Reconfiguring the Private Cloud Appliance Network Environment

The network environment is configured during the initial setup of Private Cloud Appliance. An appliance administrator can update this configuration. However, careful planning is advised, because these settings define the connections to the on-premises network and could disrupt system operations.

Note

It is not supported to turn off BGP authentication by changing the BGP password to null:

PCA-ADMIN> edit networkConfig adminbgppassword= 

Even if this command is completed successfully, BGP authentication remains active and the password is unchanged. This is not an error condition, but a security feature. To disable BGP authentication, you must do so explicitly. The command is:

PCA-ADMIN> edit networkConfig adminbgpauthentication=false
Important

Enter the IP addresses for the uplinks exactly as they appear in the network configuration spreadsheet you filled out in preparation. The order of entry is important, especially when multiple IPs are added in the same field, because they map to specific spine and data center switches in the uplink topology.

Routing Information Cannot Be Modified

Caution

It is not supported to change routing information. This applies to network topologies configured with either dynamic or static routing.

Updating Management Node Information

You can change the IP addresses and hostnames of the management nodes.

Using the Service Web UI
  1. In the navigation menu, click Network Environment.

  2. In the Network Environment Information page, click the Management Nodes tab.

    The Management Nodes details appear.

  3. In the top-right corner of the page, click Edit.

  4. Click Next to navigate to the page you want to edit, then update the appropriate fields.

    For field descriptions, see Initial System Installation Checklist.

  5. Click Save Changes.

Using the Service CLI
  1. Display the current network configuration information using the show NetworkConfig command.

    PCA-ADMIN> show NetworkConfig
    Data:
      Uplink Port Speed = 100
      Uplink Port Count = 2
      Uplink Vlan Mtu = 9216
      Spine1 Ip = 10.n.n.12
      Spine2 Ip = 10.n.n.13
      Uplink Netmask = 255.255.255.0
      Management VIP Hostname = ukpca01mn
      Management VIP 100g = 10.n.n.8
      NTP Server(s) = 100.n.n.254
      Uplink Port Fec = auto
      Public Ip range/list = 10.n.n.2/32,10.n.n.3/32,10.n.n.4/32,10.n.n.5/32,10.n.n.6/32,10.n.n.7/32
      DNS Address1 = 206.n.n.1
      DNS Address2 = 206.n.n.2
      DNS Address3 = 10.n.n.197
      Management Node1 Hostname = ukpca01-mn1
      Management Node2 Hostname = ukpca01-mn2
      Management Node3 Hostname = ukpca01-mn3
      100g Management Node1 Ip = 10.n.n.9
      100g Management Node2 Ip = 10.n.n.10
      100g Management Node3 Ip = 10.n.n.11
      Object Storage Ip = 10.n.n.1
      Enable Admin Network = false
      Static Routing = true
      Spine VIP = 10.n.n.14
      Uplink Gateway = 10.n.n.1
      Uplink VLAN = 799
      Uplink Hsrp Group = 61
      BGP Authentication = false
  2. Use the edit NetworkConfig command to change any of these management node parameters:

    • Management Node 1 IP

    • Management Node 1 Hostname

    • Management Node 2 IP

    • Management Node 2 Hostname

    • Management Node 3 IP

    • Management Node 3 Hostname

    • Management Node VIP

    • Management Node VIP Hostname

    PCA-ADMIN> edit NetworkConfig mgmt01Ip100g=172.n.n.190 mgmt02Ip100g=172.n.n.191
    JobId: 52f5177d-402a-4a52-98fe-1cff9c1f26be

Updating the Administration Network Configuration

If you use the optional Administration Network, you can update the parameters using these procedures.

Caution

If you are not currently using a separate Administration Network, the Network Environment Information page in the Service Web UI will not display an Admin Network tab or any of the related configuration parameters. The command output in the Service CLI will not display any Admin Network parameters either. You must first enable the Administration Network.

When an Administration Network is configured, it cannot be disabled again.

For general Administration Network configuration information, see Data Center Network Configuration Guidelines. For descriptions of Administration Network parameters, see Initial System Installation Checklist.
Using the Service Web UI

Scenario 1: Administration Network Disabled

If you need to enable and configure a separate Administration Network, proceed as follows:

  1. In the navigation menu, click Network Environment.

  2. In the top-right corner of the page, click Edit.

  3. In the wizard, navigate to the Admin Network tab and set Admin Networking to Enable.

  4. Enter all the required parameters in the respective fields on the form.

  5. Click Save Changes.

Scenario 2: Administration Network Enabled

If you already configured a separate Administration Network and need to edit its settings, proceed as follows:

  1. In the navigation menu, click Network Environment.

  2. In the Network Environment Information page, click the Admin Network tab.

    The Admin Network details appear.

  3. In the top-right corner of the page, click Edit.

  4. Click Next to navigate to the page you want to edit, then update the appropriate fields.

  5. Click Save Changes.

Using the Service CLI
  1. If you are not currently using a separate Administration Network, the CLI output will not display any Admin Network parameters. Enable the Administration Network first.

  2. Display the current network configuration information using the show NetworkConfig command.

    PCA-ADMIN> show NetworkConfig
    Data:
      Uplink Port Speed = 100
      Uplink Port Count = 4
      Uplink Vlan Mtu = 9216
      Spine1 Ip = 10.10.10.97,10.10.10.101
      Spine2 Ip = 10.10.10.99,10.10.10.103
      Uplink Netmask = 255.255.255.254,255.255.255.254
      Management VIP Hostname = mypca
      Management VIP = 10.10.10.107
      NTP Server(s) = 10.80.211.105,10.211.17.1,10.68.48.1
      Uplink Port Fec = auto
      Public Ip range/list = 10.10.10.114/31,10.10.10.116/31,10.10.10.118/31,10.10.10.120/31,10.10.10.122/31,10.10.10.124/31,10.10.10.126/32
      Management Node1 Hostname = pcamn01
      Management Node2 Hostname = pcamn02
      Management Node3 Hostname = pcamn03
      Management Node1 Ip = 10.10.10.108
      Management Node2 Ip = 10.10.10.109
      Management Node3 Ip = 10.10.10.110
      Object Storage Ip = 10.10.10.113
      Enable Admin Network = true
      Admin Port Speed = 100
      Admin Port Count = 1
      Admin Vlan Mtu = 9216
      Admin Port Fec = auto
      Admin VLAN = 3915
      Admin Spine1 Ip = 10.25.0.111
      Admin Spine2 Ip = 10.25.0.112
      Admin Spine VIP = 10.25.0.110
      Admin Netmask = 255.255.255.0
      Admin Hsrp Group = 152
      Static Routing = false
      Uplink VLAN = 3911
      Peer1 Asn = 50000
      Peer1 Ip = 10.10.10.96,10.10.10.98
      Oracle Asn = 136025
      Bgp Topology = mesh
      Peer2 Asn = 50000
      Peer2 Ip = 10.10.10.100,10.10.10.102
      BGP Authentication = false
      BGP KeepAlive Timer = 60
      BGP Holddown Timer = 180
      Network Config Lifecycle State = ACTIVE
      admin DNS Address1 = 10.25.0.1
      admin Management Node1 Hostname = pcamn01admin.example.com
      admin Management Node2 Hostname = pcamn02admin.example.com
      admin Management Node3 Hostname = pcamn03admin.example.com
      admin Management Node1 Ip = 10.25.0.101
      admin Management Node2 Ip = 10.25.0.102
      admin Management Node3 Ip = 10.25.0.103
      admin Management VIP Hostname = mypcaadmin.example.com
      admin Management VIP = 10.25.0.100
  3. Use the edit NetworkConfig command to change any of these administration network parameters:

    Tip

    Enter edit networkConfig ? to display the parameters available for editing.

    • Admin Network enable

    • Management node cluster Admin VIP and host name

    • Management node 1-3 Admin IP and host name

    • Admin DNS IP 1-3

    • Admin Port count, speed, FEC

    • Admin CIDR

    • Admin VLAN and MTU

    • Admin Gateway IP

    • Admin Netmask

    • Spine 1+2 Admin IP

    • Spine Admin VIP

    PCA-ADMIN> edit NetworkConfig adminPortSpeed=25
    JobId: 62f8137f-772a-4a52-98f4-1cfv9c1f24te
    
    PCA-ADMIN> edit NetworkConfig adminCidr=10.25.0.1/24
    JobId: 861381ae-cc63-44a2-a66e-8e095e4a99f9

Updating NTP Server Information

Note

You can check the NTP connection status of a running system at any time. In the Service Web UI, it's displayed in the NTP tab of the Network Environment Information page. In the Service CLI you can run this command:

PCA-ADMIN> checkNtpServers
Data:
  id              Accessible
  --              ----------
  10.64.0.252     true
  192.0.2.2       true

You can edit or add IP addresses for NTP servers.

Using the Service Web UI
  1. In the navigation menu, click Network Environment.

  2. In the Network Environment Information page, click the NTP tab.

    The NTP details appear.

  3. In the top-right corner of the page, click Edit.

  4. Click Next to navigate to the page you want to edit, then update the appropriate fields.

    For field descriptions, see Initial System Installation Checklist.

  5. Click Save Changes.

Using the Service CLI
  1. Display the current network configuration information using the show NetworkConfig command.

    PCA-ADMIN> show NetworkConfig
    Data:
      Uplink Port Speed = 100
      Uplink Port Count = 2
      Uplink Vlan Mtu = 9216
      Spine1 Ip = 10.n.n.12
      Spine2 Ip = 10.n.n.13
      Uplink Netmask = 255.255.255.0
      Management VIP Hostname = ukpca01mn
      Management VIP 100g = 10.n.n.8
      NTP Server(s) = 100.n.n.254
      Uplink Port Fec = auto
      Public Ip range/list = 10.n.n.2/32,10.n.n.3/32,10.n.n.4/32,10.n.n.5/32,10.n.n.6/32,10.n.n.7/32
      DNS Address1 = 206.n.n.1
      DNS Address2 = 206.n.n.2
      DNS Address3 = 10.n.n.197
      Management Node1 Hostname = ukpca01-mn1
      Management Node2 Hostname = ukpca01-mn2
      Management Node3 Hostname = ukpca01-mn3
      100g Management Node1 Ip = 10.n.n.9
      100g Management Node2 Ip = 10.n.n.10
      100g Management Node3 Ip = 10.n.n.11
      Object Storage Ip = 10.n.n.1
      Enable Admin Network = false
      Static Routing = true
      Spine VIP = 10.n.n.14
      Uplink Gateway = 10.n.n.1
      Uplink VLAN = 799
      Uplink Hsrp Group = 61
      BGP Authentication = false
  2. Use the edit NetworkConfig command to change the NTP servers. Enter multiple IP addresses in a comma-separated list:

    PCA-ADMIN> edit NetworkConfig ntpIps=100.n.n.254,100.n.n.253
    JobId: 42f5137f-122a-4a52-98fe-1cfv9c1f26ve

Updating DNS Server Information

You can edit or add IP addresses for DNS servers.

Using the Service Web UI
  1. In the navigation menu, click Network Environment.

  2. In the Network Environment Information page, click the DNS tab.

    The DNS details appear.

  3. In the top-right corner of the page, click Edit.

  4. Click Next to navigate to the page you want to edit, then update the appropriate fields.

    For field descriptions, see Initial System Installation Checklist.

  5. Click Save Changes.

Using the Service CLI
  1. Display the current network configuration information using the show NetworkConfig command.

    PCA-ADMIN> show NetworkConfig
    Data:
      Uplink Port Speed = 100
      Uplink Port Count = 2
      Uplink Vlan Mtu = 9216
      Spine1 Ip = 10.n.n.12
      Spine2 Ip = 10.n.n.13
      Uplink Netmask = 255.255.255.0
      Management VIP Hostname = ukpca01mn
      Management VIP 100g = 10.n.n.8
      NTP Server(s) = 100.n.n.254
      Uplink Port Fec = auto
      Public Ip range/list = 10.n.n.2/32,10.n.n.3/32,10.n.n.4/32,10.n.n.5/32,10.n.n.6/32,10.n.n.7/32
      DNS Address1 = 206.n.n.1
      DNS Address2 = 206.n.n.2
      DNS Address3 = 10.n.n.197
      Management Node1 Hostname = ukpca01-mn1
      Management Node2 Hostname = ukpca01-mn2
      Management Node3 Hostname = ukpca01-mn3
      100g Management Node1 Ip = 10.n.n.9
      100g Management Node2 Ip = 10.n.n.10
      100g Management Node3 Ip = 10.n.n.11
      Object Storage Ip = 10.n.n.1
      Enable Admin Network = false
      Static Routing = true
      Spine VIP = 10.n.n.14
      Uplink Gateway = 10.n.n.1
      Uplink VLAN = 799
      Uplink Hsrp Group = 61
      BGP Authentication = false
  2. Use the edit NetworkConfig command to change the DNS IP addresses:

    • DNS IP1

    • DNS IP2

    • DNS IP3

    PCA-ADMIN> edit NetworkConfig DnsIp2=206.n.n.2
    JobId: 42f5137f-122a-4a52-98fe-1cfv9c1f26ve

Updating the Public IP Address Configuration

You can add public IP addresses, or change the currently configured IP addresses.

Caution

Changing public IP addresses that are in use can cause system disruption.

Using the Service Web UI
  1. In the navigation menu, click Network Environment.

  2. In the Network Environment Information page, click the Uplink tab.

    The Uplink details appear.

  3. In the top-right corner of the page, click Edit.

  4. Click Next to navigate to the page you want to edit, then update the appropriate fields.

    For field descriptions, see Initial System Installation Checklist.

  5. Click Save Changes.

Using the Service CLI
  1. Display the current network configuration information using the show NetworkConfig command.

    PCA-ADMIN> show NetworkConfig
    Data:
      Uplink Port Speed = 100
      Uplink Port Count = 2
      Uplink Vlan Mtu = 9216
      Spine1 Ip = 10.n.n.12
      Spine2 Ip = 10.n.n.13
      Uplink Netmask = 255.255.255.0
      Management VIP Hostname = ukpca01mn
      Management VIP 100g = 10.n.n.8
      NTP Server(s) = 100.n.n.254
      Uplink Port Fec = auto
      Public Ip range/list = 10.n.n.2/32,10.n.n.3/32,10.n.n.4/32,10.n.n.5/32,10.n.n.6/32,10.n.n.7/32
      DNS Address1 = 206.n.n.1
      DNS Address2 = 206.n.n.2
      DNS Address3 = 10.n.n.197
      Management Node1 Hostname = ukpca01-mn1
      Management Node2 Hostname = ukpca01-mn2
      Management Node3 Hostname = ukpca01-mn3
      100g Management Node1 Ip = 10.n.n.9
      100g Management Node2 Ip = 10.n.n.10
      100g Management Node3 Ip = 10.n.n.11
      Object Storage Ip = 10.n.n.1
      Enable Admin Network = false
      Static Routing = true
      Spine VIP = 10.n.n.14
      Uplink Gateway = 10.n.n.1
      Uplink VLAN = 799
      Uplink Hsrp Group = 61
      BGP Authentication = false
  2. Use the edit NetworkConfig command to change the public IP addresses or the object storage public IP address:

    • Object Storage Public IP

    • Public IP Range/List

    PCA-ADMIN> edit NetworkConfig PublicIps= 10.n.n.17/32,10.n.n.18/32,10.n.n.19/32
    JobId: 42f5137f-122a-4a52-98fe-1cfv9c1f26ve

Configuring Appliance Proxy Settings

The initial appliance setup procedure, as described in Completing the Initial Setup and Configuration, provides no option to add a system-wide proxy configuration. However, some of the platform and infrastructure services require connectivity to endpoints outside the appliance environment. For example, for federation with an identity provider (IDP), the IAM and Admin services must acquire metadata from that external server (for users of the Compute Enclave and Service Enclave respectively.) If network traffic passes through a proxy server in the data center, requests between the appliance and the external server cannot be completed successfully.

To enable external network communication through a data center proxy server, add the proxy configuration to the appliance network setup. Ensure that the initial appliance setup procedure has been completed first.

Using the Service Web UI
  1. In the PCA Config navigation menu, click Appliance Details.

    The Appliance Details page contains system properties such as realm, region and domain.

  2. To configure a proxy at the appliance level, click the Set Rack-Wide Proxy button in the top-right corner.

    A proxy configuration window appears.

  3. Fill out the proxy configuration parameters:

    • Proxy Name: Enter the fully qualified domain name of the proxy server.

    • Proxy Host: Enter the proxy server IP address.

    • Proxy Port: Enter the port number the proxy server uses for routing requests.

    • Proxy User Name: If required, enter a user name for authentication with the proxy server.

    • Proxy Password: If required, enter the password for the proxy user name.

    • Proxy Confirm Password: If required, enter the proxy password again for confirmation.

    The user name and password parameters are optional, in case the proxy server requires authentication. The details are stored in the Secret Service (Vault), where services can retrieve them securely to establish their external connection.

  4. Click Set Rack-Wide Proxy to save the proxy configuration.

    The proxy configuration is displayed in a separate tab on Appliance Details page.

  5. To delete the proxy configuration from the appliance, go to the Appliance Details page and click Clear Rack-Wide Proxy in the top-right corner.

  6. If you need to modify the stored proxy configuration, delete it and fill out the proxy configuration window again with the correct parameters.

Using the Service CLI
  1. Add the proxy configuration details using the setProxy command.

    Syntax (entered on a single line):

    PCA-ADMIN> setProxy
    proxyName=<proxy_fqdn>
    proxyHost=<proxy_ip>
    proxyPort=<proxy_port>
    proxyUsername=<proxy_user>
    proxyPassword=<proxy_password>
    proxyConfirmPassword=<proxy_password>

    Example:

    PCA-ADMIN> setProxy proxyName=myproxy.example.com
    proxyHost=172.16.0.100
    proxyPort=8080
    proxyUsername=proxyuser
    proxyPassword=********
    proxyConfirmPassword=********

    The user name and password parameters are optional, in case the proxy server requires authentication. The details are stored in the Secret Service (Vault), where services can retrieve them securely to establish their external connection.

  2. To delete the proxy configuration from the appliance, enter the clearProxy command. No command parameters are required.

  3. If you need to modify the stored proxy configuration, run the setProxy command again with the correct parameters.

Enabling External IPv6 Connectivity

The connection between Private Cloud Appliance and the on-premises network can optionally be configured to support IPv6 traffic. This is a dual stack implementation, meaning an IPv4 base configuration is applied during initial system installation and configuration, and IPv6 support is enabled in parallel.

Important

IPv6 virtual network connectivity is currently only supported for compute instances with SR-IOV (single root I/O virtualization) VNICs.

Tip

Keep equivalent IPv4 and IPv6 addresses and CIDRs easy to identify by using a human readable conversion scheme.

Using the Service Web UI (preferred)

IPv6 compute instance connectivity requires IPv6 packets to be routed over the uplinks and into the subnets where the compute instances have an IPv6 address. The Service Web UI provides a network configuration page for this purpose.

  1. In the navigation menu, under PCA Config, select IPv6 Network Environment.

  2. In the IPv6 Network Environment Information page, in the upper right corner, click Edit.

    The IPv6 Network Configuration window is displayed.


    Figure showing the IPv6 Network Environment Information page.
  3. Fill out the required IPv6 parameters for the system uplinks.

    The example shows a mesh topology with dynamic routing. For static routing, uplink gateway and spine virtual IPs are required parameters.

  4. Click Submit to apply the IPv6 configuration to the uplinks.

  5. To remove the IPv6 configuration, edit and submit with empty parameter fields.

Using the Service CLI

Alternatively, set the IPv6 configuration parameters from the CLI, using the edit NetworkConfigV6 command.

Command syntax:

PCA-ADMIN> edit networkConfigV6 
uplinkGatewayV6Ip=<value>
peer1V6Ip=<value>
peer2V6Ip=<value>
spineV6Vip=<value>
spine1V6Cidr=<value>
spine2V6Cidr=<value>

Example:

PCA-ADMIN> edit networkConfig \
peer1V6Ip=2001:0db8:1234:0100:1000:000f::128,2001:0db8:1234:0100:1000:000f::130 \
peer2V6Ip=2001:0db8:1234:0100:1000:000f::132,2001:0db8:1234:0100:1000:000f::134 \
spine1V6Cidr=2001:0db8:1234:0100:1000:000f::129/127,2001:0db8:1234:0100:1000:000f::135/127 \
spine2V6Cidr=2001:0db8:1234:0100:1000:000f::133/127,2001:0db8:1234:0100:1000:000f::131/127

To remove the IPv6 configuration, enter the same command with the parameters set to empty values.

PCA-ADMIN> edit networkConfigV6 peer1V6Ip= peer2V6Ip= spine1V6Cidr= spine2V6Cidr=