Working with Safety Documents
Oracle Utilities Network Management System Safety Documents, which are an electronic representation of paper safety documents used for switching operations, provide information about a particular operation and record the issuance and release of tags on assets. For switching operations, safety tags are first physically placed on assets, and then the safety document is issued; note that the safety tag must match the safety document type (for example, Hold tags are used with Hold safety documents). Issuing the safety document effectively gives the crew permission to begin work. When the work is completed, the safety document is released, warning the crew that they must stay clear. Once the safety document is released, safety tags may be removed from the assets and the switches may then be closed.
This section includes the following topics:
Understanding Safety Document Types
Oracle Utilities Network Management System Web Switching Management includes a group of safety documents that represent common utility safety document types. These standard forms may be used to represent established safety documents in your organization.
• Clearance - indicates that clearance for work on an asset or in an area has been obtained from the proper authority. The proper authority might be a control center supervisor or a regional dispatcher. Clearance documents imply that the assets or area that requires work has been made safe to work on or in.
• Delegated Control - safety document (DCZ) allows users to identify a section of the network that has been turned over to the field for operation. The operator is no longer in control of the section of the network. It is the responsibility of the crew to operate in a safe and secure manner and document actions taken. See Delegating Control of a Network Area for more information.
• Hold - indicates that the tagged assets should not be operated (for example, if the assets is open, it should remain open). Hold safety documents are used when the asset is to be held open or closed in order to complete work in an area of the distribution system. The purpose of the Hold safety document is to protect crew members and prevent injury to human life. Hold safety documents are placed and removed by individuals who have authority over a specific area or operation and serve to restrict the operation of an asset.
• Information Note - provides some pertinent information about the assets. Information Note safety documents are for informational purposes only. These safety documents do not restrict operation of the asset, but provide information that a crew member or utility employee should be aware of when working on the assets.
• Warning Tag - provides warning information about the tagged assets. Like Information Note safety documents, Warning Tags are for informational purposes only. These safety documents do not restrict operation of the assets, but provide information that a crew member or utility employee should be aware of when working on the tagged assets.
While safety document names and features may vary, understanding these types will help you understand the general use of most safety documents. Crews typically "own" safety documents and must authorize their release when they are finished working in an area or on an asset.
Mapping Step Types to Safety Document Types
Safety document types are associated with certain types of steps. These step-to-safety document mappings are configurable. The following list shows what types of steps each safety document type is pre-configured to accept.
• Clearance:
• Place Clearance Tag
• Remove Clearance Tag
• Delegated Control (DCZ)
• Place DCZ Tag
• Remove DCZ Tag
• Hold:
• Place Hold Tag
• Remove Hold Tag
• Informational Note:
• Place INFO Tag
• Remove INFO Tag
• Warning Tag:
• Place WARN Tag
• Remove WARN Tag
Using Safety Documents in Switching Plans
Understanding the Safety Documents Tab
The Switching Sheet Safety Documents tab displays a list of all safety documents associated with a switching sheet. The Safety Documents tab displays the following fields and menu bar buttons:
Fields
• Type displays the type of safety document. (See Understanding Safety Document Types.)
• Doc # displays the safety document number.
• Status displays the status of the safety document. Valid statuses are: New, Issued, Released, Unissued, Aborted, Deleted, and Completed.
• Crews displays the crews assigned to this safety document.
• Description displays a description of the safety document.
Menu Bar Buttons
• The Refresh button() refreshes the safety document list.
• The Create a Safety Document button () opens an context menu that allows you to choose a safety document type or open the Select Safety Type dialog box.
• The Open button () opens the selected safety document. (Alternatively, you can double-click the document in the list.)
• The Associate button () displays the Switching Sheet Association dialog box. From the dialog box you can associate the safety document to a different switching sheet. See Switching Sheet Associations for more details.
• The Disassociate button (), when pressed, displays a confirmation dialog box pertaining to the disassociation of the safety document. Confirming the action will cause the safety document to be disassociated from the switching sheet. Once disassociated, the document is converted into a stand alone safety document.
• The Delete button () deletes the selected safety document. Safety documents can only be deleted if there are no steps associated to the document. Deleted safety documents are not removed from the database.
Safety Document Dialog Overview
The Safety Documents associated to switching sheets are displayed as detached windows. When working with Web Safety, when there is no originating switching sheet, the document takes on a slightly different behavior and look. For more information on Stand Alone Safety Documents see Web Safety.
Toolbar Icons
• The Save button () saves your changes to the safety document.
• The Print Preview button () allows you to select a report format and then preview the safety document in the selected format.
• The Print button () allows you to select a printer and then print a hard copy of the safety document to the selected printer.
• The Email button () allows you to email a version of safety document. You will be prompted to select a report format (PDF, HTML, RTF, or XML); click Email... to generate the file, which will be attached to a new message launched from your default email application.
• The Validate button (), which is available on the DCZ safety documents, is used to determine whether the listed assets potentially isolate an area of the network. If the list of assets is not sufficient, a dialog will suggest the first missing asset needed, provide an option to add it, and re-validate the new list.
• The Issue button () adds a step for issuing the selected safety document. The step is added to the end of the steps list or after the step insertion indicator (if one has been placed). This button is enabled when a document is in the New and Released states so the document may be issued and released multiple times. If any of the assets in the Tag Points list are not associated to steps, then the appropriate conditions will be placed on those assets when the document is transitioned to the Issued state.
• The Unissue button () is used to place an Issued safety document or a Released safety document into an Unissued (edit) state where the asset lists can be altered. While in the Unissued state, you can add assets to the lists and mark assets already in the list for removal. Only when the safety document transitions back to the Issued state will the changes be applied.
• The Release button () adds a step for releasing the selected safety document. The step is added to the end of the steps list or after the step insertion indicator (if one has been placed). This button is only enabled if the safety document has been issued. Selecting this button will cause the Complete button to be enabled.
• The Complete button () adds a step for completing the selected safety document. The step is added to the end of the steps list or after the step insertion indicator (if one has been placed). If any of the assets in the Tag Points list are not associated to steps, then the appropriate conditions will be removed from those assets when the document is transitioned to the Completed state.
• The Abort button () allows you to set the status of the safety document to Aborted. The system prompts you to confirm the action before aborting. This button is only available in real-time mode and only for safety documents that are in the New state.
Safety Document Panes
The safety document dialog box displays the following panes:
• Tag Points display the assets that the safety document is associated with.
Table Columns
• Edit State (untitled): an iconic representation of the edited state of the asset in the Unissued state. The edits will be applied when the document is issued. When working in Study mode, the edit state indicators will remain visible until the document is issued in real time.
• : The asset has been marked for removal.
• : The asset has been added to the asset list and will be used as a boundary point the next time the document is issued.
• Asset: the asset used to define the area or point of coverage of the safety document.
Toolbar Buttons
• Screen capture of Record button showing a red filled circle followed by the word ’Record" / Screen capture of Stop button showing a blue filled square followed by the word ’Stop": Toggles recording of assets off or on. The Tag Points list allows users to record assets via selections from the Viewer. To enable this feature, simply turn on recording and select assets in the Viewer.
• The Add Asset... button () allows you to manually add an asset to the list.
• The Undo Asset Edit button () allows you to undo an addition or removal of an asset from the list. This option is only available when making asset modifications in the Unissued state.
• The Remove Asset button () allows you to remove a selected asset from the Tag Points asset list.
• The Object Focus button () focuses the Viewer 1 window on the selected asset.
• Nominal Pressure Zone displays the pressure zones for the assets listed in the Tag Points assets list.
• The Update button () is used to populate the Nominal Pressure Zones field with the list of Pressure Zones associated to the linked switching sheet step assets and the assets listed on the safety document.
• The Reset Pressure Zone Value button () is used to replace the safety document's current pressure zone value with the associated switching sheet Nominal Pressure Zones field value when the safety document was created. The switching sheet's Nominal Pressure Zones field is found on the Request tab.
• Nominal Lift Station displays the nominal lift station for the assets listed in the Tag Points list. To alter this value, enter your new value into the field.
• The Update button () is used to populate the Nominal Lift Station field with the list of lift station associated to the linked switching sheet step assets and the assets listed on the safety document.
• The Reset Lift Station Value button () is used to replace the safety document's current lift station value with the associated switching sheet Nominal Lift Station field value. The switching sheet's Nominal Lift Station field is found on the Request tab.
• Current Pressure Zone displays the current pressure zones for the assets listed in the Tag Points list. This value is read-only and will dynamically update as long as the safety document is loaded.
• Current Lift Station displays the current lift station for the assets listed in the Tag Points list. This value is read-only and will dynamically update as long as the safety document is loaded.
• Assigned Crews displays a table list of the Crew IDs of the crews that the safety document has been issued to, as well as each crew's mobile number, mobile carrier, alternate number, alternate number type, pager number, and crew type. The crew IDs are auto-populated with the value from the Instructed To field in the safety state transition switching step. A crew is required in this list before an Issue safety state transition step can be completed in real-time.
• To select a crew to assign to this safety document, click the Select Crew... () button to open the Select Safety Crew dialog box. See Assigning Crews to a Safety Document.
• To display the selected crew information, click the Crew Info... () button.
• To indicate whether the crew is issued or clear of the zone defined by the safety document, click the Crew Issued/Clear () button and select either Issued or Clear. The Position column will be updated with the status.
• To delete crews from this list, click the crews and then click the Remove Crews button (). At least one crew must remain assigned while the document is in the Issued state.
• Description is a text field that allows you to enter notes for the safety document.
• Audit Log contains the following information:
• Table Fields:
• Date: the date and time of each entry.
• Description: a description of the state change or asset operation.
• Asset: the asset associated with the step.
• User: the name of the user who recorded the action.
• Crews: the crew identifiers pertaining to the audit log entry.
• The Comment section of the Audit Log pane allows you to add a comment to the log.
• Edit Log tracks the changes made to the entry fields of the document. It contains the following information:
• State: the state of the safety document when the entry was added.
• Field: The name of the field that was updated.
• Previous Value: The previous value of the field before the update.
Creating a Safety Document from a Switching Sheet
Assets may be added automatically to a Safety Document by creating a safety document from step selections within the Steps list of the originating switching sheet. You may create a safety document in two ways:
1. Create a Safety Document for a Selected Step:
• On the Steps tab, select the steps to which you want the safety document associated. For instance, select Hold Tag steps to create Hold safety documents. These steps then define the isolation points for the safety document.
• Click the Create Safety Document for Selected Step toolbar button ().
• If the selected step maps to multiple types of safety documents, the Select Safety Type dialog box prompts you to select the document type.
Your selected step must conform or map to at least one safety document type. If a selected step does not map to a safety document type, the system will return an error message in the Invalid Step Selection dialog box. Click OK to close the dialog box.
• Select the safety document type and click OK.
Note: For a list of step types to safety document types, see Mapping Step Types to Safety Document Types. The steps in the sheet will also be updated with an additional entry in the Operation text indicating which safety document the step is associated to.
2. Create a Safety Document Without Selecting a Step:
• To create a safety document without selecting a step, click the Create Safety Document () button, which provides an context menu allowing you to select a specific safety document type or open the Select Safety Document Type dialog box.
• If you select a safety document type, the new safety document will be created. If you select Select Safety Type Dialog..., the Select Safety Type dialog box will open allowing you to choose the document type. Select the safety document type, and click OK.
The Select Safety Crew dialog box allows you to assign crews to the safety document. You may also create contractor crews from the Contractors tab. By default, the dialog box will open showing the crews listed on the parent switching sheet's Crews list. The Switching Sheet Crews tab will only be visible for safety documents associated to switching sheets.
Populating Crews from the Switching Sheet
Crews are automatically assigned to safety documents when the safety document is created from a switching sheet where the switching sheet has crews listed in the Crews list. If a subset of the switching sheet's crews should be used to populate the safety document's Crews list, then simply select the crews prior to creating the safety document from the switching sheet.
1. Add a list of crews to the switching sheet's Crews list.
2. Click the switching sheet's Create Safety Document button and select the desired safety document type.
The safety document will be created with a list of assigned crews matching the crews listed in the parent switching sheet. If none or all of the crews were highlighted in the switching sheet, then all of these crews will be assigned to the safety document. If a subset of the crews were highlighted in the switching sheet, then only those crews will be assigned to the safety document when it is created.
Selecting Crews from the System Crews List
To assign a standard (system) crew to the safety document:
1. Click the Select Crew... button () to open the Select Safety Crew dialog box
2. On the System Crews tab, select one or more crew rows in the table.
Note: You may Shift+Click to select multiple adjacent rows or Control+Click to select non-adjacent rows.
3. Click OK to assign the crews and close the dialog box.
Note: Click Apply to assign the selected crews without closing the dialog box. Crews will appear in the "Unknown" position.
Creating and Assigning Contractor Crews from the Contractor Entry Form
You may add a new contractor crew using the Contractor Entry Form. The created crews are assigned to the current safety document and added to the Contractor Crew List from which they may be assigned to other safety documents or switching sheets.
The form contains the following fields:
• Crew ID: the crew name or identifier.
• Contact: the name of the crew contact person.
• Mobile #: the crew's mobile number.
• Mobile Carrier: the wireless company providing service to the mobile phone or radio.
• Alternate #: an alternate number for the crew.
• Alternate Type: the crew's alternate number type (for example, home, personal mobile, and so on).
• Pager #: the crew's pager number.
• Type: crew option menu that allows you to choose the crew type.
• Comments: text field for comments.
Actions
• Create and Assign Crew (): assigns the new crew entry to the safety document and adds them to the contractor crew list.
Note: The Select Safety Crew dialog box closes once the add button () is clicked.
• Clear Crew Fields (): clears the entry form.
Using the Contractor Crew List
The Contractor Crew List allows you to assign existing contractor crews to the safety document or populate the Contractor Entry Form to reuse crew data when creating additional contractor crews.
The form contains the following toolbar buttons:
• Refresh Crew List (): refreshes the contractor crew list with the full list of active contractors found in the database.
• Assign Crew (): assigns crews to the safety document.
• Transfer Crew Data (): transfers the selected crew's data up to the Contractor Entry Form fields. This allows contractors to be copied with minimal effort.
• Obsolete Crew (): obsoletes a crew so that it no longer shows up in the Contractor Crew List. If the crew is still part of an active safety document or switching sheet, an error will be generated. The crew is not deleted from the system as it is still needed for auditing purposes in completed switching sheets and safety documents.
Assigning an Existing Contractor Crew
1. Select the crew rows in the Contractor Crew List.
2. Click the Assign Crew button () to assign the crews to the sheet.
Assigning a New Contractor Crew Using Existing Crew Data
To create an additional contractor crew using data from an existing crew, do the following
1. In the Contractor Crew List, select the row with the desired crew data.
2. Click the Transfer Crew Data button () to copy the data to the Contractor Entry Form.
3. Edit the data for the new crew.
4. Click the Create and Assign Crew button () to assign the new crew to the safety document and add them to the Contractor Crew List.
Adding a Safety State Transition Step
Each safety state transition step performs a single action, such as issuing or releasing a safety document. To add safety state transition steps, do the following:
1. From a switching, create a new safety document. See Creating a Safety Document from a Switching Sheet for more information.
2. Validate that step recording is still turned on in the Steps tab.
3. Click the Issue button () on the safety document. A new safety state transition step is recorded into the switching sheet steps list. The Operation column of the step indicates the type of operation being performed.
Notes:
Conditions associated to the assets in the Tag Points list has to be on the assets for the document to be issued. If the conditions are not on the assets, an error dialog box will be displayed with the list of conditions that could not be found. The switching steps associated to those conditions will be highlighted in the switching sheet. This is mode specific, so when in study mode, the conditions have to be on the assets in your study session. Conditions are not required when only the Other Assets field is filled out.
When recording the safety state transition steps in Real-Time, the safety document must have an assigned crew before it can be issued. This is not a requirement when in Study mode.
4. Select the Release and Complete buttons on the safety document. New safety state transition steps are recorded into the Steps list for the Release and Complete operations.
5. Close the safety document.
Note: If you changed the Other Assets or Description field, you will be asked to save the changes. All other fields are automatically saved within the associated switching steps.
For instructions on executing safety state transition steps, see Executing Safety State Transition Steps.
Safety State Transition Failed Dialog Box
When a safety document is issued the conditions (tags) associated with it are locked. If some of the expected conditions are missing or fail to lock, the Safety Transition Failed dialog box is displayed. The Failed Safety Actions table contains the list of switching steps associated with the safety document, that caused the failure.
The switching steps placing those conditions will be highlighted on the Steps tab. Affected rows in the Tag Points list in the safety document will also be highlighted.
Editing the Asset List
The Tag Points lists on the Hold, Clearance, Delegated Control, Information, and Warning safety documents may only be altered when in the New or Unissued states.
Adding Assets to a Non-Execute Safety Document
You can add additional assets to a safety document through one of three ways.
• The first method involves associated steps with assets to the safety document. The second method allows you to added assets directly to the safety document through asset selections in the Viewer. The third method uses the Add Asset dialog box, from which you can enter or search for an asset to be added to the list.
Step Association Method
The step association method is accomplished by doing the following:
1. Open a non-execute version of a safety document. (A non-execute version is loaded from the Safety Lists and the Control Tool. It displays a toolbar at the top of the dialog box and no Execute button at the bottom.)
From the associated switching sheet steps list, select the step with the asset operation you want added to the safety document. For example, if you select an Add or Remove Tag step, the assets is added to the Tag Points list on the safety document dialog box.
2. Click the Link Switching Step Asset button () on the safety document dialog box. The new asset is added to the appropriate asset list.
Notes:
• If the selected step is already associated to a safety document, then an error dialog box indicates which safety document the step is already associated to.
• If the select step type is not configured for the safety document type, then an error will be displayed indicating the step that does not conform to the configured step to safety document type rules. For a list of step types to safety document types, see Mapping Step Types to Safety Document Types.
Asset Recording Method
The asset recording method is accomplished by doing the following:
1. Open a non-execute version of a safety document. (A non-execute version is loaded from the Safety Lists and the Control Tool. It displays a toolbar at the top of the dialog box without an Execute button.)
2. Click the Record button on the Tag Points toolbar to turn recording on for that asset list.
3. In the Viewer, select assets that should be added to the Tag Points asset list.
Safety Document Add Asset Dialog Method
Using the Safety Document Add Asset dialog box, assets can be added to the Tag Points list by doing the following:
2. Click the Add Asset… button () found on the Tag Points toolbar. The Safety Document Add Asset dialog box is displayed.
3. From the dialog box, enter part or all of an asset alias. The search button () can be used to find an asset from a partial asset id.
4. Click Add Asset (). The asset will be added to the Tag Points list.
5. Continue to add assets and when completed, click Close.
Removing Assets
You can remove assets from an asset list in two ways.
Option 1
2. Select the asset you would like to remove from the Tag Points list.
3. Click the Remove Asset button () from the appropriate asset list toolbar. The asset is removed from the list if the document is in the New state or is marked for removal if the document is in the Unissued state
Option 2
1. From the associated switching sheet steps list, select the step with the asset operation that you want removed from the safety document. For instance, if you select an Add or Remove tag step, the asset will be removed from the Tag Points list.
2. Click the Unlink From a Safety Document button () on the Steps tab toolbar. The asset is removed from the safety document's asset list if the document is in the New state or is marked for removal if the document is in the Unissued state.
Note: The Unlink From a Safety Document button can only be used for assets in the safety document that are associated to steps. Assets added without step associations will have to be removed using Option 1 described above.
Adding a Comment to the Audit Log
The Comment section of the Audit Log pane allows you to add a comment to the log. Select the Comment field and enter a comment; click the Add button () to add the comment to the Audit Log.
Once a safety state transition step has been recorded, executing (completing) the step causes the Execute Safety Step dialog box to be displayed. This dialog box looks just like the original safety document dialog box except that it has no toolbar and it displays two buttons: Execute and Cancel. Use this dialog box to verify that the safety document information is correct, and then click Execute to execute the step.
When a tag step with an associated safety document is executed, the Control Tool executes placement of the appropriate tag (Hold, Clearance, and so on) on the asset. The symbol on the asset indicates that a condition exists on the asset, that the area has not been issued to the crew, and is not yet isolated. After the safety document has been issued, the symbol on the asset changes to indicate that the tag is under the control of the safety document. For example, if configured in your project, a Hold tag may change to indicate Hold with a small lock symbol next to it. When a tag changes to a locked state, the safety document must be released before the tags can be removed using the Control Tool. Likewise, when the safety document is transitioned to the Unissued state, the tag symbols on the assets will change to indicate that they are still part of an active safety document, but are in a state to where they can be removed; they are allowed to be removed so that the zone of coverage for the safety document can be altered while in the Unissued state.
For more information, see one of the following topics:
Issuing Safety Documents
Safety documents are issued when an Issue safety document switching step is completed and the Execute button is clicked on the safety document.
Note: The appropriate tag type must be placed on the asset prior to the safety document being issued. For example, to issue a Hold document, you must place a Hold tag on the asset before the safety document can be issued. This only pertains to assets associated to switching steps. Assets not associated to steps will automatically have conditions placed on the them when the document is issued.
When a safety document is transitioned from the Unissued state to the Issued state, all of the pending asset list changes will be applied. If the transition is initiated in real-time mode, then any assets marked for removal will be removed from the list and related audit log entries will be created for each asset change.
Once a safety document is issued:
• Crews are transitioned to the "Issued" position.
• You cannot complete, delete, or reissue the safety document. The asset lists cannot be altered while in the Issued state.
• The only state related button options available on the safety document dialog box are Unissue and Release.
• The Viewer displays a symbol on all assets that are specified in the safety document to indicate that the safety document has been issued.
Issuing Safety Documents Manually
To issue a safety document manually:
1. Open the safety document (if it is not already open) by selecting the document on the Safety Documents tab and clicking the Open button.
2. Click Issue on the open safety document. A symbol appears on all assets that are specified in the safety document to indicate that the safety document has been issued.
Note: If you manually Issue a safety document in real-time mode, a safety state transition step is automatically recorded to the Steps list, regardless of whether step recording is turned on. This is the audit of the safety documents transitions.
Issuing Safety Documents While Executing Steps
To issue a safety document through step execution:
1. From the Steps List, select the Issue safety state transition step and click the Complete button. The Execute Safety Step dialog box opens, and the Execute and Cancel buttons are enabled.
Note: When instructing safety state transition steps in real-time mode, the safety document dialog box is not displayed. It is only displayed when the step is completed.
2. Click the Execute button. A symbol appears on all assets in the Viewer that are specified in the safety document to indicate that the safety document has been issued. The safety state transition step is also marked as Completed.
If any of the assets in the Tag Points list were not associated to switching steps, then conditions will be applied to the assets first. After all the conditions are on the assets, then the conditions will be changed to indicate that they are under the control of the safety document.
Releasing Safety Documents
Safety documents are released when switching steps associated to a releasing safety document are completed and the safety document's Execute button is clicked. The symbol for the safety document is removed from the asset in the Viewer and the original tag symbols are placed back onto the asset. At this point the Safety Document can either be reissued to a different crew or completed.
Note: Safety Documents cannot be released if any crews are still in the "Issued" position. Crews need to be "Clear" to proceed.
Releasing Safety Documents Manually
To release a safety document manually:
Note: The document must already be issued before it can be released.
1. Open the safety document (if it is not already open) by selecting the document on the Safety Documents tab and click Open.
2. In the safety document, click Release. The symbol for the safety document is removed from the asset and the original tag symbols are placed on the asset.
Note: If you manually release a safety document in real-time mode, a safety state transition step is automatically recorded to the Steps list, regardless of whether step recording is turned on. This is the audit of the safety documents transitions.
Releasing Safety Documents While Executing Steps
To release a safety document through step execution:
1. From the Steps List, select the Release safety state transition step and click Complete. The Execute Safety Step dialog box opens, and the Execute and Cancel buttons are enabled.
2. Click Execute. The symbol for the safety document is removed from the assets and the original tag symbols are placed on the assets. The safety state transition step is also marked as Completed.
Deleting a Safety Document
Safety documents can be marked as Deleted from the associated switching sheets Safety Documents tab. Safety documents can only transition to the Deleted state when they do not have safety state transition steps linked to them in the switching sheet's Steps list. Attempting to mark a safety document as Deleted with linked safety state transition steps will result in an error dialog box. You will need to delete the safety state transition steps before the safety document can be marked as Deleted.
To mark a safety document as Deleted:
1. Navigate to the associated switching sheets Safety Documents tab.
2. From the safety documents list, select the document entry, and click Delete. The document will be marked as Deleted. Safety documents can only be marked as Deleted when in the New state.
When you issue a DCZ Safety document, the system delegates the segment of the network bounded by the listed assets. No operations are allowed on any assets in the segment until the document is released.
Your assets must completely bound an area to be considered adequate for Delegated Control. That is, there should be no alternate way to supply any of the assets in the area.
Safety Document List
The Safety Document List is a tool used to manage active safety documents and any safety documents associated to switching sheets that have been completed in the last 30 days. To load safety documents no longer available in the Safety Document List, use the Search Safety Document window.
The Safety Document List will load the full list from the database when it is first displayed. After the initial load of the data, the list will dynamically update with changes from all users on the system. Dynamic updates happen periodically at 15 second intervals. A safety document's updates will only be broadcast out to the other users once it has been saved to the database.
The full list of safety documents will be queried from the database when you alter your subscribed zones via the Authority tool. The full list will also be queried if you select the Refresh button from the Actions menu. Once the full list has been loaded, the list will go back to being dynamically updated.
The Safety Document List serves as the primary mechanism from which to load safety documents outside or not associated to switching sheets. You can either double click on a single entry or highlight multiple entries and click the Open... toolbar option.
Note: When loading multiple safety documents, a progress bar will be displayed at the bottom of the window.
Once an open request has been initiated, it cannot be canceled, but the system does restrict you from having more than 15 switching sheets open at any one time. Each safety document is linked to a switching sheet.
The Safety Document List will be filtered based on the control zones you are subscribed to. The asset listed on the parent sheet's Request tab determines the control zone that a safety document is associated with; however, if no asset is entered, then the safety document will fall within the FUZZY zone.
Menu and Toolbar Features
This section lists and describes the menu options and toolbar icons available in the Safety Document List.
File Menu
The table below describes the options available on the File menu.
Menu Option
Description
Icon
Open...
Opens the selected safety documents and their associated switching sheets. If the window is not pinned or docked, the window will be closed once the safety documents are loaded.
Note: If the safety is locked by another user, the Failed to Establish User Lock dialog box will be displayed; see Opening Locked Documents for information.
Export Table...
Opens a dialog box to allow you to save the current table view data to a comma separated value (csv) file.
Print
Displays the Print Preview dialog box so you can view or print the list.
Toggle Dockable Window
Changes a standalone window to a pane that may be moved or docked in another window or frame. See Understanding Docked Panes and Standalone Window Tools for more information on dockable and standalone windows.
Exit
Closes the Safety Document List window.
Sort Menu
The table below describes the options available on the Sort menu.
Menu Option
Description
Icon
Sort Dialog...
Opens the Sort dialog, allowing you to create, modify, apply, and save user-defined sorts. See Using the Sort Dialog Box.
Doc #
Applies the default sort, which is the doc # in descending order.
Actions Menu
The table below describes the options available on the Actions menu.
Menu Option
Description
Toolbar Icon
Refresh
Refresh the safety document list with the latest data from the database.
• Unpin
• Pin
• Unpin the window so that it will close after an open safety document request.
• Pin the window so that it will not close after an open safety document request.
Note: The icon shows the current state (that is, unpinned).
Help Menu
The table below describes the options available on the Help menu.
Menu Option
Description
Toolbar Icon
Safety Document List Help
Opens the online help system to the Safety Document List help content.
Safety Document List Data Fields
The Safety Document List provides a tabular view of the safety document. The sort and filter criteria are displayed above the table.
• The Status column displays the status of the safety document.
• The Type column displays the safety document type.
• The Doc # column displays the safety document number.
• The Sheet # column displays the switching sheet the document is associated to.
• The Nominal Pressure Zone, Current Pressure Zone, Nominal Lift Station, and Current Lift Station columns display values as displayed on the safety document.
• The Issued Date column displays the date the document was last issued.
• The Crews column displays the crews the document was issued to.
• The Description is the description of the safety document as entered on the document.
• The Released Date displays the date the document was last released.
• The Completed Date displays the date the document was completed.
Understanding the Safety Document List Filter Pane
The Safety Document List provides the following Global filters.
Global Filter
Description
Active
Displays all the active safety documents (safety documents with statuses of Issued, Unissued, and Released).
All
Displays all safety documents and safety documents associated to completed switching sheets from the last 30 days.
Completed
Displays safety documents that are in the Completed state that are not associated to a switching sheet that has been completed longer than 30 days.
Issued
Displays all safety documents in the Issued state.
New
Displays all safety documents in the New state.
Opening Existing Safety Documents
Note: If the sheet is locked by another user, the Failed to Establish User Lock dialog box will be displayed; see Opening Locked Documents for information.
From the Web Workspace File Menu
1. Select Open and then Safety Documents… The Safety Documents List appears.
2. Select the safety document you want to open and click the Open button or double-click on the document in the list. The safety document is opened. If the safety document is associated with a switching sheet, the switching sheet will also open.
From the Web Workspace Search Safety Document Dialog
To search for an existing safety document:
1. From the Web Workspace File menu, select Safety Document Search... from the Open option.
2. In the Search Safety Document dialog box, enter the desired text to search and press Enter or click the Search () button.
Note: The search results will be filtered based on the parent sheet's master asset NCG and your subscribed zones of authority. The NCG for stand alone safety documents will be determined by the asset populated in the safety document's Asset field. The filtering of the results, based on NCG, will not apply to the Administration user type.
Open a Safety Document from an Open Switching Sheet
1. Click the Safety Documents tab.
2. Select the safety document you want to open and click the Open button or double-click the document in the list. The safety document dialog box is displayed.
Open a Safety Document from a Switching Step on the Steps Tab
1. Right-click on one or more steps that have safety document associations, then select Load Safety Documents… from the context menu. The safety document dialog boxes are displayed.
Note: Steps with associated safety documents display the document type and number displayed in the Operation step column.
Open a Safety Document from the Control Tool
1. For active safety documents, double-click an asset in the Viewer.
2. From the Control Tool, click Safety Documents… and then select Open Safety Documents... from the submenu.
• If only one safety document is currently active on this asset, then the safety document dialog box is displayed.
• If multiple safety documents are active, the Asset to Safety Document List displays a list of safety documents for the asset. The list includes only safety documents that are part of an active sheet and documents that were completed in the last 30 days. Select the safety document you want to load from this list.
The safety document and the associated switching sheet are opened. The safety document will be opened in the same mode that the Control Tool is in.
Completing Safety Documents
When you have completed all steps in a switching sheet, you should complete all safety documents associated with the sheet.
To complete a safety document, use either of the following methods.
Option 1
1. Follow the steps described above to open the safety document.
2. Click the Complete button on the safety document dialog box.
Note: Once completed, the document is locked from further editing. When manually completing a safety document in real-time mode, the action is automatically recorded in the associated switching sheet's Steps list.
Any assets in the Tag Points list, that were not associated to steps, will have their conditions removed.
3. Repeat these steps for all safety documents associated with the switching sheet.
Option 2
1. Record a Complete safety state transition step (as described in the previous sections) and use that step to complete the safety document. Repeat for all safety documents associated with the switching sheet.
Aborting Safety Documents
If a switching sheet is aborted, you will need to abort any associated safety documents before you can complete the switching sheet.
Note: The Abort option is only available in real-time mode when the safety document is in the New state.
To abort a safety document, follow these steps:
2. Double-click the safety document you want to abort.
3. Click the Abort button on the toolbar.
4. When prompted, confirm you action.
Safety documents can be associated to different switching sheets and even disassociated and converted into a stand alone safety document. Safety documents can only be associated to different sheets or disassociated if the safety document does not have any switching sheet step links. An error will be issued to you if you attempt to disassociate or move a safety document that has linked switching sheet steps. A safety document's type and number will be displayed in the step's Operation column if a link exists.
When disassociating a safety document from a switching sheet, a confirmation dialog box will be displayed to you. You must confirm the operation before the disassociation will proceed. When the document is disassociated, it will be converted into a stand alone safety document. The audit log of the switching sheet and the safety document will indicate when and who initiated the operation.
Safety document associations originate from the Switching Sheet Association dialog box. This dialog box allows you to select a sheet from a list of switching sheets you already have loaded or you can search for a particular switching sheet in the system. Completed switching sheets and switching sheets that cannot accept safety document associations will be filtered out of the list. Safety document association changes will result in audit log entries in the original switching sheet along with the target switching sheet and the safety document.
