Space Requirements
Ensure that your site meets the space requirements for each Oracle Compute Cloud@Customer rack.
Use the information in this section along with the Space Checklist to prepare your site.
Dimensions and Weight Specifications
Specification | Metric | Standard |
---|---|---|
Height |
2000 mm |
78.74 " |
Width |
600 mm |
23.62 " |
Depth (front door handle to rear door handle) |
1197 mm |
47.12 " |
Depth (doors removed) |
1112 mm |
43.78 " |
Weight (base rack, fully populated) |
1000 kg |
2204 lbs |
Space Requirements
Minimum Ceiling Height
The minimum ceiling height for the cabinet is 2914 mm (114.72 inches), measured from the true floor or raised floor, whichever is higher. This includes an additional 914 mm (36 inches) of space required above the rack height for maintenance access.
Surrounding Space
The space surrounding the cabinet must not restrict the movement of cool air between the air conditioner and the front of the systems within the cabinet, or the movement of hot air coming out of the rear of the cabinet.
Receiving Specifications
Before the Compute Cloud@Customer rack arrives, ensure that the receiving area is large enough for the package. The following are the package dimensions and weights for a rack:
-
Shipping height: 2159 mm (85 inches)
-
Shipping width: 1118 mm (44 inches)
-
Shipping depth: 1543 mm (60.75 inches)
-
Shipping weight (base rack, fully populated): 1118 kg (2465 lbs)
If your loading dock meets the height and ramp requirements for a standard freight carrier truck, then you can use a pallet jack to unload the rack. If the loading dock does not meet the requirements, then you must provide a standard forklift or other means to unload the rack. You can also request that the rack be shipped in a truck with a lift gate.
When the rack arrives, leave the rack in its shipping packaging until it arrives at its installation site. Use a conditioned space to remove the packaging material to reduce particles before entering the data center. The entire access route to the installation site should be free of raised-pattern flooring that can cause vibration.
Allow enough space for unpacking the system from its shipping cartons. Ensure that there is enough clearance and clear pathways for moving the rack from the unpacking location to the installation location. The following table lists the access route requirements for the rack.
Access Route Item |
With Shipping Pallet |
Without Shipping Pallet |
---|---|---|
Minimum door height |
2159 mm (85 inches) |
2000 mm (78.74 inches) |
Minimum door width |
1118 mm (44 inches) |
600 mm (23.62 inches) |
Minimum elevator depth |
1543 mm (60.75 inches) |
1058.2 mm (41.66 inches) |
Maximum incline |
6 degrees |
6 degrees |
Maximum elevator, pallet jack, and floor loading capacity |
1145 kg (2520 lbs) |
1145 kg (2520 lbs) |
Maintenance Access Requirements
The maintenance area must be large enough for the rack, and have the required access space. For example, the required space to remove the side panels is 675.64 mm (26.6 inches).
The following table lists the maintenance access requirements for theOracle Compute Cloud@Customer rack.
Location |
Maintenance Access Requirement |
---|---|
Rear maintenance |
914 mm (36 inches) |
Front maintenance |
1232 mm (48.5 inches) |
Top maintenance |
914 mm (36 inches) |