G Multirack Cabling Tables
InfiniBand cables connect multiple racks together, in addition to connecting the components within a rack. The cable lengths provided in these tables are for adjacent racks with the cables running underneath the racks. If the racks are apart or the cables run above the racks, then longer cables might be required. The cable lengths listed here are only guidelines. You should always verify the actual cable lengths required.
This appendix contains the following sections:
About Multirack Cabling
You can connect up to 18 full Recovery Appliance racks. The racks do not include spare cables or a third Sun Datacenter InfiniBand Switch 36, which functions as the spine switch. To extend a rack, order the cables and a Sun Datacenter InfiniBand Switch 36.
This section contains the following topics:
Cables Provided With a Spine Switch
The Sun Datacenter InfiniBand Switch 36 switches attach to standard Quad Small Form-factor Pluggable (QSFP) connectors at the ends of the InfiniBand cables.
Table G-1lists the cables for the Sun Datacenter InfiniBand Switch 36 spine switch.
Table G-1 InfiniBand Cables Provided with InfiniBand switch.
| Cable | Interswitch |
|---|---|
|
InfiniBand 2 meter cable |
7 |
|
InfiniBand 3 meter cable |
2 |
Optical Cables Required for Four or More Racks
Connecting four or more racks requires additional 10-meter optical QSFP-to-QSFP QDR InfiniBand cables. Each optical cable requires two QSFP SR transceivers. Table G-2 lists the cables needed to connect the racks.
Table G-2 Cable Requirements for Multirack Installations
| Number of Racks | 3 Meter Cables | 5 Meter Cables | 10 Meter Cables |
|---|---|---|---|
|
2 |
16 |
16 |
0 |
|
3 |
18 |
30 |
0 |
|
4 |
16 |
40 |
8 |
|
5 |
20 |
42 |
18 |
|
6 |
24 |
46 |
26 |
|
7 |
28 |
44 |
40 |
|
8 |
16 |
52 |
60 |
Cabling Three Switches Within a Rack
In a single rack, the two leaf switches are interconnected using seven connections. In addition, each leaf switch has one connection to the spine switch. The leaf switches connect to the spine switch as shown in Figure G-1.
Figure G-1 In-Rack Connections Between Spine Switch and Leaf Switches

Description of "Figure G-1 In-Rack Connections Between Spine Switch and Leaf Switches"
The servers connect to the leaf switches as shown in Figure G-2.
Figure G-2 In-Rack Connections Between the Servers and the Leaf Switches

Description of "Figure G-2 In-Rack Connections Between the Servers and the Leaf Switches"
Cabling the Switches in Two Racks
When you connect up to eight racks, remove the seven interswitch connections between the leaf switches and the two connections between the leaf switches and the spine switch. From each leaf switch, distribute eight connections over the spine switches in all racks. In multirack environments, the leaf switches inside a rack are not directly connected.
Figure G-3 shows that each leaf switch in rack 1 connects to the following switches:
-
Four in-rack connections to the spine switch in rack 1
-
Four external connections to the spine switch in rack 2
The spine switch in rack 1 connects to the following switches:
-
Eight in-rack connections to both leaf switches in rack 1
-
Eight external connections to both leaf switches in rack 2
Figure G-3 Connecting Switches Across Two Racks

Description of "Figure G-3 Connecting Switches Across Two Racks"
Cabling the Switches in Up to Eight Racks
As the number of racks increases from two to eight, the pattern continues, as shown in Figure G-4. Because not all of the racks are shown, not all of the cables are shown either.
Each leaf switch has eight interswitch connections distributed across all spine switches. Each spine switch has 16 interswitch connections distributed across all leaf switches. The leaf switches are not directly connected to other leaf switches, and the spine switches are not directly connected to the other spine switches.
Figure G-4 Connecting Switches Across Eight Racks

Description of "Figure G-4 Connecting Switches Across Eight Racks"
Cabling Switches in Up to 18 Racks
When you connect racks 9 through 18, remove the interswitch connections between the leaf switches, and disconnect the spine switches from the InfiniBand fabric. Figure G-5 shows that the eight links from every leaf switch connect to the spine switches in racks 1 to 8.
The connections among racks 1 to 8 do not change you add the cables for racks 9 to 18.
Figure G-5 Connecting Switches Across 18 Racks

Description of "Figure G-5 Connecting Switches Across 18 Racks"
Note:
Cable lengths are specified for racks 1 through 8. Cable lengths for racks 9 through 18 vary depending on the layout of the racks.
Key to Cabling Table Abbreviations
The following abbreviations are used in the tables:
| Abbreviation | Description |
|---|---|
|
Rn |
Rack n, where n is the number of the rack, such as R1. |
|
IBn |
Unit location in rack, where n is the number, such as IB3. |
|
Pn |
InfiniBand port n, where n is port number, such as P8A. |
Two-Rack Cabling
Table G-3 shows the cable connections for the first spine switch (R1-U1) when two full racks are cabled together.
See Also:
Table G-3 Leaf Switch Connections for Rack 1 in a Two-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R1 IB3 within Rack 1 |
R1-IB3-P8A to R1-U1-P3A R1-IB3-P8B to R1-U1-P4A R1-IB3-P9A to R1-U1-P5A R1-IB3-P9B to R1-U1-P6A |
3 meters |
|
R1 IB3 to Rack 2 |
R1-IB3-P10A to R2-U1-P7A R1-IB3-P10B to R2-U1-P8A R1-IB3-P11A to R2-U1-P9A R1-IB3-P11B to R2-U1-P10A |
5 meters |
|
R1 IB2 within Rack 1 |
R1-IB2-P8A to R1-U1-P3B R1-IB2-P8B to R1-U1-P4B R1-IB2-P9A to R1-U1-P5B R1-IB2-P9B to R1-U1-P6B |
3 meters |
|
R1 IB2 to Rack 2 |
R1-IB2-P10A to R2-U1-P7B R1-IB2-P10B to R2-U1-P8B R1-IB2-P11A to R2-U1-P9B R1-IB2-P11B to R2-U1-P10B |
5 meters |
Table G-4 shows the cable connections for the second spine switch (R2-U1) when two full racks are cabled together.
Table G-4 Leaf Switch Connections for Rack 2 in a Two-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R2 IB3 within Rack 2 |
R2-IB3-P8A to R2-U1-P3A R2-IB3-P8B to R2-U1-P4A R2-IB3-P9A to R2-U1-P5A R2-IB3-P9B to R2-U1-P6A |
3 meters |
|
R2 IB3 to Rack 1 |
R2-IB3-P10A to R1-U1-P7A R2-IB3-P10B to R1-U1-P8A R2-IB3-P11A to R1-U1-P9A R2-IB3-P11B to R1-U1-P10A |
5 meters |
|
R2 IB2 within Rack 2 |
R2-IB2-P8A to R2-U1-P3B R2-IB2-P8B to R2-U1-P4B R2-IB2-P9A to R2-U1-P5B R2-IB2-P9B to R2-U1-P6B |
3 meters |
|
R2 IB2 to Rack 1 |
R2-IB2-P10A to R1-U1-P7B R2-IB2-P10B to R1-U1-P8B R2-IB2-P11A to R1-U1-P9B R2-IB2-P11B to R1-U1-P10B |
5 meters |
Three-Rack Cabling
Table G-5 shows the cable connections for the first spine switch (R1-U1) when three full racks are cabled together.
Table G-5 Leaf Switch Connections for Rack 1 in a Three-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R1 IB3 within Rack 1 |
R1-IB3-P8A to R1-U1-P3A R1-IB3-P8B to R1-U1-P4A R1-IB3-P9A to R1-U1-P5A |
3 meters |
|
R1 IB3 to Rack 2 |
R1-IB3-P9B to R2-U1-P6A R1-IB3-P10A to R2-U1-P7A R1-IB3-P10B to R2-U1-P8A |
5 meters |
|
R1 IB3 to Rack 3 |
R1-IB3-P11A to R3-U1-P9A R1-IB3-P11B to R3-U1-P10A |
5 meters |
|
R1 IB2 within Rack 1 |
R1-IB2-P8A to R1-U1-P3B R1-IB2-P8B to R1-U1-P4B R1-IB2-P9A to R1-U1-P5B |
3 meters |
|
R1 IB2 to Rack 2 |
R1-IB2-P9B to R2-U1-P6B R1-IB2-P10A to R2-U1-P7B R1-IB2-P10B to R2-U1-P8B |
5 meters |
|
R1 IB2 to Rack 3 |
R1-IB2-P11A to R3-U1-P9B R1-IB2-P11B to R3-U1-P10B |
5 meters |
Table G-6 shows the cable connections for the second spine switch (R2-U1) when three full racks are cabled together.
Table G-6 Leaf Switch Connections for Rack 2 in a Three-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R2 IB3 within Rack 2 |
R2-IB3-P8A to R2-U1-P3A R2-IB3-P8B to R2-U1-P4A R2-IB3-P9A to R2-U1-P5A |
3 meters |
|
R2 IB3 to Rack 1 |
R2-IB3-P11A to R1-U1-P9A R2-IB3-P11B to R1-U1-P10A |
5 meters |
|
R2 IB3 to Rack 3 |
R2-IB3-P9B to R3-U1-P6A R2-IB3-P10A to R3-U1-P7A R2-IB3-P10B to R3-U1-P8A |
5 meters |
|
R2 IB2 within Rack 2 |
R2-IB2-P8A to R2-U1-P3B R2-IB2-P8B to R2-U1-P4B R2-IB2-P9A to R2-U1-P5B |
3 meters |
|
R2 IB2 to Rack 1 |
R2-IB2-P11A to R1-U1-P9B R2-IB2-P11B to R1-U1-P10B |
5 meters |
|
R2 IB2 to Rack 3 |
R2-IB2-P9B to R3-U1-P6B R2-IB2-P10A to R3-U1-P7B R2-IB2-P10B to R3-U1-P8B |
5 meters |
Table G-7 shows the cable connections for the third spine switch (R3-U1) when three full racks are cabled together.
Table G-7 Leaf Switch Connections for Rack 3 in a Three-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R3 IB3 within Rack 3 |
R3-IB3-P8A to R3-U1-P3A R3-IB3-P8B to R3-U1-P4A R3-IB3-P9A to R3-U1-P5A |
3 meters |
|
R3 IB3 to Rack 1 |
R3-IB3-P9B to R1-U1-P6A R3-IB3-P10A to R1-U1-P7A R3-IB3-P10B to R1-U1-P8A |
5 meters |
|
R3 IB3 to Rack 2 |
R3-IB3-P11A to R2-U1-P9A R3-IB3-P11B to R2-U1-P10A |
5 meters |
|
R3 IB2 within Rack 3 |
R3-IB2-P8A to R3-U1-P3B R3-IB2-P8B to R3-U1-P4B R3-IB2-P9A to R3-U1-P5B |
3 meters |
|
R3 IB2 to Rack 1 |
R3-IB2-P9B to R1-U1-P6B R3-IB2-P10A to R1-U1-P7B R3-IB2-P10B to R1-U1-P8B |
5 meters |
|
R3 IB2 to Rack 2 |
R3-IB2-P11A to R2-U1-P9B R3-IB2-P11B to R2-U1-P10B |
5 meters |
Four-Rack Cabling
Table G-8 shows the cable connections for the first spine switch (R1-U1) when four full racks are cabled together.
Table G-8 Leaf Switch Connections for Rack 1 in a Four-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R1 IB3 within Rack 1 |
R1-IB3-P8A to R1-U1-P3A R1-IB3-P8B to R1-U1-P4A |
3 meters |
|
R1 IB3 to Rack 2 |
R1-IB3-P9A to R2-U1-P5A R1-IB3-P9B to R2-U1-P6A |
5 meters |
|
R1 IB3 to Rack 3 |
R1-IB3-P10A to R3-U1-P7A R1-IB3-P10B to R3-U1-P8A |
5 meters |
|
R1 IB3 to Rack 4 |
R1-IB3-P11A to R4-U1-P9A R1-IB3-P11B to R4-U1-P10A |
10 meters |
|
R1 IB2 within Rack 1 |
R1-IB2-P8A to R1-U1-P3B R1-IB2-P8B to R1-U1-P4B |
3 meters |
|
R1 IB2 to Rack 2 |
R1-IB2-P9A to R2-U1-P5B R1-IB2-P9B to R2-U1-P6B |
5 meters |
|
R1 IB2 to Rack 3 |
R1-IB2-P10A to R3-U1-P7B R1-IB2-P10B to R3-U1-P8B |
5 meters |
|
R1 IB2 to Rack 4 |
R1-IB2-P11A to R4-U1-P9B R1-IB2-P11B to R4-U1-P10B |
10 meters |
Table G-9 shows the cable connections for the second spine switch (R2-U1) when four full racks are cabled together.
Table G-9 Leaf Switch Connections for Rack 2 in a Four-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R2 IB3 within Rack 2 |
R2-IB3-P8A to R2-U1-P3A R2-IB3-P8B to R2-U1-P4A |
3 meters |
|
R2 IB3 to Rack 1 |
R2-IB3-P11A to R1-U1-P9A R2-IB3-P11B to R1-U1-P10A |
5 meters |
|
R2 IB3 to Rack 3 |
R2-IB3-P9A to R3-U1-P5A R2-IB3-P9B to R3-U1-P6A |
5 meters |
|
R2 IB3 to Rack 4 |
R2-IB3-P10A to R4-U1-P7A R2-IB3-P10B to R4-U1-P8A |
5 meters |
|
R2 IB2 within Rack 2 |
R2-IB2-P8A to R2-U1-P3B R2-IB2-P8B to R2-U1-P4B |
3 meters |
|
R2 IB2 to Rack 1 |
R2-IB2-P11A to R1-U1-P9B R2-IB2-P11B to R1-U1-P10B |
5 meters |
|
R2 IB2 to Rack 3 |
R2-IB2-P9A to R3-U1-P5B R2-IB2-P9B to R3-U1-P6B |
5 meters |
|
R2 IB2 to Rack 4 |
R2-IB2-P10A to R4-U1-P7B R2-IB2-P10B to R4-U1-P8B |
5 meters |
Table G-10 shows the cable connections for the third spine switch (R3-U1) when four full racks are cabled together.
Table G-10 Leaf Switch Connections for Rack 3 in a Four-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R3 IB3 within Rack 3 |
R3-IB3-P8A to R3-U1-P3A R3-IB3-P8B to R3-U1-P4A |
3 meters |
|
R3 IB3 to Rack 1 |
R3-IB3-P10A to R1-U1-P7A R3-IB3-P10B to R1-U1-P8A |
5 meters |
|
R3 IB3 to Rack 2 |
R3-IB3-P11A to R2-U1-P9A R3-IB3-P11B to R2-U1-P10A |
5 meters |
|
R3 IB3 to Rack 4 |
R3-IB3-P9A to R4-U1-P5A R3-IB3-P9B to R4-U1-P6A |
5 meters |
|
R3 IB2 within Rack 3 |
R3-IB2-P8A to R3-U1-P3B R3-IB2-P8B to R3-U1-P4B |
3 meters |
|
R3 IB2 to Rack 1 |
R3-IB2-P10A to R1-U1-P7B R3-IB2-P10B to R1-U1-P8B |
5 meters |
|
R3 IB2 to Rack 2 |
R3-IB2-P11A to R2-U1-P9B R3-IB2-P11B to R2-U1-P10B |
5 meters |
|
R3 IB2 to Rack 4 |
R3-IB2-P9A to R4-U1-P5B R3-IB2-P9B to R4-U1-P6B |
5 meters |
Table G-11 shows the cable connections for the fourth spine switch (R4-U1) when four full racks are cabled together.
Table G-11 Leaf Switch Connections for Rack 4 in a Four-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R4 IB3 within Rack 4 |
R4-IB3-P8A to R4-U1-P3A R4-IB3-P8B to R4-U1-P4A |
3 meters |
|
R4 IB3 to Rack 1 |
R4-IB3-P9A to R1-U1-P5A R4-IB3-P9B to R1-U1-P6A |
10 meters |
|
R4 IB3 to Rack 2 |
R4-IB3-P10A to R2-U1-P7A R4-IB3-P10B to R2-U1-P8A |
5 meters |
|
R4 IB3 to Rack 3 |
R4-IB3-P11A to R3-U1-P9A R4-IB3-P11B to R3-U1-P10A |
5 meters |
|
R4 IB2 within Rack 4 |
R4-IB2-P8A to R4-U1-P3B R4-IB2-P8B to R4-U1-P4B |
3 meters |
|
R4 IB2 to Rack 1 |
R4-IB2-P9A to R1-U1-P5B R4-IB2-P9B to R1-U1-P6B |
10 meters |
|
R4 IB2 to Rack 2 |
R4-IB2-P10A to R2-U1-P7B R4-IB2-P10B to R2-U1-P8B |
5 meters |
|
R4 IB2 to Rack 3 |
R4-IB2-P11A to R3-U1-P9B R4-IB2-P11B to R3-U1-P10B |
5 meters |
Five-Rack Cabling
Table G-12 shows the cable connections for the first spine switch (R1-U1) when five full racks are cabled together.
Table G-12 Leaf Switch Connections for Rack 1 in a Five-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R1 IB3 within Rack 1 |
R1-IB3-P8A to R1-U1-P3A R1-IB3-P8B to R1-U1-P4A |
3 meters |
|
R1 IB3 to Rack 2 |
R1-IB3-P9A to R2-U1-P5A R1-IB3-P9B to R2-U1-P6A |
5 meters |
|
R1 IB3 to Rack 3 |
R1-IB3-P10A to R3-U1-P7A R1-IB3-P10B to R3-U1-P8A |
5 meters |
|
R1 IB3 to Rack 4 |
R1-IB3-P11A to R4-U1-P9A |
10 meters |
|
R1 IB3 to Rack 5 |
R1-IB3-P11B to R5-U1-P10A |
10 meters |
|
R1 IB2 within Rack 1 |
R1-IB2-P8A to R1-U1-P3B R1-IB2-P8B to R1-U1-P4B |
3 meters |
|
R1 IB2 to Rack 2 |
R1-IB2-P9A to R2-U1-P5B R1-IB2-P9B to R2-U1-P6B |
5 meters |
|
R1 IB2 to Rack 3 |
R1-IB2-P10A to R3-U1-P7B R1-IB2-P10B to R3-U1-P8B |
5 meters |
|
R1 IB2 to Rack 4 |
R1-IB2-P11A to R4-U1-P9B |
10 meters |
|
R1 IB2 to Rack 5 |
R1-IB2-P11B to R5-U1-P10B |
10 meters |
Table G-13 shows the cable connections for the second spine switch (R2-U1) when five full racks are cabled together.
Table G-13 Leaf Switch Connections for Rack 2 in a Five-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R2 IB3 within Rack 2 |
R2-IB3-P8A to R2-U1-P3A R2-IB3-P8B to R2-U1-P4A |
3 meters |
|
R2 IB3 to Rack 1 |
R2-IB3-P11B to R1-U1-P10A |
5 meters |
|
R2 IB3 to Rack 3 |
R2-IB3-P9A to R3-U1-P5A R2-IB3-P9B to R3-U1-P6A |
5 meters |
|
R2 IB3 to Rack 4 |
R2-IB3-P10A to R4-U1-P7A R2-IB3-P10B to R4-U1-P8A |
5 meters |
|
R2 IB3 to Rack 5 |
R2-IB3-P11A to R5-U1-P9A |
10 meters |
|
R2 IB2 within Rack 2 |
R2-IB2-P8A to R2-U1-P3B R2-IB2-P8B to R2-U1-P4B |
3 meters |
|
R2 IB2 to Rack 1 |
R2-IB2-P11B to R1-U1-P10B |
5 meters |
|
R2 IB2 to Rack 3 |
R2-IB2-P9A to R3-U1-P5B R2-IB2-P9B to R3-U1-P6B |
5 meters |
|
R2 IB2 to Rack 4 |
R2-IB2-P10A to R4-U1-P7B R2-IB2-P10B to R4-U1-P8B |
5 meters |
|
R2 IB2 to Rack 5 |
R2-IB2-P11A to R5-U1-P9B |
10 meters |
Table G-14 shows the cable connections for the third spine switch (R3-U1) when five full racks are cabled together.
Table G-14 Leaf Switch Connections for Rack 3 in a Five-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R3 IB3 within Rack 3 |
R3-IB3-P8A to R3-U1-P3A R3-IB3-P8B to R3-U1-P4A |
3 meters |
|
R3 IB3 to Rack 1 |
R3-IB3-P11A to R1-U1-P9A |
5 meters |
|
R3 IB3 to Rack 2 |
R3-IB3-P11B to R2-U1-P10A |
5 meters |
|
R3 IB3 to Rack 4 |
R3-IB3-P9A to R4-U1-P5A R3-IB3-P9B to R4-U1-P6A |
5 meters |
|
R3 IB3 to Rack 5 |
R3-IB3-P10A to R5-U1-P7A R3-IB3-P10B to R5-U1-P8A |
5 meters |
|
R3 IB2 within Rack 3 |
R3-IB2-P8A to R3-U1-P3B R3-IB2-P8B to R3-U1-P4B |
3 meters |
|
R3 IB2 to Rack 1 |
R3-IB2-P11A to R1-U1-P9B |
5 meters |
|
R3 IB2 to Rack 2 |
R3-IB2-P11B to R2-U1-P10B |
5 meters |
|
R3 IB2 to Rack 4 |
R3-IB2-P9A to R4-U1-P5B R3-IB2-P9B to R4-U1-P6B |
5 meters |
|
R3 IB2 to Rack 5 |
R3-IB2-P10A to R5-U1-P7B R3-IB2-P10B to R5-U1-P8B |
5 meters |
Table G-15 shows the cable connections for the fourth spine switch (R4-U1) when five full racks are cabled together.
Table G-15 Leaf Switch Connections for Rack 4 in a Five-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R4 IB3 within Rack 4 |
R4-IB3-P8A to R4-U1-P3A R4-IB3-P8B to R4-U1-P4A |
3 meters |
|
R4 IB3 to Rack 1 |
R4-IB3-P10A to R1-U1-P7A R4-IB3-P10B to R1-U1-P8A |
10 meters |
|
R4 IB3 to Rack 2 |
R4-IB3-P11A to R2-U1-P9A |
5 meters |
|
R4 IB3 to Rack 3 |
R4-IB3-P11B to R3-U1-P10A |
5 meters |
|
R4 IB3 to Rack 5 |
R4-IB3-P9A to R5-U1-P5A R4-IB3-P9B to R5-U1-P6A |
5 meters |
|
R4 IB2 within Rack 4 |
R4-IB2-P8A to R4-U1-P3B R4-IB2-P8B to R4-U1-P4B |
3 meters |
|
R4 IB2 to Rack 1 |
R4-IB2-P10A to R1-U1-P7B R4-IB2-P10B to R1-U1-P8B |
10 meters |
|
R4 IB2 to Rack 2 |
R4-IB2-P11A to R2-U1-P9B |
5 meters |
|
R4 IB2 to Rack 3 |
R4-IB2-P11B to R3-U1-P10B |
5 meters |
|
R4 IB2 to Rack 5 |
R4-IB2-P9A to R5-U1-P5B R4-IB2-P9B to R5-U1-P6B |
5 meters |
Table G-16 shows the cable connections for the fifth spine switch (R5-U1) when five full racks are cabled together.
Table G-16 Leaf Switch Connections for Rack 5 in a Five-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R5 IB3 within Rack 5 |
R5-IB3-P8A to R5-U1-P3A R5-IB3-P8B to R5-U1-P4A |
3 meters |
|
R5 IB3 to Rack 1 |
R5-IB3-P9A to R1-U1-P5A R5-IB3-P9B to R1-U1-P6A |
10 meters |
|
R5 IB3 to Rack 2 |
R5-IB3-P10A to R2-U1-P7A R5-IB3-P10B to R2-U1-P8A |
10 meters |
|
R5 IB3 to Rack 3 |
R5-IB3-P11A to R3-U1-P9A |
5 meters |
|
R5 IB3 to Rack 4 |
R5-IB3-P11B to R4-U1-P10A |
5 meters |
|
R5 IB2 within Rack 5 |
R5-IB2-P8A to R5-U1-P3B R5-IB2-P8B to R5-U1-P4B |
3 meters |
|
R5 IB2 to Rack 1 |
R5-IB2-P9A to R1-U1-P5B R5-IB2-P9B to R1-U1-P6B |
10 meters |
|
R5 IB2 to Rack 2 |
R5-IB2-P10A to R2-U1-P7B R5-IB3-P10B to R2-U1-P8B |
10 meters |
|
R5 IB2 to Rack 3 |
R5-IB2-P11A to R3-U1-P9B |
5 meters |
|
R5 IB2 to Rack 4 |
R5-IB2-P11B to R4-U1-P10B |
5 meters |
Six-Rack Cabling
Table G-17 shows the cable connections for the first spine switch (R1-U1) when six full racks are cabled together.
Table G-17 Leaf Switch Connections for Rack 1 in a Six-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R1 IB3 within Rack 1 |
R1-IB3-P8A to R1-U1-P3A R1-IB3-P8B to R1-U1-P4A |
3 meters |
|
R1 IB3 to Rack 2 |
R1-IB3-P9A to R2-U1-P5A R1-IB3-P9B to R2-U1-P6A |
5 meters |
|
R1 IB3 to Rack 3 |
R1-IB3-P10A to R3-U1-P7A |
5 meters |
|
R1 IB3 to Rack 4 |
R1-IB3-P10B to R4-U1-P8A |
10 meters |
|
R1 IB3 to Rack 5 |
R1-IB3-P11A to R5-U1-P9A |
10 meters |
|
R1 IB3 to Rack 6 |
R1-IB3-P11B to R6-U1-P10A |
10 meters |
|
R1 IB2 within Rack 1 |
R1-IB2-P8A to R1-U1-P3B R1-IB2-P8B to R1-U1-P4B |
3 meters |
|
R1 IB2 to Rack 2 |
R1-IB2-P9A to R2-U1-P5B R1-IB2-P9B to R2-U1-P6B |
5 meters |
|
R1 IB2 to Rack 3 |
R1-IB2-P10A to R3-U1-P7B |
5 meters |
|
R1 IB2 to Rack 4 |
R1-IB2-P10B to R4-U1-P8B |
10 meters |
|
R1 IB2 to Rack 5 |
R1-IB2-P11A to R5-U1-P9B |
10 meters |
|
R1 IB2 to Rack 6 |
R1-IB2-P11B to R6-U1-P10B |
10 meters |
Table G-18 shows the cable connections for the second spine switch (R2-U1) when six full racks are cabled together.
Table G-18 Leaf Switch Connections for Rack 2 in a Six-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R2 IB3 within Rack 2 |
R2-IB3-P8A to R2-U1-P3A R2-IB3-P8B to R2-U1-P4A |
3 meters |
|
R2 IB3 to Rack 1 |
R2-IB3-P11B to R1-U1-P10A |
5 meters |
|
R2 IB3 to Rack 3 |
R2-IB3-P9A to R3-U1-P5A R2-IB3-P9B to R3-U1-P6A |
5 meters |
|
R2 IB3 to Rack 4 |
R2-IB3-P10A to R4-U1-P7A |
5 meters |
|
R2 IB3 to Rack 5 |
R2-IB3-P10B to R5-U1-P8A |
10 meters |
|
R2 IB3 to Rack 6 |
R2-IB3-P11Ato R6-U1-P9A |
10 meters |
|
R2 IB2 within Rack 2 |
R2-IB2-P8A to R2-U1-P3B R2-IB2-P8B to R2-U1-P4B |
3 meters |
|
R2 IB2 to Rack 1 |
R2-IB2-P11B to R1-U1-P10B |
5 meters |
|
R2 IB2 to Rack 3 |
R2-IB2-P9A to R3-U1-P5B R2-IB2-P9B to R3-U1-P6B |
5 meters |
|
R2 IB2 to Rack 4 |
R2-IB2-P10A to R4-U1-P7B |
5 meters |
|
R2 IB2 to Rack 5 |
R2-IB2-P10B to R5-U1-P8B |
10 meters |
|
R2 IB2 to Rack 6 |
R2-IB2-P11Ato R6-U1-P9B |
10 meters |
Table G-19 shows the cable connections for the third spine switch (R3-U1) when six full racks are cabled together.
Table G-19 Leaf Switch Connections for Rack 3 in a Six-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R3 IB3 within Rack 3 |
R3-IB3-P8A to R3-U1-P3A R3-IB3-P8B to R3-U1-P4A |
3 meters |
|
R3 IB3 to Rack 1 |
R3-IB3-P11A to R1-U1-P9A |
5 meters |
|
R3 IB3 to Rack 2 |
R3-IB3-P11B to R2-U1-P10A |
5 meters |
|
R3 IB3 to Rack 4 |
R3-IB3-P9A to R4-U1-P5A R3-IB3-P9B to R4-U1-P6A |
5 meters |
|
R3 IB3 to Rack 5 |
R3-IB3-P10A to R5-U1-P7A |
5 meters |
|
R3 IB3 to Rack 6 |
R3-IB3-P10B to R6-U1-P8A |
10 meters |
|
R3 IB2 within Rack 3 |
R3-IB2-P8A to R3-U1-P3B R3-IB2-P8B to R3-U1-P4B |
3 meters |
|
R3 IB2 to Rack 1 |
R3-IB2-P11A to R1-U1-P9B |
5 meters |
|
R3 IB2 to Rack 2 |
R3-IB2-P11B to R2-U1-P10B |
5 meters |
|
R3 IB2 to Rack 4 |
R3-IB2-P9A to R4-U1-P5B R3-IB2-P9B to R4-U1-P6B |
5 meters |
|
R3 IB2 to Rack 5 |
R3-IB2-P10A to R5-U1-P7B |
5 meters |
|
R3 IB2 to Rack 6 |
R3-IB2-P10B to R6-U1-P8B |
10 meters |
Table G-20 shows the cable connections for the fourth spine switch (R4-U1) when six full racks are cabled together.
Table G-20 Leaf Switch Connections for Rack 4 in a Six-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R4 IB3 within Rack 4 |
R4-IB3-P8A to R4-U1-P3A R4-IB3-P8B to R4-U1-P4A |
3 meters |
|
R4 IB3 to Rack 1 |
R4-IB3-P10B to R1-U1-P8A |
10 meters |
|
R4 IB3 to Rack 2 |
R4-IB3-P11A to R2-U1-P9A |
5 meters |
|
R4 IB3 to Rack 3 |
R4-IB3-P11B to R3-U1-P10A |
5 meters |
|
R4 IB3 to Rack 5 |
R4-IB3-P9A to R5-U1-P5A R4-IB3-P9B to R5-U1-P6A |
5 meters |
|
R4 IB3 to Rack 6 |
R4-IB3-P10A to R6-U1-P7A |
5 meters |
|
R4 IB2 within Rack 4 |
R4-IB2-P8A to R4-U1-P3B R4-IB2-P8B to R4-U1-P4B |
3 meters |
|
R4 IB2 to Rack 1 |
R4-IB2-P10B to R1-U1-P8B |
10 meters |
|
R4 IB2 to Rack 2 |
R4-IB2-P11A to R2-U1-P9B |
5 meters |
|
R4 IB2 to Rack 3 |
R4-IB2-P11B to R3-U1-P10B |
5 meters |
|
R4 IB2 to Rack 5 |
R4-IB2-P9A to R5-U1-P5B R4-IB2-P9B to R5-U1-P6B |
5 meters |
|
R4 IB2 to Rack 6 |
R4-IB2-P10A to R6-U1-P7B |
5 meters |
Table G-21 shows the cable connections for the fifth spine switch (R5-U1) when six full racks are cabled together.
Table G-21 Leaf Switch Connections for Rack 5 in a Six-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R5 IB3 within Rack 5 |
R5-IB3-P8A to R5-U1-P3A R5-IB3-P8B to R5-U1-P4A |
3 meters |
|
R5 IB3 to Rack 1 |
R5-IB3-P10A to R1-U1-P7A |
10 meters |
|
R5 IB3 to Rack 2 |
R5-IB3-P10B to R2-U1-P8A |
10 meters |
|
R5 IB3 to Rack 3 |
R5-IB3-P11A to R3-U1-P9A |
5 meters |
|
R5 IB3 to Rack 4 |
R5-IB3-P11B to R4-U1-P10A |
5 meters |
|
R5 IB3 to Rack 6 |
R5-IB3-P9A to R6-U1-P5A R5-IB3-P9B to R6-U1-P6A |
5 meters |
|
R5 IB2 within Rack 5 |
R5-IB2-P8A to R5-U1-P3B R5-IB2-P8B to R5-U1-P4B |
3 meters |
|
R5 IB2 to Rack 1 |
R5-IB2-P10A to R1-U1-P7B |
10 meters |
|
R5 IB2 to Rack 2 |
R5-IB3-P10B to R2-U1-P8B |
10 meters |
|
R5 IB2 to Rack 3 |
R5-IB2-P11A to R3-U1-P9B |
5 meters |
|
R5 IB2 to Rack 4 |
R5-IB2-P11B to R4-U1-P10B |
5 meters |
|
R5 IB2 to Rack 6 |
R5-IB2-P9A to R6-U1-P5B R5-IB2-P9B to R6-U1-P6B |
5 meters |
Table G-22 shows the cable connections for the sixth spine switch (R6-U1) when six full racks are cabled together.
Table G-22 Leaf Switch Connections for Rack 6 in a Six-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R6 IB3 within Rack 6 |
R6-IB3-P8A to R6-U1-P3A R6-IB3-P8B to R6-U1-P4A |
3 meters |
|
R6 IB3 to Rack 1 |
R6-IB3-P9A to R1-U1-P5A R6-IB3-P9B to R1-U1-P6A |
10 meters |
|
R6 IB3 to Rack 2 |
R6-IB3-P10A to R2-U1-P7A |
10 meters |
|
R6 IB3 to Rack 3 |
R6-IB3-P10B to R3-U1-P8A |
10 meters |
|
R6 IB3 to Rack 4 |
R6-IB3-P11A to R4-U1-P9A |
5 meters |
|
R6 IB3 to Rack 5 |
R6-IB3-P11B to R5-U1-P10A |
5 meters |
|
R6 IB2 within Rack 6 |
R6-IB2-P8A to R6-U1-P3B R6-IB2-P8B to R6-U1-P4B |
3 meters |
|
R6 IB2 to Rack 1 |
R6-IB2-P9A to R1-U1-P5B R6-IB2-P9B to R1-U1-P6B |
10 meters |
|
R6 IB2 to Rack 2 |
R6-IB3-P10A to R2-U1-P7B |
10 meters |
|
R6 IB2 to Rack 3 |
R6-IB2-P10B to R3-U1-P8B |
10 meters |
|
R6 IB2 to Rack 4 |
R6-IB2-P11A to R4-U1-P9B |
5 meters |
|
R6 IB2 to Rack 5 |
R6-IB2-P11B to R5-U1-P10B |
5 meters |
Seven-Rack Cabling
Table G-23 shows the cable connections for the first spine switch (R1-U1) when seven racks are cabled together.
Table G-23 Leaf Switch Connections for Rack 1 in a Seven-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R1 IB3 within Rack 1 |
R1-IB3-P8A to R1-U1-P3A R1-IB3-P8B to R1-U1-P4A |
3 meters |
|
R1 IB3 to Rack 2 |
R1-IB3-P9A to R2-U1-P5A |
5 meters |
|
R1 IB3 to Rack 3 |
R1-IB3-P9B to R3-U1-P6A |
5 meters |
|
R1 IB3 to Rack 4 |
R1-IB3-P10A to R4-U1-P7A |
10 meters |
|
R1 IB3 to Rack 5 |
R1-IB3-P10B to R5-U1-P8A |
10 meters |
|
R1 IB3 to Rack 6 |
R1-IB3-P11A to R6-U1-P9A |
10 meters |
|
R1 IB3 to Rack 7 |
R1-IB3-P11B to R7-U1-P10A |
10 meters |
|
R1 IB2 within Rack 1 |
R1-IB2-P8A to R1-U1-P3B R1-IB2-P8B to R1-U1-P4B |
3 meters |
|
R1 IB2 to Rack 2 |
R1-IB2-P9A to R2-U1-P5B |
5 meters |
|
R1 IB2 to Rack 3 |
R1-IB2-P9B to R3-U1-P6B |
5 meters |
|
R1 IB2 to Rack 4 |
R1-IB2-P10A to R4-U1-P7B |
10 meters |
|
R1 IB2 to Rack 5 |
R1-IB2-P10B to R5-U1-P8B |
10 meters |
|
R1 IB2 to Rack 6 |
R1-IB2-P11A to R6-U1-P9B |
10 meters |
|
R1 IB2 to Rack 7 |
R1-IB2-P11B to R7-U1-P10B |
10 meters |
Table G-24 shows the cable connections for the second spine switch (R2-U1) when seven full racks are cabled together.
Table G-24 Leaf Switch Connections for Rack 2 in a Seven-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R2 IB3 within Rack 2 |
R2-IB3-P8A to R2-U1-P3A R2-IB3-P8B to R2-U1-P4A |
3 meters |
|
R2 IB3 to Rack 1 |
R2-IB3-P11B to R1-U1-P10A |
5 meters |
|
R2 IB3 to Rack 3 |
R2-IB3-P9A to R3-U1-P5A |
5 meters |
|
R2 IB3 to Rack 4 |
R2-IB3-P9B to R4-U1-P6A |
5 meters |
|
R2 IB3 to Rack 5 |
R2-IB3-P10A to R5-U1-P7A |
10 meters |
|
R2 IB3 to Rack 6 |
R2-IB3-P10B to R6-U1-P8A |
10 meters |
|
R2 IB3 to Rack 7 |
R2-IB3-P11A to R7-U1-P9A |
10 meters |
|
R2 IB2 within Rack 2 |
R2-IB2-P8A to R2-U1-P3B R2-IB2-P8B to R2-U1-P4B |
3 meters |
|
R2 IB2 to Rack 1 |
R2-IB2-P11B to R1-U1-P10B |
5 meters |
|
R2 IB2 to Rack 3 |
R2-IB2-P9A to R3-U1-P5B |
5 meters |
|
R2 IB2 to Rack 4 |
R2-IB2-P9B to R4-U1-P6B |
5 meters |
|
R2 IB2 to Rack 5 |
R2-IB2-P10A to R5-U1-P7B |
10 meters |
|
R2 IB2 to Rack 6 |
R2-IB2-P10Bto R6-U1-P8B |
10 meters |
|
R2 IB2 to Rack 7 |
R2-IB2-P11A to R7-U1-P9B |
10 meters |
Table G-25 shows the cable connections for the third spine switch (R3-U1) when seven full racks are cabled together.
Table G-25 Leaf Switch Connections for Rack 3 in a Seven-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R3 IB3 within Rack 3 |
R3-IB3-P8A to R3-U1-P3A R3-IB3-P8B to R3-U1-P4A |
3 meters |
|
R3 IB3 to Rack 1 |
R3-IB3-P11A to R1-U1-P9A |
5 meters |
|
R3 IB3 to Rack 2 |
R3-IB3-P11B to R2-U1-P10A |
5 meters |
|
R3 IB3 to Rack 4 |
R3-IB3-P9A to R4-U1-P5A |
5 meters |
|
R3 IB3 to Rack 5 |
R3-IB3-P9B to R5-U1-P6A |
5 meters |
|
R3 IB3 to Rack 6 |
R3-IB3-P10A to R6-U1-P7A |
10 meters |
|
R3 IB3 to Rack 7 |
R3-IB3-P10B to R7-U1-P8A |
10 meters |
|
R3 IB2 within Rack 3 |
R3-IB2-P8A to R3-U1-P3B R3-IB2-P8B to R3-U1-P4B |
3 meters |
|
R3 IB2 to Rack 1 |
R3-IB2-P11A to R1-U1-P9B |
5 meters |
|
R3 IB2 to Rack 2 |
R3-IB2-P11B to R2-U1-P10B |
5 meters |
|
R3 IB2 to Rack 4 |
R3-IB2-P9A to R4-U1-P5B |
5 meters |
|
R3 IB2 to Rack 5 |
R3-IB2-P9B to R5-U1-P6B |
5 meters |
|
R3 IB2 to Rack 6 |
R3-IB2-P10A to R6-U1-P7B |
10 meters |
|
R3 IB2 to Rack 7 |
R3-IB2-P10B to R7-U1-P8B |
10 meters |
Table G-26 shows the cable connections for the fourth spine switch (R4-U1) when seven full racks are cabled together.
Table G-26 Leaf Switch Connections for Rack 4 in a Seven-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R4 IB3 within Rack 4 |
R4-IB3-P8A to R4-U1-P3A R4-IB3-P8B to R4-U1-P4A |
3 meters |
|
R4 IB3 to Rack 1 |
R4-IB3-P10B to R1-U1-P8A |
10 meters |
|
R4 IB3 to Rack 2 |
R4-IB3-P11A to R2-U1-P9A |
5 meters |
|
R4 IB3 to Rack 3 |
R4-IB3-P11B to R3-U1-P10A |
5 meters |
|
R4 IB3 to Rack 5 |
R4-IB3-P9A to R5-U1-P5A |
5 meters |
|
R4 IB3 to Rack 6 |
R4-IB3-P9B to R6-U1-P6A |
5 meters |
|
R4 IB3 to Rack 7 |
R4-IB3-P10A to R7-U1-P7A |
10 meters |
|
R4 IB2 within Rack 4 |
R4-IB2-P8A to R4-U1-P3B R4-IB2-P8B to R4-U1-P4B |
3 meters |
|
R4 IB2 to Rack 1 |
R4-IB2-P10B to R1-U1-P8B |
10 meters |
|
R4 IB2 to Rack 2 |
R4-IB2-P11A to R2-U1-P9B |
5 meters |
|
R4 IB2 to Rack 3 |
R4-IB2-P11B to R3-U1-P10B |
5 meters |
|
R4 IB2 to Rack 5 |
R4-IB2-P9A to R5-U1-P5B |
5 meters |
|
R4 IB2 to Rack 6 |
R4-IB2-P9B to R6-U1-P6B |
5 meters |
|
R4 IB2 to Rack 7 |
R4-IB2-P10A to R7-U1-P7B |
10 meters |
Table G-27 shows the cable connections for the fifth spine switch (R5-U1) when seven full racks are cabled together.
Table G-27 Leaf Switch Connections for Rack 5 in a Seven-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R5 IB3 within Rack 5 |
R5-IB3-P8A to R5-U1-P3A R5-IB3-P8B to R5-U1-P4A |
3 meters |
|
R5 IB3 to Rack 1 |
R5-IB3-P10A to R1-U1-P7A |
10 meters |
|
R5 IB3 to Rack 2 |
R5-IB3-P10B to R2-U1-P8A |
10 meters |
|
R5 IB3 to Rack 3 |
R5-IB3-P11A to R3-U1-P9A |
5 meters |
|
R5 IB3 to Rack 4 |
R5-IB3-P11B to R4-U1-P10A |
5 meters |
|
R5 IB3 to Rack 6 |
R5-IB3-P9A to R6-U1-P5A |
5 meters |
|
R5 IB3 to Rack 7 |
R5-IB3-P9B to R7-U1-P6A |
5 meters |
|
R5 IB2 within Rack 5 |
R5-IB2-P8A to R5-U1-P3B R5-IB2-P8B to R5-U1-P4B |
3 meters |
|
R5 IB2 to Rack 1 |
R5-IB2-P10A to R1-U1-P7B |
10 meters |
|
R5 IB2 to Rack 2 |
R5-IB3-P10B to R2-U1-P8B |
10 meters |
|
R5 IB2 to Rack 3 |
R5-IB2-P11A to R3-U1-P9B |
5 meters |
|
R5 IB2 to Rack 4 |
R5-IB2-P11B to R4-U1-P10B |
5 meters |
|
R5 IB2 to Rack 6 |
R5-IB2-P9A to R6-U1-P5B |
5 meters |
|
R5 IB2 to Rack 7 |
R5-IB2-P9B to R7-U1-P6B |
5 meters |
Table G-28 shows the cable connections for the sixth spine switch (R6-U1) when seven full racks are cabled together.
Table G-28 Leaf Switch Connections for Rack 6 in a Seven-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R6 IB3 within Rack 6 |
R6-IB3-P8A to R6-U1-P3A R6-IB3-P8B to R6-U1-P4A |
3 meters |
|
R6 IB3 to Rack 1 |
R6-IB3-P9B to R1-U1-P6A |
10 meters |
|
R6 IB3 to Rack 2 |
R6-IB3-P10A to R2-U1-P7A |
10 meters |
|
R6 IB3 to Rack 3 |
R6-IB3-P10B to R3-U1-P8A |
10 meters |
|
R6 IB3 to Rack 4 |
R6-IB3-P11A to R4-U1-P9A |
5 meters |
|
R6 IB3 to Rack 5 |
R6-IB3-P11B to R5-U1-P10A |
5 meters |
|
R6 IB3 to Rack 7 |
R6-IB3-P9A to R7-U1-P5A |
5 meters |
|
R6 IB2 within Rack 6 |
R6-IB2-P8A to R6-U1-P3B R6-IB2-P8B to R6-U1-P4B |
3 meters |
|
R6 IB2 to Rack 1 |
R6-IB2-P9B to R1-U1-P6B |
10 meters |
|
R6 IB2 to Rack 2 |
R6-IB3-P10A to R2-U1-P7B |
10 meters |
|
R6 IB2 to Rack 3 |
R6-IB2-P10B to R3-U1-P8B |
10 meters |
|
R6 IB2 to Rack 4 |
R6-IB2-P11A to R4-U1-P9B |
5 meters |
|
R6 IB2 to Rack 5 |
R6-IB2-P11B to R5-U1-P10B |
5 meters |
|
R6 IB2 to Rack 7 |
R6-IB3-P9A to R7-U1-P5B |
5 meters |
Table G-29 shows the cable connections for the seventh spine switch (R7-U1) when seven full racks are cabled together.
Table G-29 Leaf Switch Connections for Rack 7 in a Seven-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R7 IB3 within Rack 7 |
R7-IB3-P8A to R7-U1-P3A R7-IB3-P8B to R7-U1-P4A |
3 meters |
|
R7 IB3 to Rack 1 |
R7-IB3-P9A to R1-U1-P5A |
10 meters |
|
R7 IB3 to Rack 2 |
R7-IB3-P9B to R2-U1-P6A |
10 meters |
|
R7 IB3 to Rack 3 |
R7-IB3-P10A to R3-U1-P7A |
10 meters |
|
R7 IB3 to Rack 4 |
R7-IB3-P10B to R4-U1-P8A |
10 meters |
|
R7 IB3 to Rack 5 |
R7-IB3-P11A to R5-U1-P9A |
5 meters |
|
R7 IB3 to Rack 6 |
R7-IB3-P11B to R6-U1-P10A |
5 meters |
|
R7 IB2 within Rack 7 |
R7-IB2-P8A to R7-U1-P3B R7-IB2-P8B to R7-U1-P4B |
3 meters |
|
R7 IB2 to Rack 1 |
R7-IB2-P9A to R1-U1-P5B |
10 meters |
|
R7 IB2 to Rack 2 |
R7-IB3-P9B to R2-U1-P6B |
10 meters |
|
R7 IB2 to Rack 3 |
R7-IB2-P10A to R3-U1-P7B |
10 meters |
|
R7 IB2 to Rack 4 |
R7-IB2-P10B to R4-U1-P8B |
10 meters |
|
R7 IB2 to Rack 5 |
R7-IB2-P11A to R5-U1-P9B |
5 meters |
|
R7 IB2 to Rack 6 |
R7-IB3-P11B to R6-U1-P10B |
5 meters |
Eight-Rack Cabling
Table G-30 shows the cable connections for the first spine switch (R1-U1) when eight full racks are cabled together.
Table G-30 Leaf Switch Connections for Rack 1 in an Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R1 IB3 within Rack 1 |
R1-IB3-P8A to R1-U1-P3A |
3 meters |
|
R1 IB3 to Rack 2 |
R1-IB3-P8B to R2-U1-P4A |
5 meters |
|
R1 IB3 to Rack 3 |
R1-IB3-P9A to R3-U1-P5A |
5 meters |
|
R1 IB3 to Rack 4 |
R1-IB3-P9B to R4-U1-P6A |
10 meters |
|
R1 IB3 to Rack 5 |
R1-IB3-P10A to R5-U1-P7A |
10 meters |
|
R1 IB3 to Rack 6 |
R1-IB3-P10B to R6-U1-P8A |
10 meters |
|
R1 IB3 to Rack 7 |
R1-IB3-P11A to R7-U1-P9A |
10 meters |
|
R1 IB3 to Rack 8 |
R1-IB3-P11B to R8-U1-P10A |
10 meters |
|
R1 IB2 within Rack 1 |
R1-IB2-P8A to R1-U1-P3B |
3 meters |
|
R1 IB2 to Rack 2 |
R1-IB2-P8B to R2-U1-P4B |
5 meters |
|
R1 IB2 to Rack 3 |
R1-IB2-P9A to R3-U1-P5B |
5 meters |
|
R1 IB2 to Rack 4 |
R1-IB2-P9B to R4-U1-P6B |
10 meters |
|
R1 IB2 to Rack 5 |
R1-IB2-P10A to R5-U1-P7B |
10 meters |
|
R1 IB2 to Rack 6 |
R1-IB2-P10B to R6-U1-P8B |
10 meters |
|
R1 IB2 to Rack 7 |
R1-IB2-P11A to R7-U1-P9B |
10 meters |
|
R1 IB2 to Rack 8 |
R1-IB2-P11B to R8-U1-P10B |
10 meters |
Table G-31 shows the cable connections for the second spine switch (R2-U1) when eight full racks are cabled together.
Table G-31 Leaf Switch Connections for Rack 2 in an Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R2 IB3 within Rack 2 |
R2-IB3-P8A to R2-U1-P3A |
3 meters |
|
R2 IB3 to Rack 1 |
R2-IB3-P11B to R1-U1-P10A |
5 meters |
|
R2 IB3 to Rack 3 |
R2-IB3-P8B to R3-U1-P4A |
5 meters |
|
R2 IB3 to Rack 4 |
R2-IB3-P9A to R4-U1-P5A |
5 meters |
|
R2 IB3 to Rack 5 |
R2-IB3-P9B to R5-U1-P6A |
10 meters |
|
R2 IB3 to Rack 6 |
R2-IB3-P10A to R6-U1-P7A |
10 meters |
|
R2 IB3 to Rack 7 |
R2-IB3-P10B to R7-U1-P8A |
10 meters |
|
R2 IB3 to Rack 8 |
R2-IB3-P11A to R8-U1-P9A |
10 meters |
|
R2 IB2 within Rack 2 |
R2-IB2-P8A to R2-U1-P3B |
3 meters |
|
R2 IB2 to Rack 1 |
R2-IB2-P11B to R1-U1-P10B |
5 meters |
|
R2 IB2 to Rack 3 |
R2-IB2-P8B to R3-U1-P4B |
5 meters |
|
R2 IB2 to Rack 4 |
R2-IB2-P9A to R4-U1-P5B |
5 meters |
|
R2 IB2 to Rack 5 |
R2-IB2-P9B to R5-U1-P6B |
10 meters |
|
R2 IB2 to Rack 6 |
R2-IB2-P10A to R6-U1-P7B |
10 meters |
|
R2 IB2 to Rack 7 |
R2-IB2-P10B to R7-U1-P8B |
10 meters |
|
R2 IB2 to Rack 8 |
R2-IB2-P11A to R8-U1-P9B |
10 meters |
Table G-32 shows the cable connections for the third spine switch (R3-U1) when eight full racks are cabled together.
Table G-32 Leaf Switch Connections for Rack 3 in an Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R3 IB3 within Rack 3 |
R3-IB3-P8A to R3-U1-P3A |
3 meters |
|
R3 IB3 to Rack 1 |
R3-IB3-P11A to R1-U1-P9A |
5 meters |
|
R3 IB3 to Rack 2 |
R3-IB3-P11B to R2-U1-P10A |
5 meters |
|
R3 IB3 to Rack 4 |
R3-IB3-P8B to R4-U1-P4A |
5 meters |
|
R3 IB3 to Rack 5 |
R3-IB3-P9A to R5-U1-P5A |
5 meters |
|
R3 IB3 to Rack 6 |
R3-IB3-P9B to R6-U1-P6A |
10 meters |
|
R3 IB3 to Rack 7 |
R3-IB3-P10A to R7-U1-P7A |
10 meters |
|
R3 IB3 to Rack 8 |
R3-IB3-P10B to R8-U1-P8A |
10 meters |
|
R3 IB2 within Rack 3 |
R3-IB2-P8A to R3-U1-P3B |
3 meters |
|
R3 IB2 to Rack 1 |
R3-IB2-P11A to R1-U1-P9B |
5 meters |
|
R3 IB2 to Rack 2 |
R3-IB2-P11B to R2-U1-P10B |
5 meters |
|
R3 IB2 to Rack 4 |
R3-IB2-P8B to R4-U1-P4B |
5 meters |
|
R3 IB2 to Rack 5 |
R3-IB2-P9A to R5-U1-P5B |
5 meters |
|
R3 IB2 to Rack 6 |
R3-IB2-P9B to R6-U1-P6B |
10 meters |
|
R3 IB2 to Rack 7 |
R3-IB2-P10A to R7-U1-P7B |
10 meters |
|
R3 IB2 to Rack 8 |
R3-IB2-P10B to R8-U1-P8B |
10 meters |
Table G-33 shows the cable connections for the fourth spine switch (R4-U1) when eight full racks are cabled together.
Table G-33 Leaf Switch Connections for Rack 4 in an Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R4 IB3 within Rack 4 |
R4-IB3-P8A to R4-U1-P3A |
3 meters |
|
R4 IB3 to Rack 1 |
R4-IB3-P10B to R1-U1-P8A |
10 meters |
|
R4 IB3 to Rack 2 |
R4-IB3-P11A to R2-U1-P9A |
5 meters |
|
R4 IB3 to Rack 3 |
R4-IB3-P11B to R3-U1-P10A |
5 meters |
|
R4 IB3 to Rack 5 |
R4-IB3-P8B to R5-U1-P4A |
5 meters |
|
R4 IB3 to Rack 6 |
R4-IB3-P9A to R6-U1-P5A |
5 meters |
|
R4 IB3 to Rack 7 |
R4-IB3-P9B to R7-U1-P6A |
10 meters |
|
R4 IB3 to Rack 8 |
R4-IB3-P10A to R8-U1-P7A |
10 meters |
|
R4 IB2 within Rack 4 |
R4-IB2-P8A to R4-U1-P3B |
3 meters |
|
R4 IB2 to Rack 1 |
R4-IB2-P10B to R1-U1-P8B |
10 meters |
|
R4 IB2 to Rack 2 |
R4-IB2-P11A to R2-U1-P9B |
5 meters |
|
R4 IB2 to Rack 3 |
R4-IB2-P11B to R3-U1-P10B |
5 meters |
|
R4 IB2 to Rack 5 |
R4-IB2-P8B to R5-U1-P4B |
5 meters |
|
R4 IB2 to Rack 6 |
R4-IB2-P9A to R6-U1-P5B |
5 meters |
|
R4 IB2 to Rack 7 |
R4-IB2-P9B to R7-U1-P6B |
10 meters |
|
R4 IB2 to Rack 8 |
R4-IB2-P10A to R8-U1-P7B |
10 meters |
Table G-34 shows the cable connections for the fifth spine switch (R5-U1) when eight full racks are cabled together.
Table G-34 Leaf Switch Connections for Rack 5 in a Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R5 IB3 within Rack 5 |
R5-IB3-P8A to R5-U1-P3A |
3 meters |
|
R5 IB3 to Rack 1 |
R5-IB3-P10A to R1-U1-P7A |
10 meters |
|
R5 IB3 to Rack 2 |
R5-IB3-P10B to R2-U1-P8A |
10 meters |
|
R5 IB3 to Rack 3 |
R5-IB3-P11A to R3-U1-P9A |
5 meters |
|
R5 IB3 to Rack 4 |
R5-IB3-P11B to R4-U1-P10A |
5 meters |
|
R5 IB3 to Rack 6 |
R5-IB3-P8B to R6-U1-P4A |
5 meters |
|
R5 IB3 to Rack 7 |
R5-IB3-P9A to R7-U1-P5A |
5 meters |
|
R5 IB3 to Rack 8 |
R5-IB3-P9B to R8-U1-P6A |
10 meters |
|
R5 IB2 within Rack 5 |
R5-IB2-P8A to R5-U1-P3B |
3 meters |
|
R5 IB2 to Rack 1 |
R5-IB2-P10A to R1-U1-P7B |
10 meters |
|
R5 IB2 to Rack 2 |
R5-IB3-P10B to R2-U1-P8B |
10 meters |
|
R5 IB2 to Rack 3 |
R5-IB2-P11A to R3-U1-P9B |
5 meters |
|
R5 IB2 to Rack 4 |
R5-IB2-P11B to R4-U1-P10B |
5 meters |
|
R5 IB2 to Rack 6 |
R5-IB2-P8B to R6-U1-P4B |
5 meters |
|
R5 IB2 to Rack 7 |
R5-IB2-P9A to R7-U1-P5B |
5 meters |
|
R5 IB2 to Rack 8 |
R5-IB2-P9B to R8-U1-P6B |
10 meters |
Table G-35 shows the cable connections for the sixth spine switch (R6-U1) when eight full racks are cabled together.
Table G-35 Leaf Switch Connections for Rack 6 in a Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R6 IB3 within Rack 6 |
R6-IB3-P8A to R6-U1-P3A |
3 meters |
|
R6 IB3 to Rack 1 |
R6-IB3-P9B to R1-U1-P6A |
10 meters |
|
R6 IB3 to Rack 2 |
R6-IB3-P10A to R2-U1-P7A |
10 meters |
|
R6 IB3 to Rack 3 |
R6-IB3-P10B to R3-U1-P8A |
10 meters |
|
R6 IB3 to Rack 4 |
R6-IB3-P11A to R4-U1-P9A |
5 meters |
|
R6 IB3 to Rack 5 |
R6-IB3-P11B to R5-U1-P10A |
5 meters |
|
R6 IB3 to Rack 7 |
R6-IB3-P8B to R7-U1-P4A |
5 meters |
|
R6 IB3 to Rack 8 |
R6-IB3-P9A to R8-U1-P5A |
5 meters |
|
R6 IB2 within Rack 6 |
R6-IB2-P8A to R6-U1-P3B |
3 meters |
|
R6 IB2 to Rack 1 |
R6-IB2-P9B to R1-U1-P6B |
10 meters |
|
R6 IB2 to Rack 2 |
R6-IB3-P10A to R2-U1-P7B |
10 meters |
|
R6 IB2 to Rack 3 |
R6-IB2-P10B to R3-U1-P8B |
10 meters |
|
R6 IB2 to Rack 4 |
R6-IB2-P11A to R4-U1-P9B |
5 meters |
|
R6 IB2 to Rack 5 |
R6-IB2-P11B to R5-U1-P10B |
5 meters |
|
R6 IB2 to Rack 7 |
R6-IB3-P8B to R7-U1-P4B |
5 meters |
|
R6 IB2 to Rack 8 |
R6-IB2-P9A to R8-U1-P5B |
5 meters |
Table G-36 shows the cable connections for the seventh spine switch (R7-U1) when eight full racks are cabled together.
Table G-36 Leaf Switch Connections for Rack 7 in a Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R7 IB3 within Rack 7 |
R7-IB3-P8A to R7-U1-P3A |
3 meters |
|
R7 IB3 to Rack 1 |
R7-IB3-P9A to R1-U1-P5A |
10 meters |
|
R7 IB3 to Rack 2 |
R7-IB3-P9B to R2-U1-P6A |
10 meters |
|
R7 IB3 to Rack 3 |
R7-IB3-P10A to R3-U1-P7A |
10 meters |
|
R7 IB3 to Rack 4 |
R7-IB3-P10B to R4-U1-P8A |
10 meters |
|
R7 IB3 to Rack 5 |
R7-IB3-P11A to R5-U1-P9A |
5 meters |
|
R7 IB3 to Rack 6 |
R7-IB3-P11B to R6-U1-P10A |
5 meters |
|
R7 IB3 to Rack 8 |
R7-IB3-P8B to R8-U1-P4A |
5 meters |
|
R7 IB2 within Rack 7 |
R7-IB2-P8A to R7-U1-P3B |
3 meters |
|
R7 IB2 to Rack 1 |
R7-IB2-P9A to R1-U1-P5B |
10 meters |
|
R7 IB2 to Rack 2 |
R7-IB3-P9B to R2-U1-P6B |
10 meters |
|
R7 IB2 to Rack 3 |
R7-IB2-P10A to R3-U1-P7B |
10 meters |
|
R7 IB2 to Rack 4 |
R7-IB2-P10B to R4-U1-P8B |
10 meters |
|
R7 IB2 to Rack 5 |
R7-IB2-P11A to R5-U1-P9B |
5 meters |
|
R7 IB2 to Rack 6 |
R7-IB3-P11B to R6-U1-P10B |
5 meters |
|
R7 IB2 to Rack 8 |
R7-IB3-P8B to R8-U1-P4B |
5 meters |
Table G-37 shows the cable connections for the eighth spine switch (R8-U1) when eight full racks are cabled together.
Table G-37 Leaf Switch Connections for Rack 8 in a Eight-Rack System
| Leaf Switch | Connection | Cable Length |
|---|---|---|
|
R8 IB3 within Rack 8 |
R8-IB3-P8A to R8-U1-P3A |
3 meters |
|
R8 IB3 to Rack 1 |
R8-IB3-P8B to R1-U1-P4A |
10 meters |
|
R8 IB3 to Rack 2 |
R8-IB3-P9A to R2-U1-P5A |
10 meters |
|
R8 IB3 to Rack 3 |
R8-IB3-P9B to R3-U1-P6A |
10 meters |
|
R8 IB3 to Rack 4 |
R8-IB3-P10A to R4-U1-P7A |
10 meters |
|
R8 IB3 to Rack 5 |
R8-IB3-P10B to R5-U1-P8A |
10 meters |
|
R8 IB3 to Rack 6 |
R8-IB3-P11A to R6-U1-P9A |
5 meters |
|
R8 IB3 to Rack 7 |
R8-IB3-P11B to R7-U1-P10A |
5 meters |
|
R8 IB2 within Rack 8 |
R8-IB2-P8A to R8-U1-P3B |
3 meters |
|
R8 IB2 to Rack 1 |
R8-IB2-P8B to R1-U1-P4B |
10 meters |
|
R8 IB2 to Rack 2 |
R8-IB3-P9A to R2-U1-P5B |
10 meters |
|
R8 IB2 to Rack 3 |
R8-IB2-P9B to R3-U1-P6B |
10 meters |
|
R8 IB2 to Rack 4 |
R8-IB2-P10A to R4-U1-P7B |
10 meters |
|
R8 IB2 to Rack 5 |
R8-IB2-P10B to R5-U1-P8B |
10 meters |
|
R8 IB2 to Rack 6 |
R8-IB3-P11A to R6-U1-P9B |
5 meters |
|
R8 IB2 to Rack 7 |
R8-IB3-P11B to R7-U1-P10B |
5 meters |
Nine-Rack Cabling
Table G-38 shows the cable connections for the switches when nine full racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-38 Leaf Switch Connections for Rack 9
| Leaf Switch | Connection |
|---|---|
|
R9 IB3 to Rack 1 |
R9-IB3-P8B to R1-U1-P11A |
|
R9 IB3 to Rack 2 |
R9-IB3-P9A to R2-U1-P11A |
|
R9 IB3 to Rack 3 |
R9-IB3-P9B to R3-U1-P11A |
|
R9 IB3 to Rack 4 |
R9-IB3-P10A to R4-U1-P11A |
|
R9 IB3 to Rack 5 |
R9-IB3-P10B to R5-U1-P11A |
|
R9 IB3 to Rack 6 |
R9-IB3-P11A to R6-U1-P11A |
|
R9 IB3 to Rack 7 |
R9-IB3-P11B to R7-U1-P11A |
|
R9 IB3 to Rack 8 |
R9-IB3-P9A to R8-U1-P11A |
|
R9 IB2 to Rack 1 |
R9-IB2-P8B to R1-U1-P11B |
|
R9 IB2 to Rack 2 |
R9-IB2-P9A to R2-U1-P11B |
|
R9 IB2 to Rack 3 |
R9-IB2-P9B to R3-U1-P11B |
|
R9 IB2 to Rack 4 |
R9-IB2-P10A to R4-U1-P11B |
|
R9 IB2 to Rack 5 |
R9-IB2-P10B to R5-U1-P11B |
|
R9 IB2 to Rack 6 |
R9-IB2-P11A to R6-U1-P11B |
|
R9 IB2 to Rack 7 |
R9-IB2-P11B to R7-U1-P11B |
|
R9 IB2 to Rack 8 |
R9-IB2-P8A to R8-U1-P11B |
10-Rack Cabling
Table G-39 shows the cable connections for the switches when 10 full racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-39 Leaf Switch Connections for Rack 10
| Leaf Switch | Connection |
|---|---|
|
R10 IB3 to Rack 1 |
R10-IB3-P8B to R1-U1-P12A |
|
R10 IB3 to Rack 2 |
R10-IB3-P9A to R2-U1-P12A |
|
R10 IB3 to Rack 3 |
R10-IB3-P9B to R3-U1-P12A |
|
R10 IB3 to Rack 4 |
R10-IB3-P10A to R4-U1-P12A |
|
R10 IB3 to Rack 5 |
R10-IB3-P10B to R5-U1-P12A |
|
R10 IB3 to Rack 6 |
R10-IB3-P12A to R6-U1-P12A |
|
R10 IB3 to Rack 7 |
R10-IB3-P12B to R7-U1-P12A |
|
R10 IB3 to Rack 8 |
R10-IB3-P8A to R8-U1-P12A |
|
R10 IB2 to Rack 1 |
R10-IB2-P8B to R1-U1-P12B |
|
R10 IB2 to Rack 2 |
R10-IB2-P9A to R2-U1-P12B |
|
R10 IB2 to Rack 3 |
R10-IB2-P9B to R3-U1-P12B |
|
R10 IB2 to Rack 4 |
R10-IB2-P10A to R4-U1-P12B |
|
R10 IB2 to Rack 5 |
R10-IB2-P10B to R5-U1-P12B |
|
R10 IB2 to Rack 6 |
R10-IB2-P12A to R6-U1-P12B |
|
R10 IB2 to Rack 7 |
R10-IB2-P12B to R7-U1-P12B |
|
R10 IB2 to Rack 8 |
R10-IB2-P8A to R8-U1-P12B |
11-Rack Cabling
Table G-40 shows the cable connections for the switches when 11 full racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-40 Leaf Switch Connections for Rack 11
| Leaf Switch | Connection |
|---|---|
|
R11 IB3 to Rack 1 |
R11-IB3-P8B to R1-U1-P13A |
|
R11 IB3 to Rack 2 |
R11-IB3-P9A to R2-U1-P13A |
|
R11 IB3 to Rack 3 |
R11-IB3-P9B to R3-U1-P13A |
|
R11 IB3 to Rack 4 |
R11-IB3-P10A to R4-U1-P13A |
|
R11 IB3 to Rack 5 |
R11-IB3-P10B to R5-U1-P13A |
|
R11 IB3 to Rack 6 |
R11-IB3-P13A to R6-U1-P13A |
|
R11 IB3 to Rack 7 |
R11-IB3-P13B to R7-U1-P13A |
|
R11 IB3 to Rack 8 |
R11-IB3-P8A to R8-U1-P13A |
|
R11 IB2 to Rack 1 |
R11-IB2-P8B to R1-U1-P13B |
|
R11 IB2 to Rack 2 |
R11-IB2-P9A to R2-U1-P13B |
|
R11 IB2 to Rack 3 |
R11-IB2-P9B to R3-U1-P13B |
|
R11 IB2 to Rack 4 |
R11-IB2-P10A to R4-U1-P13B |
|
R11 IB2 to Rack 5 |
R11-IB2-P10B to R5-U1-P13B |
|
R11 IB2 to Rack 6 |
R11-IB2-P13A to R6-U1-P13B |
|
R11 IB2 to Rack 7 |
R11-IB2-P13B to R7-U1-P13B |
|
R11 IB2 to Rack 8 |
R11-IB2-P8A to R8-U1-P13B |
12-Rack Cabling
Table G-41 shows the cable connections for the switches when cabling twelve full racks together. The cabling between racks 1 through 8 does not change.
Table G-41 Leaf Switch Connections for Rack 12
| Leaf Switch | Connection |
|---|---|
|
R12 IB3 to Rack 1 |
R12-IB3-P8B to R1-U1-P14A |
|
R12 IB3 to Rack 2 |
R12-IB3-P9A to R2-U1-P14A |
|
R12 IB3 to Rack 3 |
R12-IB3-P9B to R3-U1-P14A |
|
R12 IB3 to Rack 4 |
R12-IB3-P10A to R4-U1-P14A |
|
R12 IB3 to Rack 5 |
R12-IB3-P10B to R5-U1-P14A |
|
R12 IB3 to Rack 6 |
R12-IB3-P14A to R6-U1-P14A |
|
R12 IB3 to Rack 7 |
R12-IB3-P14B to R7-U1-P14A |
|
R12 IB3 to Rack 8 |
R12-IB3-P8A to R8-U1-P14A |
|
R12 IB2 to Rack 1 |
R12-IB2-P8B to R1-U1-P14B |
|
R12 IB2 to Rack 2 |
R12-IB2-P9A to R2-U1-P14B |
|
R12 IB2 to Rack 3 |
R12-IB2-P9B to R3-U1-P14B |
|
R12 IB2 to Rack 4 |
R12-IB2-P10A to R4-U1-P14B |
|
R12 IB2 to Rack 5 |
R12-IB2-P10B to R5-U1-P14B |
|
R12 IB2 to Rack 6 |
R12-IB2-P14A to R6-U1-P14B |
|
R12 IB2 to Rack 7 |
R12-IB2-P14B to R7-U1-P14B |
|
R12 IB2 to Rack 8 |
R12-IB2-P8A to R8-U1-P14B |
13-Rack Cabling
Table G-42 shows the cable connections for the switches when 13 full racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-42 Leaf Switch Connections for Rack 13
| Leaf Switch | Connection |
|---|---|
|
R13 IB3 to Rack 1 |
R13-IB3-P8B to R1-U1-P15A |
|
R13 IB3 to Rack 2 |
R13-IB3-P9A to R2-U1-P15A |
|
R13 IB3 to Rack 3 |
R13-IB3-P9B to R3-U1-P15A |
|
R13 IB3 to Rack 4 |
R13-IB3-P10A to R4-U1-P15A |
|
R13 IB3 to Rack 5 |
R13-IB3-P10B to R5-U1-P15A |
|
R13 IB3 to Rack 6 |
R13-IB3-P15A to R6-U1-P15A |
|
R13 IB3 to Rack 7 |
R13-IB3-P15B to R7-U1-P15A |
|
R13 IB3 to Rack 8 |
R13-IB3-P8A to R8-U1-P15A |
|
R13 IB2 to Rack 1 |
R13-IB2-P8B to R1-U1-P15B |
|
R13 IB2 to Rack 2 |
R13-IB2-P9A to R2-U1-P15B |
|
R13 IB2 to Rack 3 |
R13-IB2-P9B to R3-U1-P15B |
|
R13 IB2 to Rack 4 |
R13-IB2-P10A to R4-U1-P15B |
|
R13 IB2 to Rack 5 |
R13-IB2-P10B to R5-U1-P15B |
|
R13 IB2 to Rack 6 |
R13-IB2-P15A to R6-U1-P15B |
|
R13 IB2 to Rack 7 |
R13-IB2-P15B to R7-U1-P15B |
|
R13 IB2 to Rack 8 |
R13-IB2-P8A to R8-U1-P15B |
14-Rack Cabling
Table G-43 shows the cable connections for the switches when cabling 14 racks together. The cabling among racks 1 through 8 does not change.
Table G-43 Leaf Switch Connections for Rack 14
| Leaf Switch | Connection |
|---|---|
|
R14 IB3 to Rack 1 |
R14-IB3-P8B to R1-U1-P16A |
|
R14 IB3 to Rack 2 |
R14-IB3-P9A to R2-U1-P16A |
|
R14 IB3 to Rack 3 |
R14-IB3-P9B to R3-U1-P16A |
|
R14 IB3 to Rack 4 |
R14-IB3-P10A to R4-U1-P16A |
|
R14 IB3 to Rack 5 |
R14-IB3-P10B to R5-U1-P16A |
|
R14 IB3 to Rack 6 |
R14-IB3-P16A to R6-U1-P16A |
|
R14 IB3 to Rack 7 |
R14-IB3-P16B to R7-U1-P16A |
|
R14 IB3 to Rack 8 |
R14-IB3-P8A to R8-U1-P16A |
|
R14 IB2 to Rack 1 |
R14-IB2-P8B to R1-U1-P16B |
|
R14 IB2 to Rack 2 |
R14-IB2-P9A to R2-U1-P16B |
|
R14 IB2 to Rack 3 |
R14-IB2-P9B to R3-U1-P16B |
|
R14 IB2 to Rack 4 |
R14-IB2-P10A to R4-U1-P16B |
|
R14 IB2 to Rack 5 |
R14-IB2-P10B to R5-U1-P16B |
|
R14 IB2 to Rack 6 |
R14-IB2-P16A to R6-U1-P16B |
|
R14 IB2 to Rack 7 |
R14-IB2-P16B to R7-U1-P16B |
|
R14 IB2 to Rack 8 |
R14-IB2-P8A to R8-U1-P16B |
15-Rack Cabling
Table G-44 shows the cable connections for the switches when 15 racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-44 Leaf Switch Connections for Rack 15
| Leaf Switch | Connection |
|---|---|
|
R15 IB3 to Rack 1 |
R15-IB3-P8B to R1-U1-P17A |
|
R15 IB3 to Rack 2 |
R15-IB3-P9A to R2-U1-P17A |
|
R15 IB3 to Rack 3 |
R15-IB3-P9B to R3-U1-P17A |
|
R15 IB3 to Rack 4 |
R15-IB3-P10A to R4-U1-P17A |
|
R15 IB3 to Rack 5 |
R15-IB3-P10B to R5-U1-P17A |
|
R15 IB3 to Rack 6 |
R15-IB3-P17A to R6-U1-P17A |
|
R15 IB3 to Rack 7 |
R15-IB3-P17B to R7-U1-P17A |
|
R15 IB3 to Rack 8 |
R15-IB3-P8A to R8-U1-P17A |
|
R15 IB2 to Rack 1 |
R15-IB2-P8B to R1-U1-P17B |
|
R15 IB2 to Rack 2 |
R15-IB2-P9A to R2-U1-P17B |
|
R15 IB2 to Rack 3 |
R15-IB2-P9B to R3-U1-P17B |
|
R15 IB2 to Rack 4 |
R15-IB2-P10A to R4-U1-P17B |
|
R15 IB2 to Rack 5 |
R15-IB2-P10B to R5-U1-P17B |
|
R15 IB2 to Rack 6 |
R15-IB2-P17A to R6-U1-P17B |
|
R15 IB2 to Rack 7 |
R15-IB2-P17B to R7-U1-P17B |
|
R15 IB2 to Rack 8 |
R15-IB2-P8A to R8-U1-P17B |
16-Rack Cabling
Table G-45 shows the cable connections for the switches when 16 full racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-45 Leaf Switch Connections for Rack 16
| Leaf Switch | Connection |
|---|---|
|
R16 IB3 to Rack 1 |
R16-IB3-P8B to R1-U1-P0A |
|
R16 IB3 to Rack 2 |
R16-IB3-P9A to R2-U1-P0A |
|
R16 IB3 to Rack 3 |
R16-IB3-P9B to R3-U1-P0A |
|
R16 IB3 to Rack 4 |
R16-IB3-P10A to R4-U1-P0A |
|
R16 IB3 to Rack 5 |
R16-IB3-P10B to R5-U1-P0A |
|
R16 IB3 to Rack 6 |
R16-IB3-P0A to R6-U1-P0A |
|
R16 IB3 to Rack 7 |
R16-IB3-P0B to R7-U1-P0A |
|
R16 IB3 to Rack 8 |
R16-IB3-P8A to R8-U1-P0A |
|
R16 IB2 to Rack 1 |
R16-IB2-P8B to R1-U1-P0B |
|
R16 IB2 to Rack 2 |
R16-IB2-P9A to R2-U1-P0B |
|
R16 IB2 to Rack 3 |
R16-IB2-P9B to R3-U1-P0B |
|
R16 IB2 to Rack 4 |
R16-IB2-P10A to R4-U1-P0B |
|
R16 IB2 to Rack 5 |
R16-IB2-P10B to R5-U1-P0B |
|
R16 IB2 to Rack 6 |
R16-IB2-P0A to R6-U1-P0B |
|
R16 IB2 to Rack 7 |
R16-IB2-P0B to R7-U1-P0B |
|
R16 IB2 to Rack 8 |
R16-IB2-P8A to R8-U1-P0B |
17-Rack Cabling
Table G-46 shows the cable connections for the switches when 17 racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-46 Leaf Switch Connections for Rack 17
| Leaf Switch | Connection |
|---|---|
|
R17 IB3 to Rack 1 |
R17-IB3-P8B to R1-U1-P1A |
|
R17 IB3 to Rack 2 |
R17-IB3-P9A to R2-U1-P1A |
|
R17 IB3 to Rack 3 |
R17-IB3-P9B to R3-U1-P1A |
|
R17 IB3 to Rack 4 |
R17-IB3-P10A to R4-U1-P1A |
|
R17 IB3 to Rack 5 |
R17-IB3-P10B to R5-U1-P1A |
|
R17 IB3 to Rack 6 |
R17-IB3-P1A to R6-U1-P1A |
|
R17 IB3 to Rack 7 |
R17-IB3-P1B to R7-U1-P1A |
|
R17 IB3 to Rack 8 |
R17-IB3-P8A to R8-U1-P1A |
|
R17 IB2 to Rack 1 |
R17-IB2-P8B to R1-U1-P1B |
|
R17 IB2 to Rack 2 |
R17-IB2-P9A to R2-U1-P1B |
|
R17 IB2 to Rack 3 |
R17-IB2-P9B to R3-U1-P1B |
|
R17 IB2 to Rack 4 |
R17-IB2-P10A to R4-U1-P1B |
|
R17 IB2 to Rack 5 |
R17-IB2-P10B to R5-U1-P1B |
|
R17 IB2 to Rack 6 |
R17-IB2-P1A to R6-U1-P1B |
|
R17 IB2 to Rack 7 |
R17-IB2-P1B to R7-U1-P1B |
|
R17 IB2 to Rack 8 |
R17-IB2-P8A to R8-U1-P1B |
18-Rack Cabling
Table G-47 shows the cable connections for the switches when 18 racks are cabled together. The cabling among racks 1 through 8 does not change.
Table G-47 Leaf Switch Connections for Rack 18
| Leaf Switch | Connection |
|---|---|
|
R18 IB3 to Rack 1 |
R18-IB3-P8B to R1-U1-P2A |
|
R18 IB3 to Rack 2 |
R18-IB3-P9A to R2-U1-P2A |
|
R18 IB3 to Rack 3 |
R18-IB3-P9B to R3-U1-P2A |
|
R18 IB3 to Rack 4 |
R18-IB3-P10A to R4-U1-P2A |
|
R18 IB3 to Rack 5 |
R18-IB3-P10B to R5-U1-P2A |
|
R18 IB3 to Rack 6 |
R18-IB3-P2A to R6-U1-P2A |
|
R18 IB3 to Rack 7 |
R18-IB3-P2B to R7-U1-P2A |
|
R18 IB3 to Rack 8 |
R18-IB3-P8A to R8-U1-P2A |
|
R18 IB2 to Rack 1 |
R18-IB2-P8B to R1-U1-P2B |
|
R18 IB2 to Rack 2 |
R18-IB2-P9A to R2-U1-P2B |
|
R18 IB2 to Rack 3 |
R18-IB2-P9B to R3-U1-P2B |
|
R18 IB2 to Rack 4 |
R18-IB2-P10A to R4-U1-P2B |
|
R18 IB2 to Rack 5 |
R18-IB2-P10B to R5-U1-P2B |
|
R18 IB2 to Rack 6 |
R18-IB2-P2A to R6-U1-P2B |
|
R18 IB2 to Rack 7 |
R18-IB2-P2B to R7-U1-P2B |
|
R18 IB2 to Rack 8 |
R18-IB2-P8A to R8-U1-P2B |