24.4 Single Phase Power Distribution Unit Cabling
This topic shows the cabling routes from each single-phase power distribution unit (PDU) to the power supplies configured in each Oracle Exadata Storage Expansion Rack X9M-2.
The cables are terminated to PDU-A on the left (when looking at the rear of the rack), and routed to the right to enter the cable management arm (CMA). The cables are bundled in groups of four. The PDU connections list the group and outlet on the PDU. So, for example, G5-5 refers to group 5 outlet 5.
The following table shows the cable connections from the PDUs to the rack units in Oracle Exadata Storage Expansion Rack X9M-2.
Table 24-3 Single Phase PDU Cabling for Oracle Exadata Storage Expansion Rack X9M-2
| Rack Slot | PDU-A / PSU 0 | PDU-B / PSU 1 | Cable Length |
| U42 | G5-6 | G0-0 | 3 meters |
| U41 | G4-6 | G1-0 | 3 meters |
| U40 | G4-2 | G1-4 | 3 meters |
| U39 | G4-4 | G1-2 | 3 meters |
| U37 | G1-5 | G4-1 | 3 meters |
| U35 | G3-1 | G2-5 | 3 meters |
| U33 | G1-3 | G4-3 | 3 meters |
| U31 | G3-3 | G2-3 | 3 meters |
| U29 | G4-0 | G1-6 | 3 meters |
| U27 | G5-2 | G0-4 | 3 meters |
| U26 | G0-6 | G5-0 | 3 meters |
| U25 | G3-0 | G2-6 | 3 meters |
| U24 | G4-1 | G1-5 | 3 meters |
| U23 | G5-0 | G0-6 | 3 meters |
| U22 | G1-6 | G4-0 | 3 meters |
| U21 | G0-4 | G5-2 | 3 meters |
| U20 | G0-3 | G5-3 | 3 meters |
| U19 | G3-2 | G2-4 | 3 meters |
| U18 | G2-5 | G3-1 | 3 meters |
| U17 | G1-2 | G4-4 | 3 meters |
| U16 | G1-4 | G4-2 | 3 meters |
| U14 | G5-3 | G0-3 | 3 meters |
| U12 | G5-4 | G0-2 | 3 meters |
| U10 | G2-3 | G3-3 | 3 meters |
| U08 | G2-4 | G3-2 | 3 meters |
| U06 | G2-6 | G3-0 | 3 meters |
| U04 | G0-2 | G5-4 | 3 meters |
| U02 | G0-5 | G5-1 | 3 meters |
| U01 | G4-3 | G1-3 | 3 meters |