Realm configuration is divided into the following functional areas, and the steps for configuring each are set out in this chapter: identity and IP address prefix, realm interfaces, realm service profiles, QoS measurement, QoS marking, address translation profiles, and DNS server configuration.

Before You Configure

Before you configure realms, you want to establish the phy and network interfaces with which the realm will be associated.

  • Configure a phy-interface to define the physical characteristics of the signaling line.
  • Configure a network-interface to define the network in which this realm is participating and optionally to create VLANs.

If you wish to use QoS, you should also determine if your Oracle Enterprise Session Border Controller is QoS enabled.

Remember that you will also use this realm in other configurations to accomplish the following:

  • Set a signaling port or ports at which the Oracle Enterprise Session Border Controller listens for signaling messages.
  • Configure sessions agents to point to ingress and egress signaling devices located in this realm in order to apply constraint for admission control.
  • Configure session agents for defining trusted sources for accepting signaling messages.

Configure realm-config

To access the realm configuration parameters in the ACLI:

  1. Access the realm-config configuration element.
    ORACLE# configure terminal
    ORACLE(configure)# media-manager
    ORACLE(media-manager)# realm-config
    ORACLE(realm-config)# 
  2. Press Enter.
    The system prompt changes to let you know that you can begin configuring individual parameters. To view all realm configuration parameters, enter a ? at the system prompt.

Identity and IP Address Prefix

The first parameters you configure for a realm are its name (a unique identifier) and an IP address prefix and subnet mask.

The IP address and subnet mask establish a set of matching criteria for the realm, and distinguishes between realms that you assign to the same network interface.

To configure a realm’s identity and IP address prefix in the ACLI:

  1. identifier—Enter the name of the realm. This parameter uniquely identifies the realm. You will use this parameter in other configurations when asked for a realm identifier value.
  2. addr-prefix—Enter the IPv4 or IPv6 address and subnet mask combination to set the criteria the Oracle Enterprise Session Border Controller uses to match packets sent or received on the network interface associated with this realm. This matching determines the realm, and subsequently what resources are used for that traffic. This setting determines whether the realm is an IPv4 or IPv6 realm.

    This parameter must be entered in the correct format where the IPv4 or IPv6 address comes first and is separated by a slash (/) from the subnet mask value. For example, 172.16.0.0/24.

    The default for this parameter is 0.0.0.0. When you leave this parameter set to the default, all addresses match.

Realm Interfaces

The realm points to one network interface on the Oracle Enterprise Session Border Controller.

Note:

Only one network-interface can be assigned to a single realm-config object, except for Local multi-homing SCTP deployments.

To assign interfaces to a realm:

  1. network-interfaces—Enter the physical and network interface(s) that you want this realm to reference. These are the network interfaces though which this realm can be reached by ingress traffic, and through which this traffic exits the system as egress traffic.

    Enter the name and port in the correct format where the name of the interface comes first and is separated by a colon (:) from the port number. For example, f10:0.

    The parameters you set for the network interfaces must be unique.

    Enter multiple network interfaces for this list by typing an open parenthesis, entering each field value separated by a Space, typing a closed parenthesis, and then pressing Enter.

    ORACLE(realm-config)# network-interfaces fe1:0

    You must explicitly configure a realm's network interface as either IPv4 or IPv6 when the applicable interface is either dual-stack or IPv6. You do this by appending the realm's network-interface with a .4 or a .6, as shown below.

    ORACLE(realm-config)# network-interfaces fe1:0.6

    For single-stack interface configurations that do not specify this format, the Oracle Enterprise Session Border Controller assumes an IPv4 interface. Dual stack interface configurations fail if this IP version family suffix is not specified.

Realm Service Profile

The parameters you configure to establish the realm service profile determine how bandwidth resources are used and how media is treated in relation to the realm. Bandwidth constraints set for realm service profiles support the Oracle Enterprise Session Border Controller (Enterprise SBC) admission control feature.

Peer-to-peer media between endpoints can be treated in one of three different ways:

  • Media can be directed between sources and destinations within this realm on this specific Enterprise SBC. Media travels through the Enterprise SBC rather than straight between the endpoints.
  • Media can be directed through the Enterprise SBC between endpoints that are in different realms, but share the same subnet.
  • For SIP only, media can be released between multiple Enterprise SBCs.

    To enable SIP distributed media release, you must set the appropriate parameter in the realm configuration. You must also set the SIP options parameter to media-release with the appropriate header name and header parameter information. This option defines how the Enterprise SBC encodes IPv4 address and port information for media streams described by, for example, SDP.

    Note:

    The nat-traversal parameter can establish an important media handling behavior. If you set nat-traversal on a sip-interface to always, this setting supersedes any multi-media configuration that would otherwise release the media. Instead, the Enterprise SBC recognizes when a flow's leg is behind a NAT during the signaling, and ignores any configuration that would release the media. The Enterprise SBC then sets up the end to end media flow in MBCD and performs its HNT function for that flow.

    To configure realm service profile:

  1. max-bandwidth—Enter the total bandwidth budget in kilobits per second for all flows to/from the realm defined in this element. The default is 0 which allows for unlimited bandwidth. The valid range is:
    • Minimum—0

    • Maximum—999999999

  2. mm-in-realm—Enable this parameter to treat media within this realm on this Enterprise SBC. The default is disabled. Valid values are:
    • enabled | disabled

  3. mm-in-network—Enable this parameter to treat media within realms that have the same subnet mask on this Enterprise SBC. The default is enabled. Valid values are:
    • enabled | disabled

  4. msm-release—Enable or disable the inclusion of multi-system (multiple Enterprise SBCs) media release information in the SIP signaling request sent into the realm identified by this realm-config element. If this field is set to enabled, another Enterprise SBC is allowed to decode the encoded SIP signaling request message data sent from a SIP endpoint to another SIP endpoint in the same network to restore the original SDP and subsequently allow the media to flow directly between those two SIP endpoints in the same network serviced by multiple Enterprise SBCs. If this field is disabled, the media and signaling will pass through both Enterprise SBCs. Remember that for this feature to work, you must also set the options parameter in the SIP configuration accordingly. The default is disabled. Valid values are:
    • enabled | disabled

QoS Measurement

This chapter provides detailed information about when to configure the qos-enable parameter. If you are not using QoS or a QoS-capable Oracle Enterprise Session Border Controller, then you can leave this parameter set to disabled (default).

QoS Marking

QoS marking allows you to apply a set of TOS/DiffServ mechanisms that enable you to provide better service for selected networks

You can configure a realm to perform realm-based packet marking by media type, either audio/voice or video.

The realm configuration references a set of media policies that you configure in the media policy configuration. Within these policies, you can establish TOS/DiffServ values that define an individual type (or class) of service, and then apply them on a per-realm basis. In the media profiles, you can also specify:

  • One or more audio media types for SIP and/or H.323
  • One or more video types for SIP and/or H.323
  • Both audio and video media types for SIP and/or H.323

    To establish what media policies to use per realm in the ACLI:

  1. media-policy—Enter the name (unique identifier) of the media policy you want to apply in the realm. When the Oracle Enterprise Session Border Controller first sets up a SIP or H.323 media session, it identifies the egress realm of each flow and then determines the media-policy element to apply to the flow. This parameter must correspond to a valid name entry in a media policy element. If you leave this parameter empty, then QoS marking for media will not be performed for this realm.

Address Translation Profiles

If you are not using this feature, you can leave the in-translationid and out-translationid parameters blank.

Realm Support of DNS Servers

You can configure DNS functionality on a per-realm basis. Configuring DNS servers for your realms means that you can have multiple DNS servers in connected networks. In addition, this allows you to specify which DNS server to use for a given realm because the DNS might actually be in a different realm with a different network interface.

This feature is available for SIP only.

To configure realm-specific DNS in the ACLI:

  1. Access the realm-config configuration element.
    ORACLE# configure terminal
    ORACLE(configure)# media-manager
    ORACLE(media-manager)# realm-config
    ORACLE(realm-config)# 
  2. dns-realm—Enter the name of the network interface that is configured for the DNS service you want to apply in this realm. If you do not configure this parameter, then the realm will use the DNS information configured in its associated network interface.

    Note:

    Note: If DNS is not configured on the associated network-interface of that realm, then following other configured realms shall be used to send out the query. These are listed in order of their preference.
    1. dns-realm of that realm.
    2. dns-realm of egress-realm-id under sip-config, if configured. If not configured, egress-realm-id would be used.
    3. dns-realm of home-realm-id under sip-config, if configured. If not configured, home-realm-id would be used.

    This is only applicable for SIP.

DoS ACL Configuration

If you are not using this functionality, you can leave the parameters at their default values: average-rate-limit, peak-rate-limit, maximum-burst-size, access-control-trust-level, invalid-signal-threshold, and maximum-signal-threshold.

Enabling RTP-RTCP UDP Checksum Generation

The Oracle Enterprise Session Border Controller can generate a UDP checksum for RTP/ RTCP packets on a per-realm basis. This feature is useful in cases where devices performing network address translation (NAT) do not pass through packets with a zero checksum from the public Internet. These packets do not make it through the NAT, even if they have the correct to and from IP address and UDP port information. The Oracle Enterprise Session Border Controller calculates a checksum for these packets and thereby enables them to traverse a NAT successfully.

If a checksum is already present when the traffic arrives at the hardware, the system simply relays it.

Hiding Media Updates

The Real-Time Transport Protocol uses timestamps, sequence numbers, and synchronization source (SSRC) endpoint identifiers to identify and maintain media streams between endpoints. Unexpected changes to these can cause some VoIP terminals to drop calls. You can configure the Oracle Enterprise Session Border Controller (Enterprise SBC) to Hide Media Update (HMU) changes from endpoints and prevent the associated media flows from failing on a per-realm basis.

The HMU function monitors SSRC, timestamp, and sequence number data within RTP media traffic. The Enterprise SBC stores this data within the context of individual NAT flows, and manages the flows internally with H.248. Changes to SSRC and sequence number trigger HMU logic. When triggered, the Enterprise SBC refers to the SSRC, sequence number and timestamp stored in the flow information, calculates the preferred values for all three, calculates a new header checksum, and writes them to the egress media streams. The Enterprise SBC keeps track of these events and provides you with the ability to review these changes.

The preferred values the Enterprise SBC writes include:

  • The original SSRC
  • A new sequence number, calculated from the last sequence number
  • A new timestamp, calculated from the new received timestamp and the timestamp delta

When any change to SSRC occurs, the Enterprise SBC can recognize the issue and, if configured, invoke the HMU logic. Refer to the section on HMU Support for RTP to SRTP Interworking for an explanation about the use of HMU for monitoring sequence numbers.

A common cause for SSRC changes is call transfer. The diagram below depicts a transfer from UE #2 to US #3. The call transfer creates an SSRC change that the administrator has determined may not be accepted by UE #3. By configuring HMU on the egress realm, the administrator prevents these changes from causing the call to fail.


This figure shows the Enterprise SBC managing call termination changes with HMU

The HMU function operates on traffic at the egress realm. The Enterprise SBC evaluates SSRC changes when the traffic reaches the egress interface and corrects RTP data before it egresses the Enterprise SBC. You may determine that the Enterprise SBC needs to hide media changes from one realm only. If you are not configuring bi-directional HMU monitoring, refer to the following table to understand where to apply your HMU configuration.

Ingress Realm HMU Enabled Egress Realm HMU Enabled Result
No No HMU not used
No Yes HMU applied to response RTP
Yes No HMU not applied to response RTP
Yes Yes HMU applied to response RTP

Although the feature is RTC, the system only performs HMU on new calls after configuration. In addition, HMU supports HA. The Enterprise SBC maintains all established calls across a failover. Failover may cause sessions that have HMU active to have a jump in SSRC, timestamps and sequence number. This may trigger the HMU logic and generate RTP data rewrites for flows.

The Enterprise SBC maintains HMU status messages whenever received RTP packets trigger the HMU logic. You can verify how many HMU transitions have occurred on interfaces using the show media host stats command, and the HMU index per media flow using the show nat by-index command.

Note:

HMU is not supported for RTCP or SRTCP packets. Regardless of HMU configuration, the Enterprise SBC supports only up to 7 SSRC changes per SRTP session. Also, if HMU is disabled, the Enterprise SBC supports only up to 7 SSRC changes per SRTP session for RTP and RTCP packets.

HMU State Machine

The Enterprise SBC implements a state machine to manage HMU behavior that includes 5 states:

  • INIT—For the first packet of a particular stream, The Enterprise SBC stores sequence number, SSRC and timestamp in an HMU translation table identified by the index derived from the flow id.
  • LEARN—For the next packet of a particular stream, HMU checks if there is change of SSRC. If the SSRC has not changed, the Enterprise SBC keep the state machine in LEARN state. If there is a change, the Enterprise SBC changes the state to WAIT.
  • WAIT—For the next packet of the stream, HMU check if there is change on SSRC, OR if change in sequence number is not within the permissible limit, it moves the state to TRANS state. It saves the last ingress sequence number and also egress sequence number.
  • TRANS—For the next packet of the stream, HMU checks if the changes observed in WAIT state are permanent; in that case it moves the state to HIDE and starts hiding the changed ingress information.
  • HIDE—From here onwards, for the RTP packets received, the Enterprise SBC calculates the sequence number from the latched last egress sequence number before forwarding packets.

Note:

The HMU state machine requires at least two consecutive packets with the same SSRC value before it begins to hide the SSRC value. This ensures that a pattern is set and there is consistency to this SSRC value, which tells the Enterprise SBC it can be used for hiding other SSRC values. Also, in the case of a REINVITE, the Enterprise SBC may create new flows. In these new flows, the HMU state machine restarts from its INIT state.
HMU Configuration

You can configure the Oracle Enterprise Session Border Controller (Enterprise SBC) to Hide Media Update (HMU) changes from endpoints on a per-realm basis to prevent unsuccessful media flows due to media updates.

Use the following procedure to enable hide-media-update on a realm. By default, hide-media-update is disabled.

Note:

Enable hide-media-update on a realm, only. Do not enable hide-media-update in the media-sec-policy configuration.
  1. In Superuser mode, use the following command sequence to access the realm-config configuration:
    ORACLE# configuration terminal
    ORACLE(configure)# media-manager
    ORACLE(media-manager)# realm-config
    ORACLE(realm-config)# 

    When configuring a preexisting realm, use select to choose the realm you want to edit.

  2. hide-egress-media-update—Set this parameter to enabled to enable HMU functionality on this realm.
    ORACLE(realm-config)# hide-egress-media-update enabled
    
  3. Use the hmu-window-size option to configure the RTP sequence-number window that HMU uses when evaluating sequence-number changes.
    The default window is 127. Valid values are 127 through 65535. Increase this value only when packet traces show expected RTP sequence-number jumps that should not trigger HMU sequence-number adjustment. For example, if an expected sequence-number jump is approximately 1000, configure a larger window such as 2000 or 3000.
    ORACLE(realm-config)# options hmu-window-size=2000
  4. Use done and exit to complete the configuration.

Aggregate Session Constraints Per Realm

You can set session constraints for the Oracle Enterprise Session Border Controller’s global SIP configuration, specified session agents, and specified SIP interfaces. This forces users who have a large group of remote agents to create a large number of session agents and SIP interfaces.

With this feature implemented, however, you can group remote agents into one or more realms on which to apply session constraints.

To enable sessions constraints on a per realm basis:

  1. constraint-name—Enter the name of the constraint you want to use for this realm. You set up in the session-constraints confiuration.

Admission Control Configuration

You can set admission control based on bandwidth for each realm by setting the max-bandwidth parameter for the realm configuration. Details about admission control are covered in this guide’s Admission Control and QoS chapter.