3 Preparing Your Networks for Recovery Appliance
This chapter describes the network requirements for Recovery Appliance, so that you can prepare your data center for installation.
This chapter contains the following sections:
Overview of Network Requirements
Recovery Appliance includes two compute servers, 3 to 18 storage servers (depending on your hardware version), and the equipment to connect these servers to your network. The network connections allow the servers to be administered remotely, and for data to move from the protected databases to Recovery Appliance. Use the information in this section to prepare your data center for the addition of Recovery Appliance.
See Also:
"About Ingest Over InfiniBand" for information about configuring local Oracle Exadata Database Machine racks to backup to Recovery Appliance over the InfiniBand network
About the Network Components and Interfaces
Each compute server in the X7 configuration consists of the following network components and interfaces:
-
Ethernet ingest and replication network connectivity
-
On-board: 2 x 10 Gb copper Ethernet (eth1)
-
On-board: 2 x 10/25 Gb optical Ethernet Ports (eth2)
-
PCIe card: 2 x 10/25 Gb optical Ethernet Ports (eth3 and eth4)
-
-
1 dual-port 4X QDR (40 Gbps) InfiniBand Host Channel Adapter (HCA) (IB0 and IB1)
-
1 Ethernet port for Oracle Integrated Lights Out Manager (ILOM) remote management
-
1 dual-port 32 GB FC Converged Network Adapter (CNA) FC ports 0 and 1.
Note:
The corresponding SFP modules that work with the 10/25 GbE PCIe 2.0 network cards are purchased separately.
Figure 3-1 X7 Back—plane External Network Connectivity

Description of "Figure 3-1 X7 Back—plane External Network Connectivity"
Given that the base rack has two (2) compute servers, the maximum for ingest is 2 x 10 Gb or 2 x 25 Gb Ethernet ports, while the maximum for replication is 2 x 10 Gb or 2 x 25 Gb Ethernet ports. The following are valid combinations of the options.
-
2 x 10Gb on-board copper (ingest) + 2 x 10/25Gb PCIe card optical (replication)
-
2 x 10/25Gb PCIe card optical (ingest) + 2 x 10Gb on-board copper (replication)
-
2 x 10/25Gb PCIe card optical (ingest) + 2 x 10/25Gb on-board optical (replication)
-
2 x 10/25Gb on-board optical (ingest) + 2 x 10/25Gb PCIe card optical (replication)
Note:
If ingest and replication traffic is desired to be configured on the same network, define the required network interface in OEDA in the ingest network section, and leave the replication network section blank. With this setup, Recovery Appliance will use the ingest network for replication traffic.Each storage server consists of the following network components and interfaces:
-
1 embedded Gigabit Ethernet port (NET0)
-
1 dual-port 4X QDR (40 Gbps) InfiniBand Host Channel Adapter (HCA) (IB0 and IB1)
-
1 Ethernet port for Oracle Integrated Lights Out Manager remote management (Oracle ILOM)
Additional configuration, such as defining multiple virtual local area networks (VLANs) for the management (NET0 and/or ILOM) interfaces or enabling routing, might be required for the switch to operate properly in your environment and is beyond the scope of the installation service. If additional configuration is needed, then your network administrator must perform the necessary configuration steps during installation of Recovery Appliance.
About the Networks
To deploy Recovery Appliance, ensure that you meet the minimum network requirements. There are up to five networks.
Note:
Each network must be on a distinct and separate subnet from the others. The only exception is that the replication network defaults to using physical ingest network, if not assigned in OEDA.
The network descriptions are as follows:
-
Management network: This required, 1 gigabit, Ethernet (GbE) network connects to your existing management network. You use it to do administrative work on all components of Recovery Appliance. The management network connects to the servers, Oracle ILOM, and InfiniBand switches through the Cisco Ethernet switch in the rack.
There are three uplinks to the management network:
-
One from the Ethernet switch
-
One from each of the two power distribution units (PDUs). Network connectivity to the PDUs is required only if the electric current is monitored remotely.
Each server has two network interfaces for management. One provides management access to the operating system through the NET0 Ethernet interface, and the other provides access to Oracle ILOM through the ILOM Ethernet interface. Recovery Appliance is delivered with the ILOM and NET0 interfaces connected to the Ethernet switch on the rack.
Cabling or configuration changes to these interfaces is not permitted. Do not use the management network interfaces for client or application network traffic. Instead, you can use NET1, NET2, NET3, or the two interfaces on the PCI slot.
-
-
Ingest network: This required network connects the protected Oracle Database servers to Recovery Appliance for backup within the same data center. Also known as a backup network, this high-speed, private Ethernet network must be designed to support the transfer of large volumes of data. Recovery Appliance connects to this network using two 10/25 GB connections to each of the two compute servers in the rack. You can configure the two connections as active/passive (redundant) or active/active. The compute servers support channel bonding to provide higher bandwidth and availability.
Single client access name (SCAN) supports failover between the two compute servers in Recovery Appliance. In an installation with multiple Recovery Appliance racks configured as a cluster, virtual IP (VIP) addresses support failover among the racks. The protected database systems can resolve the host names to dynamically assigned addresses.
Third-party tape hardware and software also uses the ingest network.
-
Replication network: The optional replication network connects the local Recovery Appliance (the upstream appliance) with a remote Recovery Appliance (the downstream appliance). Oracle recommends a broadband, encrypted network, instead of an insecure public network, wherever possible.
Recovery Appliance supports the following configurations between the upstream and downstream appliances:
-
One way: Data flows from the upstream appliance to the downstream appliance.
-
Bidirectional: Data flows in both directions between the upstream appliance and the downstream appliance.
-
Hub and spoke: Data flows from multiple upstream appliances to one downstream appliance.
Note:
A downstream Recovery Appliance or a tape library can reside in the local data center. The replication network is not used in a local configuration.
-
-
Fibre Channel SAN network: If you are using Oracle Secure Backup, then you can back up Recovery Appliance to the storage area network (SAN) in your data center for backups to tape. The network connections depend on whether you have an Oracle tape solution or use third-party hardware.
-
InfiniBand private network: This network connects the compute servers and storage servers using the InfiniBand switches. Oracle Database uses this network for Oracle RAC cluster interconnect traffic and for accessing data on the storage servers. This nonroutable network is fully contained in Recovery Appliance.
This network does not connect to your data center networks. It is automatically configured during installation.
See Also:
-
Oracle Clusterware Administration and Deployment Guide for a discussion of SCANs and VIPs in network configurations for Oracle Database.
-
"Connecting Recovery Appliance to a Tape Library" for information about how a fibre channel SAN network is configured for backups to tape in a Recovery Appliance environment.
Example of Network Connections for Recovery Appliance
Figure 3-2 shows the network cabling of a sample configuration. Two Recovery Appliance racks are installed in separate data centers. The protected Oracle databases are connected to the upstream Recovery Appliance over the ingest network. The upstream Recovery Appliance is connected to the downstream Recovery Appliance over the replication network. Both racks are configured to use an Oracle tape solution.
Figure 3-2 Network Diagram for Recovery Appliance

Description of "Figure 3-2 Network Diagram for Recovery Appliance"
Connecting Recovery Appliance Rack Components to the Networks
Figure 3-3 shows the network connections to components of Recovery Appliance rack.
The management network connects through the Ethernet switch to the compute servers, the storage servers, and the InfiniBand switches. The management network connects directly to the PDUs.
The ingest network, the optional replication network, and the optional fiber channel SAN network connect to the two compute servers.
The InfiniBand network connects the InfiniBand switches to the compute servers and the storage servers.
Figure 3-3 Network Connections to the Recovery Appliance Rack Components

Description of "Figure 3-3 Network Connections to the Recovery Appliance Rack Components"
Connecting Recovery Appliance to a Tape Library
The network connections between Recovery Appliance and an optional tape library depend on whether you are using Oracle or third-party tape components. See "About Tape Backup Infrastructure" for the differences in support provided by Recovery Appliance.
Oracle Recommended Stack
When you use the Oracle recommended tape solution, a fiber channel adapter is installed in each compute server to provide a connection to the fiber channel storage area network (SAN). Tape backups are isolated on this network, and thus do not interfere with the performance of the other networks. Figure 3-4 provides an overview of the network connections when using an Oracle tape system.
Figure 3-4 Recovery Appliance Connection to an Oracle Tape System

Description of "Figure 3-4 Recovery Appliance Connection to an Oracle Tape System"
Third-Party Tape Systems
When you use a third-party tape system, the backups to tape use the 10 Gb ingest network. This is the same network that the local protected databases use to backup to Recovery Appliance. Figure 3-5 provides an overview of the network connections when using a third-party tape system.
Figure 3-5 Recovery Appliance Connection to a Third-Party Tape System

Description of "Figure 3-5 Recovery Appliance Connection to a Third-Party Tape System"
Using Network VLAN Tagging with Recovery Appliance
The Recovery Appliance supports VLAN port tagging only on the ingest network. You configure VLAN port tagging after you complete the Recovery Appliance installation.
If applicable, ensure that you also set the Access VLAN on the network switches, including on the Cisco switch that is included in the Recovery Appliance rack for the management network.
See Also:
"Installing the Software on Recovery Appliance" for instructions on when and how to configure VLAN tagging
Registering Recovery Appliance in the Domain Name System
Before receiving your Recovery Appliance rack, use Oracle Exadata Deployment Assistant. The assistant generates a file to be used when setting up the system. The host names and IP addresses specified in the assistant-generated file must be registered in Domain Name System (DNS) before the initial configuration. In addition, all public addresses, single client access name (SCAN) addresses, and VIP addresses must be registered in DNS before installation.
The assistant-generated file defines the SCAN as a single name with three IP addresses on the client access network. The three SCAN addresses provide service access for clients to Recovery Appliance. Configure DNS for round robin resolution for the SCAN name to these three SCAN addresses.
All addresses registered in DNS must be configured for both forward resolution and reverse resolution. Reverse resolution must be forward confirmed (forward-confirmed reverse DNS) such that both the forward and reverse DNS entries match each other.
See Also:
-
Oracle Grid Infrastructure Installation Guide for Linux for additional information about SCAN addresses
-
Your DNS vendor documentation for additional information about configuring round-robin name resolution
Factory IP Address Settings
Recovery Appliance has default IP addresses set at the factory:
-
Gateway: 192.168.1.254 in all devices as required
-
Subnet Mask: 255.255.252.0 in all devices as required
-
IP Address Range: 192.168.1.1 to 192.168.1.203
Before connecting Recovery Appliance to the network, ensure that these IP addresses do not conflict with other addresses on the network. The checkip.sh script checks for conflicts. Oracle recommends running the script before connecting the network to avoid problems, even when a check was performed before Recovery Appliance was delivered. See "Installing the Software on Recovery Appliance" for additional information about the checkip.sh script.
Table 3-1 lists the factory IP addresses for a Recovery Appliance full rack.
Table 3-1 Factory IP Addresses for Recovery Appliance
| Rack Unit | Component | Management Network Addresses | InfiniBand Active Bonded IP Addresses | Oracle ILOM IP Addresses |
|---|---|---|---|---|
|
U41 |
Storage server |
192.168.1.23 |
192.168.10.45 |
192.168.1.123 |
|
U39 |
Storage server |
192.168.1.22 |
192.168.1.43 |
192.168.1.122 |
|
U37 |
Storage server |
192.168.1.21 |
192.168.10.41 |
192.168.1.121 |
|
U35 |
Storage server |
192.168.1.20 |
192.168.10.39 |
192.168.1.120 |
|
U33 |
Storage server |
192.168.1.19 |
192.168.10.37 |
192.168.1.119 |
|
U31 |
Storage server |
192.168.1.18 |
192.168.10.35 |
192.168.1.118 |
|
U29 |
Storage server |
192.168.1.17 |
192.168.10.33 |
192.168.1.117 |
|
U27 |
Storage server |
192.168.1.16 |
192.168.10.31 |
192.168.1.116 |
|
U25 |
Storage server |
192.168.1.14 |
192.168.10.27 |
192.168.1.114 |
|
U23 |
Storage server |
192.168.1.12 |
192.168.10.23 |
192.168.1.112 |
|
U22 |
InfiniBand switch |
Not applicable |
Not applicable |
192.168.1.203 |
|
U21 |
Ethernet switch |
Not applicable |
Not applicable |
192.168.1.200 |
|
U20 |
InfiniBand switch |
Not applicable |
Not applicable |
192.168.1.202 |
|
U18 |
Storage server |
192.168.1.10 |
192.168.10.19 |
192.168.1.110 |
|
U17 |
Compute server |
192.168.1.9 |
192.168.10.17 |
192.168.1.109 |
|
U16 |
Compute server |
192.168.1.8 |
192.168.10.15 |
192.168.1.108 |
|
U14 |
Storage server |
192.168.1.7 |
192.168.10.13 |
192.168.1.107 |
|
U12 |
Storage server |
192.168.1.6 |
192.168.10.11 |
192.168.1.106 |
|
U10 |
Storage server |
192.168.1.5 |
192.168.10.9 |
192.168.1.105 |
|
U08 |
Storage server |
192.168.1.4 |
192.168.10.7 |
192.168.1.104 |
|
U06 |
Storage server |
192.168.1.3 |
192.168.10.5 |
192.168.1.103 |
|
U04 |
Storage server |
192.168.1.2 |
192.168.10.3 |
192.168.1.102 |
|
U02 |
Storage server |
192.168.1.1 |
192.168.10.1 |
192.168.1.101 |
Port Assignments When Using a Firewall
When network communication between Recovery Appliance and other components requires access through a firewall, you must open ports used by the Recovery Appliance services.
Note:
A firewall may not be used between components of the Recovery Appliance.
Table 3-2 lists the ports used by services on Recovery Appliance. Review the list and open the necessary ports. All ports are on the management network, unless otherwise noted.
Table 3-2 Open Ports for the Firewall
| Source | Target | Protocol | Port | Application |
|---|---|---|---|---|
|
NA |
Database management |
SSH over TCP |
22 |
SSH |
|
NA |
Compute servers, storage servers, and InfiniBand ILOMs |
SSH over TCP |
22 |
SSH |
|
NA |
Storage management |
SSH over TCP |
22 |
SSH |
|
Storage servers |
email server |
SMTP |
25 465 if using SSL |
SMTP (Simple Mail Transfer Protocol) |
|
Compute servers, storage servers, and InfiniBand ILOMs |
NA |
TFTP over UDP |
69 |
Outgoing TFTP (Trivial File Transfer Protocol) |
|
NA |
Compute servers, storage servers, and InfiniBand ILOMs |
HTTP over TCP |
80 |
Web (user configurable) |
|
NA |
PDU |
HTTP over TCP |
80 |
Browser interface |
|
Database management |
NA |
NTP over UDP |
123 |
Outgoing Network Time Protocol (NTP) |
|
Compute servers, storage servers, and InfiniBand ILOMs |
NA |
NTP over UDP |
123 |
Outgoing NTP |
|
Storage management |
NA |
NTP over UDP |
123 |
Outgoing NTP |
|
ASR Manager |
ASR asset |
SNMP (get) |
161 |
FMA enrichment for additional diagnostic information |
|
NA |
Compute servers, storage servers, and InfiniBand ILOMs |
SNMP over UDP |
161 |
SNMP (Simple Network Management Protocol) (user configurable) |
|
NA |
PDU |
SNMP over UDP |
161 |
SNMP (user configurable) |
|
Storage servers |
SNMP subscriber such as Oracle Enterprise Manager Cloud Control or an SNMP manager |
SNMP |
162 |
SNMP version 1 (SNMPv1) outgoing traps (user-configurable) |
|
Compute servers and storage server ILOMs |
ASR Manager |
SNMP |
162 |
Telemetry messages sent to ASR Manager |
|
Compute servers, storage servers, and InfiniBand ILOMs |
NA |
IPMI over UDP |
162 |
Outgoing IPMI (Intelligent Platform Management Interface) Platform Event Trap (PET) |
|
PDU |
NA |
SNMP over UDP |
162 |
Outgoing SNMPv2 traps |
|
NA |
Compute servers, storage servers, and InfiniBand ILOMs |
LDAP over UDP/TCP |
389 |
Outgoing LDAP (Lightweight Directory Access Protocol) (user configurable) |
|
ASR Manager |
ASR back end |
HTTPS |
443 |
Telemetry messages sent to ASR back end |
|
NA |
Compute servers, storage servers, and InfiniBand ILOMs |
HTTPS over TCP |
443 |
Web (user configurable) |
|
NA |
PDU |
HTTPS over TCP |
443 |
Browser interface |
|
Compute servers, storage servers, and InfiniBand ILOMs |
NA |
Syslog over UDP |
514 |
Outgoing Syslog |
|
PDU |
NA |
Syslog over UDP |
514 |
Outgoing Syslog |
|
Compute servers, storage servers, and InfiniBand ILOMs |
NA |
DHCP over UDP |
546 |
client DHCP (Dynamic Host Configuration Protocol) |
|
PDU |
NA |
DHCP over UDP |
546 |
DHCP (Dynamic Host Configuration Protocol) client |
|
NA |
Compute servers, storage servers, and InfiniBand ILOMs |
IPMI over UDP |
623 |
IPMI (Intelligent Platform Management Interface) |
|
Oracle Enterprise Manager Cloud Control |
NA |
TCP |
1159 |
Oracle Enterprise Manager Cloud Control HTTPS upload port |
|
Oracle Enterprise Manager Cloud Control |
NA |
TCP |
1159 |
Oracle Enterprise Manager Cloud Control HTTPS upload port |
|
NA |
Database data |
SQL*Net over TCP |
1521 |
Database listener |
|
Protected database |
Recovery Appliance |
SQL*Net over TCP |
1521 (ingest network) |
RMAN backup and restore |
|
Upstream Recovery Appliance |
Downstream Recovery Appliance |
SQL*Net over TCP |
1522 (replication network) |
Recovery Appliance Replication |
|
Compute servers, storage servers, and InfiniBand ILOMs |
NA |
RADIUS over UDP |
1812 |
Outgoing RADIUS (Remote Authentication Dial In User Service) (user configurable) |
|
Oracle Enterprise Manager Grid Control |
NA |
TCP |
4889 |
Oracle Enterprise Manager Cloud Control HTTP upload port |
|
Oracle Enterprise Manager Grid Control |
NA |
TCP |
4889 |
Oracle Enterprise Manager Cloud Control HTTP upload port |
|
NA |
Compute server and storage server ILOMs |
TCP |
5120 |
ILOM remote console: CD |
|
NA |
Compute server and storage server ILOMs |
TCP |
5121 |
ILOM remote console: keyboard and mouse |
|
NA |
Compute server and storage server ILOMs |
TCP |
5123 |
ILOM remote console: diskette |
|
NA |
Compute server and storage server ILOMs |
TCP |
5555 |
ILOM remote console: encryption |
|
NA |
Compute server and storage server ILOMs |
TCP |
5556 |
ILOM remote console: authentication |
|
ASR Manager |
Compute server and storage server ILOMs |
HTTP |
6481 |
Service tags listener for asset activation |
|
NA |
Compute server and storage server ILOMs |
TCP |
6481 |
ILOM remote console: |
|
NA |
Compute server and storage server ILOMs |
TCP |
7578 |
ILOM remote console: video |
|
NA |
Compute server and storage server ILOMs |
TCP |
7579 |
ILOM remote console: serial |
|
NA |
Compute servers |
TCP |
7777 |
Oracle Enterprise Manager Grid Control HTTP console port |
|
NA |
Storage servers |
TCP |
7777 |
Oracle Enterprise Manager Grid Control HTTP console port |
|
NA |
Compute servers |
TCP |
7799 |
Oracle Enterprise Manager Grid Control HTTPS console port |
|
NA |
Storage servers |
TCP |
7799 |
Oracle Enterprise Manager Grid Control HTTPS console port |
|
Protected database |
Recovery Appliance |
HTTP |
8001 (ingest network) |
RMAN backup and restore |
|
Upstream Recovery Appliance |
Downstream Recovery Appliance |
HTTP |
8001 (replication network) |
Recovery Appliance Replication |