Understanding the Grid DERMS Dashboard
The Grid DERMS Dashboard is available in Web Workspace and Flex Operations. Use the section for your client to learn how to view DER information and forecasts.
Using the Grid DERMS Dashboard in Web Workspace
Oracle Utilities Network Management System's Grid DERMS Dashboard provides information related to distributed energy resources (DERs) connected to an electric distribution system. This information can be used to better assess the amount of current DER contribution, as well as the forecasted DER contributions.
Note: Feeder Load Management must be installed and configured for data population in the DERMS Dashboard. In Web Workspace, the DERMS Dashboard menu option requires the Grid DERMS license and an eligible Web Workspace user type: Trainer, View Only, Administration, or Full Operations. Feeder Load Management licensing alone does not enable the DERMS Dashboard menu option.
The Grid DERMS Dashboard provides high level and detailed forecast information broken out by different DER technology types (for example, PV, Wind, Gas, and so on).
The Grid DERMS Dashboard also displays Approved eVPP Reduction and Proposed eVPP Reduction for current and historical feeder data. Approved values come from active eVPP schedule rows that were applied to the power flow solve. Proposed values come from active rows that were retained for reporting but were not applied. The dashboard attributes both values to the owning feeder and feeder network connectivity group recorded by Feeder Load Management. For more information, see Edge Virtual Power Plants.
The Grid DERMS Dashboard provides a tabbed user interface containing summary and forecast information related to DERs for an electrical distribution system. It is accessed by selecting DERMS Dashboard... from the Web Workspace Tools menu.
On the scheduled events chart, use Show Canceled Events to include canceled scheduled Grid DERMS events in the chart. Click a scheduled event label to open the corresponding Grid DERMS Event details.
Menus and Toolbar
The DERMS Dashboard window has the following menu and toolbar options.
File Menu
Menu Option
Description
Toolbar Icon
Print
Prints the DERMS Summary tab information.
Exit
Closes the DERMS Dashboard window.
Actions
Menu Option
Description
Toolbar Icon
View
Focuses the Viewer on the selected DER unit.
Understanding the DERMS Summary Tab
The DERMS Summary tab displays high level information related to the system, weather zones, and large scale utility DERs. All of the information is based on real-time conditions and current output of all resources. It is meant to provide as a quick reference overview broken down by technology types that are currently having an impact on the system. This tab contains three tables that display the following information:
• The System Summary table contains the current output (MW and MVAr) for each technology type of DER, the current total DER output, the total generation capacity (MVA), and the current total load for the entire distribution system.
• The Weather Zone Summary table displays the current output (kW and kVAr) of each weather affected DER technology type for each weather zone. It also has a column for the total output and generation capacity (kVA) for the weather zone that sums the various technology types present.
• The Utility DER Summary table displays the current output (kW and kVAr) of the individual DER units that do not belong to a weather zone (for example, utility scale gas generators or batteries). This table will also show the generation capacity (kVA) of the unit.
System Summary Table
• Wind (MW/MVAr): The total wind generation on the system in MW and MVAr.
• PV (MW/MVAr): The total photovoltaic (PV) generation on the system in MW and MVAr.
• Fuel (MW/MVAr): The total fuel generation on the system in MW and MVAr.
• Battery (MW/MVAr): The total battery generation on the system in MW and MVAr.
• DR (MW/MVAr): The total demand response contributions on the system in MW and MVAr.
• Total Generation (MW/MVAr): The total generation of all DER technology types summed together in MW and MVAr for the system.
• Generation Capacity (MVA): The total generation capacity of all DER technology types summed together in MVA for the system.
• Total Load (MW/MVAr): The total demand on the system from loads.
Weather Zone Summary Table
• Weather Zone: The name of the weather zone.
• Wind (kW/kVAr): The total wind generation in kW and kVAr for the weather zone.
• PV (kW/kVAr): The total Photovoltaic (PV) generation in kW and kVAr for the weather zone.
• Fuel (kW/kVAr): The total fuel generation in kW and kVAr for the weather zone.
• Battery (kW/kVAr): The total battery generation in kW and kVAr for the weather zone.
• DR (kW/kVAr): The total demand response contributions in kW and kVAr for the weather zone.
• Total Generation (kW/kVAr): The total generation of DER technology types summed together in kW and kVAr for the weather zone.
• Generation Capacity (MVA): The total generation capacity of all DER technology types summed together in MVA for the weather zone.
Utility DER Summary Table
• Resource Name: The name of the utility scale DER (for example, Large Battery or Diesel Generator).
• Substation: The substation the DER is a part of.
• Feeder: The feeder the DER is connected to.
• Power Source: The technology type associated to the unit (for example, Battery, Fuel, Hydro, and so on).
• Islandable: Indicates if the DER is capable of islanding an area of de-energized network.
• Capacity (kVA): The generation capacity of the unit in kVA.
• Output (kW/kVAr): The total output of the resource in kW and kVAr.
• Availability Price ($/MWH): The availability pricing in $/MWH for the DER unit.
• Utilization Price ($/MWH): The utilization pricing in $/MWH for the DER unit.
• Solution Time: The time the solution was last solved for this particular DER.
• DERMS Bid Status: Displays the DERMS Bid Status if the DER is setup as a market participant. This will specify if the bid is accepted, denied, or curtailed.
Understanding the Weather Zone Forecasts Tab
The Weather Zone Forecasts tab allows you to see weather zone forecast information for a selected zone. With this information, you can see the forecast data (provided via an external weather service and/or the DERMS system via an adapter to NMS), and the current and forecasted output (kW, kVAr) for each DER technology type. The following information is available in the Weather Zone Forecasts tab:
• Date/Time
• Temp (F)
• Wind Speed (mph)
• Cloud Cover
• Wind Output (kW/kVAr)
• PV Output (kW/kVAr)
• Fuel Output (kW/kVAr)
• Battery Output (kW/kVAr)
The Weather Zone Forecasts tab shows information related to a specific weather zone. The forecast information displayed is for the real time output and configured forecast range. It is meant to show how DER output can change based on upcoming weather trends and forecasted conditions. For example, if the current day is supposed to transition to a cloudy day with no wind, you will be able to see how the forecasted PV and wind output begin to decrease as conditions start to change.
You can navigate to the Weather Zone Forecast tab in two ways:
• Select the Weather Zone Forecasts tab. Once the tab has opened, you need to select the zone you are interested in from the Weather Zone drop-down list.
• Select a weather zone row in the DERMS Summary tab's Weather Zone Summary table, right-click, and select View Forecast... from the context menu. The Weather Zone Forecasts tab will open with the selected zone forecast displayed.
Note: That peak forecast solves will not be reflected in the weather zone forecasts table. Due to the nature of peaks solves they are done at the electrical island level and a weather zone is an abstract polygon that could include many islands. Since a weather zone could contain many electrical islands they could have differing peak solve times (for example, Sub A peaks at 5pm whereas Sub B peaks at 4pm) that may not coincide with each other, due to this only the real-time and hourly forecast will be displayed here.
Weather Zone Forecasts Table
• Date/Time: The date and time for the row of forecast and weather data that is displayed.
• Temp (F): The forecast temperature for the weather zones forecast date/time.
• Wind Speed (mph): The forecast wind speed for the weather zone forecast date/time.
• Cloud Cover: The forecast cloud cover level for the weather zones forecast date/time.
• Wind (kW/kVAr): The total forecasted wind generation in kW and kVAr for the weather zones forecast date/time.
• PV (kW/kVAr): The total forecasted Photovoltaic (PV) generation in kW and kVAr for the weather zones forecast date/time
• Fuel (kW/kVAr): The total forecasted fuel generation in kW and kVAr for the weather zones forecast date/time.
• Battery (kW/kVAr): The total forecasted battery generation in kW and kVAr for the weather zones forecast date/time.
• DR (kw/KVAr): The total forecasted demand response contributions in kW and kVAr for the weather zones forecast date/time.
• Total Generation (kW/kVAr): The total forecasted generation of DER technology types summed together in kW and kVAr for the weather zones forecast date/time.
Understanding the Utility DER Forecast Tab
The Utility DER Forecasts tab allows you to see Utility Scale DER forecast information for a selected resource. With this information, you can see the forecasted output (kW, kVAr) of the resource that has been provided via an external DERMS system via an adapter to NMS.
The forecast information displayed is for the real-time output and configured forecast range. It is meant to show you how DER output can change based on the forecast data provided for the resource (for example, battery used for peak shaving).
You can navigate to a specific Utility DER Forecast in two ways:
• From the DERMS Summary tab:
• Select the resource you are interested in from the Utility DER Summary table. Right-click and select View Forecast… from the context menu. The DERMS Dashboard window will display the Utility DER Forecasts tab with the selected resource name populated in the Resource Name field, and with the resource's forecast data displayed in the Utility DER Forecast table.
• From the Utility DER Forecast tab:
• Select the resource you are interested in from the Resource Name drop-down list. The Utility DER Forecasts table will be populated with the selected resource's forecast data.
The Utility DER Forecasts tab will also show information related to Grid DERMS if the device is configured as a DERMS participant. The Grid DERMS proposed schedule will be displayed on a table within this page and represent the results of the analysis stating for each configured forecast interval the bid status of the unit and its recommended output.
Utility DER Forecasts Tab Layout
The top section contains the following information:
• Market Participant: Specifies if this DER is bidding into the day ahead market and is consider in the Network Capacity Allocation Analysis.
• Aggregator: Displays either Y or N if the DER belongs to an aggregator or not.
Utility DER Forecasts Table
The Utility DER Forecasts table contains the following information:
• Date/Time: The date and time for the row of forecast data that is displayed.
• Output (kW/kVAr): The forecasted total output of the resource in kW and kVAr
Grid DERMS Proposed Schedule
The Grid DERMS Proposed Schedule table specifies the results of the DERMS analysis and displays the proposed output and recommended output for each forecast interval.. This information will be displayed for any DER that is configured within a Grid DERMS area that is configured for a DERMS objective such as (NCA, Economic Dispatch, and so on).
• Date/Time: The date and time the NCA analysis row corresponds to.
• Proposed Output (kW/kVAr): The total output in kW and kVAr the generator wanted to bid into the market.
• Allowed Output (kW/kVAr): The total output in kW and kVAr the generator can produce as determined by the NCA analysis. If the generator exceeds the allowed output flow constraints will be created on the network.
• Price ($/MWH): The price of generation for this particular interval as provided with from the generator with the bid.
• Bid Status: The bid status for this NCA analysis interval; the values may be Accepted, Denied, or Curtailed. For example, if the NCA analysis determined the generator cannot produce any power during this interval without creating flow constraints, the Bid Status would be set to Denied. If the generator output needed to be reduced from the proposed output, but not fully reduced, the bid status would be Curtailed. If the proposed generator output does not create any flow constraints and can be fully utilized, the bid status will show as Accepted. Note that for other objectives, such as economic dispatch or peak shaving where bids are not applicable, this field will display N/A.
Viewing Violations for a DERMS Proposed Schedule
When viewing the NCA forecast for a particular DER, the flow and/or voltage violations that caused schedule adjustment can be displayed. You can view these issues for each forecast hour. Right click the forecast of interest, and then select View Violation.... When the Grid DERMS Violations dialog box opens, you can then select the option to view the Proposed or Allowed violations. The Proposed violations correspond to issues that would occur with the proposed generator output, this is essentially the output the generator intended to supply. The Allowed violations correspond to issues that would occur with the NMS recommended generator plan, under ideal circumstances the number of allowed violations should be zero. The following columns will be displayed in the Grid DERMS Violations dialog box.
• Device: The device name where the violation has occurred.
• DER Name: The DER name that has sensitivity to the violation.
• Feeder Name: The name of the feeder where the violation has occurred.
• Violation: The type of violation that has occurred (for example, Switch Overload, Conductor Overload).
• Phase: The phase on which the violation has occurred
• Value: The power flow value on the device (for example, amps for switches/conductors, kV for voltage issues).
• %: The percent overload of the violation
• Limit: The limit on the overloaded device
• Pre-Existing Viol: Specifies if this was a pre-existing violation that existed before any generator schedules were taken into account.
Using the Grid DERMS Dashboard in Flex Operations
Open DERMS Dashboard in Flex Operations to view load, generation, alerts, DER resources, and scheduled events. Available data and actions depend on your licenses, permissions, and system configuration. Use the Control Zone Filter to select the network areas to include. When both modes are available, select Grid to work with Grid DERMS or Edge to work with Edge DERMS.
In Flex Operations, the DERMS Dashboard requires either the Grid DERMS license (derms) or the Edge DERMS license (ge_derms), together with the Access Derms Dashboard permission. Dashboard summaries and the VPP count do not grant permission to open VPP management or edit VPPs. Those operations require the Grid DERMS license and the applicable VPP tool and action permissions.
Select a dashboard summary card to display its corresponding information:
Load/Generation
The Load/Generation view displays historical and forecast information in the Load/Generation Timeline, Alerts, Load Trends, and DER Generation Trends charts. Use the time-range control to focus on the period of interest. Chart series depend on the selected mode and the data available for the selected control zones. Open chart details to examine the selected chart in more detail.
DER Summary
The DER Summary view lists resources for the selected control zones. In Grid mode, use DER Type to select FTM (front-of-the-meter), BTM (behind-the-meter), or All resources. Select a resource to open its DER Details or View Schedule. View Schedule opens the Schedule tab of Grid DER Details. Use View On Map to locate the selected resource in the Map.
In Edge mode, use DER View to display DERs, Aggregators, or Groups. The information and actions available depend on the selected view. For Edge DER device information, see Understanding the DER Details Dialog Box.
Scheduled Events
The Scheduled Events view displays events on a timeline. Point to an event to view its available details, such as its objective and start and end times. Use Show Canceled Events to include canceled events. For a Grid DERMS event with an associated switching sheet, use the event's context menu to open that sheet.
In Grid mode, the Virtual Power Plants summary card provides access to eVPP management, subject to your permissions. For eVPP creation, schedule management, approval, and analysis behavior, see Edge Virtual Power Plants in this chapter.
Grid DER Details
For the Grid DER Details display and the ways to open it from the dashboard and other Flex Operations tools, see Understanding the Grid DER Details View below.
You can open the Grid DER Details view from the following tools:
1. DERMS Dashboard - DER Summary:
Select the DERMS dashboard and go to the DER Summary tab. When you select a DER, you will have the option to view the DER Details.
2. Map View:
Open the Map and center it on a DER. In the map’s control tool pane, you will find an option to view DER Details.
3. Feeder Load Summary Tool:
Launch the Feeder Load Summary tool and select a feeder to view its load management details. Next, select a forecast and view its details. Then, in the Distributed Generator tab, choose a DER to access the DER Details option.
4. GRID DERMS Management Tool:
Open the GRID DERMS Management tool. Select any DER to access the option to view its details.
5. Edge Virtual Power Plants Tool:
Open the Edge Virtual Power Plants tool and select an eVPP. Select Details to open the Grid DER Details view on the Overview tab, or select Schedule to open it on the Schedule tab.
There are five different DER type representations:
1. Battery Energy Storage Systems (BESS)
2. Electric Vehicle Supply Equipment (EVSE)
3. Solar
4. Wind
5. Default (for DERs that do not fall into any of the above categories)
The left section of the DER Details varies based on the type of DER selected; the right section contains a table, which is common for all DER types.
• The SCADA Keys and SCADA Values section is visible if the DER has SCADA.
• The Settings section depends on the DER type selected.
• Regulation Parameters depends on the DER type. Attributes may be edited unless they have SCADA links, which are read only.
• The Optimization panel has same options for all the DER types.
Overview and Charts
For a DER, the Overview tab displays device-specific information, operating values, regulation parameters, optimization settings, and available power-flow results. When SCADA is available, use the table controls to switch between Values, SCADA Keys, and SCADA Values. Attributes linked to SCADA are read only.
When Dynamic Operating Envelope data is available, the Overview displays the applicable lower and upper operating limits. A Violation indicator appears when the current real-power output is below the lower limit or above the upper limit.
Generation Trends displays real power (kW) and reactive power (kVAr) together. Use Weather to display Temperature, Cloud Cover, or Wind Speed when data is available. Missing power values appear as N/A in chart tooltips.
The Optimal DER Schedule chart displays optimized real-power output in kW for the available DERMS schedules, including Day Ahead Market dispatch. Proposed schedules use dashed lines. Active schedules use solid lines and have legend labels beginning with “Active:”. Separate schedules remain separate chart series, including when their intervals overlap. Intervals without schedule data are not displayed as zero-valued points. The chart uses the same time range as Generation Trends and the Dynamic Operating Envelope chart.
The NCA and Peak Shaving forecast chart displays real power in kW only and uses the same time range as Generation Trends and the Dynamic Operating Envelope chart. Intervals without schedule data are not shown as zero-valued forecast points.
Edge Virtual Power Plant (eVPP)
For an eVPP, the Overview tab displays its description, enabled state, approval state, containment mode, External ID, schedule count, earliest start, latest end, and scheduled energy and reactive energy impact, including Scheduled Impact (MWh). Map eVPPs show their map anchor; Control Zone eVPPs show their Control Zone and do not display map-anchor power-flow information. Children have Inherited approval and use the parent's enablement and approval. Scheduled Impact is the sum of each interval's MW Reduction multiplied by its duration in hours. The power-flow results panel is not displayed for an eVPP.
The Schedule tab displays the signed schedule as a graph and as a table containing Start, End, MW Reduction, MVAr Reduction, and Price ($/MW). For a parent with child-owned schedules, these views show the aggregate of the child schedules. Overlapping intervals add together. Positive values reduce managed load and negative values increase managed load. The parent aggregate is a summary of the hierarchy, not an additional reduction applied on top of its children. The trend chart displays MW and MVAr reductions together. Chart values use up to six decimal places so small nonzero reductions remain visible.
Viewing DER Schedules
For a DER, open the Schedule tab and select one of these views. The number beside each option indicates the number of rows in that view.
Option
Information displayed
Utility Forecast
Forecast real and reactive output and the solution time. This is the initial selection.
Schedule intervals associated with DERMS or Day Ahead Market switching sheets in the New state.
DERMS Active Schedule
Schedule intervals associated with switching sheets in the Scheduled or Executing state.
Export and import capacity bids and the allowed upper and lower operating limits.
DERMS Proposed Schedule displays intervals from switching sheets in the New state. DERMS Active Schedule displays intervals from sheets in the Scheduled or Executing state: these schedules have been scheduled for execution or are already being executed. An active schedule can include future intervals; “active” describes the sheet’s execution state, not whether an interval is occurring now. Sheets in the Completed, Canceled, Error, or Deleted state are excluded from both views.
The DERMS views show schedules associated with switching sheets. An analysis without an associated eligible sheet does not appear. Multiple analyses or sheets can contain intervals for the same forecast time; these remain separate schedule rows.
Both DERMS views contain these columns:
• Date: The forecast interval date and time.
• Objective: The schedule objective, such as NCA, Peak Shaving, Economic Dispatch, Dynamic Operating Envelopes, or Day Ahead Market.
• DERMS Sheet: The associated switching sheet number.
• Event ID: The associated event.
• Forecast Output (kW/kVAR): The input real and reactive output. For Day Ahead Market rows, the real-power value is the initial output.
• Optimized Output (kW/kVAR): The resulting real and reactive output. For Day Ahead Market rows, the real-power value is the allocated dispatch.
• Price ($/MWh): The available interval price.
• Bid Status: The allocation status, when applicable.
Unavailable or inapplicable values appear as a dash.
In DERMS Proposed Schedule, select Hide Proposals at Active Times to hide proposed rows whose forecast date and time exactly match an active row for the same DER. This filter applies across objectives and sheets. It also removes those proposed points from the Optimal DER Schedule chart. Clear the filter to display them again. The filter is initially off and does not change or cancel any schedule.
Select a DERMS schedule row and use its toolbar or context menu to:
• Open Switching Sheet: Open the associated sheet.
• View Flow Violations: Inspect violations for an NCA interval.
• View UC Dispatch Details: Inspect dispatch details for a Day Ahead Market interval.
The details action’s label changes with the selected row. Detailed results are available for NCA and Day Ahead Market rows.
Viewing UC Dispatch Details
In either DERMS schedule view, select a Day Ahead Market row and choose View UC Dispatch Details. The dialog displays the selected DER and interval, including Interval, Date, Resource Name, Committed, Economic Min (MW), Economic Max (MW), Allocated Dispatch MW, and Cost ($).
Viewing Grid DERMS Violations
Use the Schedule tab to inspect network flow violations associated with an NCA (Network Capacity Allocation) interval in either a proposed or active DERMS schedule.
1. Open DER Details for the DER and select the Schedule tab.
2. Select DERMS Proposed Schedule or DERMS Active Schedule, then select a row with the NCA objective.
3. Select View Flow Violations from the schedule toolbar or the selected row’s context menu.
4. In the Grid DERMS Violations dialog, check Forecast Date/Time to identify the selected interval. Proposed is selected initially. Select Allowed to view violations after allocation, or Proposed to return to the proposed results. Both stages refer to the same DER, analysis, and forecast interval. These stage selections are independent of whether you opened the dialog from the proposed or active schedule. If the selected stage has no violations, the table is empty.
5. Select a violation and choose View Device from the table toolbar or context menu to locate the violating device in Network Viewer.
The table contains these columns:
• Device: The device with the flow violation.
• DER Name: The DER associated with the result.
• Feeder Name: The feeder associated with the violation.
• Violation: The type of flow violation.
• Phase: The affected phase.
• Value: The calculated value, with its unit (kV, A, or kVA).
• %: The violation percentage.
• Limit: The applicable limit, with its unit.
• Pre-Existing Viol: Whether the violation was already present before allocation.
Groups and Contract
For a DER, the Groups tab lists its group memberships, including Group Name, Type, Capacity (MVA), DERs Online / Offline, and Updated. Select a group and choose Open Group Details to inspect it.
When contract information is available, the Contract tab displays the contract details, current usage, rank, and availability information.