- Verify that the "Operational State" is Available.
- Enable Optional Features:
- Navigate to Main Menu, Diameter, Maintenance, and then Applications.
- Select the optional feature application configured before and click Enable.
- If required, re-enable transport:
- Navigate to Main Menu, Transport Manager, Maintenance, and then Transport.
- Select each transport and click Enable.
- Verify that the Operational Status for each transport is Up.
- Re-enable MAPIWF application if needed:
- Navigate to Main Menu, Sigtran, Maintenance, and then Local SCCP Users.
- Click Enable corresponding to MAPIWF application Name.
- Verify that the SSN status is Enabled.
- Re-enable links if needed.
- Navigate to Main Menu, Sigtran, Maintenance, and then Links.
- Click Enable for each link.
- Verify that the Operational Status for each link is Up.
- Examine All Alarms:
- Navigate to Main Menu, Alarms & Events and View Active.
- Examine all active alarms and refer to the on-line help on how to address them. For any queries contact My Oracle Support (MOS).
- Perform key exchange with Export Server:
- Navigate to Main Menu, Administration, Remote Servers and then Data Export.
- Click Key Exchange, enter the password and click OK.
- Examine All Alarms:
- Navigate to Main Menu, Alarms & Events and View Active.
- Examine all active alarms and refer to the on-line help on how to address them. For any queries contact My Oracle Support (MOS).
- Restore GUI Usernames and Passwords:
- If applicable, run steps in Section 6.0 to recover the user and group information restored.
- Backup and archive all the databases from the recovered system:
- Run DSR database backup to back up the Configuration databases.
4.1.4 Recovery Scenario 4 (Partial Server Outage with one NOAM server and one SOAM server intact)
For a partial outage with an NOAM server and an SOAM server intact and available, only base recovery of software is needed. The intact NOAM and SOAM servers are capable of restoring the database via replication to all servers. The major activities are summarized in the list below. Use this list to understand the recovery procedure summary. Do not use this list to execute the procedure. The actual detailed steps are in procedure 4. The major activities are summarized as follows:
Recover Standby NOAM server by recovering software.
The database is intact at the active NOAM server and does not require restoration at the standby NOAM server.
- Recover any failed SO and MP servers by recovering software.
- Recover the software.
The database in intact at the active NOAM server and does not require restoration at the SOAM and MP servers.
- Re-apply signaling networks configuration if the failed VM is an MP.
Note:
If this procedure fails, contact My Oracle Support (MOS).- Refer to workarounds for issues not fixed in this release to understand or apply any workarounds required during this procedure.
- Gather the documents and required materials listed in the Required Materials section.
- Establish a GUI session on the NOAM server by using the VIP IP address of the
NOAM server. Open the web browser and enter the following url
http://<Primary_NOAM_VIP_IP_Address>
. Log in as the guiadmin user. - Navigate to Main Menu, Status &
Manage, and then HA.
- Click Edit and set "Max Allowed HA Role" to OOS and click OK.
- For VMware based deployments:
- For NOAMs run the following procedures:
- Procedure 1 (VMware). Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 2 (VMware Only). Configure NOAM guests based on resource profile.
- Procedure 1 (VMware). Import DSR OVA
- For SOAMs run the following procedures:
- Procedure 1 (VMWare). Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 3 (VMWare Only). Configure Remaining DSR guests based on resource profile
- Procedure 1 (VMWare). Import DSR OVA
- For failed MPs run the following procedures:
- Procedure 1 (VMWare). Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Procedure 3 (VMWare Only). Configure Remaining DSR guests based on resource profile.
- Procedure 1 (VMWare). Import DSR OVA.
- For NOAMs run the following procedures:
- Procedure 4 (KVM / Openstack) Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Procedure 5 (KVM / Openstack Only). Configure NOAM guests based on resource profile.
- Procedure 4 (KVM / Openstack) Import DSR OVA.
- For SOAMs run the following procedures:
- Procedure 4 (KVM / Openstack) Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 6 (KVM / Openstack Only). Configure Remaining DSR guests based on resource profile.
- Procedure 4 (KVM / Openstack) Import DSR OVA.
- For OVM-S / OVM-M based deployments run the following
procedures:
- Procedure 7 (OVM-S/OVM-M) Import DSR OVA and prepare for VM creation.
- Procedure 8 (OVM-S/OVM-M) Configure each DSR
VM.
Note:
While running procedure 8, configure the required failed VMs only (NOAMs/SOAMs/MPs).
- For NOAMs run the following procedures:
- If required, repeat step 5 for all remaining failed servers.
- Establish a GUI session on the NOAM server by using the VIP IP address of the
NOAM server. Open the web browser and enter the following url
http://<Primary_NOAM_VIP_IP_Address>
. Login as the guiadmin user: - Install the second NOAM server by running the following procedures:
- Procedure 15 Configure the Second NOAM Server, steps 1, 3 to 7.
- Procedure 16 complete Configuring the NOAM Server Group, step 4
Note:
If topology or nodeId alarms are persistent after the database restore, refer to workarounds for issues not fixed in this release or the next step.
- If the failed server is an SOAM, recover the remaining SOAM servers (standby,
spare) by repeating the following steps for each SOAM server:
- Install the remaining SOAM servers by running procedure 22 Configure the
SOAM Servers, step 1 and 3 to 7.
Note:
Before continuing to next step, wait for the server to reboot.
- Install the remaining SOAM servers by running procedure 22 Configure the
SOAM Servers, step 1 and 3 to 7.
- Navigate to Main Menu, Status &
Manage, and then HA.
- Click Edit for each server whose "Max Allowed HA Role" is set to Standby, set it to Active and click OK.
- Navigate to Main Menu, Status & Manage, and then Server. Select the recovered server and click Restart.
- Establish a SSH session to the C Level server being recovered, log in as admusr.
- Run the following procedure for each server that has been recovered.
- Procedure 25 Configure the MP Virtual Machines, Step 1 and 8 to 14 ( step 15 if required).
- Run the following procedure for each server that has been recovered.
- Navigate to Main Menu, Status &
Manage, and then HA.
- Click Edit for each server whose "Max Allowed HA Role" is set to Standby, set it to Active and click OK.
- Navigate to Main Menu, Status & Manage, and then Server. Select the recovered servers and click Restart.
- Login to the recovered Active NOAM through SSH terminal as admusr user.
- Perform key exchange between the Active NOAM and recovered servers:
- Establish an SSH session to the Active NOAM, log in as admusr.
- Run the following command to perform a keyexchange from the active NOAM
to each recovered
server:
$ keyexchange admusr@<Recovered Server Hostname>
- Activate Optional Features:
- Establish an SSH session to the active NOAM, log in as admusr.
Note:
If you have PCA installed in the system being recovered, run the procedure "PCA Activation on Stand By NOAM server" on recovered standBy NOAM Server and procedure "PCA Activation on Stand By SOAM server" on recovered StandBy SOAM Server from [3] to re-activate PCA. - Refer to Optional Features to activate any features that were previously activated.
Note:
- While running the activation script, the following error
message (and corresponding messages) output may be seen,
which can be ignored
iload#31000{S/W Fault}
. - If any of the MPs are failed and recovered, then these MP servers should be restarted after Activation of the feature.
- While running the activation script, the following error
message (and corresponding messages) output may be seen,
which can be ignored
- Establish an SSH session to the active NOAM, log in as admusr.
- Navigate to Main Menu, Status &
Manage, and then Database.
- Select the Active NOAM server and click Report.
- Click Save to save the report to the local machine.
- Log in to the Active NOAM through SSH terminal as admusr user. Run the following
command:
$ sudo irepstat –m Output like below shall be generated: -- Policy 0 ActStb [DbReplication] ----------------------------------- ---------------------------------------------------------------------- -------------------------------------- RDU06-MP1 -- Stby BC From RDU06-SO1 Active 0 0.50 ^0.17%cpu 42B/s A=none CC From RDU06-MP2 Active 0 0.10 ^0.17 0.88%cpu 32B/s A=none RDU06-MP2 -- Active BC From RDU06-SO1 Active 0 0.50 ^0.10%cpu 33B/s A=none CC To RDU06-MP1 Active 0 0.10 0.08%cpu 20B/s A=none RDU06-NO1 -- Active AB To RDU06-SO1 Active 0 0.50 1%R 0.03%cpu 21B/s RDU06-SO1 -- Active AB From RDU06-NO1 Active 0 0.50 ^0.04%cpu 24B/s BC To RDU06-MP1 Active 0 0.50 1%R 0.04%cpu 21B/s BC To RDU06-MP2 Active 0 0.50 1%R 0.07%cpu 21B/s
- Navigate to Main Menu, Status &
Manage, and then Database.
- Verify that the "OAM Max HA Role" is either "Active" or "Standby" for NOAM and SOAM and "Application Max HA Role" for MPs is Active, and the status is Normal.
- Navigate to Main Menu, Status &
Manage, and then HA.
- Select the row for all of the servers. Verify that the HA Role is either Active or Standby.
- Navigate to Main Menu, Diameter, Configuration and then Local Node. Verify that all the peer nodes are shown.
- Navigate to Main Menu, Diameter, Configuration and then Connections. Verify that all the connections are shown.
- To verify the vSTP MP Local nodes info:
- Log in to the SOAM VIP Server console as admusr.
- Run the following command
[admusr@SOAM1 ~]$ mmiclient.py /vstp/localhosts
- Verify the output similar to the below output.
Figure 4-10 Output
- To verify the vSTP MP Remote nodes info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/remotehosts
- Verify the output similar to the below output:
Figure 4-11 Output
- To verify the vSTP MP Connections info:
- Log in to the SOAM VIP server console as admusr.
- Run the following
command:
[admusr@SOAM1 ~]$ mmiclient.py /vstp/connections
- Verify the output similar to the below output:
Figure 4-12 Output
- Disable SCTP Auth Flag:
- For SCTP connections without DTLS enabled, refer to Enable/Disable DTLS Appendix from reference [1].
- Run this procedure on all failed MP servers.
- Navigate to Main Menu, Diameter,
and then Connections.
- Select each connection and click Enable.
- Alternatively enable all the connections by selecting EnableAll.
- Verify that the Operational State is Available.
- Navigate to Main Menu, Diameter,
Maintenance and then
Applications.
- Select the optional feature application and click Enable.
- Navigate to Main Menu, Transport
Manager, Maintenance and then
Transport.
- Select each transport and click Enable.
- Verify that the Operational Status for each transport is Up.
- Navigate to Main Menu, Sigtran,
Maintenance and then Local SCCP
Users.
- Click Enable corresponding to MAPIWF Application Name.
- Verify that the SSN Status is Enabled.
- Navigate to Main Menu, Sigtran,
Maintenance and then Links.
- Click Enable for each link.
- Verify that the Operational Status for each link is Up.
- Examine All Alarms:
- Navigate to Main Menu, Alarms &
Events, and then View Active.
- Examine all active alarms and refer to the on-line help on how to address them.
- If required contact My Oracle Support (MOS).
- Navigate to Main Menu, Alarms &
Events, and then View Active.
- If required, restart
oampAgent
.Note:
If alarm 10012 the responder for a monitored table failed to respond to a table change is raised, theoampAgent
needs to be restarted.- Establish an SSH session to each server that has the alarm. Log in as admusr.
- Run the following
commands:
$ sudo pm.set off oampAgent $ sudo pm.set on oampAgent
- Run DSR database backup to backup the configuration databases.
4.1.5 Recovery Scenario 5 (Partial server outage with both NOAM servers failed with DR-NOAM Available)
For a partial outage with both NOAM servers failed but a DR NOAM available, the DR NOAM is switched from secondary to primary then recovers the failed NOAM servers. The major activities are summarized in the list below. Use this list to understand the recovery procedure summary. Do not use this list to run the procedure. The actual detailed steps are in procedure 5. The major activities are summarized as follows:
Switch DR NOAM from secondary to primary
Recover the failed NOAM servers by recovering base hardware and software.
- Recover the base hardware.
- Recover the software.
- The database is intact at the newly active NOAM server and does not require restoration.
If applicable, recover any failed SOAM and MP servers by recovering base hardware and software.
- Recover the base hardware.
- Recover the software.
- The database in intact at the active NOAM server and does not require restoration at the SOAM and MP servers.
Note:
If this procedure fails, contact My Oracle Support (MOS).- Refer to workarounds for issues not fixed in this release to understand or apply any workarounds required during this procedure.
- Gather the documents and required materials listed in the Required Materials section.
- Refer Diameter Signaling Router SDS NOAM Failover User Guide.
- For VMWare based deployments:
- For NOAMs run the following procedures:
- Procedure 1 (VMware). Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 2 (VMware Only). Configure NOAM guests based on resource profile.
- Procedure 1 (VMware). Import DSR OVA
- For SOAMs run the following procedures:
- Procedure 1 (VMWare). Import DSR OVA
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 3 (VMWare Only). Configure Remaining DSR guests based on resource profile
- Procedure 1 (VMWare). Import DSR OVA
- For failed MPs run the following procedures:
- procedure 1 (VMWare). Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Procedure 3 (VMWare Only). Configure Remaining DSR guests based on resource profile.
For KVM or Openstack based deployments:
- procedure 1 (VMWare). Import DSR OVA.
- For NOAMs run the following procedures:
- Procedure 4 (KVM / Openstack) Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA - Procedure 5 (KVM / Openstack Only). Configure NOAM guests based on resource profile.
- Procedure 4 (KVM / Openstack) Import DSR OVA.
- For SOAMs run the following procedures:
- Procedure 4 (KVM / Openstack) Import DSR OVA.
Note:
If OVA is already imported and present in the Infrastructure Manager, skip this procedure of importing OVA. - Procedure 6 (KVM / Openstack Only). Configure Remaining DSR guests based on resource profile.
- Procedure 4 (KVM / Openstack) Import DSR OVA.
- For OVM-S / OVM-M based deployments run the following
procedures:
- Procedure 7 (OVM-S/OVM-M) Import DSR OVA and prepare for VM creation.
- Procedure 8 (OVM-S/OVM-M) Configure each DSR
VM.
Note:
While running procedure 8, configure the required failed VMs only (NOAMs/SOAMs/MPs).
- For NOAMs run the following procedures:
- If all SOAM servers have failed, run Procedure 2.
- Establish a GUI session on the DR-NOAM server by using the VIP IP address of the
DR-NOAM server. Open the web browser and enter the following url
http://<Primary_DR-NOAM_VIP_IP_Address>
. Log in as the guiadmin user. - Navigate to Main Menu, and then
Status & Manage, and then
HA.
- Click Edit, select the standby for the failed NOAM servers and click OK.
- Navigate to Main Menu,
Configuration, and then
Servers.
From the GUI screen, select the failed NOAM server and then select Export to generate the initial configuration data for that server
- Obtain a terminal session to the DR-NOAM VIP, log in as the admusr user. Run the
following command to configure the failed NOAM
server:
$ sudo scp -r /var/TKLC/db/filemgmt/TKLCConfigData.<Failed_NOAM_Hostnam e>.sh admusr@<Failed_NOAM_xmi_IP_address>:/var/tmp/TKLCConfigDa ta.sh
- Establish an SSH session to the recovered NOAM server
(Recovered_NOAM_xmi_IP_address).
- Login as the admusr user.
The automatic configuration daemon will look for the file named "TKLCConfigData.sh" in the
/var/tmp
directory, implement the configuration in the file, and then prompt the user to reboot the server. - Verify
awpushcfg
called by checking the following file$ sudo cat /var/TKLC/appw/logs/Process/install.log Verify the following message is displayed: [SUCCESS] script completed successfully!
- Following is the command to reboot the
server:
$ sudo init 6
Wait for the server to reboot.
- Login as the admusr user.
- Run the following command on the failed NOAM server and ensure that no errors
are
returned:
$ sudo syscheck Running modules in class hardware...OK Running modules in class disk...OK Running modules in class net...OK Running modules in class system...OK Running modules in class proc...OK LOG LOCATION: /var/TKLC/log/syscheck/fail_log
- Repeat steps 8 to 11 for the 2nd failed NOAM server.
- Perform a keyexchange between the newly active NOAM and the recovered NOAM
servers:
From a terminal window connection on the active NOAM as the admusr user, exchange SSH keys for admusr between the active NOAM and the recovered NOAM servers using the keyexchange utility, using the host names of the recovered NOAMs.
When prompted for the password, enter the password for the admusr user of the recovered NOAM servers.
$ keyexchange admusr@<Recovered_NOAM Hostname>
- Navigate to Main Menu,
Configuration, and then HA
- Click Edit, for each NOAM server whose Max Allowed HA Role is set to Standby, set it to Active and click OK.
- Navigate to Main Menu, and then Status &
Manage, and then Server.
Select each recovered NOAM server and click Restart.
- Activate the features Map-Diameter Interworking (MAP-IWF) and Policy and
Charging Application (PCA) as follows:
- For PCA: Establish SSH sessions to all the recovered NOAM servers and
log in as admusr. Refer and run procedure "PCA Activation on Standby
NOAM" server on all recovered NOAM Servers to re-activate
PCA.
Establish SSH session to the recovered active NOAM, login as admusr. For MAP-IWF:
- Establish SSH session to the recovered active NOAM, login as
admusr. Refer activate Map-Diameter Interworking (MAP-IWF).
Note:
- While running the activation script, the following
error message (and corresponding messages) output
may be seen which can be ignored
iload#31000{S/W Fault}
. - If any of the MPs are failed and recovered, then these MP servers should be restarted after activation of the feature.
- While running the activation script, the following
error message (and corresponding messages) output
may be seen which can be ignored
- Establish SSH session to the recovered active NOAM, login as
admusr. Refer activate Map-Diameter Interworking (MAP-IWF).
- For PCA: Establish SSH sessions to all the recovered NOAM servers and
log in as admusr. Refer and run procedure "PCA Activation on Standby
NOAM" server on all recovered NOAM Servers to re-activate
PCA.
- Switch DR NOAM back to secondary: After the system has been recovered. Refer to Diameter Signaling router SDS NOAM Failover Users Guide.
- Navigate to Main Menu,
Administration, Remote Servers
and then Data Export.
- Click Key Exchange. Enter the Password and click OK.
- Navigate to Main Menu, Alarms & Events, and then View Active.
- Verify the recovered servers that are not contributing to any active alarms (Replication, Topology misconfiguration, database impairments, NTP, etc).
- If required, refer to procedure 3 to recover any standby or spare SOAMs as well as any C-level servers.
4.1.6 Recovery Scenario 6 (Database Recovery)
Case 1
For a partial outage with Cloud Disaster Recovery guide:
- Server having a corrupted database.
- Replication channel from parent is inhibited because of upgrade activity.
- Due to upgrade activities, the server is in a different release than its active parent.
- Verify that the Server runtime backup files performed at the start of
the upgrade are present in
/var/TKLC/db/filemgmt
area in the following format:- Backup.DSR.HPC02-NO2.FullDBParts.NETWORK_OAMP.20140524_223507.UPG.tar.bz2
- Backup.DSR.HPC02-NO2.FullRunEnv.NETWORK_OAMP.20140524_223507.UPG.tar.bz2
Note:
During recovery, the corrupted database will get replaced by the sever runtime backup. Any configuration done after taking the backup will not be visible post recovery.Perform the following procedure for recovery if database is corrupted in the system:
Note:
If this procedure fails, contact My Oracle Support (MOS), and ask for assistance.- Refer to workarounds for issues not fixed in this release to understand or apply any workarounds required during this procedure.
- Navigate to Main Menu, and then Status & Manage, and then HA.
- Select Edit and from the dropdown menu, set the "Max Allowed HA" role to OOS for the failed servers and Select OK.
- Establish an SSH session to the server in question. Log in as an admusr user.
- Run the following command to bring the system to runlevel
3:
$ sudo init 3
- Run the following command and follow the instructions appearing in the console
prompt:
$ sudo /usr/TKLC/appworks/sbin/backout_restore
- Run the following command to bring the system back to runlevel
4:
$ sudo init 6
- Run the following command to verify if the processes are up and
running:
$ sudo pm.getprocs
- Navigate to Main Menu, and then Status & Manage, and then HA.
- Click Edit, for each failed server whose Max Allowed HA Role is set to OOS, set it to Active and click OK.
- Run DSR database backup to back up the Configuration databases.
Case 2
For a partial outage with:
- Server having a corrupted database.
- Replication channel is not inhibited.
- Server has the same release as that of its Active parent.
Perform the following procedure if database got corrupted in the system and system is in the state to get replicated:
Note:
If this procedure fails, contact My Oracle Support (MOS).- Refer to any workarounds required during this procedure.
- Navigate to Main Menu, and then Status & Manage, and then HA.
- Click Edit and from the dropdown menu, set the "Max Allowed HA" role to OOS for the failed servers and select OK.
- Establish an SSH session to the server in question. Log in as admusr user.
- Run the following command to take the server out of
service.
$ sudo bash –l $ sudo prod.clobber
- Run the following commands to take the server to
Dbup
and start the DSR application:$ sudo bash –l $ sudo prod.start
- Run the following command to verify if replication channels are up and
running:
$ sudo irepstat
- Run the following command to verify if merging channels are up and
running:
$ sudo inetmstat
- Run the following command to verify if replication channels are up and
running:
- Navigate to Main Menu, and then Status & Manage, and then Server. Select each recovered server and click Restart.
- Navigate to Main Menu, and then Status &
Manage, and then HA.
- Click Edit and from the dropdown menu, set the "Max Allowed HA" role to OOS for the failed servers and select OK.
- Run DSR database backup to back up the Configuration databases.