Understanding the SCADA Summary Filter Pane
The SCADA Summary provides the following standard Global filters:
Viewing Data in the SCADA Summary
Viewing All SCADA Data
To open the SCADA Summary for all measurements, select SCADA Summary... from the Web Workspace Tools menu.
Viewing SCADA Data for a Selected Asset
To open the SCADA Summary for a specific asset, select the asset or pressure zone in the Viewer and launch the Control Tool. Click SCADA Summary... and select one of the options:
• Asset...: loads the SCADA Summary with the SCADA measurement data for the selected asset.
• Pressure Zone...: loads the SCADA Summary with SCADA measurement data for the selected asset's pressure zone.
• Lift Station...: loads the SCADA Summary with SCADA measurement data for the selected asset's lift station.
When the SCADA Summary is launched from the Control Tool, the data source is shown in a bar above the table.
Note: If you select
Load All from the SCADA Summary
Actions menu or click the
X button (
) on the bar above the table, the table will be repopulated with all measurements and the bar will be removed.
Loading SCADA Summary Data for a Different Asset
Once the SCADA Summary has been opened (from the Control Tool), you can view data for a different asset by selecting it in the Viewer, and then clicking the Load button in the bar above the data table.
Preventing Measurement Updates
To prevent a SCADA measurement from accepting updates from SCADA, complete the following steps:
1. Select SCADA Summary... from the Web Workspace Tools menu. The SCADA Summary window opens.
2. Select a row in the SCADA Summary table corresponding to the asset measurement that you want to prevent from updating.
3. Click the Inhibit button.
Manual Entry and Override of SCADA Measurement Values
Occasionally, you may need to manually enter a status, digital value, or analog value for a SCADA measurement.
If the value for the selected measurement is a valve status measurement (that is, open/close), you must choose Show Control Tool... from the context menu to manually operate the switch. Otherwise, use the following procedure to enter a value manually:
2. Select the SCADA measurement row in the SCADA Summary list.
3. Click either the Manual Entry or Manual Override button.
Note: Manual Entry allows future SCADA value changes to replace the manually entered value. Manual Override prevents SCADA measurements received by the system from changing the manually entered value. Manual Override can be useful when testing specific assets or RTU communications offline, since the test operations can be prevented from creating outages in Oracle Utilities Network Management System by putting manual overrides on the appropriate status measurements.
If the value for the measurement is a multi-state digital, analog, or any type of measurement other than a valve status measurement (open/close), a dialog box opens, allowing you to enter a value.
Note: Multi-state digitals are not available through the Oracle Utilities Network Management System SCADA ICCP Block 1, 2, and 5 Adapter.
4. Select or enter the value you want to change the measurement to.
5. Click OK.
Note: Clicking Manual Override blocks any new values coming from the SCADA measurement. It does not affect the physical SCADA asset, it only blocks the value reported by the SCADA asset to Oracle Utilities Network Management System.
Adding and Modifying Comments for SCADA Status Changes
When you change the SCADA state to Inhibit, Manual Override, or Disabled in Power Flow, you can enter comments to record why the state was changed. When you initiate an Inhibit action, a dialog box will open allowing you to enter a comment; for Manual Override, a Comment field is available below the Value field. The comment text, user, and date and time the comment was entered will be added to the selected asset's SCADA Summary row.
Existing comments may be edited by selecting the SCADA Summary row and selecting Edit Comment... from the Actions menu.
The SCADA Trend Graph tool displays historic or real-time trend lines for up to 9 SCADA measurements as long as there are no more than two distinct units of measure (for example, Amps and kW) between them.
The tool contains two main parts: the graph that displays trend lines and the Trends collapsible panel that contains the list of saved SCADA Trend Graph configurations.
Components of the SCADA Trend Graph
Trends Collapsible Panel
Contains a list of saved SCADA Trend Graph configurations accessible to the user. Each item has a unique name and represents a list of SCADA measurements, type of trend (real-time or historic), and date range.
SCADA Trend Graph configuration can be loaded by double-clicking on an item in the list or using the Load option from the File menu SCADA Trend Graph tool.
Graph Panel
For historic trends, the start and end dates can be changed by selecting a date and time in the Begin Date and End Date fields.
Real-time trending mode can be enabled by the Real-Time check‑box. In this mode, the Begin Date and End Date fields are replaced with the Time Window drop‑down list. Data is displayed for the selected time period going back from the current time.
Newly received values for the displayed measurements are added to the graph dynamically. The graph can show the predicted values and the actual measurements over the given period of time. If you hover the mouse over a point on the graph, the details of the measurement will be shown.