Data Categories
The ADMS applications use the following data categories. Full details can be found in the Modeling Workbook and the "DMS Modeling Requirements" document.
Sources
pf_sources table
Required for:
Providing source energization into the model
Used by:
All ADMS modules to determine energization sources
Notes:
Generally default data is acceptable though FLA accuracy is dependent on getting impedances correct.
Loads
pf_loads table; ultimately used in the pf_loads_profile_view, which combines the loads with their load profile data. The pf_loads_profile_view table is a near replica of the pf_loads table with the exception of the profile_id column. If no data exists for a device in the pf_loads_profile_override the profile_id data will come from the pf_loads table but as soon a device is populated with a value in the pf_loads_profile_override table the profile_id data will come from that table instead.
Please see the Load Profile Data section below for more information.
Required for:
Modeling the point of consumption of energy
Used by:
All ADMS modules to determine where power is utilized
Usage:
Aside from SCADA measurements, the flow of power around the network is determined by the expected load size at each point of consumption. Therefore accurate load data is particularly important for Load Flow accuracy.
Additional the mixture of Constant Power, Constant Current and Constant Impedance load is important in optimization applications for determining optimal configurations.
Load Profile Data
pf_load_interval_data: Contains default, customer class, and/or device specific load profiles. Data within this table can come from the Power Flow Engineering Data workbook and/or the NMS Profile Adapter. Typically default profiles and customer class profiles will be defined in the Power Flow Engineering Data workbook and imported into this table. These records will have a default indicator set within the table. The Profile Adapter can also be setup to write to this table with device specific profiles. The adapter will not touch any profiles that are marked as a default.
pf_loads_profile_override: This table is only written to by the NMS Profile Adapter and is used to mark which profiles have been loaded by the adapter and are device specific. This is used to override the value in profile_id within table pf_loads. For example, a load may initially be configured with a profile_id of "Residential" but once the adapter loads a specific profile for the device a value will be placed in table pf_loads_profile_override of "T10520". Once this takes place the view pf_loads_profile_view which is a combination of pf_loads and pf_loads_profile_override will pick up the fact a specific profile is available and the profie_id column will be populated with data from pf_loads_profile_override instead of pf_loads.
pf_loads_profile_samples: This table is only written to by the NMS Profile Adapter and is used to track how many times different day type/hour/temperature combinations have been sampled. The frequency at which certain data points have been sampled is used in the averaging algorithm by the adapter.
Required for:
Modeling the changes in load consumption over time and temperature
Used by:
All ADMS applications to improve the accuracy of power flow. Particularly important for applications where future forecasts are required, these are: Feeder Load Management, FLISR, Suggested Switching and Optimization
Notes:
Load profile data is used to model how load changes over time. A single load profile represents the change in load levels over a 24-hour period. Multiple profiles may be associated with a single load to represent different load behavior for different types of day (for example, weekday, weekend) and for different temperatures (for example, 80°F - 90°F, 90°F - 100°F). The use of load profile data improves the accuracy of the DMS applications by providing more realistic loading scenarios for the current or predicted analysis time period. For example, profiles are used to verify switch plans, determine suggested switching recommendations, and generate daily and seasonal peak limit alarms.
The Oracle Utilities Network Management System supports a variety of sources of load profile data such as load class profiles or individual transformer profiles. Once processed, all profile data is placed in the pf_load_interval_data table. For load class profiles, the profile_id column in the pf_loads table can be set to point to the appropriate data in the pf_load_interval_data table. For transformer specific profiles, the adapter will populate a table pf_loads_profile_override; this table will be used to specify which transformers have specific profiles as opposed to just load class profiles. Anything defined in the pf_loads_profile_override table will override the profile_id field in the pf_loads table.
Please see the "Modeling Loads" section in Chapter 8 of the Oracle Utilities Network Management System Configuration Guide for more information.
Transformers (and Voltage Regulators)
pf_xfmrs, pf_xfmrs_tanks table, pf_xfmr_limits for seasonal, temperature, and dynamic ratings.
Required for:
Modeling the locations where voltage is changed and/or regulated
Used by:
All ADMS applications to determine accurate voltage levels across the network
Feeder Load management and FLISR to generate overload and voltage violations.
Optimization to determine regulation parameters for optimal network configuration.
Notes:
Some data (for example, regulation parameters) can be defaulted if voltage accuracy is not critically important.
FLA requires accurate impedance information to correctly determine fault currents
• As of NMS v2.4+, projects will not be required to populating indicators specifying if grounds or neutrals are present on the primary and secondary windings. This information will be inferred from the transformer winding type specified for each device. The various winding types supported and details about the grounding information can be found in the Power Flow Engineering Data workbook.
• As of NMS v2.5+, two new transformer winding types have been made available for unique cases. A Zigzag winding has been added which is a single winding transformer that can be used as a grounding bank to create a grounding point on delta configured circuits. The second new type is a Scott winding that takes 3 phases at 120Degree rotation and converts to 2 phases with 90Degree rotation.
• The following configuration will be needed if transformers operate at a different voltage level than the system base. The primary and secondary ratios will need to be adjusted for the voltage the transformer outputs at the neutral tap position. The voltages configured for the unit should be based on what the voltages base that should be used for displaying results.
For example, if a transformer had voltages levels from 138kV to 13.8kV on network at a 13.2kV system base, the primary ratio would be set to 1, the secondary ratio set to 1.04, the primary voltage would be set to 138kV, and the secondary voltage set to 13.2kV. If the device is auto regulating, the voltage target would then be set in P.U. based on a 13.2kV system base. With this scenario, the transferrer would output 13.8kV assuming no load and a 138kV input at the neutral LTC position. The power flow details would indicate this in the balloon as 1.04P.U. based on a 13.2kV system base.
Capacitors (and Reactors)
pf_capacitors table
Required for:
Power flow, in particular to determine reactive power flow
Used by:
All DMS applications to determine accurate load flow.
Notes:
Capacitors have significant impact on power flow. The reactive flow around the network affects current magnitude, voltage and power factor.
Capacitors must be modeled shunted off the feeder. The device should either be directly connected to the feeder or with a handful of devices to create a simple path between the device and feeder (for example, conductors and switch). If things like bypasses or junctions exist between the capacitor and feeder the NMS tracing during power flow services (PFService, FLMService, FLTService, and VVOService) startup may not be able to properly identify the monitored device for regulation.
By default, amp and var regulating capacitors monitor the flow near the connection point. If the default location is incorrect, the actual metering location can be specified in the source data.