7.7.1.2 ALTER CELL
Purpose
The ALTER CELL command changes the attributes of the cell.
Syntax
ALTER CELL {
SHUTDOWN SERVICES { RS | MS | CELLSRV [IGNORE REDUNDANCY] | ALL [IGNORE REDUNDANCY] |
EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
RESTART SERVICES { RS | MS | CELLSRV [IGNORE REDUNDANCY] | ALL [IGNORE REDUNDANCY] |
EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
STARTUP SERVICES { RS | MS | CELLSRV | ALL |
EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
DISABLE SERVICES { EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
OFFLINE |
ONLINE |
LED {ON | OFF} |
DONOTSERVICELED {ON | OFF [FORCE]} |
VALIDATE { MAIL | SNMP | CONFIGURATION } |
VALIDATE SYSLOGCONF selector.node |
CONFIGUREBMC |
RESTART BMC |
BBU { DROP FOR REPLACEMENT | REENABLE } |
attribute_name = attribute_value
[, attribute_name = attribute_value]...
}- ALTER CELL Commands for Managing Services
- ALTER CELL Commands for Managing Exadata Storage Server Hardware
- ALTER CELL Commands for Configuration Validation
- ALTER CELL Commands for Setting Attributes
Parent topic: ALTER
7.7.1.2.1 ALTER CELL Commands for Managing Services
Syntax
ALTER CELL {
SHUTDOWN SERVICES { RS | MS | CELLSRV [IGNORE REDUNDANCY] | ALL [IGNORE REDUNDANCY] |
EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
RESTART SERVICES { RS | MS | CELLSRV [IGNORE REDUNDANCY] | ALL [IGNORE REDUNDANCY] |
EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
STARTUP SERVICES { RS | MS | CELLSRV | ALL |
EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
DISABLE SERVICES { EGS | USREDS | SYSEDS | ERS | BSM | BSW | IFD } |
OFFLINE |
ONLINE |
}Usage Notes
The following table lists the arguments and options for the ALTER CELL commands that perform service management operations:
| Argument | Description |
|---|---|
|
|
Shuts down the Restart Server ( |
|
|
Shuts down the Cell Server ( If you include |
|
|
Shuts down the specified Exascale service. |
|
|
Shuts down If you include |
|
|
Stops and then restarts the Restart Server ( |
|
|
Stops and then restarts the Cell Server ( If you include |
|
|
Stops and then restarts the specified Exascale service. |
|
|
Stops and then restarts If you include |
|
|
Starts the specified service or A service can be an Exadata service (
To enable a disabled Exascale service, you must start it specifically by name. |
|
|
Shuts down and disables the specified Exascale service. A disabled service is prevented from automatically restarting and is not included in To enable a disabled service, you must start it specifically by name. |
|
|
Gracefully deactivates grid disks and pool disks, and takes services offline, ensuring that storage and service redundancy remain intact. Then, shuts down all Exadata and Exascale software services. This option is available starting with Oracle Exadata System Software release 25.2.0. |
|
|
Starts all software services on the cell, reactivates grid disks and pool disks, and rejoins the Exascale cluster if necessary. This option is available starting with Oracle Exadata System Software release 25.2.0. |
The following are additional usage notes for the ALTER CELL commands that perform service management:
-
When shutting down the Cell Server service (
CELLSRV), the system first verifies that the operation can proceed without compromising storage and service redundancy. If it is safe to proceed, the grid disks and pool disks are deactivated andCELLSRVgoes offline. Otherwise, if it is not safe to proceed, the services stay unchanged and an error is displayed.Note:
Redundancy checks for
CELLSRVwith Exascale storage are first introduced in Oracle Exadata System Software version 25.2.2 (September 2025). In earlier versions, you must manually confirm that it is safe to shut downCELLSRVon any cell in an Exascale cluster. -
The
IGNORE REDUNDANCYoption bypasses redundancy checks and performs the requested operation immediately. Use this option with extreme caution. Shutting downCELLSRVwithout redundancy checks may cause an Oracle ASM disk group or Exascale storage pool to go offline. -
The Restart Server (RS) service must be running before you can start other services individually. To restart RS, run
ALTER CELL STARTUP SERVICES RSorALTER CELL RESTART SERVICES RS. Or, you can restart all services by runningALTER CELL STARTUP SERVICES ALL. -
For details about Exascale services, see:
Parent topic: ALTER CELL
7.7.1.2.2 ALTER CELL Commands for Managing Exadata Storage Server Hardware
Syntax
ALTER CELL {
RESTART BMC
| LED {ON | OFF}
| DONOTSERVICELED {ON | OFF [FORCE]}
| CONFIGUREBMC
| BBU { DROP FOR REPLACEMENT | REENABLE }
| attribute_name = attribute_value [, attribute_name = attribute_value]...
}Usage Notes
The following table lists the arguments and options for the ALTER CELL commands that perform Exadata storage server hardware management operations:
| Argument | Options | Description |
|---|---|---|
|
|
none |
Restarts the Baseboard Management Controller (BMC). |
|
|
|
You can manually light the LED to indicate that a cell requires maintenance. The LED also turns on automatically if a component fails. |
|
|
|
Turns the Do Not Service LED on and off. This LED is available with Oracle Exadata Database Machine X7 and later models. |
|
|
none |
Configures the BMC for hardware alerts to the local cell so that Management Server (MS) can pick up the alerts. |
|
|
|
|
The following are additional usage notes for the ALTER CELL commands that perform storage server hardware management:
-
The
ALTER CELL BBU DROP FOR REPLACEMENTcommand is run prior to replacement of a hard disk controller battery. The command changes the caching policy fromwritebacktowritethrough, and turns on the locator LED. The new battery is enabled automatically. -
The
ALTER CELL BBU REENABLEcommand is run when a battery is removed and then the same battery is re-inserted. The command changes the caching policy fromwritethroughtowriteback, and turns off the locator LED.
Attributes Related to Hardware Management
-
The
bbuLearnCycleTimeattribute is used to set the start time for the battery learn cycle. After the learn cycle has completed, the attribute reverts to its default quarterly cycle. -
The
bbuLearnScheduleattribute is used to set the next battery learn cycle. The following parameters are used with thebbuLearnScheduleattribute:month: Values are1through12. The month entered must be within the current month and the next three months. For example, if thebbuLearnScheduleattribute is set in February, then the months could be February, March, April or May.week: Values are1through5. The value1represents the first week of the month,2represents the second week, and so on. Theweekvalue must be specified when specifyingmonthandday.day: Values are1through7. The value1represents Sunday,2represents Monday, and so on. Thedayvalue must be specified when specifyingmonthandweek.date: Values are1through31. The values represent the days of the month. The default date is17.hour: Values are0through23. The value0represents 12:00 a.m.,1represents 1:00 a.m., and so on.minute: Values are0to59. The values represent the minutes in an hour.second: Values are0to59. The values represent the seconds in a minute.
-
The
ALTER CELL eighthRack=truecommand enables or disables an Eighth Rack configuration on Oracle Exadata Database Machine X3-2 Quarter Racks or later. The options aretrueto enable the Eighth Rack configuration, andfalseto disable the Eighth Rack configuration. TheALTER CELL eighthRack=truecommand requires that there are no cell disks because enabling the Eighth Rack configures only half of the hard disks and flash capacity. After using this command you must restart Cell Server (CELLSRV) to make the new changes effective and prevent unexpected results.
Examples
Example 7-3 Setting the Cell LED Off and On
This example shows how to set the Fault-Service Required LED on and off for the cell.
CellCLI> ALTER CELL LED OFF
CellCLI> ALTER CELL LED ON
Example 7-4 Setting the Battery Learn Cycle
This example shows how to schedule for the battery learn cycle. In this example, the command sets the battery learn cycle to occur January 17 3:00:59, and then the following learn cycles are April 17 3:00:59, July 17 3:00:59, and October 17 3:00:59. The default setting is "MONTH 1 DATE 17 HOUR 2 MINUTE 0."
CellCLI> ALTER CELL bbuLearnSchedule = "MONTH 1 HOUR 3 SECOND 59"
Parent topic: ALTER CELL
7.7.1.2.3 ALTER CELL Commands for Configuration Validation
Syntax
ALTER CELL {
VALIDATE { MAIL | SNMP | CONFIGURATION }
| VALIDATE SYSLOGCONF selector.node
}Usage Notes
The following table lists the arguments and options for the ALTER CELL commands that perform configuration validation operations:
| Argument | Description |
|---|---|
|
|
The |
|
|
The |
|
|
The |
|
|
The |
Usage Notes
For more information about SYSLOG configuration, see SYSLOG Attributes.
Examples
Example 7-5 shows how to validate the e-mail setup on a cell.
Example 7-6 shows how to validate the Oracle ASR e-mail setup on a cell.
Example 7-7 shows how to validate the SNMP setup on a cell.
Example 7-8 shows how to validate the configuration on a cell.
Example 7-9 shows a sample error message when configuration on a cell is incorrect.
Example 7-5 Validating E-mail on a Cell
CellCLI> ALTER CELL VALIDATE MAIL
Example 7-6 Validating Oracle ASR E-mail on a Cell
CellCLI> ALTER CELL VALIDATE SNMP type=asr
Example 7-7 Validating SNMP on a Cell
CellCLI> ALTER CELL VALIDATE SNMP
Example 7-8 Validating Configuration on a Cell
CellCLI> ALTER CELL VALIDATE CONFIGURATION
Cell CD_01_cell01 successfully altered
Example 7-9 Checking an Incorrect Configuration on a Cell
CellCLI> ALTER CELL VALIDATE CONFIGURATION
CELL-02827: Cell configuration check for hardware and firmware encountered the
following issues:
ILOM check has detected the following issue(s):
Attribute Name : ILOMVersion
Required : 3.0.6.10.a r49240
Found : 3.0.6.10.a r49385
Parent topic: ALTER CELL
7.7.1.2.4 ALTER CELL Commands for Setting Attributes
Syntax
ALTER CELL
attribute_name = attribute_value
[, attribute_name = attribute_value]...
Usage Notes
The attributes that can be changed using the ALTER CELL
command are shown as modifiable in Example 7-96 or described below.
- Caching Attributes
- Alert Notification Attributes
- Alert Summary Attributes
- SYSLOG Attributes
- Disk Scrubbing Attributes
- Security Certificate Attributes
- Persistence Attributes
- Real-Time Insight Attributes
- Miscellaneous Attributes
Parent topic: ALTER CELL
7.7.1.2.4.1 Caching Attributes
Flash Cache Mode
The flashCacheMode attribute is used to display and set the current value for flash cache. The values are writethrough (the default) or writeback. Note the following about the flashCacheMode attribute:
-
If the attribute is modified from
writebacktowritethroughand there is existing flash cache, then an error is displayed. The flash cache must be flushed and dropped before changing the attribute towritethrough. -
If the attribute is to be modified from
writethroughtowriteback, then flash cache must be dropped before modifying the attribute. -
Write back caching can be disabled on the grid disks that do not need caching, such as the grid disks in the RECO disk group. This allows other objects to use the cache space.
See Also:
- ALTER GRIDDISK for information about disabling caching on grid disks
- Oracle Exadata Database Machine Maintenance Guide for information about enabling and disabling flash cache
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.2 Alert Notification Attributes
Configuring Alert Notifications
To set up the cell to send notifications about alerts, you can configure the following cell attributes:
mailServer: Fully qualified domain name of the email relay server used to send alert notifications. This attribute only requires specification in cases where DNS returns an unreachable or invalid mail exchange (MX) record for the email server specified insmtpToAddr.smtpPort: Email server port used to send alert notificationssmtpUseSSL: Specification to use Secure Socket Layer (SSL) encryption for alert notifications.smtpFrom: User name that appears in theFrom:header of the alert notificationssmtpFromAddr: Email address that appears in theFrom:header of the alert notifications. This email address is not authenticated with the email server.smtpToAddr: Address to which email is sent. It can be a comma-delimited list in quotation marks to allow multiple subscribers to alerts.snmpSubscriber: List of hosts that subscribe to the SNMP alert notificationssnmpUser: Defines users who receives SNMP alertssnmpEngineID: An identifier used by the SNMP managers to subscribe to alerts from the storage cellsnotificationMethod: Notification method for alertsnotificationPolicy: Indicator for severity alerts to be sent to subscribersemailFormat: File format for email messagesemailSubscriber: List of names that subscribe to the alert notifications
Usage Notes
-
mailServerThe
mailServerattribute identifies the email relay server used to send alert notifications. When you modify themailServerattribute value, the Exadata Management Server (MS) automatically configures and restarts the sendmail service. You can clear themailServerattribute and remove the email relay server from the sendmail configuration by settingmailServerto an empty string enclosed by quotation marks (mailServer=''). -
smtpPortThe
smtpPortattribute can be reset to the default value by setting it to an empty string enclosed by quotation marks (smtpPort=''). -
smtpUseSSLThe
smtpUseSSLattribute enables Secure Socket Layer (SSL) encryption on the email notifications when the attribute is set totrue. -
smtpToAddrThe
smtpToAddrattribute can be used to set a list of comma-delimited email addresses that are the recipients of the alert notification. The list must be enclosed in quotation marks. -
snmpSubscriberThe
snmpSubscriberattribute can be set to a list of SNMP targets to which the SNMP alert notification is sent. The targets are specified as follows:snmpSubscriber[-|+]=( (host=host[,port=port][,type=subscriber_type][,community=community][,snmpuser=snmp_user_name][,fromIP="ip"][,asrmPort="ASRManager_port"]) [,(host=host[,port=port][,type=subscriber_type][,community=community][,snmpuser=snmp_user_name][,fromIP="ip"][,asrmPort="ASRManager_port"])] ...)The
snmpSubscriberattribute uses the following values:-
The
hostmust be specified as either a host name or an IP address. Enclose the host name or IP address in quotation marks if it contains non-alphanumeric characters. -
The default value for
portis162. This value is optional. -
The valid
typevalues arev1,ASR,v3, andv3ASR.-
Starting with Oracle Exadata System Software release 24.1.0, you must specify the
typevalue.Previously, setting the
typeis optional, and the default value isv1. -
The
type=v3andtype=v3ASRoptions use SNMP V3. SNMP V3 is considered more secure than earlier SNMP versions, and should be used where possible. -
The
snmpSubscriberwithtype=ASRortype=v3ASRshould only be configured to point to Oracle ASR Manager. -
The
type=ASRandtype=v3ASRoptions set the Oracle ASR destination for Oracle Exadata Storage Server, and its ILOM. Removing allsnmpSubscriberentries withtype=ASRandtype=v3ASRfrom the SNMP subscriber list disables the Oracle ASR trap mechanism for Oracle Exadata Storage Server and its ILOM. -
For the
v3ASRtype, the user must be defined withauthProtocol=SHA, andprivProtocol=AES. These are the only protocols supported by Oracle ASR Manager. Setting thesnmpSubscriberas typev3ASRalso sets the ILOM properties and rules for traps sent by ILOM.
-
-
Starting with Oracle Exadata System Software release 24.1.0, you must specify the
communityvalue for subscribers withtype=v1ortype=ASR. Also, common default values such aspublicandprivateare discouraged for security reasons.Previously, setting the
communityis optional, and the default value ispublic. -
For subscribers with
type=v3ortype=v3ASR, you must specify an SNMP user name (snmpuser=snmp_user_name), which is already configured within the server.For example:
CellCLI> ALTER CELL snmpuser.snmpuser1=(authprotocol=SHA,authpassword=*) ... CellCLI> ALTER CELL snmpSubscriber=((host=newhost,port=162,type=v3,snmpuser=snmpuser1)) -
The
fromIPfield enables you to specify an IP address from which the trap is sent. If this field is not specified, it defaults to the IP address associated with eth0. Use this field if the default IP address is not registered with Oracle ASR Manager. Oracle ASR Manager only processes SNMP traps that are sent from IP addresses that it recognizes.The
fromIPfield is allowed only for SNMP subscribers whose type is eitherASRorv3ASR.For example:
CellCLI> ALTER CELL snmpSubscriber=((host=asrhost,port=162,community=asrcommunity,fromIP="1.1.1.1",type=ASR))The following example returns an error because the type is not
ASRorv3ASR.CellCLI> ALTER CELL snmpSubscriber=((host=localhost,port=162,community=asrcommunity,fromIP="1.1.1.1",type=v1)) CELL-00068: The fromIP field is only supported for ASR SNMP subscribers. -
The
asrmPortfield enables you to specify the port number on an Oracle ASR Manager machine that MS uses to communicate with Oracle ASR Manager. This port must be the same as the HTTP port of Oracle ASR Manager’s HTTP Receiver. You can check this by runningasr show_http_receiveron the Oracle ASR Manager machine.The
asrmPortfield is allowed only for SNMP subscribers whose type is eitherASRorv3ASR. The default value for this port is 16161.
By default,
ALTER CELL snmpSubscriber=(SNMPtargets)replaces the existingsnmpSubscribervalue. However, starting with Oracle Exadata System Software release 21.2.0, you can add to the existing list of SNMP targets by usingsnmpSubscriber+=(SNMPtarget). For example:CellCLI> ALTER CELL snmpSubscriber+=((host=newhost,port=162,community=snmpcommunity,type=v1))Also, starting with Oracle Exadata System Software release 22.1, you can remove an entry from the existing list of SNMP targets by using
snmpSubscriber-=(SNMPtarget). For example:CellCLI> ALTER CELL snmpSubscriber-=((host=myhost,port=162,community=snmpcommunity,type=v1))After startup of the Management Server (MS), the
snmpSubscriberlist entries withtype=ASRare added to the ILOM for theCELL. This ensures that when an ILOM is replaced, the entries are set for the new ILOM. If the entries are removed from the ILOM, then they must be manually added to the ILOM using theALTER CELL ... snmpUser=command. -
-
snmpUserThe
snmpUserattribute defines users who receives SNMP alerts. This command can only be run in interactive mode. There are two methods for configuring this attribute.snmpuser=((user_clause1)[,(user_clauseN)]...) snmpuser.name=(user_clause)-
If you specify
snmpuser, then you must provide a user_clause for every configured user. If you omit a user, then that user will no longer receive SNMP alerts. The((user_clause1)[,(user_clauseN)]...)string that you provide overwrites the previous string used for thesnmpuserattribute. -
If you specify
snmpuser.name, then you must provide a user_clause for only the specified user. This allows you to add, delete, or modify each user individually, without having to supply the entiresnmpuserattribute string each time. - If you use
snmpuser='', then all SNMP users are removed. If you usesnmpuser.name='', then only the specified user is removed. You cannot remove an SNMP user while it is still referenced by a V3 SnmpSubscriber.
Each method uses a user_clause, which has the following general format:
([name=user1,] authProtocol=auth_type, authPassword=* [, privProtocol=priv_type, privPassword=*]) [,(name=userN, authProtocol=auth_type, authPassword=* [, privProtocol=priv_type, privPassword=*] )]...If updating a single user using the
snmpuser.namenotation, do not include the phrasename=user1in the user_clause.-
nameis the user name. -
Only
*is allowed for the password values in the command. Passwords are not stored or displayed. Secure hash keys are computed and used for trap authentication and encryption. -
authProtocolspecifies the authentication protocol.Options include
MD5andSHA. Additionally, Oracle Exadata System Software release 24.1.0 introduces the following SHA2 authentication protocols for SNMP V3 subscribers:SHA-224,SHA-256,SHA-384, andSHA-512.The
authProtocolmust be specified for thesnmpUserattribute.The system prompts for the authentication password. The authentication password must have 8 to 12 alphanumeric characters.
-
privProtocolis encryption protocol. Options arenone,AES, orDES. The default isnonewhen theprivProtocolattribute is not specified.The system prompts for an encryption password if the encryption protocol is specified. The password is exactly 8 alphanumeric characters, and they are case sensitive.
-
-
snmpEngineIDThe
ALTER CELL snmpEngineIDcommand is used by the SNMP managers to subscribe to alerts from the storage cells. ThesnmpEngineIDparameter can be up to 20 characters. It should be unique for each target within a data center. The default is the cell name. This default is used if thesnmpEngineIDattribute is not set before the SNMP users are defined.Note:
The engine identifier should not be changed after SNMP users are defined. Any change to an engine identifier causes the user keys to be re-computed, and user passwords must be re-entered. -
notificationMethodThe
notificationMethodattribute value can bemail,snmp,none, or a combination ofmailandsnmp, such asnotificationMethod='mail,snmp'. The default value ismail. -
notificationPolicyThe
notificationPolicyattribute value can benoneor a combination ofcritical,warning, orclear, such asnotificationPolicy='warning,clear.'- The
criticalvalue refers to hardware-generated alerts or alerts generated by Automatic Diagnostic Repository (ADR) or BMC. Thecriticalvalue also refers to a metric alert when the value exceeds the critical threshold specified in the metric definition. - The
warningvalue refers to a metric alert when the value exceeds the warning threshold specified in the metric definition. - The
clearvalue refers to a metric alert when the value is below the threshold boundary after having previously exceeded a warning or critical threshold. - The
maintenancevalue refers to all hardware-related errors. The hardware errors are reported as "Maintenance" in email message subject lines.
- The
-
emailFormatThe
emailFormatattribute can behtmlortext. By default, email notifications are sent in HTML format. Change the value totextto receive plain text email notifications. -
emailSubscriberThe
ALTER CELL emailSubscribercommand sets a list of comma-delimited email addresses that are the recipients of alert notifications for specific alert types. The syntax for this command is:ALTER CELL emailSubscriber = ((email="email_address1", \ alertType="alert_type") \ [, (email="email_address2",alertType="alert_type"), ...])-
The email address must be a valid email address. The
emailparameter is mandatory. -
The
alertTypeparameter specifies the type of alert, and is optional. The alert types areHARDWARE,SOFTWARE,METRICorADR. If the alert type is not specified, then the subscription is for all alert types. -
An empty input string removes the current set of subscribers.
-
The notification policy must be set before alert notifications can be received. The policy applies to all email subscribers. The notification policy for these alerts are the same as for
snmpSubscriberalerts.
To validate that email messages are successfully sent for cell alerts or events, use the
ALTERcommand with theVALIDATE MAILoption. The validation process sends a test email message to the configured recipient. If that test email message is not received, then an email configuration setting is not valid. -
Examples
Example 7-10 shows how to set the asrmPort field for an snmpSubscriber.
Example 7-11 shows how to set up email notifications for the cell.
Example 7-12 shows how to modify the SNMP user.
Example 7-13 shows how to modify a single SNMP user.
Example 7-14 shows how to specify the type of email alerts. In the example, one subscriber gets hardware and software alerts, and the other subscriber gets ADR alerts.
Example 7-15 shows how to change the format of email messages.
Example 7-16 shows how to unsubscribe from email alerts.
Example 7-17 shows how to reset the notificationPolicy attribute to its default value.
Example 7-10 Setting the asrmPort for an snmpSubscriber
CellCLI> ALTER CELL snmpSubscriber=((host=host1,port=162,community=asrcommunity,type=asr,asrmPort=16161))Example 7-11 Configuring Email Notifications for a Cell
The example includes multiple SNMP subscribers. Note that because
host2 is an SNMP v3 subscriber, there is no community
specification. Instead, for SNMP v3 subscribers, you must specify an existing SNMP user. See
also the following for examples for modifying an SNMP user.
CellCLI> ALTER CELL mailServer='my_mail_relay.example.com', -
smtpFromAddr='john.doe@example.com', -
smtpFrom='John Doe', -
smtpToAddr='jane.smith@example.com', -
snmpSubscriber=((host=host1,port=162,community=snmpcommunity,type=v1), -
(host=host2,port=162,snmpuser=user2,type=v3)), -
notificationPolicy='clear', -
notificationMethod='mail,snmp'
Example 7-12 Modifying the SNMP User
This example shows SNMP user configuration, where the administrator is prompted to enter the passwords. The example contains one user definition, but the same approach can be expanded to define multiple SNMP users in the same command.
CellCLI> ALTER CELL snmpuser = ((name=ASR, authprotocol=md5, authpassword=*, \
privprotocol=AES, privpassword=*))
snmpUser ASR authpassword: password
Confirm snmpUser ASR authpassword: password
snmpUser ASR privpassword: password
Confirm snmpUser ASR privpassword: password
Example 7-13 Modifying an SNMP User
The following code examples show adding an SNMP user, changing that user's password, and then removing that user.
## adding users individually
CellCLI> ALTER CELL snmpuser.user2=(authprotocol=SHA,authpassword=*)
snmpUser user2 authpassword: password
Confirm snmpUser user2 authpassword: password
snmpUser ((name=user1, authProtocol=SHA, privProtocol=AES)) has been replaced with
((name=user1, authProtocol=SHA, privProtocol=AES),(name=user2, authProtocol=SHA)).
...
## changing a password of an existing user
CellCLI> ALTER CELL snmpuser.user2 = (authprotocol=SHA,authpassword=password)
## delete a user individually
CellCLI> ALTER CELL snmpuser.user2=''
snmpUser ((name=user1, authProtocol=SHA, privProtocol=AES),(name=user2, authProtocol=SHA)) has
been replaced with ((name=user1, authProtocol=SHA, privProtocol=AES)).
...Example 7-14 Specifying the Type of Email Alert
ALTER CELL emailSubscriber= \
((email="email1@example.com",alertType="HARDWARE,SOFTWARE"), \
(email="email2@example.com",alertType="ADR"))
Example 7-15 Changing the Format of Email Messages
CellCLI> ALTER CELL emailFormat='text'
CellCLI> ALTER CELL emailFormat='html'
Example 7-16 Unsubscribing from Email Alerts
ALTER CELL emailSubscriber=""
Example 7-17 Setting the Default Value for the notificationPolicy Attribute
This example shows how to set the default value for the notificationPolicy attribute.
CellCLI> alter cell notificationPolicy=""
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.3 Alert Summary Attributes
Configuring Alert Summaries
-
The
alertSummaryIntervalattribute sets the frequency of the open alerts summary e-mail message. The open alerts e-mail message is an HTML document that provides a concise summary of all open issues on a cell even without access to the cell. Valid options aredaily,weekly,biweeklyandnone.The default value isweekly. -
The
alertSummaryStartTimeattribute sets the delivery time for the open alerts summary e-mail message. The command accepts any valid time stamp.
Example 7-18 Setting the Frequency for the Open Alerts Summary E-mail Message
This example shows how to set the frequency for the open alerts summary e-mail message to weekly.
CellCLI> ALTER CELL alertSummaryInterval=weekly
Example 7-19 Setting the Time for Open Alerts Message Delivery
This example shows how to set the delivery time for the open alerts summary e-mail message.
CellCLI> ALTER CELL alertSummaryStartTime="2013-04-23T12:57:00-06:00"
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.4 SYSLOG Attributes
Configuring SYSLOG
Attributes: syslogconf and
syslogFormat
The syslogconf attribute extends syslog
rules for a cell. The attribute can be used to designate that
syslog messages be forwarded to a specified management server.
On the management server, the forwarded messages are directed to
a file, console, or management application, depending on the
syslog configuration on the management server. The syntax for
configuring this attribute is:
syslogconf = ('selector @node' [, 'selector @node']... )
In the preceding syntax, selector is the message type, and node is the specified server.
Both variables follow syslog.conf standard
syntax rules.
-
The
facilityoption for thesyslogconfattribute must be one of the following:auth,authpriv,cron,daemon,ftp,kern,lpr,mail,mark,news,security,syslog,user,uucp,local0,local1,local2,local3,local4,local5,local6,local7,none, and*. -
The
priorityoption for thesyslogconfattribute must be one of the following:alert,crit,debug,emerg,err,error,info,notice,panic,warn,warning,none, and*(asterisk).
The ALTER CELL VALIDATE syslogconf selector command
sends a test log message. The test message is directed as
specified by rules in the /etc/syslog.conf file.
If the syslogconf assignment extends the syslog
rules, then a test message is forwarded to the specified
management servers.
Starting with Oracle Exadata System Software release 19.1.0, you can use the syslogFormat attribute to change the standard format for syslog to any format by setting the value to the desired format string. Setting the syslogFormat attribute to an empty string removes the format change, reverting the syslog format to the default format. If the format string contains a control character, it must be preceded by a backslash when entering the command.
See Example 7-23 for examples of the syntax.
Starting with Oracle Exadata System Software release 19.3.0, you can use the syslogFormat attribute to enable sending syslog in an encrypted format. For the complete configuration steps, refer to Encrypting System Log Information.
Example 7-20 Using the syslogconf Attribute
This example shows how to add a rule using the syslogconf attribute.
CellCLI> ALTER CELL syslogconf=('*.err;authpriv.none @loghost', -
'*.emerg @loghost')
Example 7-21 Adding and Validating a Rule
This example shows how to add and validate a rule with test message.
CellCLI> ALTER CELL syslogconf=('kern.crit @loghost')
CellCLI> ALTER CELL VALIDATE syslogconf 'kern.crit'
Example 7-22 Removing All syslog.conf Rules
This example shows how to remove the syslog.conf rule.
CellCLI> ALTER CELL syslogconf=''
Example 7-23 Setting the Syslog Format to a Custom String Then Reverting to the Default Format
This example shows how to specify a customized format for syslog.
CellCLI> ALTER CELL syslogformat="%TIMESTAMP:::date-rfc3339% %HOSTNAME%%syslogtag%
%syslogseverity-text%:%msg:::sp-if-no-1st-sp%%msg:::drop-last-lf%\\n"
CellCLI> ALTER CELL syslogformat="%TIMESTAMP% %HOSTNAME% %msg%\\n"
CellCLI> ALTER CELL syslogformat=""
Configuring additional log forwarding:
syslogInput
Starting with Oracle Exadata System Software release 22.1, the syslogInput attribute enables syslog on
the local host (database server or storage server) to forward additional logs to remote log
servers.
The syntax for configuring the syslogInput attribute is:
syslogInput = ('selector @[@]node[:remote_port]' [, 'selector @[@]node[:remote_port]']... )
In the preceding syntax, selector specifies the additional logs being forwarded. The selector value can contain the following entries:
-
audit- Specifies the audit log at/var/log/audit/audit.log. -
aide- Specifies the Advanced Intrusion Detection Environment (AIDE) log at/var/log/aide/aide.log. -
yum- Specifies the YUM log at/var/log/yum.log.
Multiple selector entries must be separated by
a semicolon (;) character.
Each node is specified using the hostname or IP address preceded by one or two at sign (@) characters. You can include one at sign (@) to use UDP for communications or specify two at sign characters (@@) to use TCP.
By default, the remote system receives communications on port 514, which is the
default rsyslogd port. You can specify another port number by appending a colon
(:) character and remote port number to the node specification
In the following example, loghost1 is configured
to receive audit and AIDE logs using UDP on the default rsyslogd port (514). Also, loghost2 is configured to receive YUM logs using TCP on port
10514.
CellCLI> ALTER CELL syslogInput=('audit;aide @loghost1','yum @@loghost2:10514')
To stop and remove additional log forwarding, set syslogInput
to an empty string. For example:
CellCLI> ALTER CELL syslogInput=''
Configuring the ILOM SYSLOG: ilomSyslogClients
Starting with Oracle Exadata System Software release 21.2.0, the
ilomSyslogClients attribute specifies the remote destination to forward syslog
messages from the Integrated Lights Out Manager (ILOM) service
processor (SP).
The ilomSyslogClients attribute accepts a
comma-separated list of up to two loghost servers. For each loghost server, you must specify
a valid hostname or IP address.
For example:
CellCLI> ALTER CELL ilomSyslogClients="192.0.2.101,192.0.2.201"
Note:
The specified ilomSyslogClients must listen on port 514 to
receive the ILOM syslog messages.
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.5 Disk Scrubbing Attributes
Configuring Disk Scrubbing Attributes
Disk scrubbing proactively inspects and repairs hard disks. If a bad sector is detected on a hard disk, Oracle Exadata System Software automatically orchestrates the repair using data from another mirror copy.
Disk scrubbing is a long-running operation. The time required to complete a scrubbing operation depends mainly on disk size and workload. As a guide, allow between 1 and 2 hours for each terabyte of disk capacity to scrub an otherwise idle disk.
On an idle system, disk scrubbing can drive disk utilization to 100%. However, Exadata I/O Resource Management (IORM) throttles disk scrubbing so that user workloads are prioritized and should not be affected by disk scrubbing.
The ALTER CELL hardDiskScrubInterval command activates
(or deactivates) automatic scrubbing and sets the scrubbing interval. Valid options
are daily, weekly, biweekly, and
none. Using the none option stops all active
disk scrubbing operations and deactivates automatic scrubbing.
The ALTER CELL hardDiskScrubStartTime command sets the
start time for the scrubbing schedule. Valid options are a specific date and time or
now.
In the alert log, you may see messages such as Begin scrubbing
celldisk and Finished scrubbing celldisk. These are
expected informational messages, and no action is necessary.
Example 7-24 Setting the Disk Scrubbing Interval to Weekly
This example shows how to activate automatic weekly disk scrubbing.
CellCLI> ALTER CELL hardDiskScrubInterval=weekly
Example 7-25 Setting the Start Time for Proactive Disk Scrubbing
This example shows how to set a specific start time for disk scrubbing.
CellCLI> ALTER CELL hardDiskScrubStartTime='2013-08-07T21:19:22-07:00'
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.6 Security Certificate Attributes
Configuring CA-Certified Security Certificate Attributes
To set up CA-certified security certificates on the cell for use with ExaCLI, use the following attributes:
Note:
The following attributes can be used only if you are running theALTER CELL command from ExaCLI.
securityPubKey- Specifies the URL to the public key file.securityPrivKey- Specifies the URL to the private key file.securityPrivKeyPW- Specifies the password to use if the private key file is encrypted.
After you upload the CA-certified security certificate, you must restart MS before the new security certificate is visible.
CellCLI> ALTER CELL RESTART SERVICES MSSee Also:
Using a CA-Certified Security Certificate in Oracle Exadata Database Machine Maintenance GuideExample 7-26 Configuring the Security Keys for a Storage Server
This example shows how to configure the security keys for a storage server, including supplying the password after entering the command.
exacli -e 'ALTER CELL securityPubKey="http://www.example.com/security/newkey.crt", -
securityPrivKey="http://www.example.com/security/newkey.key", -
securityPrivKeyPW=*'
password=****************
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.7 Persistence Attributes
Persistent Columnar Cache
Starting with Oracle Exadata System Software
release 21.2.0, the
columnarCachePersMode attribute controls the persistent
columnar cache feature. The valid attribute setting are:
-
on- Enables the persistent columnar cache feature. -
off- Disables the persistent columnar cache feature. -
auto- Oracle Exadata System Software decides whether to enable or disable the persistent columnar cache feature. If thecolumnarCachePersModeattribute is not set, then theautosetting is implied.Starting with Oracle Exadata System Software release 21.2.11, the
autosetting enables the persistent columnar cache feature (equivalent tocolumnarCachePersMode=on). Previously, theautosetting disabled the persistent columnar cache feature (equivalent tocolumnarCachePersMode=off).
After you alter the columnarCachePersMode attribute, you must
restart the cell server to implement the change.
Persistent Storage Index
Starting with Oracle Exadata System Software
release 21.2.0, the
storageIndexPersMode attribute controls the persistent storage
index feature. The valid attribute setting are:
-
on- Enables the persistent storage index feature. -
off- Disables the persistent storage index feature. -
auto- Oracle Exadata System Software decides whether to enable or disable the persistent storage index feature. If thestorageIndexPersModeattribute is not set, then theautosetting is implied.Starting with Oracle Exadata System Software release 21.2.11, the
autosetting enables the persistent storage index feature (equivalent tostorageIndexPersMode=on). Previously, theautosetting disabled the persistent storage index feature (equivalent tostorageIndexPersMode=off).
After you alter the storageIndexPersMode attribute, you must restart
the cell server to implement the change.
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.8 Real-Time Insight Attributes
Commencing with Oracle Exadata System Software 22.1.0, you can use the Real-Time Insight feature to enable real-time monitoring of your Exadata systems.
Fine-Grained Metric Collection
The metricFGCollIntvlInSec attribute controls
fine-grained metric collection.
-
To enable fine-grained metric collection, you must set the collection interval to a value between 1 and 60 seconds.
For example:
CellCLI> ALTER CELL metricFGCollIntvlInSec=1The
metricFGCollIntvlInSecsetting is related to the automatic upload frequency specified in themetricStreamIntvlInSecattribute. When automatic metric upload and fine-grained collection are both enabled (metricStreamIntvlInSec>0andmetricFGCollIntvlInSec>0),metricStreamIntvlInSecmust be between 5 and 30 timesmetricFGCollIntvlInSec. For example, ifmetricStreamIntvlInSec=60, thenmetricFGCollIntvlInSecmust be between 2 and 12. -
To disable fine-grained metric collection on a server, set
metricFGCollIntvlInSec=0.For example:
CellCLI> ALTER CELL metricFGCollIntvlInSec=0Fine-grained metric collection can be disabled only when automatic metric upload is disabled (
metricStreamIntvlInSec=0) or the automatic upload frequency is between 5 and 30 minutes (metricStreamIntvlInSecis between 300 and 1800).
Automatic Metric Upload
The metricStreamIntvlInSec attribute sets the upload
interval (in seconds) for automatic uploads to the metric streaming endpoints
specified by the metricStreamEndPoint attribute.
-
To enable automatic metric uploads, set the
metricStreamIntvlInSecattribute to a non-zero value.For example:
CellCLI> ALTER CELL metricStreamIntvlInSec=25The
metricStreamIntvlInSecsetting is related to the fine-grained collection frequency specified in themetricFGCollIntvlInSecattribute:-
When automatic metric upload and fine-grained collection are both enabled (
metricStreamIntvlInSec>0andmetricFGCollIntvlInSec>0),metricStreamIntvlInSecmust be between 5 and 30 timesmetricFGCollIntvlInSec. For example, ifmetricFGCollIntvlInSecis set to 5, thenmetricStreamIntvlInSecmust be between 25 and 150. -
When automatic metric upload is enabled and fine-grained collection is disabled (
metricStreamIntvlInSec>0andmetricFGCollIntvlInSec=0), the automatic upload frequency must be between 5 and 30 minutes (metricStreamIntvlInSecmust be between 300 and 1800).
-
-
To disable automatic metric uploads, set
metricStreamIntvlInSec=0.For example:
CellCLI> ALTER CELL metricStreamIntvlInSec=0
Metric Upload Endpoints
The metricStreamEndPoint attribute specifies one or
more collection endpoints that automatically receive the metric stream. You can set
metricStreamEndPoint as follows:
metricStreamEndPoint[+]=((host="endpoint-URL"[,type="stream-format"][,token="authentication-token"][,{httpProxy|httpsProxy}="proxy-server"])
[,(host="endpoint-URL"[,type="stream-format"][,token="authentication-token"][,{httpProxy|httpsProxy}="proxy-server"])]...)
In the metricStreamEndPoint definition:
-
host: Specifies the URL for the collection endpoint. The URL can use HTTP or HTTPS. -
type: Optionally specifies the format of the stream. Supported values are:-
json: Provides the stream in a JSON format -
plaintext: Provides the stream in a plain text format
The default value is
json. -
-
token: Optionally specifies the authentication token for the collection endpoint. Consult the metric collection platform for details about generating the token. -
httpProxyorhttpsProxy: Optionally specifies a proxy server to facilitate network connectivity to the collection endpoint. A proxy server is required if a firewall resides between the Exadata system and the collection endpoint.
You can use the optional += operator to add collection
endpoints to an existing metricStreamEndPoint definition.
Otherwise, the = operator overwrites the previous attribute
value.
Metric Tags
The metricStreamTags attribute defines a set of metric
tags, which are included in every metric observation generated by the server. These
tags can help you to organize and group observations generated by numerous Exadata
servers.
You can set the metricStreamTags attribute to a valid
JSON string containing tag and value pairs as follows:
metricStreamTags='{"tag1":"value1"[,"tag2":"value2"]...}'
For example:
CellCLI> ALTER CELL metricStreamTags='{"application":"personnel","department":"HR"}'
Parent topic: ALTER CELL Commands for Setting Attributes
7.7.1.2.4.9 Miscellaneous Attributes
Note:
For a complete list of cell attributes, see DESCRIBE CELL.
dbPerfDataSuppress
Use the dbPerfDataSuppress attribute to hide performance output information for specific databases. Specify the databases to mask as a comma-delimited list of names. The performance information for the specified databases is still collected, but is only visible when queried from that database. If you query V$CELL_DB from a different database, then the performance information for the hidden databases appears in the category of OTHER.
diagPackEmailAttach
Use the diagPackEmailAttach attribute to turn on and off adding the diagnostic pack attachment to emails, for example:
alter cell diagPackEmailAttach=FALSESee CREATE DIAGPACK for information about diagnostic packs.
diagPackUploadEnabled
Use the diagPackUploadEnabled attribute to enable or disable automatically uploading diagnostic data to a service request using Oracle ASR.
Example 7-27 Enabling/Disabling Auto Diagpack Upload
You can enable or disable this feature by setting the diagPackUploadEnabled attribute on the cell object.
Set the attribute to false to disable this feature, true to enable it. The default is true.
CellCLI> ALTER CELL diagPackUploadEnabled=FALSEenableSmartStorage
The enableSmartStorage attribute can be set to TRUE to enable the use of Oracle Exadata System Software capabilities such as Smart Scan and Storage Index on Exadata Extended (XT) Storage Server after you have procured the necessary software licenses.
httpsAccess
Starting with Oracle Exadata System Software release 19.1.0, the httpsAccess attribute can be used to specify a list of IP addresses or IP subnet masks that control who can access the RESTful service via HTTPs. The value you specify for httpsAccess overwrites any previous value. You can use the following values for httpsAccess:
ALL— to allow access to all hosts (Default)NONE— to disable the HTTPs port completelyIP1, IP2,..., IPn— to only allow access to hosts with IP addresses IP1, IP2,..., IPn where IPn is a valid IP address in IPv4, IPv4 subnet, IPv6 or IPv4-embedded IPv6 format. You can specify a maximum of 512 IP addresses for the access control list.
Additionally, instead of a single IP address, you can use the / character to specify a range of IP addresses using a subnet mask. For example the range '192.168.10.0/24' corresponds to hosts having IP addresses from 192.168.10.1 to 192.168.10.255. If you specify an IP address range, you need to enclose the IP address string in quotes.
Example 7-28 Restricting HTTPS Access to the Exadata RESTful Service
This example shows how to configure an access control list for HTTPs access to the Exadata RESTful service. The following command allows HTTPs port access to hosts having IP addresses in the range from 192.168.10.1 to 192.168.10.255.
CellCLI> ALTER CELL httpsAccess="192.168.10.0/24"
interconnectN
The ALTER CELL interconnectN="" command removes the RDMA Network Fabric configuration information for the cell for the specified interface (N).
If the IP address to an RDMA Network Fabric interface is changed, then the command service openibd restart must be run as the root user before the service network restart command.
After changing an IP address, you must restart all services using the ALTER CELL RESTART SERVICES ALL command.
Example 7-29 Setting RDMA Network Fabric Interconnections
This example shows how to set the RDMA Network Fabric interconnections.
For systems that use InfiniBand Network Fabric, use a command such as the following:
CellCLI> ALTER CELL interconnect1='ib0', interconnect2='ib1'For systems that use RoCE Network Fabric, use a command such as the following:
CellCLI> ALTER CELL interconnect1='re0', interconnect2='re1'After making the updates, restart all services in the storage server:
CellCLI> ALTER CELL RESTART SERVICES ALLiotimeoutthreshold
Use the iotimeoutthreshold attribute to change the timeout threshold. If cell I/O takes longer than the defined threshold, then the I/O is canceled, and Oracle ASM redirects the I/O to another mirror copy of the data. Any I/Os issued to the last valid mirror copy of the data are not canceled, even if the timeout threshold is exceeded.
The default value for iotimeoutthreshold is 1000s. The command takes a value, such as 5, and a unit. The valid unit is s, for seconds.
Caution:
Setting the timeout threshold too low can negatively impact system performance. Oracle recommends reviewing the Automatic Workload Repository (AWR) reports of peak I/O loads, and setting the threshold value to a value higher than the peak I/O latency with sufficient safety margin.Example 7-30 Setting the iotimeoutthreshold Value
This example demonstrates how to set the iotimeoutthreshold to 5 seconds.
CellCLI> ALTER CELL iotimeoutthreshold = '5s'To reset the iotimeoutthreshold to the default value, use the following command:
CellCLI> ALTER CELL iotimeoutthreshold = ""listeningInterface
Starting with Oracle Exadata System Software release 24.1.0, the
listeningInterface attribute specifies the network interfaces that listen
for commands using the Exadata RESTful service. The value you specify for
listeningInterface overwrites any previous value. You can use the
following values for listeningInterface:
ALL: allows access on all network interfaces (Default)NONE: disables access on all network interfacesNET1, NET2, ..., NETn: allows access only through the specified list of network interface names
The listeningInterface attribute complements the httpsAccess attribute. The listeningInterface attribute specifies which network interfaces accept REST requests, while the httpsAccess attribute restricts the source of requests to the Exadata RESTful service.
Example 7-31 Restricting Access to the Exadata RESTful Service
This example shows how to identify a specific network interface on the server that listens for commands using the Exadata RESTful service.
CellCLI> ALTER CELL listeningInterface='bondeth0'
name
The name attribute contains the host name of the storage server, for example, dm01celladm01.
Example 7-32 Altering Cell Name
This example shows the ALTER command with the CELL object.
CellCLI> ALTER CELL name=cell02traceLevel
The level for which trace messages are written. The default is FINE. The value can be:
-
A valid Java logging level
SEVEREWARNINGINFOCONFIGFINEFINERFINEST
-
A valid Oracle Diagnostic Logging (ODL) logging level
INCIDENT_ERROR:1ERROR:1WARNING:1NOTIFICATION:1NOTIFICATION:16TRACE:1TRACE:16TRACE:32
To reset this attribute to its default value, use a value of "".
Examples
Example 7-33 Setting the traceLevel Value to its Default Value
This example shows how to set the traceLevel value to its default value.
CellCLI> ALTER CELL traceLevel=""
Parent topic: ALTER CELL Commands for Setting Attributes