20 Cabling Tables for Oracle Exadata Database Machine X2-2 and Oracle Exadata Database Machine X2-8 Full Rack
The tables in this chapter show the cable layouts for Oracle Exadata Database Machine X2-2 and Oracle Exadata Database Machine X2-8 Full Rack.
- Rack Layout Diagrams
The diagrams in this topic show the rack layout for Oracle Exadata Database Machine X2-2 and Oracle Exadata Database Machine X2-8 Full Rack. - Keyboard, Video and Mouse Network Cabling Tables
- Sun Integrated Lights Out Manager Cabling Tables
- Administrative Gigabit Ethernet Port Cabling Tables
- Single Phase Power Distribution Unit Cabling Tables
- Three Phase Power Distribution Unit Cabling Tables
- InfiniBand Network Cabling Tables
Parent topic: Cabling Information for Oracle Exadata Database Machine
20.1 Rack Layout Diagrams
The diagrams in this topic show the rack layout for Oracle Exadata Database Machine X2-2 and Oracle Exadata Database Machine X2-8 Full Rack.
Note:
For ease of reading, the name "Oracle Exadata Rack" is used when information refers to both Oracle Exadata Database Machine and Oracle Exadata Storage Expansion Rack.The following abbreviations are used in the tables:
Abbreviation | Description |
---|---|
Rn |
Rack n, where n is the number of the rack, such as R1. |
Un |
Unit height in rack, where n is the number, such as U20. |
Pn |
InfiniBand port n, where n is port number, such as P8A. |
The cables used in Oracle Exadata Database Machine are color-coded as follows:
- Black: InfiniBand cables, or AC power jumper cables
- Red: Integrated Lights Out Manager (ILOM) cables
- Blue: Gigabit Ethernet cables
- Orange: KVM switch cables (not used in Oracle Exadata Database Machine X2-8 Full Rack)
The following table shows the front and rear views of Oracle Exadata Database Machine X2-2 Full Rack. The front is shown on the left, and the rear is shown on the right.
Figure 20-1 Rack Layout of Oracle Exadata Database Machine X2-2 Full Rack
Description of "Figure 20-1 Rack Layout of Oracle Exadata Database Machine X2-2 Full Rack "
The following table shows the front and rear views of Oracle Exadata Database Machine X2-2 Half Rack.
Note:
The Sun Datacenter InfiniBand Switch 36 switch in rack position U1 is included in Oracle Exadata Database Machine X2-2 Half Racks with the Sun Fire X4170 M2 Oracle Database Servers.Figure 20-2 Rack Layout for Oracle Exadata Database Machine X2-2 Half Rack
Description of "Figure 20-2 Rack Layout for Oracle Exadata Database Machine X2-2 Half Rack "
The following table shows the front and rear views of Oracle Exadata Database Machine X2-2 Quarter Rack.
Figure 20-3 Rack Layout of Oracle Exadata Database Machine X2-2 Quarter Rack
Description of "Figure 20-3 Rack Layout of Oracle Exadata Database Machine X2-2 Quarter Rack"
The following table shows the front and rear views of Oracle Exadata Database Machine X2-8 Full Rack.
Figure 20-4 Rack Layout of Oracle Exadata Database Machine X2-8 Full Rack
Description of "Figure 20-4 Rack Layout of Oracle Exadata Database Machine X2-8 Full Rack"
20.2 Keyboard, Video and Mouse Network Cabling Tables
This section contains the tables for the keyboard, video and mouse (KVM) network cabling. The KVM port on the servers is labeled SER MGT, and connects to the KVM switch is located in rack unit 22. The following tables are in this section:
Table 20-1 shows the cable connections from the servers to the KVM switch in Oracle Exadata Database Machine X2-2 Full Rack:
Table 20-1 KVM Cabling for Oracle Exadata Database Machine X2-2 Full Rack
From Rack Unit | Type of Equipment | KVM Port |
---|---|---|
U41 |
Exadata Storage Server |
1 |
U39 |
Exadata Storage Server |
2 |
U37 |
Exadata Storage Server |
3 |
U35 |
Exadata Storage Server |
4 |
U33 |
Exadata Storage Server |
5 |
U31 |
Exadata Storage Server |
6 |
U29 |
Exadata Storage Server |
7 |
U28 |
Database server |
8 |
U27 |
Database server |
9 |
U26 |
Database server |
10 |
U25 |
Database server |
11 |
U19 |
Database server |
12 |
U18 |
Database server |
13 |
U17 |
Database server |
14 |
U16 |
Database server |
15 |
U14 |
Exadata Storage Server |
16 |
U12 |
Exadata Storage Server |
17 |
U10 |
Exadata Storage Server |
18 |
U8 |
Exadata Storage Server |
19 |
U6 |
Exadata Storage Server |
20 |
U4 |
Exadata Storage Server |
21 |
U2 |
Exadata Storage Server |
22 |
Table 20-2 shows the cable connections from the servers to the KVM switch in Oracle Exadata Database Machine X2-2 Half Rack:
Table 20-2 KVM Cabling for Oracle Exadata Database Machine X2-2 Half Rack
From Rack Unit | Type of Equipment | KVM Port |
---|---|---|
U19 |
Database server |
12 |
U18 |
Database server |
13 |
U17 |
Database server |
14 |
U16 |
Database server |
15 |
U14 |
Exadata Storage Server |
16 |
U12 |
Exadata Storage Server |
17 |
U10 |
Exadata Storage Server |
18 |
U8 |
Exadata Storage Server |
19 |
U6 |
Exadata Storage Server |
20 |
U4 |
Exadata Storage Server |
21 |
U2 |
Exadata Storage Server |
22 |
Table 20-3 shows the cable connections from the servers to the KVM switch in Oracle Exadata Database Machine X2-2 Quarter Rack:
Table 20-3 KVM Cabling for Oracle Exadata Database Machine X2-2 Quarter Rack
From Rack Unit | Type of Equipment | KVM Port |
---|---|---|
U17 |
Database server |
14 |
U16 |
Database server |
15 |
U6 |
Exadata Storage Server |
20 |
U4 |
Exadata Storage Server |
21 |
U2 |
Exadata Storage Server |
22 |
20.3 Sun Integrated Lights Out Manager Cabling Tables
This section contains the tables for the Sun Integrated Lights Out Manager (ILOM) network cabling. The ILOM port on the servers is labeled NET MGT, and connects to the Gigabit Ethernet port located in rack unit 21 on Oracle Exadata Database Machine X2-2 racks. The ILOM port connects to the Gigabit Ethernet port located in rack unit 22 on Oracle Exadata Database Machine X2-8 Full Rack racks.
The following tables are in this section:
Table 20-4 shows the cable connections from the servers to the ILOM switch in Oracle Exadata Database Machine X2-2 Full Rack:
Table 20-4 ILOM Cabling for Oracle Exadata Database Machine X2-2 Full Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U41 |
Exadata Storage Server |
2 |
U39 |
Exadata Storage Server |
4 |
U37 |
Exadata Storage Server |
6 |
U35 |
Exadata Storage Server |
8 |
U33 |
Exadata Storage Server |
10 |
U31 |
Exadata Storage Server |
12 |
U29 |
Exadata Storage Server |
14 |
U28 |
Database server |
16 |
U27 |
Database server |
18 |
U26 |
Database server |
20 |
U25 |
Database server |
22 |
U19 |
Database server |
24 |
U18 |
Database server |
26 |
U17 |
Database server |
28 |
U16 |
Database server |
30 |
U14 |
Exadata Storage Server |
32 |
U12 |
Exadata Storage Server |
34 |
U10 |
Exadata Storage Server |
36 |
U8 |
Exadata Storage Server |
38 |
U6 |
Exadata Storage Server |
40 |
U4 |
Exadata Storage Server |
42 |
U2 |
Exadata Storage Server |
44 |
Table 20-5 shows the cable connections from the servers to the ILOM switch in Oracle Exadata Database Machine X2-2 Half Rack:
Table 20-5 ILOM Cabling for Oracle Exadata Database Machine X2-2 Half Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U19 |
Database server |
24 |
U18 |
Database server |
26 |
U17 |
Database server |
28 |
U16 |
Database server |
30 |
U14 |
Exadata Storage Server |
32 |
U12 |
Exadata Storage Server |
34 |
U10 |
Exadata Storage Server |
36 |
U8 |
Exadata Storage Server |
38 |
U6 |
Exadata Storage Server |
40 |
U4 |
Exadata Storage Server |
42 |
U2 |
Exadata Storage Server |
44 |
Table 20-6 shows the cable connections from the servers to the ILOM switch in Oracle Exadata Database Machine X2-2 Quarter Rack:
Table 20-6 ILOM Cabling for Oracle Exadata Database Machine X2-2 Quarter Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U17 |
Database server |
28 |
U16 |
Database server |
30 |
U6 |
Exadata Storage Server |
40 |
U4 |
Exadata Storage Server |
42 |
U2 |
Exadata Storage Server |
44 |
Table 20-7 shows the cable connections from the servers to the ILOM switch in Oracle Exadata Database Machine X2-8 Full Rack:
Table 20-7 ILOM Cabling for Oracle Exadata Database Machine X2-8 Full Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U41 |
Exadata Storage Server |
2 |
U39 |
Exadata Storage Server |
4 |
U37 |
Exadata Storage Server |
6 |
U35 |
Exadata Storage Server |
8 |
U33 |
Exadata Storage Server |
10 |
U31 |
Exadata Storage Server |
12 |
U29 |
Exadata Storage Server |
14 |
U24 |
Database server |
16 |
U16 |
Database server |
18 |
U14 |
Exadata Storage Server |
20 |
U12 |
Exadata Storage Server |
22 |
U10 |
Exadata Storage Server |
24 |
U8 |
Exadata Storage Server |
26 |
U6 |
Exadata Storage Server |
28 |
U4 |
Exadata Storage Server |
30 |
U2 |
Exadata Storage Server |
32 |
20.4 Administrative Gigabit Ethernet Port Cabling Tables
This section contains the tables for the administrative Gigabit Ethernet network cabling. The Gigabit Ethernet switch is located in rack unit 21 on Oracle Exadata Database Machine X2-2 racks. The Gigabit Ethernet switch is located in rack unit 22 on Oracle Exadata Database Machine X2-8 Full Rack racks.
The following tables are in this section:
Table 20-8 shows the cable connections from the servers to the Gigabit Ethernet switch in Oracle Exadata Database Machine X2-2 Full Rack:
Table 20-8 Gigabit Ethernet Cabling for Oracle Exadata Database Machine X2-2 Full Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U41 |
Exadata Storage Server |
1 |
U39 |
Exadata Storage Server |
3 |
U37 |
Exadata Storage Server |
5 |
U35 |
Exadata Storage Server |
7 |
U33 |
Exadata Storage Server |
9 |
U31 |
Exadata Storage Server |
11 |
U29 |
Exadata Storage Server |
13 |
U28 |
Database server |
15 |
U27 |
Database server |
17 |
U26 |
Database server |
19 |
U25 |
Database server |
21 |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
45 |
U20 |
Sun Datacenter InfiniBand Switch 36 switch |
46 |
U19 |
Database server |
23 |
U18 |
Database server |
25 |
U17 |
Database server |
27 |
U16 |
Database server |
29 |
U14 |
Exadata Storage Server |
31 |
U12 |
Exadata Storage Server |
33 |
U10 |
Exadata Storage Server |
35 |
U8 |
Exadata Storage Server |
37 |
U6 |
Exadata Storage Server |
39 |
U4 |
Exadata Storage Server |
41 |
U2 |
Exadata Storage Server |
43 |
U1 |
Sun Datacenter InfiniBand Switch 36 switch |
47 |
Table 20-9 shows the cable connections from the servers to the Gigabit Ethernet switch in Oracle Exadata Database Machine X2-2 Half Rack:
Table 20-9 Gigabit Ethernet Cabling for Oracle Exadata Database Machine X2-2 Half Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
45 |
U20 |
Sun Datacenter InfiniBand Switch 36 switch |
46 |
U19 |
Database server |
23 |
U18 |
Database server |
25 |
U17 |
Database server |
27 |
U16 |
Database server |
29 |
U14 |
Exadata Storage Server |
31 |
U12 |
Exadata Storage Server |
33 |
U10 |
Exadata Storage Server |
35 |
U8 |
Exadata Storage Server |
37 |
U6 |
Exadata Storage Server |
39 |
U4 |
Exadata Storage Server |
41 |
U2 |
Exadata Storage Server |
43 |
U1 |
Sun Datacenter InfiniBand Switch 36 switch |
47 |
Table 20-10 shows the cable connections from the servers to the Gigabit Ethernet switch in Oracle Exadata Database Machine X2-2 Quarter Rack:
Table 20-10 Gigabit Ethernet Cabling for Oracle Exadata Database Machine X2-2 Quarter Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
45 |
U20 |
Sun Datacenter InfiniBand Switch 36 switch |
46 |
U17 |
Database server |
27 |
U16 |
Database server |
29 |
U6 |
Exadata Storage Server |
39 |
U4 |
Exadata Storage Server |
41 |
U2 |
Exadata Storage Server |
43 |
Table 20-11 shows the cable connections from the servers to the Gigabit Ethernet switch in Oracle Exadata Database Machine X2-8 Full Rack:
Table 20-11 Gigabit Ethernet Cabling for Oracle Exadata Database Machine X2-8 Full Rack
From Rack Unit | Type of Equipment | Gigabit Ethernet Port |
---|---|---|
U41 |
Exadata Storage Server |
1 |
U39 |
Exadata Storage Server |
3 |
U37 |
Exadata Storage Server |
5 |
U35 |
Exadata Storage Server |
7 |
U33 |
Exadata Storage Server |
9 |
U31 |
Exadata Storage Server |
11 |
U29 |
Exadata Storage Server |
13 |
U24 |
Database server |
15 |
U23 |
Sun Datacenter InfiniBand Switch 36 |
33 |
U21 |
Sun Datacenter InfiniBand Switch 36 |
34 |
U16 |
Database server |
17 |
U14 |
Exadata Storage Server |
19 |
U12 |
Exadata Storage Server |
21 |
U10 |
Exadata Storage Server |
23 |
U8 |
Exadata Storage Server |
25 |
U6 |
Exadata Storage Server |
27 |
U4 |
Exadata Storage Server |
29 |
U2 |
Exadata Storage Server |
31 |
U1 |
Sun Datacenter InfiniBand Switch 36 |
35 |
20.5 Single Phase Power Distribution Unit Cabling Tables
This section contains the tables for single phase cabling from each power distribution unit (PDU) to the power supplies configured in each rack. The cables are terminated to PDU-A on the left, and routed to the right to enter CMA, and are bundled in groups of four.
The following tables are in this section:
Table 20-12 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-2 Full Rack.
Table 20-12 Single Phase PDU Cabling for Oracle Exadata Database Machine X2-2 Full Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U41 |
G5-6 |
G0-0 |
2 meters |
U39 |
G5-3 |
G0-3 |
2 meters |
U37 |
G5-0 |
G0-6 |
2 meters |
U35 |
G4-6 |
G1-0 |
2 meters |
U33 |
G4-4 |
G1-2 |
2 meters |
U31 |
G4-2 |
G1-4 |
2 meters |
U29 |
G3-6 |
G2-0 |
2 meters |
U28 |
G4-0 |
G1-6 |
2 meters |
U27 |
G3-5 |
G2-1 |
2 meters |
U26 |
G3-4 |
G2-2 |
2 meters |
U25 |
G3-3 |
G2-3 |
2 meters |
U24 |
G3-1 |
G2-5 |
1 meters |
U23 |
N/A |
G3-0 |
included |
U22 |
G2-5 |
G3-1 |
2 meter |
U21 |
G3-0 |
G2-6 |
2 meters |
U20 |
G2-4 |
G3-2 |
2 meters |
U19 |
G2-3 |
G3-3 |
2 meters |
U18 |
G2-2 |
G3-4 |
2 meters |
U17 |
G2-1 |
G3-5 |
2 meters |
U16 |
G1-6 |
G4-0 |
2 meters |
U14 |
G2-0 |
G3-6 |
2 meters |
U12 |
G1-4 |
G4-2 |
2 meters |
U10 |
G1-2 |
G4-4 |
2 meters |
U8 |
G1-0 |
G4-6 |
2 meters |
U6 |
G0-6 |
G5-0 |
2 meters |
U4 |
G0-4 |
G5-2 |
2 meters |
U2 |
G0-2 |
G5-4 |
2 meters |
U1 |
G0-0 |
G5-6 |
2 meters |
Table 20-13 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-2 Half Rack.
Table 20-13 Single Phase PDU Cabling for Oracle Exadata Database Machine X2-2 Half Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U24 |
G3-1 |
G2-5 |
1 meters |
U23 |
N/A |
G3-0 |
included |
U22 |
G2-5 |
G3-1 |
2 meter |
U21 |
G3-0 |
G2-6 |
2 meters |
U20 |
G2-4 |
G3-2 |
2 meters |
U19 |
G2-3 |
G3-3 |
2 meters |
U18 |
G2-2 |
G3-4 |
2 meters |
U17 |
G2-1 |
G3-5 |
2 meters |
U16 |
G1-6 |
G4-0 |
2 meters |
U14 |
G2-0 |
G3-6 |
2 meters |
U12 |
G1-4 |
G4-2 |
2 meters |
U10 |
G1-2 |
G4-4 |
2 meters |
U8 |
G1-0 |
G4-6 |
2 meters |
U6 |
G0-6 |
G5-0 |
2 meters |
U4 |
G0-4 |
G5-2 |
2 meters |
U2 |
G0-2 |
G5-4 |
2 meters |
U1 |
G0-0 |
G5-6 |
2 meters |
Table 20-14 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-2 Quarter Rack.
Table 20-14 Single Phase PDU Cabling for Oracle Exadata Database Machine X2-2 Quarter Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U24 |
G3-1 |
G2-5 |
1 meters |
U23 |
N/A |
G3-0 |
included |
U22 |
G2-5 |
G3-1 |
2 meter |
U21 |
G3-0 |
G2-6 |
2 meters |
U20 |
G2-4 |
G3-2 |
2 meters |
U17 |
G2-1 |
G3-5 |
2 meters |
U16 |
G1-6 |
G4-0 |
2 meters |
U6 |
G0-6 |
G5-0 |
2 meters |
U4 |
G0-4 |
G5-2 |
2 meters |
U2 |
G0-2 |
G5-4 |
2 meters |
U1 |
G0-0 |
G5-6 |
2 meters |
Table 20-15 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-8 Full Rack.
Table 20-15 Single Phase PDU Cabling for Oracle Exadata Database Machine X2-8 Full Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U41 |
G5-6 |
G0-0 |
2 meters |
U39 |
G5-4 |
G0-2 |
2 meters |
U37 |
G5-2 |
G0-4 |
2 meters |
U35 |
G5-0 |
G0-6 |
2 meters |
U33 |
G4-6 |
G1-0 |
2 meters |
U31 |
G4-3 |
G1-3 |
2 meters |
U29 |
G3-6 |
G2-0 |
2 meters |
U24 |
G4-0 |
G1-6 |
1 meter |
U24 |
G3-5 |
G2-1 |
1 meter |
U23 |
G3-1 |
G2-5 |
2 meters |
U22 |
G2-6 |
G3-0 |
2 meters |
U21 |
G3-0 |
G2-6 |
2 meters |
U16 |
G2-1 |
G3-5 |
1 meter |
U16 |
G1-6 |
G4-0 |
1 meter |
U14 |
G2-0 |
G3-6 |
2 meters |
U12 |
G1-3 |
G4-3 |
2 meters |
U10 |
G1-0 |
G4-6 |
2 meters |
U8 |
G0-6 |
G5-0 |
2 meters |
U6 |
G0-4 |
G5-2 |
2 meters |
U4 |
G0-3 |
G5-3 |
2 meters |
U2 |
G0-1 |
G5-5 |
2 meters |
U1 |
G0-0 |
G5-6 |
2 meters |
20.6 Three Phase Power Distribution Unit Cabling Tables
This section contains the tables for three phase cabling from each power distribution unit (PDU) to the power supplies configured in each rack. The cables are terminated to PDU-A on the left, and routed to the right to enter CMA, and are bundled in groups of four.
The following tables are in this section:
Table 20-16 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-2 Full Rack.
Table 20-16 Three Phase PDU Cabling for Oracle Exadata Database Machine X2-2 Full Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U41 |
G5-6 |
G2-0 |
2 meters |
U39 |
G5-3 |
G2-3 |
2 meters |
U37 |
G5-0 |
G2-6 |
2 meters |
U35 |
G4-6 |
G1-0 |
2 meters |
U33 |
G4-4 |
G1-2 |
2 meters |
U31 |
G4-2 |
G1-4 |
2 meters |
U29 |
G3-6 |
G0-0 |
2 meters |
U28 |
G4-0 |
G1-6 |
2 meters |
U27 |
G3-5 |
G0-1 |
2 meters |
U26 |
G3-4 |
G0-2 |
2 meters |
U25 |
G3-3 |
G0-3 |
2 meters |
U24 |
G3-1 |
G0-5 |
1 meters |
U23 |
N/A |
G5-0 |
included |
U22 |
G2-5 |
G5-1 |
2 meter |
U21 |
G3-0 |
G0-6 |
2 meters |
U20 |
G2-4 |
G5-2 |
2 meters |
U19 |
G2-3 |
G5-3 |
2 meters |
U18 |
G2-2 |
G5-4 |
2 meters |
U17 |
G2-1 |
G5-5 |
2 meters |
U16 |
G1-6 |
G4-0 |
2 meters |
U14 |
G2-0 |
G5-6 |
2 meters |
U12 |
G1-4 |
G4-2 |
2 meters |
U10 |
G1-2 |
G4-4 |
2 meters |
U8 |
G1-0 |
G4-6 |
2 meters |
U6 |
G0-6 |
G3-0 |
2 meters |
U4 |
G0-4 |
G3-2 |
2 meters |
U2 |
G0-2 |
G3-4 |
2 meters |
U1 |
G0-0 |
G3-6 |
2 meters |
Table 20-17 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-2 Half Rack.
Table 20-17 Three Phase PDU Cabling for Oracle Exadata Database Machine X2-2 Half Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U24 |
G3-1 |
G0-5 |
1 meters |
U23 |
N/A |
G5-0 |
included |
U22 |
G2-5 |
G5-1 |
2 meter |
U21 |
G3-0 |
G0-6 |
2 meters |
U20 |
G2-4 |
G5-2 |
2 meters |
U19 |
G2-3 |
G5-3 |
2 meters |
U18 |
G2-2 |
G5-4 |
2 meters |
U17 |
G2-1 |
G5-5 |
2 meters |
U16 |
G1-6 |
G4-0 |
2 meters |
U14 |
G2-0 |
G5-6 |
2 meters |
U12 |
G1-4 |
G4-2 |
2 meters |
U10 |
G1-2 |
G4-4 |
2 meters |
U8 |
G1-0 |
G4-6 |
2 meters |
U6 |
G0-6 |
G3-0 |
2 meters |
U4 |
G0-4 |
G3-2 |
2 meters |
U2 |
G0-2 |
G3-4 |
2 meters |
U1 |
G0-0 |
G3-6 |
2 meters |
Table 20-18 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-2 Quarter Rack.
Table 20-18 Three Phase PDU Cabling for Oracle Exadata Database Machine X2-2 Quarter Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U24 |
G3-1 |
G0-5 |
1 meters |
U23 |
N/A |
G5-0 |
included |
U22 |
G2-5 |
G5-1 |
2 meter |
U21 |
G3-0 |
G0-6 |
2 meters |
U20 |
G2-4 |
G5-2 |
2 meters |
U17 |
G2-1 |
G5-5 |
2 meters |
U16 |
G1-6 |
G4-0 |
2 meters |
U6 |
G0-6 |
G3-0 |
2 meters |
U4 |
G0-4 |
G3-2 |
2 meters |
U2 |
G0-2 |
G3-4 |
2 meters |
U1 |
G0-0 |
G3-6 |
2 meters |
Table 20-19 shows the cable connections from the PDUs to the rack units in Oracle Exadata Database Machine X2-8 Full Rack.
Table 20-19 Three Phase PDU Cabling for Oracle Exadata Database Machine X2-8 Full Rack
Rack Unit | PDU-A/PS-00 | PDU-B/PS-01 | Cable Length |
---|---|---|---|
U41 |
G5-5 |
G2-1 |
2 meters |
U39 |
G5-4 |
G2-2 |
2 meters |
U37 |
G5-2 |
G2-4 |
2 meters |
U35 |
G5-1 |
G2-5 |
2 meters |
U33 |
G5-0 |
G2-6 |
2 meters |
U31 |
G4-6 |
G1-0 |
2 meters |
U29 |
G4-4 |
G1-2 |
2 meters |
U24 |
G4-1 |
G1-5 |
1 meter |
U24 |
G3-6 |
G0-0 |
1 meter |
U23 |
G3-3 |
G0-3 |
2 meters |
U22 |
G3-0 |
G0-6 |
2 meters |
U21 |
G2-5 |
G5-1 |
2 meters |
U16 |
G2-1 |
G5-5 |
1 meter |
U16 |
G1-6 |
G4-0 |
1 meter |
U14 |
G1-3 |
G4-3 |
2 meters |
U12 |
G1-0 |
G4-6 |
2 meters |
U10 |
G0-6 |
G3-0 |
2 meters |
U8 |
G0-5 |
G3-1 |
2 meters |
U6 |
G0-4 |
G3-2 |
2 meters |
U4 |
G0-2 |
G3-4 |
2 meters |
U2 |
G0-1 |
G3-5 |
2 meters |
U1 |
G0-0 |
G3-6 |
2 meters |
20.7 InfiniBand Network Cabling Tables
This section contains the tables for the InfiniBand network cabling. The Sun Datacenter InfiniBand Switch 36 switches are located in located in rack unit 1, 20 and 24.
The following tables are in this section:
Table 20-20 lists the location, ports and cables for the InfiniBand connections for Oracle Exadata Database Machine X2-2 Full Rack.
Table 20-20 InfiniBand Network Cabling for Oracle Exadata Database Machine X2-2 Full Rack
From InfiniBand Switch Rack Unit | Port | To Rack Unit | Type of Equipment | Port | Cable Description |
---|---|---|---|---|---|
U24 |
0A |
U41 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
0B |
U39 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
1A |
U37 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
1B |
U35 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
2A |
U33 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
2B |
U31 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
3A |
U29 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
3B |
U28 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U24 |
4A |
U27 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U24 |
4B |
U26 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U24 |
5A |
U25 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U24 |
12B |
U19 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
13A |
U18 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
13B |
U17 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
14A |
U16 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
14B |
U14 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
15A |
U12 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
15B |
U10 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
16A |
U8 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
0A |
U41 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
0B |
U39 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
1A |
U37 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
1B |
U35 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
2A |
U33 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
2B |
U31 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
3A |
U29 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
3B |
U28 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U20 |
4A |
U27 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U20 |
4B |
U26 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U20 |
5A |
U25 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U20 |
12B |
U19 |
Database Server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
13A |
U18 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
13B |
U17 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
14A |
U16 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
14B |
U14 |
Exadata Storage Server |
PCIe 3, P1 |
2 meter QDR InfiniBand cable |
U20 |
15A |
U12 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
15B |
U10 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
16A |
U8 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U24 |
8B |
U1 |
Sun Datacenter InfiniBand Switch 36 switch |
0B |
3 meter QDR InfiniBand cable |
U20 |
8B |
U1 |
Sun Datacenter InfiniBand Switch 36 switch |
1B |
3 meter QDR InfiniBand cable |
U20 |
9B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
9A |
1 meter QDR InfiniBand cable |
U20 |
10B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
10A |
1 meter QDR InfiniBand cable |
U20 |
11B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
11A |
1 meter QDR InfiniBand cable |
U20 |
8A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
8A |
1 meter QDR InfiniBand cable |
U20 |
9A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
9B |
1 meter QDR InfiniBand cable |
U20 |
10A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
10B |
1 meter QDR InfiniBand cable |
U20 |
11A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
11B |
1 meter QDR InfiniBand cable |
U1 |
1B |
U20 |
Sun Datacenter InfiniBand Switch 36 switch |
8B |
3 meter QDR InfiniBand cable |
U1 |
0B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
8B |
3 meter QDR InfiniBand cable |
Table 20-21 lists the location, ports and cables for the InfiniBand connections for Oracle Exadata Database Machine X2-2 Half Rack.
Note:
The Sun Datacenter InfiniBand Switch 36 switch in rack position U1 is included in Oracle Exadata Database Machine X2-2 Half Racks with Sun Fire X4170 M2 Oracle Database Servers.
Table 20-21 InfiniBand Network Cabling for Oracle Exadata Database Machine X2-2 Half Rack
From InfiniBand Switch Rack Unit | Port | To Rack Unit | Type of Equipment | Port | Cable Description |
---|---|---|---|---|---|
U24 |
12B |
U19 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
13A |
U18 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
13B |
U17 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
14A |
U16 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
14B |
U14 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
15A |
U12 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
15B |
U10 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
16A |
U8 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
12B |
U19 |
Database Server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
13A |
U18 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
13B |
U17 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
14A |
U16 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
14B |
U14 |
Exadata Storage Server |
PCIe 3, P1 |
2 meter QDR InfiniBand cable |
U20 |
15A |
U12 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
15B |
U10 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
16A |
U8 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
9B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
9A |
1 meter QDR InfiniBand cable |
U20 |
10B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
10A |
1 meter QDR InfiniBand cable |
U20 |
11B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
11A |
1 meter QDR InfiniBand cable |
U20 |
8A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
8A |
1 meter QDR InfiniBand cable |
U20 |
9A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
9B |
1 meter QDR InfiniBand cable |
U20 |
10A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
10B |
1 meter QDR InfiniBand cable |
U20 |
11A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
11B |
1 meter QDR InfiniBand cable |
U1 |
1B |
U20 |
Sun Datacenter InfiniBand Switch 36 switch |
8B |
3 meter QDR InfiniBand cable |
U1 |
0B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
8B |
3 meter QDR InfiniBand cable |
Table 20-22 lists the location, ports and cables for the InfiniBand connections for Oracle Exadata Database Machine X2-2 Quarter Rack.
Table 20-22 InfiniBand Network Cabling for Oracle Exadata Database Machine X2-2 Quarter Rack
From InfiniBand Switch Rack Unit | Port | To Rack Unit | Type of Equipment | Port | Cable Description |
---|---|---|---|---|---|
U24 |
13B |
U17 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
14A |
U16 |
Database server |
PCIe 2, P2 |
2 meter QDR InfiniBand cable |
U24 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U24 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U20 |
13B |
U17 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
14A |
U16 |
Database server |
PCIe 2, P1 |
2 meter QDR InfiniBand cable |
U20 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U20 |
9B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
9A |
1 meter QDR InfiniBand cable |
U20 |
10B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
10A |
1 meter QDR InfiniBand cable |
U20 |
11B |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
11A |
1 meter QDR InfiniBand cable |
U20 |
8A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
8A |
1 meter QDR InfiniBand cable |
U20 |
9A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
9B |
1 meter QDR InfiniBand cable |
U20 |
10A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
10B |
1 meter QDR InfiniBand cable |
U20 |
11A |
U24 |
Sun Datacenter InfiniBand Switch 36 switch |
11B |
1 meter QDR InfiniBand cable |
Table 20-23 lists the location, ports and cables for the InfiniBand connections for Oracle Exadata Database Machine X2-8 Full Rack.
Table 20-23 InfiniBand Network Cabling for Oracle Exadata Database Machine X2-8 Full Rack
From InfiniBand Switch Rack Unit | Port | To Rack Unit | Type of Equipment | Port | Cable Description |
---|---|---|---|---|---|
U23 |
0A |
U41 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
0B |
U39 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
1A |
U37 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
1B |
U35 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
2A |
U33 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
2B |
U31 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
3A |
U29 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
3B |
U24 |
Database server |
EM-3.0 P-O |
2 meter QDR InfiniBand cable |
U23 |
4A |
U24 |
Database server |
EM-2.0 P-O |
2 meter QDR InfiniBand cable |
U23 |
4B |
U24 |
Database server |
EM-1.0 P-O |
2 meter QDR InfiniBand cable |
U23 |
5A |
U24 |
Database server |
EM-0.0 P-O |
2 meter QDR InfiniBand cable |
U23 |
13A |
U16 |
Database server |
EM-2.0 P-1 |
2 meter QDR InfiniBand cable |
U23 |
13B |
U16 |
Database server |
EM-1.0 P-1 |
2 meter QDR InfiniBand cable |
U23 |
14A |
U16 |
Database server |
EM-0.0 P-1 |
2 meter QDR InfiniBand cable |
U23 |
12B |
U16 |
Database server |
EM-3.0 P-1 |
2 meter QDR InfiniBand cable |
U23 |
14B |
U14 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U23 |
15A |
U12 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U23 |
15B |
U10 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U23 |
16A |
U8 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U23 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U23 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U23 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
0A |
U41 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
0B |
U39 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
1A |
U37 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
1B |
U35 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
2A |
U33 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
2B |
U31 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
3A |
U29 |
Exadata Storage Server |
PCIe 3, P2 |
3 meter QDR InfiniBand cable |
U21 |
3B |
U24 |
Database server |
EM-3.0 P-1 |
2 meter QDR InfiniBand cable |
U21 |
4A |
U24 |
Database server |
EM-2.0 P-1 |
2 meter QDR InfiniBand cable |
U21 |
4B |
U24 |
Database server |
EM-1.0 P-1 |
2 meter QDR InfiniBand cable |
U21 |
5A |
U24 |
Database server |
EM-0.0 P-1 |
2 meter QDR InfiniBand cable |
U21 |
12B |
U16 |
Database Server |
EM-3.0 P-O |
2 meter QDR InfiniBand cable |
U21 |
13A |
U16 |
Database server |
EM-2.0 P-O |
2 meter QDR InfiniBand cable |
U21 |
13B |
U16 |
Database server |
EM-1.0 P-O |
2 meter QDR InfiniBand cable |
U21 |
14A |
U16 |
Database server |
EM-0.0 P-O |
2 meter QDR InfiniBand cable |
U21 |
14B |
U14 |
Exadata Storage Server |
PCIe 3, P1 |
2 meter QDR InfiniBand cable |
U21 |
15A |
U12 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U21 |
15B |
U10 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U21 |
16A |
U8 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U21 |
16B |
U6 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U21 |
17A |
U4 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U21 |
17B |
U2 |
Exadata Storage Server |
PCIe 3, P1 |
3 meter QDR InfiniBand cable |
U23 |
8B |
U1 |
Sun Datacenter InfiniBand Switch 36 switch |
0B |
3 meter QDR InfiniBand cable |
U21 |
8B |
U1 |
Sun Datacenter InfiniBand Switch 36 switch |
1B |
3 meter QDR InfiniBand cable |
U21 |
9B |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
9A |
1 meter QDR InfiniBand cable |
U21 |
10B |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
10A |
1 meter QDR InfiniBand cable |
U21 |
11B |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
11A |
1 meter QDR InfiniBand cable |
U21 |
8A |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
8A |
1 meter QDR InfiniBand cable |
U21 |
9A |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
9B |
1 meter QDR InfiniBand cable |
U21 |
10A |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
10B |
1 meter QDR InfiniBand cable |
U21 |
11A |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
11B |
1 meter QDR InfiniBand cable |
U1 |
1B |
U21 |
Sun Datacenter InfiniBand Switch 36 switch |
8B |
3 meter QDR InfiniBand cable |
U1 |
0B |
U23 |
Sun Datacenter InfiniBand Switch 36 switch |
8B |
3 meter QDR InfiniBand cable |