5Reviewing Permit Plans Manually

Manual Plan Review Process Flow

Building projects require a permit plan review to evaluate the projects before permits are issued.

Manual plan reviews are tracked as part of permitting workflow, but are performed without the use of integrated electronic document review software. Manual plan reviews are created for permits when the Plan Review Type is set to Manual for the associated permit type. For more information see Setting Up Permit Types.

Note: Electronic plan reviews are performed through integration with electronic document review software. For more information on electronic plan reviews, see Managing Electronic Plan Review Cycles.

The process flow for a manual plan review includes the following steps:

  1. A registered public user submits a permit application with attached documents that require review by agency staff.

  2. A permit technician accepts the permit application with a status that requires a plan review. For more information, see Using Workflow.

  3. The plan coordinator adds a plan review cycle for the permit. See Managing Manual Plan Review Cycles.

  4. The plan coordinator assigns reviewers to the plan review cycle. See Managing Manual Plan Review Cycles.

  5. The assigned plan reviewers complete their review. See Performing Manual Plan Reviews.

  6. Repeat steps 3 through 5 for additional plan review cycles as necessary until the review is complete.

Managing Manual Plan Review Cycles

The plan coordinator manages the plan review cycle, which is a building plan review completed by multiple reviewers who work with plan reviews for different types of permits.

As a plan coordinator, you perform these review cycle tasks on the Plan Reviews page in the permit details component:

  • Add plan review cycles.

  • Cancel plan review cycles.

  • Add and remove plan reviewers.

  • View the different plan review cycles.

  • Add comments for a review cycle.

  • View all plan review comments.

This example shows the Plan Reviews page for a manual review.

Example of the Plan Reviews page for a manual review
Tip: You can access this page on a mobile device as well as on a laptop or desktop computer. On a mobile device, this page enables you to view plan review status and comments. It does not enable you to add or edit plan review information.

Manual Plan Review Cycle Workflow

The plan review workflow for the plan coordinator appears on the Task Management page. As a plan coordinator, you sort tasks by Workflow.

When the last reviewer provides a decision status for a plan review cycle, it is automatically closed. Upon closing, the overall review status changes to Complete.

The system also updates the plan review cycle details with the most severe decision status from the individual plan reviewers. The decision statuses are listed here, from most to least severe: Rejected, Revision Required, Approved with Comments, Approved, and Not Required. If plans have one or more rejections, or revisions are required, the plan coordinator may require the applicant to correct the plans and resubmit them for another review cycle.

If you configured a template for the delivered Plan Review Completed or Canceled communication event, the completion or cancelation of the review cycle triggers the generation of a communication to the designated users. For example, the completion of a review cycle can send a notification to the plan coordinator. For more information on communication event templates, see Setting Up Communication Events.

Workflow is automatically moved forward to the next step when the current plan review cycle status is Complete and the plan review decision is Approved, Approved with Comments, or Not Required. The workflow process definition needs to identify the plan review task and the action to take when auto-advancing. For more information, see Using Custom Properties.

Once a plan review cycle or permit is closed or canceled, you can no longer edit comments.

Adding Manual Plan Review Cycles

Before assigning reviewers, you add plan review cycles for a permit on the Plan Reviews page.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

  4. Click the Add Review Cycle button to add a new plan review cycle.

    This button is available only when:

    • You’re adding the first plan review cycle for a permit.

    • All other plan review cycles for the permit are complete or canceled.

  5. For the initial plan review cycle, the default review cycle name is the Permit Type value, but you can enter a different cycle name on the Add Review Cycle page.

  6. If you are resubmitting a plan review, select the check box on the Add Review Cycle page to copy the reviewers from the most recent review cycle.

  7. Click the Add button.

The cycle must be canceled or complete before you can add another new plan review cycle. That is, you can have only one active plan review cycle at a time. The number of review cycles is shown in the Plan Reviews page header details, and you can switch between multiple cycles to view reviewer and decision details.

If you want to add a due date for the plan review cycle, click Edit next to the Due Date field and select a due date.

Canceling Manual Plan Review Cycles

You cancel a plan review cycle for a permit on the Plan Reviews page.

Canceling a cycle sets the review cycle status to Canceled. After canceling, the cycle and review details are read-only. All active tasks associated with the plan review are canceled when the plan review cycle is canceled.

Note: An active plan review cycle is canceled when the permit application that it is associated with is withdrawn.
  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

  4. Click the Cancel Review Cycle button to cancel a plan review cycle that is active.

    This button is available only when the plan review cycle has a status of In Progress.

Adding Reviewers to Manual Plan Reviews

After creating a plan review cycle, you add plan reviewers on the Plan Review page.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

    Note: If the permit type associated with the permit includes required plan review departments, those departments are displayed at the top of the Reviewers grid. Once a reviewer from a required department is added to the plan review cycle, that department no longer appears.
  4. Click the Add Reviewers button.

    The Add Reviewers modal page displays a list of available reviewers by plan reviewer department. For more information on plan reviewer departments, see Setting Up Plan Reviewer Departments.

    Note: Reviewers are available in the list only when they have a permit type job attribute that matches the permit type of the permit. For more information on assigning job attributes, see Managing Agency Staff Profiles.
  5. Select the check box next to each reviewer that you want to add.

  6. Click Save.

    When the Reviewers grid refreshes, you’ll see the added reviewers with an In Progress status.

Note: If you’re resubmitting a plan for review, you can elect to copy the original set of reviewers when you add a new plan review cycle. See Managing Manual Plan Review Cycles.

Removing Reviewers from Manual Plan Reviews

As a plan coordinator, you can remove or delete plan reviewers from a plan review cycle on the Plan Review page.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Review.

  4. In the Reviewers grid, click the Delete button for a reviewer.

    You can remove reviewers when:

    • The plan review cycle is active.

    • The reviewer’s status is In Progress.

    • You entered an override decision for a reviewer, but the reviewer did not enter comments or a decision before the override.

    You cannot delete a reviewer if the reviewer has added comments or entered a decision.

Note: Removing the last plan reviewer who hasn’t yet submitted a decision permanently closes the plan review cycle. If desired, you can add a new reviewer before removing the last reviewer, or close the cycle and open a new one.

Viewing the Different Plan Review Cycles

You can switch between plan review cycles to view the Reviewers grid for each cycle.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

  4. Click the Switch Cycle link in the plan review header details.

    This link is available only when there are two or more plan review cycles.

  5. On the Switch Cycle page, click the Select button for the cycle you would like to view.

    The refreshed page shows the cycle header details and reviewers for the selected cycle.

Adding Comments for a Review Cycle

Plan coordinators can add comments at the review cycle level on the Plan Reviews page.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

  4. Click Add Comment at the bottom of the Plan Reviews page to enter a comment.

    All of the comments entered for the review cycle appear on the Plan Reviews page below the Add Comment button. You can’t edit comments once the plan review cycle or permit is closed or canceled.

Viewing All Plan Review Comments

Plan coordinators, plan reviewers, and applicants can view all comments entered for all cycles of a plan review on the Plan Reviews page.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

  4. On the Plan Reviews page, click the View Plan Comments link.

    This example shows the View Plan Comments page for a manual review.

    Example of the View Plan Comments page

    The View Plan Comments page displays all of the comments entered for a plan review by all participants during every review cycle. The comments listed on this page are searchable and filterable.

Performing Manual Plan Reviews

Plan reviewers perform reviews of building plan documents prior to permit issuance.

As a plan reviewer, you view a list of plans assigned to you on the Task Management page and provide your plan review decision on the Plan Reviewer Decision Details page.

This example shows the Plan Reviewer Decision Details page.

Plan Reviewer Decision Details page

An agency’s plan coordinator can also use this page to override a plan reviewer’s decision.

The plan review functionality derives the overall plan review status from the individual plan reviewer decisions, inclusive of plan coordinator overrides, and updates the overall plan review with the most severe decision status.

Viewing Plan Reviews Assigned to You

As a plan reviewer, you can find the plan reviews assigned to you on the Task Management page.

  1. Select My Plan Reviews on the Agency Springboard.

  2. The My Plan Reviews tab of the Task Management page opens displaying tasks with the Plan Review type.

    Plan reviews are displayed in ascending order by due date. Plan coordinators enter reviewer-specific due dates on the Plan Reviewer Decision Details page.

    You can also use the filter button to filter by additional parameters, including task type, task name, task ID, transaction ID, transaction type, status, assigned to, assigned date, and scheduled date.

  3. Plan review assignments appear in the task grid. Click the View More Details button for a permit record to open the Plan Reviews page.

Note: Both manual and electronic plan reviews that are assigned to you appear on this page. For more information on electronic plan reviews, see Performing Electronic Plan Reviews.

The plan review workflow tasks for plan coordinators also appear on the Task Management page. Plan coordinators sort tasks by Workflow.

For more information on the Task Management page, see Managing Tasks.

Adding a Manual Plan Review Decision

As a plan reviewer, you can add your plan review decision on the Plan Reviewer Decision Details page in the permit details pages. You can modify your decision until the plan review cycle is closed or canceled, but you cannot modify your decision if the plan coordinator overrides your decision.

The system derives the overall plan review status from the individual plan reviewer decisions, and updates the overall plan review with the most severe decision status. The system-defined decision statuses are listed here from most to least severe: Rejected, Revision Required, Approved with Comments, Approved, and Not Required. If plans have one or more rejections, or revisions are required, the plan coordinator may require the applicant to correct the plans and resubmit them for another review cycle.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

  4. In the Reviewers grid, click the View More Details button for your row.

  5. On the Plan Reviewer Decision Details page, select a value from the Decision list.

    You can select from these system-defined decision statuses:

    • Approved

    • Approved with Comments

    • Revision Required

    • Rejected

    • Not Required

    The decision status names in the Decision list may not match the system status names, because displayed statuses can be modified by the agency. For example, if the agency changes the displayed status of Rejected, you might see Declined or Failed. However, the severity of the decision remains the same. Any displayed status associated with the system status Rejected, for example, is always calculated as the most severe status.
  6. Click Add Comments to enter comments for your review.

    You can’t edit comments once the plan review cycle or permit is closed or canceled.

  7. Click the Save button.

    The system updates the Decision Date field with a timestamp.

Note: An agency’s plan coordinator can override a plan reviewer’s existing decision but can't change decisions. When a plan coordinator overrides a decision, the decision status and timestamp appears in the Reviewers grid in the reviewer’s row.

Overriding Plan Reviewer Decisions

In some cases, the agency’s plan coordinator overrides a plan reviewer’s existing decision.

As a plan coordinator, you can override the individual plan reviewer’s decision on the Plan Reviewer Decision Details page.

  1. Select Permits on the Agency Springboard.

  2. On the Permits page, select a permit record with a status of Plan Review.

  3. In the navigation panel, select Permit Information > Plan Reviews.

  4. In the Reviewers grid, click the View More Details button for the selected plan reviewer.

  5. On the Plan Reviewer Decision Details page, select a value from the Override Decision list.

    You can select from these decisions:

    • Approved

    • Approved with Comments

    • Revision Required

    • Rejected

    • Not Required

  6. Click the Save button.

    The system updates the plan reviewer’s Decision Date timestamp and enters Yes in the Override field.

Note: If the plan coordinator overrides the last review in the plan review cycle, the override action changes the status of the plan review cycle to complete.