| Oracle® Big Data Appliance Owner's Guide Release 1 (1.0.3) Part Number E25960-03 |
|
|
PDF · Mobi · ePub |
This chapter describes the site requirements for Oracle Big Data Appliance. Use this chapter when completing the Oracle Big Data Appliance Site Checklists.
This chapter contains these topics:
Table 2-1 shows the general environmental. The other sections in this chapter provide detailed information.
Table 2-1 Environmental Requirements for Oracle Big Data Appliance
| Environmental Component | Oracle Big Data Appliance |
|---|---|
|
Weight |
909.5 kg (2005 lbs) See Also: "Flooring Requirements" |
|
Acoustic levels |
8.3 B |
|
Power |
Maximum: 12.0 kW (12.25 kVA) Typical: 8.4 kW (8.6 kVA)Foot 1 See Also: "Electrical Power Requirements" |
|
Cooling |
Maximum: 40,971 BTU/hour (41,807 kJ/hour) Typical: 28,680 BTU/hour (29,265 kJ/hour) See Also: "Temperature and Humidity Requirements" and "Ventilation and Cooling Requirements" |
|
Air flow front-to-back (subject to actual data center environment) |
Maximum: Approximately 1,886 CFM Typical: Approximately 1,340 CFM See Also: "Temperature and Humidity Requirements", and "Ventilation and Cooling Requirements" |
|
IP Addresses |
24 for Ethernet network 18 for InfiniBand network See Also: Chapter 3, "Network Requirements." |
|
Network drops |
Minimum of 2 network drops See Also: Chapter 3, "Network Requirements." |
|
External connectivity |
2 x 1 GbE Ethernet ports 18 x 10 GbE Ethernet ports See Also: Chapter 3, "Network Requirements." |
Footnote 1 Varies based on application load.
The space requirements for Oracle Big Data Appliance are as follows:
Height: 1998 mm (78.66 inches)
Width: 600 mm with side panels (23.62 inches)
Depth: 1200 mm (47.24 inches)
The minimum ceiling height for the cabinet is 2300 mm (90 inches), measured from the true floor or raised floor, whichever is higher. An additional 914 mm (36 inches) is for top clearance. The space above the cabinet and its surroundings must not restrict the movement of cool air between the air conditioner and the cabinet, or the movement of hot air coming out of the top of the cabinet.
Before Oracle Big Data Appliance arrives, ensure that the receiving area is large enough for the package. The following are the package specifications:
Shipping height: 2159 mm (85 inches)
Shipping width: 1219 mm (48 inches)
Shipping depth: 1575 mm (62 inches)
Shipping weight: 993 kgs. (2189 lbs.)
Net weight: 909.5 kgs. (2005 lbs.)
If your loading dock meets the height and ramp requirements for a standard freight carrier truck, then you can use a pallet jack to unload the rack. If not, you must provide a standard forklift or other means to unload the rack. You can also request that the rack be shipped in a truck with a lift gate.
Leave Oracle Big Data Appliance in its shipping container until it arrives at the installation site. Ensure sufficient clearance and clear pathways for moving it from the unpacking location to the installation location. The entire access route to the installation site should be free of raised-pattern flooring that can cause vibration.
Use a conditioned space when removing the packaging material to reduce particles before entering the data center. Allow enough space for unpacking Oracle Big Data Appliance from its shipping cartons. Table 2-2 lists the access route requirements.
Table 2-2 Access Route Requirements for Oracle Big Data Appliance
| Access Route Item | With Shipping Pallet | Without Shipping Pallet |
|---|---|---|
|
Minimum door height |
2184 mm (86 inches) |
2040 mm (80.32 inches) |
|
Minimum door width |
1270 (50 inches) |
640 mm (25.19 inches) |
|
Minimum elevator depth |
1625.6 mm (64 inches) |
1240 mm (48.82 inches) |
|
Maximum incline |
6 degrees |
6 degrees |
|
Minimum elevator, pallet jack, and floor loading capacity |
1134 kg (2500 lbs) |
1134 kg (2500 lbs) |
The maintenance area must be large enough for Oracle Big Data Appliance and have the required access space. For example, the required space to remove the side panels is 675. 64 mm (26.6 inches). Table 2-3 lists the maintenance access requirements.
Open tiles are required for electrical access.
Oracle recommends that Oracle Big Data Appliance be installed on raised flooring. The site floor and the raised flooring must be able to support the total weight.
Table 2-4 lists the floor load requirements.
Table 2-4 Floor Load Requirements for Oracle Big Data Appliance
| Description | Requirement |
|---|---|
|
Maximum allowable weight of installed rack equipment |
997.9 kg (2200 lbs) |
|
Maximum allowable weight of installed power distribution units |
52.16 kg (115 lbs) |
|
Maximum dynamic load (maximum allowable weight of installed equipment including PDUs) |
1004.71 kg (2215 lbs) |
Oracle Big Data Appliance can operate effectively over a wide range of voltages and frequencies. However, it must have a reliable power source. Damage may occur if the ranges are exceeded. Electrical disturbances such as the following may damage Oracle Big Data Appliance:
Fluctuations caused by brownouts
Wide and rapid variations in input voltage levels or in input power frequency
Electrical storms
Faults in the distribution system, such as defective wiring
To protect Oracle Big Data Appliance from such disturbances, you should have a dedicated power distribution system, power-conditioning equipment, and lightning arresters or power cables to protect from electrical storms.
Each rack has two pre-installed power distribution units (PDUs). The PDUs accept different power sources. You must specify the type of PDU that is correct for your Oracle Big Data Appliance and data center.
The type of PDU depends on the location where Oracle Big Data Appliance is installed:
North America, South America, Japan, and Taiwan use low-voltage PDUs.
Europe, the Middle East and Africa (EMEA) use high-voltage PDUs.
Asia Pacific (APAC) except for Japan and Taiwan use high-voltage PDUs.
Refer to the appropriate sections for your location:
Table 2-5 lists the requirements for low-voltage one-phase PDUs for North America, South America, Japan, and Taiwan. There are two PDUs per rack.
Table 2-5 Low-Voltage 15 kVA Single-Phase PDUs
| Option | Requirement per PDU |
|---|---|
|
Number of inputs |
3 x 30 A single phase |
|
Voltage |
200 - 240 VAC |
|
Frequency |
50/60 Hz |
|
Current |
24 A maximum per input |
|
Power rating |
15 kVA |
|
Output current |
72 A (3 x 24 A) |
|
Outlets |
42 x C13; 6 x C19 |
|
Outlet groups |
6 |
|
Group protectionFoot 1 |
20A |
|
Data center receptacle |
15kVA, with three 30A/250V 2-pole/3-wire NEMA L6-30P plugs |
Footnote 1 UL489 2-pole circuit breaker
The following are needed to connect Oracle Big Data Appliance to a low-voltage single-phase power source:
6 power cords for two PDUs, 30 amps at 200 - 240 VAC
6 receptacles to connect the PDUs to 6 NEMA L6-30 data center receptacles
Table 2-5 shows the low-voltage, single-phase PDU power connector for North America, South America, Japan and Taiwan.
Figure 2-1 Low-Voltage, Single-Phase Power Connector

Table 2-6 lists the requirements for low-voltage three-phase PDUs for North America, South America, Japan, and Taiwan. There are two PDUs per rack.
Table 2-6 Low-Voltage 15 kVA Three-Phase PDUs
| Option | Requirement per PDU |
|---|---|
|
Number of inputs |
1 x 60 A three phase 4-wire |
|
Voltage |
190 - 220 VAC |
|
Frequency |
50/60 Hz |
|
Current |
40 A maximum per phase |
|
Power rating |
14.4 kVA |
|
Output current |
69 A (3 x 23 A) |
|
Outlets |
42 x C13; 6 x C19 |
|
Outlet groups |
6 |
|
Group protectionFoot 1 |
20A |
|
Data center receptacle |
15kVA IEC 60309 60A 4-pin 250VAC three phase IP67 |
Footnote 1 UL489 2-pole circuit breaker
The following are needed to connect Oracle Big Data Appliance to a low-voltage three-phase power source:
2 power cords for two PDUs, 60 amps at 190 - 220 VAC three-phase
2 receptacles to connect the PDUs to 2 IEC 60309 60A 4-pin 250VAC 3ph IP67 data center receptacles
Table 2-6 shows the low-voltage three-phase PDU power connector for North America, South America, Japan and Taiwan.
Figure 2-2 Low-Voltage Three-Phase Power Connector

Table 2-7 lists the requirements for 15 kVA high-voltage one-phase PDUs for Europe, the Middle East, Africa, and Asia Pacific, except Japan and Taiwan. There are two PDUs per rack.
Table 2-7 High-Voltage 15 kVA Single-Phase PDUs)
| Option | Requirement per PDU |
|---|---|
|
Number of inputs |
3 x 25 A single phase |
|
Voltage |
220-240 VAC |
|
Frequency |
50/60 Hz |
|
Current |
25 A maximum per input |
|
Power rating |
15 kVA |
|
Output current |
72 A (3 x 24 A) |
|
Outlets |
42 x C13; 6 x C19 |
|
Outlet groups |
6 |
|
Group protectionFoot 1 |
20A |
|
Data center receptacle |
15kVA, with three blue 32A/240V splash-proof 2-pole/3-wire IEC 60309 plugs |
Footnote 1 UL489 1-pole circuit breaker
The following are needed to connect Oracle Big Data Appliance to a high-voltage single-phase power source:
6 power cords for two PDUs, 25 amps at 220/380 - 240/415 VAC 1-phase voltage
6 receptacles to connect the PDUs to 2 IEC 60309 32A 3-pin 250VAC IP44 data center receptacles, and requires 22 kVA, 1-phase
Table 2-7 shows the high-voltage single-phase PDU power connector for EMEA and APAC, except for Japan and Taiwan.
Figure 2-3 High-Voltage Single-Phase Power Connector

Table 2-8 lists the requirements for high-voltage three-phase PDUs for Europe, the Middle East, Africa, and Asia Pacific, except Japan and Taiwan. There are two PDUs per rack. The following specifications are per PDU.
Table 2-8 High-Voltage 15 kVA Three-Phase PDUs
| Option | Requirement per PDU |
|---|---|
|
Number of inputs |
1 x 25 A three phase 5 wire |
|
Voltage |
220/380 - 240/415 VAC 3 ph |
|
Frequency |
50/60 Hz |
|
Current |
25 A maximum per phase |
|
Power rating |
14.4 kVA |
|
Output current |
62.7 A (3 x 20.9 A) |
|
Outlets |
42 x C13; 6 x C19 |
|
Outlet groups |
6 |
|
Group protectionFoot 1 |
20A |
|
Data center receptacle |
15kVA,three phase, 5-pin, IEC 60309 32A, 5-pin 230/400V, three phase IP44 |
Footnote 1 UL489 1-pole circuit breaker
The following are needed to connect Oracle Big Data Appliance to a high-voltage three-phase power source:
2 power cords for two PDUs, 25 amps at 220/380 - 240/415 VAC three-phase
2 receptacles to connect the PDUs to 2 IEC 60309 32A 5-pin 230/400VAC 3ph IP44 data center receptacles
Table 2-8 shows the high-voltage three-phase PDU power connector for EMEA and APAC, except for Japan and Taiwan.
Figure 2-4 High-Voltage Three-Phase Power Connector

Electrical work and installations must obey applicable local, state, or national electrical codes. Contact your facilities manager or qualified electrician to determine what type of power is supplied to the building.
To prevent catastrophic failures, design the input power sources to ensure adequate power is provided to the PDUs. Use dedicated AC breaker panels for all power circuits that supply power to the PDU. When planning for power distribution requirements, balance the power load between available AC supply branch circuits. In the United States and Canada, ensure that the overall system AC input current load does not exceed 80 percent of the branch circuit AC current rating.
PDU power cords are 4 meters (13.12 feet) long, and 1 to 1.5 meters (3.3 to 4.9 feet) of the cord is routed within the rack cabinet. The installation site AC power receptacle must be within 2 meters (6.6 feet) of the rack.
To prevent catastrophic failures, the design of your power system must ensure that adequate power is provided to the servers. Use dedicated AC breaker panels for all power circuits that supply power to the server. Electrical work and installations must obey applicable local, state, or national electrical codes. Servers require electrical circuits be grounded to the earth.
In addition to circuit breakers, provide a stable power source, such as an uninterruptible power supply (UPS), to reduce the possibility of component failures. If computer equipment is subjected to repeated power interruptions and fluctuations, then it is susceptible to a higher rate of component failure.
Note:
The owner supplies the circuit breakers. Each power cord requires one circuit breaker.The cabinets for Oracle Big Data Appliance are shipped with grounding-type power cords. Always connect the cords to grounded power outlets. Because different grounding methods are used depending on location, check the grounding type and refer to documentation, such as International Electrotechnical Commission (IEC) documents, for the correct grounding method. Ensure that the facility administrator or qualified electrical engineer verifies the grounding method for the building and performs the grounding work.
Airflow through Oracle Big Data Appliance is from front to back. Refer to Table 2-1 for information on cooling and airflow.
Note:
Studies show that temperature increases of 10 degrees Celsius (15 degrees Fahrenheit) above 20 degrees Celsius (70 degrees Fahrenheit) reduce long-term electronics reliability by 50 percent.Excessive internal temperatures may result in full or partial shutdown of Oracle Big Data Appliance.
Table 2-9 lists the temperature, humidity and altitude requirements for operating and non-operating systems.
Table 2-9 Temperature, Humidity and Altitude Requirements
| Condition | Operating Requirement | Non-operating Requirement | Optimum |
|---|---|---|---|
|
Temperature |
5 to 32 degrees Celsius (41 to 89.6 degrees Fahrenheit) |
-40 to 70 degrees Celsius (-40 to 158 degrees Fahrenheit) |
For optimal rack cooling, data center temperatures from 21 to 23 degrees Celsius (70 to 74 degrees Fahrenheit) |
|
Relative humidity |
10 to 90 percent relative humidity, non-condensing |
Up to 93 percent relative humidity |
For optimal data center rack cooling, 45 to 50 percent, non-condensing |
|
Altitude |
3048 meters (10000 feet) maximum |
12000 meters (40000 feet) maximum |
Ambient temperature is reduced by 1 degree Celsius per 300 m above 900 m altitude above sea level |
Set conditions to the optimal temperature and humidity ranges to minimize the chance of downtime due to component failure. Operating Oracle Big Data Appliance for extended periods at or near the operating range limits, or installing it in an environment where it remains at or near non-operating range limits, could significantly increase hardware component failure.
The ambient temperature range of 21 to 23 degrees Celsius (70 to 74 degrees Fahrenheit) is optimal for server reliability and operator comfort. Most computer equipment can operate in a wide temperature range, but near 22 degrees Celsius (72 degrees Fahrenheit) is desirable because it is easier to maintain safe humidity levels. Operating in this temperature range provides a safety buffer if the air conditioning system fails.
The ambient relative humidity range of 45 to 50 percent is suitable for safe data processing operations. Most computer equipment can operate in a wide range (20 to 80 percent), but the range of 45 to 50 percent is recommended for the following reasons:
Helps protect computer systems from corrosion problems associated with high humidity levels.
Provides the greatest operating time buffer if the air conditioner control fails
Helps avoid failures or temporary malfunctions caused by intermittent interference from static discharges that may occur when relative humidity is too low.
Note:
Electrostatic discharge (ESD) is easily generated and hard to dissipate in areas of low relative humidity, such as below 35 percent. ESD becomes critical when humidity drops below 30 percent. It is not difficult to maintain humidity in a data center because of the high-efficiency vapor barrier and low rate of air changes normally present.Always provide adequate space in front and behind the rack to allow for proper ventilation. Do not obstruct the front or rear of the rack with equipment or objects that might prevent air from flowing through the rack. Rack-mountable servers and equipment typically draw cool air in through the front of the rack and let out warm air out the rear of the rack. There is no air flow requirement for the left and right sides due to front-to-back cooling.
If the rack is not completely filled with components, then cover the empty sections with filler panels. Gaps between components can adversely affect air flow and cooling within the rack.
Relative humidity is the percentage of the total water vapor that can exist in the air without condensing, and is inversely proportional to air temperature. Humidity goes down when the temperature rises, and goes up when the temperature drops. For example, air with a relative humidity of 45 percent at a temperature of 24 degrees Celsius (75 degrees Fahrenheit) has a relative humidity of 65 percent at a temperature of 18 degrees Celsius (64 degrees Fahrenheit). As the temperature drops, the relative humidity rises to more than 65 percent, and water droplets are formed.
Air conditioning facilities usually do not precisely monitor or control temperature and humidity throughout an entire computer room. Generally, monitor individual points corresponding to multiple exhaust vents in the main unit and other units in the room. Pay special consideration to humidity when using underfloor ventilation, and monitor each point close to an exhaust vent. Distribution of the temperature and humidity across the entire room is uneven.
Oracle Big Data Appliance is designed to function while mounted in a natural convection air flow. Follow these requirements to meet the environmental specification:
Ensure the server has adequate air flow.
Ensure the server has front-to-back cooling. The air inlet is at the front of the server, and the air is let out the rear.
Allow a minimum clearance of 914 mm (36 inches) at the front of the server and 914 mm (36 inches) at the rear of the server for ventilation.
Use perforated tiles, approximately 400 CFM/tile, in front of the rack for cold air intake. The tiles can be arranged in any order in front of the rack, provided that cold air from the tiles can flow into the rack. Inadequate cold air flow could result in a higher inlet temperature in the servers due to exhaust air recirculation. Oracle recommends four floor tiles for Oracle Big Data Appliance
Figure 2-5 shows a typical installation of the floor tiles for Oracle Big Data Appliance in a typical data center.
Figure 2-5 Typical Data Center Configuration for Perforated Floor Tiles

Before installation, network cables must run from your existing network infrastructure to the installation site. The requirements to connect Oracle Big Data Appliance to your existing network infrastructure are as follows:
Management network connection requirements
1 Ethernet connection for the Ethernet switch in the rack
1 Ethernet connection for the KVM switch in the rack
Client access network connection requirements
1 Ethernet connection for each server in the rack, for a total of 18 connections.
2 10 GigE connections, one to each Sun Network QDR InfiniBand Gateway Switch
See Also:
Chapter 3, "Network Requirements"Before Oracle Big Data Appliance is delivered to the site, perform these tasks to ensure the site is ready:
Task 2, "Complete the Oracle Big Data Appliance Configuration Worksheets"
Task 3, "Complete the Oracle Big Data Appliance Configuration Utility"
Review the site requirements in this chapter and in the Oracle Big Data Appliance Site Checklists to understand the requirements of Oracle Big Data Appliance.
Provide the network configuration details and select the optional software components to be installed. Complete this document for every set of appliances that will be configured as a single CDH cluster. Give the completed worksheets to your Oracle representative.
Complete the spreadsheet from the information in the Oracle Big Data Appliance Configuration Worksheets and generate the Installation Template and configuration files. This step is typically performed by an Oracle representative.
Configure the existing network using the Installation Template provided by your Oracle representative. This includes registering the networks in the Domain Name System (DNS), assigning IP addresses, and configuring data center switches and firewalls.
Prepare the site based on the requirements, such as installing the network cables and power supplies, before the arrival of Oracle Big Data Appliance:
Review the safety guidelines.
See Also:
"Reviewing Safety Guidelines"Note problems or peculiarities at the site that require special equipment. For example, ensure the doors are tall enough and wide enough for Oracle Big Data Appliance.
See Also:
"Space Requirements"Verify that the installation site flooring has a strength rating to withstand the combined weight of Oracle Big Data Appliance and any other installed equipment.
See Also:
"Flooring Requirements"Install network cables for Oracle Big Data Appliance.
See Also:
"Network Connection Requirements"Install all necessary electrical equipment, and ensure that sufficient power is provided for Oracle Big Data Appliance.
See Also:
The Sun Rack II Power Distribution Units User's Guide for the Power Distribution Unit (PDU) power requirements
Ensure that the installation site provides adequate air conditioning.
See Also:
"Ventilation and Cooling Requirements"Operate the air conditioning system for 48 hours to bring the room temperature to the appropriate level.
Clean and vacuum the area thoroughly in preparation for installation.