Installation Prerequisites
This section includes the following topics:
• Isis
Introduction
In order to successfully install the Oracle Utilities Network Management System (and underlying environment), you must have a thorough understanding of the following:
• Unix system administration.
• Oracle RDBMS installation and configuration.
• WebLogic installation and EJB deployment.
In addition, you should have at least a cursory knowledge of the Oracle Utilities Network Management System architecture and applications functionality.
The Oracle Utilities Network Management System Quick Install Guide provides an overview of the Oracle Utilities Network Management System architecture and lists the supported hardware and software configurations. Verify that your system meets system requirements prior to attempting the Oracle Utilities Network Management System installation.
Requirements for Oracle Utilities Network Management System Database
The Oracle RDBMS must be installed and configured before beginning the Oracle Utilities Network Management System. It must be installed on a server that is accessible from the Oracle Utilities Network Management System services applications. Time zone settings for the Oracle RDBMS and Oracle Utilities Network Management System services application must both be UTC. That is, on both the services machine and the database server, the TZ environment variable must be "UTC", and the database TIMEZONE value must be '+00:00'. These database and WebLogic instances should not be shared with any NMS installations running earlier versions of the code that did not yet support the UTC time zone.
Oracle recommends that any new installations should use the AL32UTF8 character set.
Refer to the “Database Configuration” chapter of the Oracle Utilities Network Management System Configuration Guide for more details regarding the installation and configuration of the Oracle RDBMS for use with the Oracle Utilities Network Management System applications.
Note: Oracle Locator, a standard component of all editions of Oracle RDBMS, is required for the Oracle Utilities Network Management System installation.
To verify that Oracle Locator has not been removed from your Oracle RDBMS, run the following SQL command:
select count(1) "Rows" from mdsys.cs_srs;
If this query returns zero or very few rows (1000+ are expected), consult your DBA to (re)install the Oracle Locator package.
Configuring the Oracle Utilities Network Management System Database
Add the following to the init.ora of the NMS database:
temp_undo_enabled = TRUE
To avoid restarting a database that is already running, you can do this command to make the change immediately:
alter system set temp_undo_enabled = true;
Requirements for Oracle Database Client Installation
The Oracle Utilities Network Management System requires that an installation of the Oracle Database Client software be made available in order to facilitate connections between the NMS services and the database. The installation must be the full installation of the Oracle Database Client software. The Instant Client package will not work, as it does not have all of the required libraries and binaries required by the NMS services. The database client version 19.3 must be used even if the database server runs a newer database version, such as Oracle RDBMS 26ai.
Requirements for Java Application Server
The Oracle Utilities Network Management System requires the installation of a WebLogic Application Server. This installation should be done before installing the Oracle Utilities Network Management System software. Refer to Oracle Fusion Middleware Installation Guide for Oracle WebLogic Server for instructions.
Requirements for Spatial Landbase
The Oracle Utilities Network Management System recommends installation of the Oracle Map Builder to simplify the process of creating and managing map, theme, and symbology metadata in the spatial database used to render spatial landbase maps. Oracle Map Builder is part of the Oracle Fusion Middleware MapViewer family of products, which is available for download from the Oracle Technology Network website (www.oracle.com/technetwork/).
Requirements for Web Maps Landbase
The Oracle Utilities Network Management System supports the use of commercial web map servers for Viewer background landbases. It is up to each NMS customer to license with a web map provider for access to a web map service. NMS currently supports the following web map services:
• Google Static Maps Basic or Trial - To configure, you will need to agree to a license agreement with Google and they will provide you with an API key. This option is not recommended for production.
• Google Static Maps for Work/Business - To configure, you will need to agree to a license agreement with Google and they will provide you with a process to define Client IDs and Google generated Crypto Keys.
• Bing Maps - To configure, you will need to agree to a license agreement with Bing/Microsoft and they will provide you with a key.
Software Requirements for Unzipping Files
The Oracle Utilities Network Management System and third party software files are compressed in the ZIP format. Most Linux/Unix-based platforms already have the binaries needed to unzip the distribution archives. An unzip utility is also included in the Oracle client under $ORACLE_HOME/bin.
Security Considerations
Please refer to the Oracle Utilities Network Management System Security Guide for security overview, recommendations, and guidelines when installing Oracle Utilities Network Management System software.
OpenSSL
Oracle Utilities Network Management System now uses OpenSSL to encrypt traffic between SwService (used in CVR and FLISR) and WebLogic server by default. As such, OpenSSL is now required to be installed with the operating system if you will be running SwService. The openssl binary as well as libssl and libcrypto are required.
To make them available, you will need to install the appropriate OS packages on your system:
• Linux: openssl and openssl-devel RPM's
Isis
Isis is the backbone of the Oracle Utilities Network Management System. It is the messaging bus through which all back-end NMS service components communicate. Refer to the “Isis Configuration” chapter of the Oracle Utilities Network Management System Configuration Guide for more details regarding the configuration of the Isis message bus for use with the Oracle Utilities Network Management System applications.
NTP Daemon
On any computer running or connecting to the Oracle Utilities Network Management System, it is important to have an accurate clock that moves monotonically forward. Many approaches, such as rdate, can cause the clock to jump unpredictably, possibly backwards. This jumping is especially deleterious to Isis timing, timer queues, and interfaces, but can easily be avoided by using the Network Time Protocol (NTP) daemon, which is designed to gracefully synchronize the system clock with any reliable time source.
NTP is available for free on all operating systems and is simple to configure. Even if all of your services and applications run on a single computer, it is important to run NTP there. If you have several computers on the same LAN, you may want to consider running an NTP server (pointing to an external time source) on one of them and pointing all of the other NTP clients on the LAN to it. All NMS servers should be configured to be in the same timezone, and have their time synchronized with NTP, including all WebLogic servers.
Client Authentication
Authorization and roles are stored in the database, but the authentication must come from an external source. No matter what the authentication source, each login name must be granted access to the system by using the Configuration Assistant. Active Directory and LDAP are supported authentication sources.
Estimating NMS Memory and CPU Requirements
In order to perform well, NMS Services should not (even under load) be forced into any type of significant memory swapping situation where inadequate physical memory forces the operating system to “swap out/in” memory blocks from running processes since this can have a major negative impact on performance.
This section helps NMS implementers estimate how much physical memory and CPU the “significant” or “core” NMS Services might require for a production NMS instance. In this context, “significant” implies NMS Services that can be expected to consume more memory as the size of the model and/or model activity grows. Many NMS Services are essentially gateway processes and do not significantly grow in size regardless of model size and/or activity (for example, DBService processes). Special emphasis is granted to the NMS Services dedicated to advanced distribution management system (ADMS) processing since they can consume significant memory and CPU resources.
For NMS 2.6.0.2.6 and above, the NMS/ADMS Services have been merged into a single DMSService process (the former PFService, FLMService, FLTService, VVOService, EMService processes from 2.6.0.1 and pre 2.6.0.2.6 are now ALL combined into the single DMSService process). The combined DMSService process has improved multi-threading which requires less RAM and CPU to support – generally improving overall efficiency and performance.
If a given NMS implementation is using any ADMS functionality additional RAM/CPU for DMSService will need to be accounted for. The numbers below are estimates based on sample NMS models. Every NMS model is different and can consume different amounts of memory. What you see below are averages but should be at least a good starting point.
DMSService generally consumes roughly 4K of memory per active NMS model component in the network components table. Each (required) concurrent study session will incrementally consume an additional 40 bytes for each active NMS model component.
For a new NMS implementation, you may have no idea how many NMS network components you may end up with. As a general rule, we can typically estimate roughly 1.5 NMS network components per meter if secondary is not modeled and 3 network components per meter if secondary is modeled.
Other core/significant NMS Services can also consume more memory based on the size of the NMS model, number of concurrent study sessions, and/or other activity. There are other specific factors involved (number of SCADA measurements, for example), but the following are rough memory estimates for the other core NMS Services that tend to grow significantly.
• MTService: Model energization solutions
• 1kB per network component
• Add 20 bytes per network component per concurrent study session
• JMService: Outage/job management processing
• Note this growth is more a function of outage activity, crews, customers, etc.
• Other NMS Services don’t tend to significantly grow. We need to account for the base size of the executables themselves. These NMS services will tend to grow more modestly with model size. These are lumped together as one memory component with allowance for model growth.
• 5GB (base) + 2.5k bytes per network component
Example sizing for 2M meter customer:
• Without secondary modeled
• Includes all NMS/OMS/ADMS modules
• 50 concurrent ADMS study sessions
2Mx1.5=3M network_components (estimated) – used for all other calculations below.
Note that NMS Services are typically not the only processes to run on these servers (project specific NMS adapters – for example) and thus an additional 5GB (minimum) should ALSO be allocated for the operating system and any other miscellaneous processes that may need to execute.
NMS/ADMS Memory Estimate
• 3Mx4kB = 12GB for ADMS modules (base)
• 3Mx40x50 = 6GB for 50 concurrent study sessions
• 18GB total
NMS/OMS Memory Estimate
• 3Mx1kB = 3GB for MTService (base)
• 3Mx20x50 = 2GB for 50 concurrent MTService study sessions
• 3Mx1kB = 2GB for JMService
• 3Mx2.5K+5GB = 10GB for executables and “other” NMS Services
• 16GB total
NMS/OMS/ADMS Combined – Memory Estimate
• 18GB for ADMS
• 16GB for OMS
• 5GB for project specific adapters and/or other processes
• 39GB for NMS/OMS/ADMS (total)
CPU Considerations
For an NMS instance to perform optimally under load also requires adequate CPU for the NMS Service (daemon) processes. If NMS daemon processes are consistently waiting for CPU – the system will not perform optimally. Note that a CPU in the context of this discussion is not a hyper-thread – but a “full” CPU. Note Unix utilities like “top” show hyper-threads, and there are typically two hyper-threads per full CPU. Also, for NMS performance in general, a few (faster) CPUs for the NMS Services tier will significantly outperform many (slower) CPUs as several NMS Services process at least certain parts of requests serially. Some guidance on CPU consumption is provided here.
NMS/OMS CPU
For a 1M meter NMS model, under storm load, MTService, DDService and JMService will tend to consume roughly 1 full CPU each. The “other” NMS Services will tend to consume roughly 1 additional CPU between them (on average) for a total of 4 full CPUs dedicated to NMS/OMS processing. This assumes the RDBMS and WebLogic components are on separate servers. For larger NMS models beyond 1M meters, for each additional 1M meters, an additional CPU is recommended. The operating system and project specific adapters will often consume at least one or two additional CPUs – for a total of 6 (for example) for a 2M meter NMS model.
NMS/ADMS CPU
For a 2M meter NMS model DMSService would at least often consume 4 or more CPUs. The SRS rule (MAX_FLM_BACKGROUND_THREADS) can be used to constrain/expand how many CPUs DMSService is allowed to consume for a given NMS implementation. We don't want a multi-threaded DMSService process to (potentially) starve OMS processes of CPU (for example) - so we generally want at least some CPU constraints in place to guard against this.
Rule of thumb is to allocate 4 full CPUs for DMService for up to a 1M meter model and 6 or more full CPUs for models larger than 1M meters. Depending on what ADMS functionality is in play (FLISR, FLA, VVO, FLM, etc), desired circuit solve frequency, data quality and whether secondary circuits are modeled CPU requirements for a given NMS implementation will vary. Some project experimentation and performance testing are generally required to further nail down CPU requirements.
NMS/ADMS/OMS CPU:
For a 2M meter customer model (with all NMS modules), we would end up with at least 4->6 CPUs for NMS/OMS and at least 4 more CPUs for ADMS for a total of at least 10 (full) CPUs – up to 14 CPUs if you want to push NMS/ADMS multi-threading.
NMS WebLogic - CPU/RAM Resource Sizing and License Considerations
High-level Considerations
• Whether or not secondary circuits are modeled is significant
• WebLogic CPU sizing is primarily a function of concurrent NMS users – types of users include:
• NMS Java – generally in a control center
• NMS Flex SCADA (Java) – generally in a control center
• NMS
• Flex Ops (browser) – typically outside a primary control center
• NMS OMA (mobile/tablet) – in the field
• WebLogic storage is primarily a function of desired log retention
• Model size also has some impact – for caching Viewer meta-data files.
• WebLogic licensing for Virtual Machines is significantly influenced by chosen hypervisor.
• Oracle KVM supports “hard partitions” which constrains license obligations.
• Use of any other hypervisor generally requires tech license for entire machine.
How an NMS model is configured can also significantly impact CPU consumed. OMA polling frequency is just one example (if/when OMA is in play) that can impact how much CPU is necessary. There are many NMS configuration options that can impact overall performance of an NMS instance – too numerous to reference here. Just be aware that some NMS configuration options and/or peak (concurrent) user loads will have corresponding NMS performance impact. To help ensure acceptable NMS production performance, if/when expected NMS configuration and/or peak concurrent user/usage volumes change – corresponding hardware requirements should also be reviewed and performance tests conducted.
General Notes
The notes in this section are estimates largely based on Oracle internal testing – using a specific test model and specific hardware – and are thus just estimates. It is strongly advised that, if at all practical, to build your full NMS model with your data, hardware and desired configuration. Once a reasonable version of your full NMS model is built you can realistically test with your expected peak storm load volume. This will generally provide a more accurate view of what hardware is necessary for your specific needs. Depending on test results changes in NMS configuration, Oracle technology configuration, hardware, Oracle technology core counts and/or RAM for each technology component can be addressed. Testing on your full model helps ensure your instance of NMS will adequately perform under a range of storm load scenarios tailored to your specific load area and expected worst case scenarios. No one likes surprises during a major storm.
• Production Hardware: As a general rule we typically focus our energy on sizing hardware for one fully active production NMS instance. The hardware at a given production site may or may not be fully redundant. Fully redundant hardware at a given production site generally implies the use of a Unix cluster of some kind and/or the use of some kind of RAC RDBMS.
• Disaster Recovery Hardware: If Disaster Recovery (DR) is also in play we generally double whatever was allocated at the primary Production site (NMS DR hardware is essentially a replica of Production hardware). This simplified approach provides consistent infrastructure that should minimize any potential performance impact if/when an NMS DR site is activated. This can be especially useful if is desired (or even mandated) for NMS to run for significant periods of time (weeks or months) at a DR site. Routinely transitioning from Production to DR and back validates NMS switchover mechanisms - including any required NMS integrations at each potential site.
• Non-Production Hardware: As a starting point we generally recommend that Non-Production Hardware be at least a copy of Production. If Production supports Disaster Recovery than Non-Production should as well (to effectively test Primary/Secondary site switchover on a non-prod env). If Production uses RAC, then non-Production should as well, etc. Most NMS customers have multiple non-Prod NMS environments they want to support (Quality Assurance, Model Validation, Development, Training, etc). Especially if Production runs on redundant hardware and/or Disaster Recovery is involved – a single (full) replication of Production hardware is often adequate to support all non-Prod NMS environments.
• Typically at least one of the non-Prod environments is very close (if not an exact replica) to Production – in terms of model size and configuration. This is where significant non-Prod performance/scalability testing can generally be done – prior to putting major changes into Production.
• The “other” non-Prod NMS environments (beyond the large model environment used for large scale performance testing) are often relatively small and can generally be supported on the same exact set of hardware as the large non-Prod NMS instance.
• This implies that “some” non-prod NMS environments will need to be shutdown during major NMS performance environments – to better replicate production conditions without competition from the “lesser” environments. If this is unacceptable, more hardware will be needed.
• If redundant hardware is in play lesser NMS non-prod environments can
• often be setup to normally run on the “backup site” non-Prod hardware – to minimize any impact to large scale NMS non-Prod testing. Performance tests (normally) don’t involve site switchover – even though that is also a valid test.
• If Disaster Recovery is in play two RDBMS instances can typically be setup.
• One RDBMS instance to support a large/full NMS model for non-Prod performance tests – for example say it is primary at SiteA. Keeping this non-Prod env reasonably close to production is generally desirable to support more realistic testing.
• Another RDBMS instance can be setup as primary at SiteB (or even ONLY at SiteB) to support ALL other non-prod NMS instances. Unless a DR test is underway the RDBMS at SiteB will not impact the RDBMS at SiteA.
• It may become desirable to shut down some of the lesser non-Prod NMS environments to avoid resource contention for some tests – but this is relatively uncommon and typically manageable.
CPU Notes (Normalized SPEC 2017 Integer Rate Base value)
1. Faster CPUs (cores) will tend to support more users per core. Faster cores are especially desirable for the NMS Services tier as some aspects of NMS Services are at least somewhat single threaded. In ALL cases we are talking about (full) cores. One CPU on x86-64 generally equates to one "hyper-thread". There are generally two x86-64 hyper-threads per core (CPU). We talk about cores because Oracle technology is licensed by cores (not hyper-threads).
2. For an NMS production instance we try to size for expected activity during peak (storm) load. We generally don't want to see an NMS system component (on its respective server) consume more than roughly 50% of available CPU (on average – even under full/peak storm load). Some spikes of a few seconds (or even a few minutes) now and then are normal/expected - but we generally want adequate CPU available to handle the spikes when they arrive.
3. The core sizing estimates below are based on the performance of a specific set of processors.
• Core count estimates are based on CPU consumed under full (peak storm) load for tests run at least three hours. If a given component consumes twelve hours of CPU during a three hour test we would calculate 12/3=4 full cores/hr (consumed) for that component. We would estimate this “component” be allocated eight cores to accommodate our target of roughly 50% CPU load (under “peak storm load”).
• Average CPU consumption of 70% or more for a significant period of time (say at least 10 to 15 minutes) will typically result in noticeable loss of performance. Ideally these might just be CPU consumption “spikes” trying to accommodate a burst of activity - and the system will naturally recover. If 50%+ loading happens on a regular basis – your system would likely benefit from more/faster CPUs.
• Faster cores will generally support more users per core and vice versa. For comparison a useful metric is the SPEC CPU2017 Integer Rate base result score which can be found at:
• http://spec.org/cpu2017/results/rint2017.html
Find a processor you are interested in along with its CPU2017 Integer Rate (Base) Result value (not the Peak value) for a given vendor and processor from the spec.org link above. For example assume you are interested in the following CPU:
• AMD EPYC 7551 - 2.00 GHz
Ideally you can find the processor (or something very close to it) represented from the hardware vendor of your choice but if not - try to find something similar. For example - the following is close to the processor noted above:
• HPE - ProLiant DL325 Gen10 (2.00 GHz, AMD EPYC 7551P)
Note the CPU2017 Integer Rate (Base) Result is 134 (there may be multiple scores from different vendors for the same chip - but they should be roughly similar). Also note this hardware has 32 cores. Divide the CPU2017 Integer Rate (Base) Result by the number of cores to get a normalized value that reflects the relative performance of a single core (for comparison purposes).
• 134/32=4.2 (Normalized CPU2017 Integer Rate Base value)
Try to be consistent in hardware vendor selection when comparing processor performance – just to eliminate another variable.
Core Counts
To see how many Linux x86-64 cores you have on any given OS (virtualized or not) run the 'lscpu' utility. Look for lines that look like the following:
• Thread(s) per core: 2
• Core(s) per socket: 8
• Socket(s): 1
Multiply the bottom two numbers together to find out how many cores you have for licensing purposes (8x1=8 in this example). You can also see (in the first line of example output above) that there are two threads/core - which means hyper-threading is enabled. Note x86-64 hyper-threading can be disabled but is generally enabled by default.
Core Factor Notes (for Oracle technology licensed by core count):
Keep in mind that for x86-64 the current Oracle licensing core-factor is 0.5. Thus if you need two cores of technology (RDBMS or WebLogic - for example) you multiply 2x0.5=1 core for Oracle licensing purposes. If you are deploying NMS on redundant hw (like a two-node Unix cluster) you can generally count the number of cores needed by the active NMS application (active node of a two-node Unix cluster) to determine license core count requirements.
For example - if you need 4 full cores of RDBMS (at all times) and you are running on a two-node RAC server you will need four full cores of RAC licensed on each node of the RAC server. For this example you license four cores of RAC RDBMS to cover both RAC nodes (because of the core factor).
• 4 cores x 2 nodes x 0.5 core factor = 4 core license
Thus for this example of an active/active RAC RDBMS you would normally be running 8 cores of RDBMS. Four cores on each node of a fully functioning two node RAC cluster - and 4 cores of RDBMS if one node of the RAC was down for whatever reason. Your license cost is still 4 cores - because of the core factor used to license x86-64 technology. Keep the core factor in mind when licensing for non-production NMS instances that may NOT be running on redundant hardware. Oracle RAC One Node provides RDBMS failover capability for a reduced license cost but only runs on one node of a RAC cluster at any given time. Repeat for other Oracle (WebLogic, RDBMS options, ODI) technology.
RAM Notes
1. For RAM we want to prevent production NMS Servers from any significant memory swapping - especially under peak system load. Significant (consistent) swapping can have a major negative impact and must be avoided to ensure best possible performance.
• WebLogic Managed Servers utilize a Java Virtual Machine (JVM) which will only use as much memory as it is configured to consume. In terms of WebLogic JVM memory allocation we have to allow for caching of any model dependent data caches along with memory used for routine transient requests.
• For each production NMS WebLogic Managed Server – we want to be confident that (even under peak load) the JVM has at least roughly 30% of allocated JVM (heap) memory to work with. If a JVM runs out of heap memory (for whatever reason) it can enter into an aggressive JVM garbage collection cycle looking for more memory – typically with major negative performance implications. Aggressive garbage collection (because the JVM has been allocated inadequate memory) is at least similar to Unix “swapping” and must be avoided to ensure optimal performance.
2. Allocate sufficient RAM for:
• Operating system
• Expected application peak load
• At least a 40% buffer - for unexpected memory consumption
• Performance monitoring agents
Oracle Technology Licensing When Using Virtual Machines
Note the impact of Oracle technology licensing when using VMware(vSphere) as a hypervisor can be significant. If you have chosen to deploy Oracle technology that is often licensed by core count (RDBMS, WebLogic, OBIEE or similar) be aware of Oracle licensing constraints with VMware. In general Oracle does NOT honor VMware/vSphere (soft) partitioning for Oracle technology licensing purposes and thus all cores managed by an instance of a VMware hypervisor must generally be licensed (unless some other license arrangement is in place).
There are typically several different approaches which can be taken to help mitigate Oracle technology licensing concerns when running NMS Servers on Virtual Machines:
1. Leverage some form of an Oracle Enterprise Unlimited License Agreement (ULA). ULAs, PULAs (Perpetual ULAs) and application specific ULAs all apply and if available generally eliminate deployment pattern concerns.
2. If you do not have any form of Oracle technology ULA you can contain various Oracle technologies on dedicated (technology specific) servers where you size the number of physical cores for each server to best match your actual needs. This may result in more (physical) servers. For example:
• Dedicated RDBMS servers.
• Dedicated WebLogic servers.
• Dedicated OBIEE servers.
• etc...
3. Deploy at least some aspect of NMS within Oracle Cloud Infrastructure (maybe some of the non-prod NMS instances could be deployed within OCI – for example). Oracle technology (RDBMS, WebLogic and/or similar) are licensed by Oracle CPUs (OCPUs) within OCI – which is often a small subset of the actual hardware the supporting VMs run on.
• Note non-prod NMS WebLogic instances can also be licensed on a “Named User Plus” basis – with a minimum of 10 Named Users per core (for WebLogic).
4. Run Oracle technology on hard partitioned (cpu pinned) virtual machines so you only license for what you need. For Linux x86-64 this generally means running Oracle Linux on an Oracle qualified hard partition (cpu pinned) VM. The Oracle KVM (Kernel based Virtual Machine) hypervisor supports hard partitioning of VMs when used with Oracle Linux. Oracle KVM can be installed on non-Oracle hardware with no license cost. Most KVM updates are also available free of charge but certain updates may require a premier or extended support contract.
Oracle KVM is the hypervisor used with all Oracle Engineered Hardware solutions:
• Oracle Database Appliance(ODA)
• Supports RDBMS and non-RDBMS partitions
• Oracle Private Cloud Appliance(PCA)
• Oracle Exadata Database Machine
• RDBMS only partitions
For more information see:
• https://www.oracle.com/a/ocom/docs/linux/ol-kvm-hard-partitioning.pdf
Production NMS WebLogic Server CPU/RAM/Storage Sizing Estimates
RAM: Allocated for WebLogic servers.
Note the RAM estimates below are for a base Operating System and each WebLogic Managed Server (JVM) that may be in play. Once the values for the desired components are all added/calculated – it is recommended to add at least an additional 50% RAM to at least the production NMS instances. This is to help accommodate any unforeseen memory consumption and to accommodate updated memory requirements for any given component (WebLogic Managed Server JVM – for example) – as use case needs and/or supporting software continues to change. On the flip side it is also worth noting that a WebLogic JVM will NOT use more memory than it is allocated.
Below are the two (primary) NMS specific Enterprise Java Bean (EJB) deployments used by NMS to support different combinations of NMS client deployments. Each EJB will typically be deployed within a given (single) WebLogic domain. RAM estimates are provided based on the type of NMS end-user each WebLogic Managed Server supports, the EJB deployment involved and the expected model size in terms of customer meters.
cesejb
• 4GB for Operating System
• 4GB - supporting Java clients (control)
• +7K/meter
• 4GB - supporting Java clients (non-control)
• +7K/meter
• 4GB - supporting Flex clients
• +7K/meter
• 4GB - supporting OMA clients
• +7K/meter
nms-ws (typically in a separate WebLogic domain from cesejb)
• + 2K/meter
• + 2K/meter
Example for 2M meter utility deploying Java Control, Flex Ops and OMA clients.
• RAM for WebLogic cesejb Managed Servers
• 4GB Operating System
• 4GB+2M*7K=18GB – Java Control
• 4GB+2M*7K=18GB – Flex Ops support
• 4GB+2M*7K=18GB – OMA support
• 58GB (total - base)
• 58GB*0.5=29GB (contingency RAM)
• 87GB (total – with 50% contingency)
• RAM for WebLogic nms-ws Managed Servers
• 4GB+2Mx2K=8GB – Flex Ops
• 20GB (total)
• 20GB*0.5=10GB (contingency RAM)
• 30GB (total – with 50% contingency)
CPU: Allocated CPU for each JVM
A normalized CPU2017 Integer Rate base value of roughly 5 was used for the CPU estimates for NMS 2.6.0.1. See CPU notes above for how to determine a normalized CPU2017 Integer Rate (Base) value for desired hardware. Faster CPUs could require less Oracle technology to support the same number of users - and vice versa.
A given host or Virtual Machine requires a certain amount of base memory (noted above) and CPU to be functional – so we have to include these base numbers in our sizing. If we deploy multiple WebLogic JVMs on the same host/VM – we certainly gain some efficiency as we only have to allocate overhead for one host/VM.
cesejb - 2 CPU minimum for tier (base CPU to support a single host/VM)
• Java clients (control & non-control)
• + 1 CPU/100 users
• Flex Ops clients
• + 1 CPU/300 users
• OMA clients
• + 1 CPU/1000 users
nms-ws - 2 CPU minimum for tier (base CPU to support a single host/VM)
• Flex clients
• + 1 CPU/200 users
• OMA clients
Example WebLogic core count for NMS instance with following peak (concurrent) user counts:
• 300 Java users
• 700 Flex Ops users
• 1000 OMA users.
cesejb – estimated cores:
• 3 cores (300/100=3) – Java users
• 3 cores (700/300=3) - Flex Ops users (because we round up)
• 1 core (1000/1000=1) – OMA users
• 2 cores – operating system (don’t replicate for subsequent cesejb deployments on same hw)
• 9 cores (total)
nms-ws – estimated cores:
• 4 cores (700/200=4) – Flex Ops users (because we typically round up)
• 2 cores - operating system (don’t replicate for subsequent nms-ws deployments)
• 7 cores (total)
Storage: Allocated to Each WebLogic Server
Storage is primarily a function of how many WebLogic Managed Server operational logs a utility might want to retain (*.out and *.log files) – and to a lesser extent model size. Policies can be setup within WebLogic (for each WebLogic Managed Server) regarding the max size for log files before rotation, how/when they are rotated and how many are retained. Note this is for EACH WebLogic Managed Server running under a WebLogic domain. The smaller the log files and the less log files that are retained, the less storage required – and vice-versa. Some high-level estimates that should be adequate for most needs if a moderate volume of log files are retained:
100GB for WebLogic domain, executables and deployments
• +50GB/Managed Server for log files
Example WebLogic Storage Estimate for NMS Instance Supporting Java, Flex Operations, and OMA clients:
• 50GB for WebLogic domain, executables and deployments
• +50GB for NMS Java client Managed Server
• +50GB for NMS Flex Ops client Managed Server
• +50GB for NMS OMA client Managed Server
• 100GB (50% contingency)
• 300GB (total)
