2 Upgrade Overview
This document defines the step-by-step actions performed to perform an upgrade of an in-service DSR from the source release to the target release. A major upgrade advances the DSR from source release 8.x to target release 9.0.x(Dual Hop Upgrade). An incremental upgrade advances the DSR from an earlier DSR 9.0.x source release to a more recent 9.2.0.0.0 target release.
Note:
Advancing a DSR from 9.0.0.0.0_97.16.0 to 9.0.1.0.0_98.15.0 is an incremental upgrade. But, advancing a DSR running 8.6.x release to an 9.0.x target release constitutes a major upgrade.2.1 Supported Upgrade Paths to 9.2.0.0.0
The following table provides information about the supported upgrade paths:
| Source Release | Target Release |
|---|---|
| 9.0.1.0.0 | 9.2.0.0.0 |
| 9.0.2.0.0 | 9.2.0.0.0 |
| 9.0.2.1.0 | 9.2.0.0.0 |
| 9.1.0.0.0 | 9.2.0.0.0 |
2.2 Geo-Diverse Site Configuration
With a geo-diverse site, the upgrade of the SOAM active/standby servers also includes an upgrade of the spare SOAM at the geo-redundant site in the same maintenance window.
2.3 Traffic Management During Upgrade
The upgrade of the NOAM and SOAM servers are not expected to affect traffic processing at the DA-MPs and other traffic-handling servers.
WARNING:
SCTP Datagram Transport Layer Security change.Oracle introduced SCTP Datagram Transport Layer Security (DTLS) in DSR by enabling SCTP AUTH extensions by default. SCTP AUTH extensions are required for SCTP DTLS. However, there are known impacts with SCTP AUTH extensions as covered by the CVEs referenced in DTLS Feature Activation Guide. These known impacts are managed by enabling SCTP AUTH Extensions. It is highly recommended that customers upgrading to Release 9.2.0.0.0 prepare clients before the DSR is upgraded. This ensures the DSR-to-Client SCTP connection establishes with DTLS with SCTP AUTH extensions enabled.
If customers do not prepare clients to accommodate the DTLS changes, then the SCTP connections to client devices do not restore after the DSR is upgraded to DSR 9.2.0.0.0. In this event, follow the procedure to enable or disable DTLS in DSR Cloud Installation Guide.
2.4 Automated Site Upgrade
You can upgrade a site using multiple methods. The newest and most efficient way to upgrade a site is the Automated Site Upgrade feature. This feature upgrades an entire site (SOAMs and all C-level servers) with minimum user interaction. Once you initiate the upgrade, it automatically prepares the server(s), performs the upgrade, and sequences to the next server or group of servers. This action continues until all servers in the site are upgraded.
Note:
The server upgrades are sequenced in a manner that preserves data integrity and processing capacity.You can use Automated Site Upgrade only for upgrading DSR servers.
You can upgrade the DSR servers through the Automated Site Upgrade. A site is defined as a SOAM server group along with all the subtending servers of that server group, regardless of physical location. Fore more information, refer to Figure 2-1, which demonstrates three physical locations, labeled TSite 1, TSite 2, and TSite 3. Each site contains a SOAM server group and an MP server group. Each SOAM server group has a spare SOAM, which despite being located at another site, is a member of the site that owns the server group. With the site upgrade, SOA-Sp upgrades with the Site 1 SOA server group, and SOB-sp upgrades with the Site 2 SOB server group. The MP server groups are upgraded in the same maintenance window as their respective site SOAMs. These sites conform to the topological site definition in Table 1-2.
- With this feature, you can initiate a site upgrade on SO-A SG and all of its children (in this example, MP1 SG) using a minimum of GUI selections. The upgrade performs the following actions: Upgrade SOA-1, SOA-2, and SOA-sp.
- Upgrade the servers in MP1 SG based on the availability setting and HA roles.
- Immediately begin the upgrade of any other server groups which are also the children of SO-A SG. These upgrades begin in parallel with step 2.
Server groups that span across sites (for example, SOAMs and SBRs) are upgraded with the server group that the server belongs to. This results in upgrading spare servers that physically reside at another site but belong to a server group in the SOAM that is targeted for site upgrade.
Note:
Automated Site Upgrade does not automatically initiate the upgrade of TSite 2 in parallel with TSite 1. However, the feature does allow the user to initiate Automated Site Upgrade of multiple sites in parallel manually.Figure 2-1 Upgrade Perspective of DSR Site Topology

Caution:
Limitations in Create a Link for ComAgent for Automated Site Upgrade can be solved by rearranging/adding the upgrade cycles. If the user does not want to create a custom upgrade plan by rearranging/adding cycles, then manual upgrade method mentioned in Overview of Automated/Manual Server Group Upgrade should be used.2.4.1 Site Upgrade Overview
Figure 2-2 Site Upgrade – NOAM View

After selecting a SOAM site tab on the Upgrade Administration screen, the site summary screenappears as shown in Figure 2-3 Figure. The first link on the site summary screen displays the view. In the view, all the server groups for the site appears in table form, with each server group populating one row. You can can view the upgrade summary of the server groups in the table columns:
- The column shows how the server group is upgraded. The upgrade method is derived from the server group function and the bulk availability option. For more information on bulk availability, see Site Upgrade Options.
- The column groups the servers by state, indicating the number of servers in the server groups in each state.
- The column indicates the current application version, indicating the number of servers in the server group existing in each version.
Figure 2-3 Site Upgrade - Entire Site View

- Server has not been upgraded yet
- The FullDBParts and FullRunEnv backup files exist in the filemgmt area
A site is eligible for Automated Site Upgrade when at least one server in the site is upgrade-ready.
Click from the screen to display the screen as shown in Figure 2-4. The screen presents the as a series of upgrade cycles. For the upgrade shown in Figure 2-4, Cycle 1 upgrades the spare and standby SOAMs in parallel.
Note:
This scenario assumes default settings for the site upgrade options as described in Site Upgrade Options. The specific servers to be upgraded in each cycle are identified in the column of the screen. Cycle 1 is an atomic operation, meaning that Cycle 2 cannot begin until Cycle 1 is complete. Once the spare and standby SOAMs are in Accept or Reject state, the upgrade sequences to Cycle 2 to upgrade the active SOAM. As Cycle 2 is also atomic, Cycle 3 does not begin until Cycle 2 completes.Note:
IPFE servers require special handling for upgrade because IPFE servers are clustered into Target Sets and assigned an IP address. This process is known as Target Set Assignment (TSA). While upgrading IPFE servers, Auto Site Upgrade ensures that there is no service outage for IPFE while upgrade is in progress, that is, IPFE servers in same TSA are not upgraded in the same cycle. If IPFE server address is not configured on screen on active SOAM GUI, that IPFE server is not included in the Upgrade Cycle; therefore, is not considered for upgrade using Automated Site Upgrade.
Figure 2-4 Site Upgrade - Site Initiate Screen

Cycles 3 through 5 upgrade all of the C-level servers for the site. These cycles are not atomic. In the above figure, Cycle 3 consists of IPFE1, IPFE3, MP1, MP4, and SBR3 because some servers can take longer to upgrade than others. Consequently, there may be some overlap in Cycle 3 and Cycle 4. For example, if IPFEs 1 and 3 complete the upgrade before SBR3 is finished (all are in Cycle 3), the upgrade allows IPFEs 2 and 4 to begin, even though they are part of Cycle 4. This is to maximize the maintenance window efficiency. The primary reason for upgrading the C-level servers is the upgrade method for the server group function (for example, bulk by HA, serial). The site upgrade is complete when every server in the site is in the Accept or Reject state.
In selecting the servers that are included in each upgrade cycle, particularly C-level, consideration is given to the server group function, the upgrade availability option, and the HA designation. The following table describes the server selection considerations for each server group function.
Note:
The minimum availability option is a central component of the server selections for site upgrade . The effect of this option on server availability is described in detail in Minimum Server Availability.Table 2-1 Server Selection vs. Server Group Function
| SG Function | Selection Considerations |
|---|---|
| DSR (multi-active cluster) (for example, DA-MP) | The selection of servers is based primarily on the minimum server availability option. Servers are divided equally (to the extent possible) among the number of cycles required to enforce minimum availability. For DA-MPs, an additional consideration is given to the MP Leader. The MP with the Leader designation is the last DA-MP to be upgraded to minimize leader changes1. |
| DSR (active/standby pair) (for example, SOAM) | The SOAM upgrade method is dependent on the Site SOAM Upgrade option on the General Options page. See Site Upgrade Options. |
| SBR | SBRs are always upgraded serially, thus the primary consideration for selection is the HA designation. The upgrade order is spare – spare – standby – active. |
| IP Front End | IPFEs require special treatment during upgrade. One consideration for selection is the minimum server availability, but the primary consideration is traffic continuity. Regardless of minimum availability, IPFE A1 is never upgraded at the same time as IPFE A2. It is always upgraded serially. The same restriction applies to IPFE B1 and B2. If minimum availability permits, IPFE A1 can be upgraded with IPFE B1, and IPFE A2 can be upgraded with B2. |
To initiate the site upgrade, you need to select a target ISO from the ISO picklist in the Upgrade Settings section of the Site Initiate screen. Once you click OK, the upgrade starts and control returns to the Upgrade Administration as shown in Figure 2-5 Figure. Once you select the Entire Site link, a summary of the upgrade status for the selected site is displayed. This summary identifies the server group(s) currently upgrading, the number of servers within each server group that are upgrading, and the number of servers that are pending upgrade. This view can be used to monitor the upgrade status of the overall site. Select the individual sever group links to obtain the detailed status. The server group view shows the status of each individual server within the selected server group.
Figure 2-5 Site Upgrade Monitoring

When a server group link is selected on the upgrade administration screen, the table rows are populated with the upgrade details of the individual servers within that server group as displayed in the following figure.
Figure 2-6 Server Group Upgrade Monitoring

Upon completion of a successful upgrade, every server in the site is in the Accept or Reject state. See Site Upgrade Options for a description of canceling and restarting the Automated Site Upgrade.
2.4.2 Minimum Server Availability
The concept of Minimum Server Availability plays a key role during an upgrade using Automated Site Upgrade. The goal of server availability is to ensure that at least a specified percentage of servers (of any given type) remains in service to process traffic and handle administrative functions while other servers are upgrading.
For example, if the specified minimum availability is 50% and there are eight servers of type X, then four remain in service while the other four upgrade. However, if there are nine servers of type X, then the minimum availability requires that five remain in service while four upgrade. The minimum availability calculation automatically rounds up in the event of a non-zero fractional remainder.
To meet the needs of a wide-ranging customer base, the minimum availability percentage is a user- configurable option, which allows for settings of 50%, 60%, and 75% minimum availability. There is also a setting of 0% for lab upgrade support. This option is described in detail in Site Upgrade Methodology.
Table 2-2 Site Upgrade Availability vs. Server Group Function
| Server Group Function | Server Availability |
|---|---|
| DSR (Multi-active cluster) | In a multi-active cluster, the availability percentage applies to all of the servers in the server group. The number of servers required to achieve minimum availability is calculated from the pool of in-service servers. |
| SBR | Availability percentage does not apply to SBR server groups. SBRs are upgraded in a very specific order: spare – spare – standby – active. |
| IP Front End | IPFEs require special treatment during upgrade. The primary consideration is traffic continuity. Regardless of minimum availability, IPFE A1 is never upgraded at the same time as IPFE A2. They are always upgraded serially. The same restriction applies to IPFE B1 and B2. |
When calculating the number of servers required to satisfy the minimum server availability, all servers in the server group (or server group cluster) are considered. Servers that are OOS or otherwise unable to perform their intended function, are included, as are servers that have already been upgraded. For example, cons ider a DA-MP server group with 10 servers; four have already been upgraded, one is OOS, and five are ready for upgrade. With a 50% minimum availability, only four of the servers that are ready for upgrade, can be upgraded in parallel. The four servers that have already been upgraded count toward the five that are needed to satisfy minimum availability. The OOS server cannot be used to satisfy minimum availability, so one of the upgrade-ready servers must remain in-service for minimum availability, thus leaving four servers to be upgraded together. Upgrading the last server would require an additional upgrade cycle.
2.4.3 Site Upgrade Options
Figure 2-7 Auto Site Upgrade General Options

The first option that affects the upgrade sequence is the Site Upgrade SOAM Method. This option determines the sequence in which the SOAMs are upgraded. The default value of 1 considers the OAM HA role of the SOAMs to determine the upgrade order. In this mode, all non-active SOAM servers are upgraded first (in parallel), followed by the active SOAM. This upgrade method requires at most two upgrade cycles to upgrade all of the SOAMs, regardless of how many are present. If there are no spare SOAMs, then this setting has no effect on the SOAM upgrade. Regardless of the SOAM upgrade method, the active SOAM is always upgraded after the standby and spare SOAMs.
The second option that affects the upgrade sequence is the Site Upgrade Bulk Availability setting. This setting determines the number of C-level servers that remain in service during the upgrade. The default setting of 1 equates to 50% availability, meaning that a minimum of one-half of the servers stay in service during the upgrade. The default setting is the most aggressive setting for upgrading the site, requiring the minimum number of cycles, thus the least amount of time. The settings of 66% and 75% increase the number of servers that remain in service during the upgrade.
Note:
Increasing the availability percentage may increase the overall length of the upgrade.The application of minimum server availability varies for the different types of C-level servers. For example, for a multi-active DA-MP server group, the minimum availability applies to all of the DA-MPs within the server group. This same setup applies to IPFEs as well. Table 2-2 defines how the Site Upgrade Bulk Availability setting on the General Options page affects the various server group function types.
The Site Upgrade General Options cannot be changed while a site upgrade is in progress. Attempting to change either option while a site upgrade is in progress results in:
[Error Code xxx] - Option cannot be changed because one or more automated site upgrades are in progress2.4.4 Cancel and Restart Auto Site Upgrade
When an Auto Site Upgrade is initiated, several tasks are created to manage the upgrade of the individual server groups as well as the servers within the server groups. You can monitor and manage these tasks via the Active Tasks screen. Click Status & Manage, then Tasks, and then Active Tasks.
Figure 2-8 Site Upgrade Active Tasks

To cancel the site upgrade, select the site upgrade task and click Cancel. A screen requests confirmation of the cancel operation. The status changes from running to completed. The Result Details column updates to display site upgrade task cancelled by user. All server group upgrade tasks that are under the control of the main site upgrade task immediately transition to completed state. However, the site upgrade cancellation has no effect on the individual server upgrade tasks that are in progress. These tasks continue until completion. The following figure shows the Active Tasks screen after a site upgrade has been canceled.
Figure 2-9 Canceled Site Upgrade Tasks

Figure 2-10 Partially Upgraded Site

Figure 2-11 Restart Site Upgrade

2.5 Automated Server Group Upgrade
The Automated Server Group (ASG) upgrade feature allows the user to upgrade all of the servers in a server group automatically by specifying a set of controlling parameters.
The purpose of ASG is to simplify and automate segments of the DSR upgrade. The DSR has long supported the ability to select multiple servers for upgrade. However, in doing so, it was incumbent on the user to determine ahead of time which servers could be upgraded in parallel, considering traffic impact. If the servers were not carefully chosen, the upgrade could adversely impact system operations.
When a server group is selected for upgrade, ASG upgrades each of the servers serially, or in parallel, or a combination of both, while enforcing minimum service availability. The number of servers in the server group that are upgraded in parallel is user selectable. The procedures in this document provide the detailed steps specifying when to use ASG, as well as the appropriate parameters that should be selected for each server group type. ASG is the default upgrade method for most server group types associated with the DSR. However, there are some instances in which the manual upgrade method is utilized. In all cases where ASG is used, procedures for a manual upgrade are also provided.
Note:
To use ASG on a server group, no servers in that server group can be already upgraded either by ASG or manually.DSR continues to support the parallel upgrade of server groups, including any combination of automated and manual upgrade methods.
2.5.1 Cancel and Restart Automated Server Group Upgrade
When a server group is upgraded using ASG, each server within that server group is automatically prepared for upgrade, upgraded to the target release, and returned to service on the target release. Once an ASG upgrade is initiated, the task responsible for controlling the sequencing of servers entering upgrade can be manually canceled by navigating to Status & Manage, then Tasks, and then Active Tasks screen as shown in the following figure, if necessary. Once the task is canceled, it cannot be restarted. However, a new ASG task can be restarted via the Upgrade Administration screen.
Figure 2-12 Active Tasks Screen

In the event that a server fails to upgrade, it automatically rolls back to the previous release in preparation for backout_restore and fault isolation. Any other servers in that server group that are in the process of upgrading continue to upgrade to completion. However, the ASG task itself is automatically canceled and no other servers in that server group are upgraded. Automatic cancelation triggers troubleshooting to correct the problem. Once the problem is solved, the users can again initiate a new server group upgrade on the upgrade screen.
2.5.2 Site Accept
You can accept the upgrade of some or all servers for a given site by clicking
Site Accept on the upgrade GUI. When you
click Site Accept a subsequent screen as shown in the
following figure displays the servers that are ready for the
Accept action. However, normal procedure calls for the Accept
Upgrade to be applied to all the servers at a site only after
the upgrade to the new release is stable and the back out option
is no longer needed. After verifying that the information
presented is accurate, Click OK to confirm the intended
action. The Accept command is issued to the site servers at a
rate of approximately one server every second. The command takes
approximately 10 seconds per server to complete. As the commands
are completed, the server status on the Upgrade Administration
screen transitions to Backup Needed. 