Using the SCADA Summary
The SCADA Summary provides the current values and qualities of all mapped SCADA measurements in Oracle Utilities Network Management System. Each row of this summary represents one measurement. There may be multiple unique measurements on one SCADA device. SCADA information includes digital and analog measurements, along with the quality codes and any user comments for each measurement. You can use the summary to view measurement information, manually replace current SCADA values, and inhibit updates.
This section includes the following topics:
Understanding the SCADA Summary Window
The SCADA Summary may be opened to view all SCADA measurements or for measurements related to a device or feeder selected in the Viewer. The SCADA Summary displays the following fields and buttons:
• The Feeder column contains the name of the feeder reporting the SCADA measurements.
• The Substation column contains the substation name.
• The Device column contains the name of the device reporting the SCADA measurements.
• The Value column contains the last reported measurement value. The value can be status, digital, or analog. For status measurements, the values are displayed as a test pair, such as open/close, on/off, and so on. Analog and digital values are shown as floating point and integer values.
• The Quality column contains the Quality codes for the measurement that indicates the quality of the SCADA measurement (for example, out of scan, inhibited, manual override). Several quality codes can be listed.
• The Point Name column displays the name of the SCADA measurement, as used in the SCADA system.
• The Attribute column contains a description of the measurement type, as configured in the ATTRIBUTES.description column in the Oracle Utilities Network Management System database for the matching attribute.
• Depending on your system's configuration, you may have the ability to enter comments when manually changing SCADA status (for example, Inhibit, Manual Override, or Disabled in Power Flow). See “Adding and Modifying Comments for SCADA Status Changes” for more information.
If this feature is configured, you will see the following columns:
• The Comments column contains the text of a comment entered when changing device status.
• The User column displays the name of the user who entered/modified comments when changing the device status.
• The Date column displays the date and time when the comment was entered or modified.
Toolbar and Menu Options
File Menu
Menu Option
Description
Toolbar Icon
Print...
Displays the Print Preview window, from which you can view and print the summary.
Toggle Dockable Window
Changes a standalone window to a pane that may be moved or docked in another window or frame. See “Understanding Docked Panes and Standalone Window Tools” for more information on dockable and standalone windows.
Exit
Closes the SCADA Summary window.
Actions Menu
Menu Option
Description
Toolbar Icon
Inhibit
Inhibit sets the inhibit quality code for the selected SCADA measurement. This suppresses any new updates from SCADA.
Cancel Inhibit
Cancel Inhibit removes the inhibit quality code from the selected SCADA measurement. This allows any new updates from SCADA to be displayed.
Manual Entry...
Manual Entry allows you to enter a new value for the selected SCADA measurement. When a changed SCADA value is received by the system, it replaces the manually entered value.
Manual Override...
Manual Override allows you to enter a new value for the selected SCADA measurement. When a new SCADA value is received by the system, the measurement is blocked and the manually entered value remains.
Cancel Override
Cancel Override cancels the manual override for the selected measurement and reverts the selected measurement to the last received value from the SCADA system.
Disable in Power Flow
Disable in Power Flow disables the selected measurements from being included in the power flow solution.
Enable in Power Flow
Enable in Power Flow re-enables the selected disabled measurements in the power flow solution.
Reverse Polarity
Reverse Polarity sets the Reversed (r) quality code on the measurement, which then negates the value, to improve power flow calculations. Note that any subsequent manual entries and manual overrides will also be negated, as if they were SCADA readings.
Undo Reverse Polarity
Undo Reverse Polarity undoes the Polarity Reversal and reverts to the last received SCADA value.
Edit Comment...
Edit Comment allows you to modify an existing comment for the selected measurement. See “Adding and Modifying Comments for SCADA Status Changes” for more information.
Control Tool
Brings up the control tool for the selected measurement's device.
Trend Graph
Trend Graph for selected attributes. Up to nine attributes for the same device can be displayed on the same trend graph as long as they have no more than two distinct units of measure (for example, Amps and kV).
View...
View focuses the Viewer on the device.
Navigate to SCADA
If configured, submenu options open windows in the native SCADA application (currently supported by OSI). For more information, see “OSI SCADA Integration”.
Load Feeder
Loads additional data for all SCADA measurements on a feeder when the SCADA Summary is displaying device data.
Note: This option is only available when the SCADA Summary is launched from the Control Tool.
Load Substation
Loads additional data for all substation measurements when the SCADA Summary is displaying device or feeder data.
Load Adjacent Sub
Loads additional data for adjacent substations.
Load All
Repopulates the SCADA Summary with all measurements. This clears any device, feeder, or substation filters; see “Viewing SCADA Data for a Selected Device”.
Help Menu
Menu Option
Description
Toolbar Icon
SCADA Summary Help
Opens the online help system to the SCADA Summary help content.
Understanding the SCADA Summary Filter Pane
The SCADA Summary provides the following standard Global filters:
Filter Name
Description
All Measurements
Displays all rows in the SCADA Summary table. All is the default view.
AMI Bellwether
Displays bellwether AMI voltage rows.
Analogs
Displays rows with analog values.
Digitals
Displays rows with digital values.
Equipment
Displays rows with equipment values.
Statuses
Displays rows with status value.
Viewing Data in the SCADA Summary
Viewing All SCADA Data
To open the SCADA Summary for all measurements, select SCADA Summary... from the Web Workspace Tools menu.
To open the SCADA Summary for a specific device, select the device or feeder in the Viewer and launch the Control Tool. Click SCADA Summary... and select one of the options:
• Device...: loads the SCADA Summary with the SCADA measurement data for the selected device.
• Feeder...: loads the SCADA Summary with SCADA measurement data for the selected device's feeder.
• Substation...: loads the SCADA Summary with SCADA measurement data for the selected device's substation.
When the SCADA Summary is launched from the Control Tool, the data source is shown in a bar above the table.
Note: If you select Load All from the SCADA Summary Actions menu or click the X button (Red X button.) on the bar above the table, the table will be repopulated with all measurements and the bar will be removed.
Loading SCADA Summary Data for a Different Device
Once the SCADA Summary has been opened (from the Control Tool), you can view data for a different device by selecting it in the Viewer, and then clicking the Load button in the bar above the data table.
Preventing Measurement Updates
To prevent a SCADA measurement from accepting updates from SCADA, complete the following steps:
1. Select SCADA Summary... from the Web Workspace Tools menu. The SCADA Summary window opens.
2. Select a row in the SCADA Summary table corresponding to the device measurement that you want to prevent from updating.
3. Click the Inhibit button.
Manual Entry and Override of SCADA Measurement Values
Occasionally, you may need to manually enter a status, digital value, or analog value for a SCADA measurement. For example, you may need to enter fault current and fault indicators to trigger Fault Location Analysis (if applicable). See Chapter 20, Fault Location Analysis for more information.
If the value for the selected measurement is a switch status measurement (that is, open/close), you must choose Show Control Tool... from the context menu to manually operate the switch. Otherwise, use the following procedure to enter a value manually:
2. Select the SCADA measurement row in the SCADA Summary list.
3. Click either the Manual Entry or Manual Override button.
Note: Manual Entry allows future SCADA value changes to replace the manually entered value. Manual Override prevents SCADA measurements received by the system from changing the manually entered value. Manual Override can be useful when testing specific devices or RTU communications offline, since the test operations can be prevented from creating outages in Oracle Utilities Network Management System by putting manual overrides on the appropriate status measurements.
If the value for the measurement is a multi-state digital, analog, or any type of measurement other than a switch status measurement (open/close), a dialog box opens, allowing you to enter a value.
Note: Multi-state digitals are not available through the Oracle Utilities Network Management System SCADA ICCP Block 1, 2, and 5 Adapter.
4. Select or enter the value you want to change the measurement to.
5. Click OK.
Note: Clicking Manual Override blocks any new values coming from the SCADA measurement. It does not affect the physical SCADA device, it only blocks the value reported by the SCADA device to Oracle Utilities Network Management System.
When you change the SCADA state to Inhibit, Manual Override, or Disabled in Power Flow, you can enter comments to record why the state was changed. When you initiate Inhibit or Disable in Power Flow actions, a dialog box will open allowing you to enter a comment; for Manual Override, a Comment field is available below the Value field. The comment text, user, and date and time the comment was entered will be added to the selected device's SCADA Summary row.
Existing comments may be edited by selecting the SCADA Summary row and selecting Edit Comment... from the Actions menu.
Disabling/Enabling Measurements in the Power Flow Solution
If you see anomalies in the SCADA data (for example, due to mapping issues, transducer issues, or temporal issues, and so on) where SCADA values seem potentially unhelpful in allowing FLMService to solve, you can disable the suspected measurements from taking part in the power flow solution by doing the following:
1. Select the suspected measurements in the SCADA Summary.
2. Click the Disable in Power Flow button from the Actions menu or the right-click option menu. The Quality column value will be set to S for the selected measurements.
To re-enable the disabled measurements:
1. Select the disabled measurements from the SCADA Summary Tool
2. Click the Enable in Power Flow button from the Actions menu or right-click context menu. The Quality column value will be changed from S to blank for the selected measurements.
SCADA Measurements Trend Graph
Menus and Toolbar Buttons
File Menu
Menu Option
Description
Toolbar Icon
Refresh
Refreshes the data in the Trend Graph window with the selected control zone's data.
Rescale
Reload the data for the currently visible time period. This option is not available in live trending mode.
Note: trend lines for which there are no data points in the new time period will not be visible after rescaling.
Print...
Prints the trend graph for the selected region.
Pin
Click to pin the graph, which will open new graphs in separate windows. If a graph is not pinned, then when the Trend Graph option is selected again, the current window will display the data for the new selection.
Note: You may pin multiple graphs.
Exit
Closes the Trend Graph window.
Help Menu
Menu Option
Description
Toolbar Icon
Graph Tool Help...
Opens the online help system to the Trend Graph help content.
The graph will show the predicted values and the actual measurements over the given period of time.
The start and end dates can be changed by selecting a date and time in the Begin Date and End Date fields. Live trending mode can be enabled by the Live Trend check box. In this mode, data is displayed for the hour prior to the current time and newly received values for the displayed measurements are added to the graph dynamically. The Begin Date and End Date fields are disabled.
If you hover the mouse over a point on the graph, the details of the measurement will be shown.