Introduction
The Oracle Utilities Network Management System Grid DERMS is a distribution-level optimization and control module designed to monitor and orchestrate distributed energy resources (DERs) across the electric distribution network. By ingesting DER schedules, forecasts, bids, and dynamic pricing alongside the live network model, Grid DERMS runs multi-interval optimal power flow (OPF) analyses to compute safe, feasible real and reactive set‑points that respect all network constraints. Supporting typical objectives such as Network Capacity Allocation, Economic Dispatch, and Peak Shaving, the system enables utilities to relieve thermal or voltage constraints, minimize operating costs, and reduce peak demand in a coordinated, constraint-aware manner. Each analysis is scheduled based on a configurable start time, forecast horizon, and interval granularity. Upon completion, Grid DERMS creates a Work Agenda event with an associated DERMS report and generates a switching sheet that can be executed in manual or automatic mode depending on system configuration and feeder eligibility. This approach ensures actionable plans are produced for operators, outcomes are tracked, and all results are stored for audit and reporting, delivering end-to-end management and optimization of distributed energy resources.
In Flex Operations, the Flex DERMS user type opens the planning list from Economic Peak Shaving in the Non-Wire Alternatives category or Network Capacity Allocation in the Market Participation category of the Tool Selector. Each entry initially selects its corresponding objective filter. Select All to display plans for all supported objectives, including Economic Dispatch, or select another objective filter as required. For the complete Flex DERMS category layout and plan-creation behavior, see Understanding the Tool Selector.
Note: Grid DERMS analyses account for planned topology changes during the configured analysis horizon. The optimizer stores interval‑specific topology models, so recommendations for DER dispatch reflect the switching state active at each solution time.
Licensing and Tool Access in Flex Operations
In NMS-hosted Flex Operations, opening a DERMS tool requires both the applicable product license and the permission for that tool in the user's effective selected user type. A license does not grant a tool permission, and a permission does not enable an unlicensed product.
Capability
Required License
Required Tool Permission
Peak Shaving, Economic Dispatch, and Network Capacity Allocation (NCA)
Grid DERMS (derms)
Access DERMS Optimization
DERMS Dashboard
Grid DERMS (derms) or Edge DERMS (ge_derms)
Access DERMS Dashboard
Virtual Power Plants (VPP)
Grid DERMS (derms)
Access DERMS VPP
Day Ahead Market (DAM)
Grid DERMS (derms)
Access DERMS Day Ahead Market
DERMS Automatic Generation Control (DAGC)
Grid DERMS (derms)
Access DERMS DAGC
Grid DERMS group management
Grid DERMS (derms)
Access Grid DERMS DER Group
Grid DERMS Management
Grid DERMS (derms)
Access DERMS Management
DER Contract Rules
Grid DERMS (derms)
Access DERMS Contract Rules
Peak Shaving, Economic Dispatch, and NCA are objectives of the same optimization tool and share one access permission. Other tools have independent permissions. Dashboard access allows dashboard summaries, including the VPP count, without granting VPP management or editing access.
DAM and DAGC users can inspect the shared group information required by their tools without receiving group-management editing rights. Ordinary VPP device and availability inspection does not require DAM access; market results and market requests require the relevant tool permission. Existing create, update, delete, execution, approval, and Switching action permissions remain required where applicable.
See Permissions under Working with the DERMS Configuration Tool in Chapter 30 for permission administration and customer-role updates.
Working with Day Ahead Market
The Day Ahead Market tool in Flex Operations enables distributed energy resources (DERs) to participate collectively in wholesale day-ahead electricity markets. Operators organize participating DERs into VPP - Market groups. The tool combines their bids and available capacity into aggregate bid packages for submission to the market. Dynamic operating envelopes (DOE) establish each DER's permitted import and export limits, accounting for distribution-network constraints.
After the market returns energy awards, NMS uses a unit commitment algorithm to disaggregate each group's awarded power target into individual DER allocations for each market interval. The algorithm determines which resources should operate and how much power each should provide, considering resource bids, operating costs, startup and shutdown costs, ramp-rate limits, and DOE-constrained capacity.
Operators can review the resulting allocation and create an advisory Day Ahead Market switching sheet. This read-only record captures the intended DER schedule, makes its planned contributions available to Feeder Load Management (FLM) forecasts, and reserves the DERs for the scheduled intervals when subsequent DOE and DERMS workflows check resource availability. The advisory sheet does not execute device controls. During the delivery period, DERMS Automatic Generation Control (DAGC) determines and executes real-time dispatch in response to market signals, such as Target MW, and records those operations separately.
Day Ahead Market Workflow
The Day Ahead Market workflow has five main stages:
1. Create or select a market group. Define the participating DERs in a VPP - Market group and open Group Details.
2. Prepare and review the aggregate offer. Select the market window and choose Set Group For Day Ahead Market. Review the DOE-constrained capacity, pricing, and individual DER contributions before submitting the aggregate bid package.
3. Submit the bid package and receive market awards. The configured market integration submits the aggregate bid package and imports the returned awards. Each award identifies the group's power target for a market interval.
4. Disaggregate the awards using unit commitment. Select Run Unit Commitment after the complete award profile has been imported. Review which DERs are committed and the power allocated to each DER for every interval.
5. Commit the planned resources. Select Commit DERs to reserve the resources and create the advisory Day Ahead Market switching sheet. The sheet records the intended allocations and makes them available to FLM forecasting.
Each successful offer preparation creates a retained offer generation. Use the Offer selector to review previous generations; select the latest generation when running unit commitment or committing resources.
If the planned reservation must be withdrawn, select Release DERs to cancel the associated advisory sheet and Work Agenda job. Real-time control remains part of the separate DAGC workflow described under Working with VPP - Market Group Details.
Creating a Market Group
1. Log in to Flex Operations with the Flex DERMS user type and select Day Ahead Market from the Tool Selector. The list displays VPP - Market groups.
2. Select Create Group and enter the group name, description, and device criteria. Groups created from this tool use the VPP - Market type. The market-participant criterion is selected automatically and cannot be changed.
3. To modify an existing group, select the group and choose Edit.
4. To open Group Details, double-click the group or select View Details from its context menu.
Note: Creating or editing groups requires Access Grid DERMS DER Group, Access to Day Ahead Market alone does not grant permission to create or edit group definitions.
Preparing a Day-Ahead Offer
1. In Group Details, set Market Window Start to a future time within the available forecast range. Market Window End is initially calculated from the configured number of forecast intervals and minutes per interval. These interval settings are defined by the DYNAMIC_OPERATING_ENVELOPES SRS rule. The end must be after the start, and the entire market window must be within the permitted forecast range.
2. Select Set Group For Day Ahead Market. The system calculates DOE-constrained availability and prepares the group offer for the selected market window. Required bid and DOE schedule data must cover that window; resolve any missing data warning before retrying.
3. Review the Day Ahead Availability graph. Export Capacity Bid and Import Capacity Bid show the proposed capacity; Operating Envelope Export Limit and Operating Envelope Import Limit show the network-constrained limits. Review the Hourly Offer Schedule and offer summary for the group. In the DERs tab, select the group row to inspect aggregated data or a DER row to inspect that DER's data.
Selecting and Reviewing Offers
A drop-down menu appears within the Analysis Results to select a retained offer. The newest available analysis is displayed by default, but previous days can be viewed as well. Preparing another offer selects the new analysis. When refreshing an existing list, a valid selected generation will remain selected.
The following fields describe the selected results:
Field
Description
Offer Generation
Identifies the retained offer being reviewed.
Market Status
Identifies the group as configured for Day Ahead Market. Use the lifecycle display for progression through the market workflow.
Awards
Indicates whether matching awards have been received.
Forecast Intervals
Number of forecast timestamps retained with this offer.
Minutes in Interval
Interval spacing derived from the selected offer's retained timestamps. It is unavailable when the retained data cannot establish spacing, such as an offer containing only one timestamp.
Last UC Run
Date and time associated with the retained Unit Commitment results, when present.
The selected offer controls the displayed retained market data, including DER membership, availability, schedules, price curves, and associated Unit Commitment results. Reviewing an older offer lets you inspect the data retained for that generation rather than substituting the newest offer's inputs.
Running Unit Commitment and Committing DERs requires the latest analysis to be selected. Reviewing historical analysis results does not authorize a new solve or a new reservation from an old generation. Select the latest offer before continuing the active workflow.
The Parameters area defines a request window. Before launching another analysis, verify those parameters as well as the selected offer; selecting historical Analysis Results is not a request to prepare another offer.
Reviewing Day Ahead Availability
In the Overview tab, review Day Ahead Availability across the selected offer's time range. The graph shows the group's proposed import and export capacity alongside its DOE-constrained operating limits. Available capacity reflects DER availability, applicable contract restrictions, and existing resource commitments.
The time-series display shows how capacity changes across the forecast intervals, helping operators identify periods when network constraints or resource availability limit the group's offer.
Graph Series
Meaning
Export Capacity Bid
Proposed export capability before the DOE-constrained allowed limit is applied.
Import Capacity Bid
Proposed import capability before the DOE-constrained allowed limit is applied.
Allowed export capability reflecting the operating envelope.
Allowed import capability reflecting the operating envelope.
Values are displayed in MW. Compare the proposed and allowed series to identify intervals in which network constraints restrict the offer. Capacity shown by these curves is planning information; it does not establish that the external market accepted the offer or that devices have reached the indicated output.
Reviewing Group and Individual DER Schedules
1. Open the DERs tab and select a resource in DER List. Selecting the group row displays the aggregated information for its DERs, identified as DER Aggregation Resource. Selecting an individual DER displays that resource's information, identified as Component DER View. The relevant charts and tables are updated to reflect the selection.
2. Review the Offer Builder Chart. It displays Economic Min and Economic Max for the selected group or DER across the analysis window, showing the permitted real-power range for each forecast interval.
3. Review the Hourly Offer Schedule. This table presents the same capacity limits by interval, together with the interval number, hour-ending label, and interval end time.
4. Select an interval in Hourly Offer Schedule to display its Offer Summary. When the group is selected in DER List, the summary shows the capacity and price of each segment in the aggregate offer. When an individual DER is selected, it shows that DER's capacity and price for the selected interval.
Hourly Offer Schedule Columns
Column
Description
Interval #
The interval's sequential position within the offer package, starting at 1.
Hour Ending (HE)
Market hour containing the interval end. Sub-hourly intervals can share an HE label. Midnight is HE24.
Interval End Time
Exclusive end of the interval, displayed using the configured UI timezone.
Economic Min (MW)
Allowed lower real-power limit for the selected group or DER during this interval.
Economic Max (MW)
Allowed upper real-power limit for the selected group or DER during this interval.
Offer Price Summary ($/MWh)
Price for the component DER's interval; this column is displayed in the component DER view. Use Offer Summary for the aggregate group's price curve.
An interval includes its start and ends immediately before the next interval. For example, for consecutive 30-minute intervals:
Interval #
Interval span
HE
Interval End Time
1
17:00 to 17:30
HE18
17:30
2
17:30 to 18:00
HE18
18:00
3
18:00 to 18:30
HE19
18:30
Use Interval # and Interval End Time together to distinguish intervals sharing an HE label. Include the date when reviewing a window crossing midnight.
Offer Builder Chart displays Economic Min and Economic Max over the schedule. Its HE labels and end markers identify interval ends; each limit applies across the preceding interval. The range badges summarize the minimum and maximum values of each limit across the displayed schedule.
Offer Summary shows the selected interval's price curve and its table of Curve Point, Cumulative MW, and Offer Price. For an aggregate resource, the stair-step curve gives the offered price for successive capacity blocks. Cumulative MW is the cumulative endpoint of a block, not an additional independent amount to add to the preceding endpoints. For a component DER, the summary represents that DER's retained interval price and capacity.
For example, a curve with cumulative endpoints of 2 MW at $40/MWh and 5 MW at $70/MWh represents a first 2 MW block at $40/MWh and a further 3 MW block at $70/MWh. Its cumulative capacity is 5 MW. This example explains the curve display; it does not determine external market clearing or settlement.
Downloading Schedule Data
Select Download <group name> Schedule CSV below Hourly Offer Schedule. The download reflects the selected offer and the current group or component DER schedule. The button uses the group name even when a component DER is selected, so check the selected resource before downloading.
The CSV follows the schedule table's current filtering and row order. It includes interval identifiers, end times, Economic Min and Economic Max, and offer-curve information for the exported intervals. Aggregate intervals can occupy multiple CSV rows because the schedule values are repeated for each price-curve point. A component export also includes its interval price summary.
Downloading the CSV exports review data. It does not by itself submit an offer to an external market.
Reviewing Market Lifecycle and Awards
Open Day Ahead Market Bids and Awards to review the lifecycle and the Bid Submission Summary, Award Import Summary, and Unit Commitment panels.
Lifecycle Label
Interpretation
Group Ready
The group is at the initial market-workflow stage.
Day Ahead Market Group Submitted
NMS has retained a prepared offer at its submitted stage. External acknowledgment depends on the market integration.
Awards Received
Matching award targets cover the offer's required intervals.
UC Ready
The workflow has advanced to the unit-commitment preparation stage.
UC Complete
The workflow has reached the completed Unit Commitment stage. Review the retained result and its status before committing resources.
Bid Submission Summary identifies the trading day, group, and retained bid status. Award Import Summary identifies award status and the retained forecast coverage when matching awards are available. Coverage is unavailable while a complete matching profile is unavailable. It does not display a partial-import count or a list of missing award intervals.
Awards must correspond to the offer generation and cover its interval timestamps. Awards belonging to a different offer or a different market window do not establish readiness for the selected offer.
For the latest offer in an active award-processing stage, Group Details periodically checks the retained award status while open. Historical offer views do not drive that polling. Receipt of awards and completion of Unit Commitment are separate from reserving resources or controlling devices.
Reviewing Awards and Running Unit Commitment
1. Select the latest offer in Analysis Results and open Day Ahead Market Bids and Awards. Review the lifecycle status and Award Import Summary to confirm that awards have been received for the selected offer.
2. After the complete market award target profile for the group's market window has been received, select Run Unit Commitment. The system uses the awarded group targets to determine individual DER commitments and power allocations for each interval. If a complete matching award profile is unavailable, the system reports that condition and does not run a new analysis.
3. Review the unit commitment summary for its status, run identifier, and solve time. Open UC Results tab to inspect the interval and per-DER allocations. Compare Market Award MW with Allocated Dispatch MW on each interval's summary row and expand the row to review the contributing DERs.
Offer preparation, receipt of market awards, and unit commitment are separate stages. Preparing an offer does not by itself confirm acceptance by the external market. Completing unit commitment calculates the planned DER allocations; it does not execute device controls.
Understanding Unit Commitment Results
Unit Commitment (UC) Results identify Run ID, Solver, Executed at, Solve Time, Total Cost, Total Dispatch, and Switching Sheet ID where available. Executed at records the UC result time; it is not evidence that field controls executed. Likewise, an Available badge indicates that a retained analysis exists; check its UC status before continuing.
Total Dispatch is labeled in MW and summarizes the retained interval outputs. It is not an energy total in MWh. Use the interval rows to compare the allocation with market requirements.
Unit Commitment Dispatch Matrix contains an expandable parent row for each interval and child rows for the individual DERs.
Column
Interpretation
Interval #
The interval's sequential position within the analysis, starting at 1.
Hour Ending (HE)
Interval End Time
Exclusive end of the interval, displayed using the configured User Interface time zone.
Resource Name
Identifies an individual DER in a child row.
Committed
Indicates whether UC committed the DER for that interval. It does not mean that a device command has executed.
Economic Min (MW)
The DER's allowed lower real-power limit for the interval. On the interval summary row, this value is the sum of the individual DER lower limits.
Economic Max (MW)
The DER's allowed upper real-power limit for the interval. On the interval summary row, this value is the sum of the individual DER upper limits.
Market Award MW
The group's awarded power target, in MW, for the interval, as returned by the market. Unit commitment seeks to meet this target by allocating dispatch among individual DERs within their operating limits. This value appears on the interval summary row.
UC allocation for a DER, or the sum of DER allocations on the parent row.
Cost ($)
DER cost for the interval, or the sum of those DER costs on the parent row.
Use DER Committed Status to select All, Committed Only, or Not Committed Only when inspecting DER rows. Use the interval parent row to compare Market Award MW with Allocated Dispatch MW and determine whether the allocation meets the award. A difference requires review; do not assume that a completed solve guarantees exact target matching. The current matrix does not provide separate shortfall and surplus columns.
For a DER row, View On Map and DER Details provide additional resource context.
Committing DERs to an Advisory Switching Sheet
1. Select the latest offer and review its successfully solved UC result.
2. In UC Results, select Commit DERs.
3. The system creates or reuses the Day Ahead Market switching sheet for that group and Unit Commitment analysis then opens it in Switching Management. It associates the sheet with a Work Agenda job and places the advisory switching sheet in Scheduled state.
4. Review the sheet identity, market window, interval blocks, DERs, and setpoints. The blocks use interval-start times, while the market tables identify interval ends.
5. Retain the UC Run ID and Switching Sheet ID when coordinating the reservation with other operators.
The Scheduled advisory sheet makes its setpoints available to Feeder Load Management forecasting and reserves the represented DERs for the scheduled intervals. Overlapping market reservations can affect subsequent DOE or DERMS eligibility. The sheet also retains explicit zero setpoints for DERs that UC did not commit, so review the full schedule rather than assuming only nonzero rows are represented.
Day Ahead Market sheets cannot enter Executing. Commit DERs approves planning intent and reservation; it does not send setpoints to the field. See Working with VPP - Market Group Details for DAGC dispatch.
Advisory sheet state
Meaning
New
Sheet creation has begun, but scheduling may still need to complete. A successful Commit DERs operation completes setup in Scheduled state.
Scheduled
Advisory setpoints are approved for forecast use during the planned window.
Canceled
The advisory reservation has been canceled.
Timeout
The platform state used for an expired advisory plan. It does not indicate that device instructions executed and timed out.
For each DER, a scheduled setpoint reserves the resource from that interval's start until the next setpoint for the same DER on the sheet, capped at the sheet finish time. The end is exclusive. For example, a 17:00 setpoint followed by an 18:00 setpoint reserves the first interval through the time immediately before 18:00. Later DOE or DERMS analysis checks overlapping intervals, not just coincident setpoint timestamps.
Repeating Commit DERs for the same analysis can return an existing New or Scheduled sheet. If an earlier sheet is terminal, another sheet can be created subject to current validation. The system revalidates the retained analysis, current group, modeled DERs, and required sheet configuration before creating the schedule.
Releasing DERs
1. In UC Results, review the associated Switching Sheet ID.
2. Select Release DERs when the associated sheet is cancelable and your permissions allow cancellation.
3. Confirm the cancellation prompt. The action cancels the advisory sheet and its associated Work Agenda job, releasing that reservation.
4. Verify the canceled sheet and job when handing the resources back to other planning workflows.
Release DERs cancels the selected advisory reservation. It is not a command to restore field output and does not describe cancellation of the separate DAGC dispatch workflow.
Supported Objectives
The Network Capacity Allocation (NCA) analysis will determine based on submitted forecasts how much generation can be offered for a 24-hour period without creating network congestion or voltage problems. Currently with the number of DER units that are being added to the distribution network situations can arise that create congestion and/or voltage issues on the system if all DER resource were contributing power at the same time. The NCA analysis will run ahead of time to determine based on generation schedules submitted by the generator's problems will arise. If it is determined that issues will be created the NCA analysis will begin curtailing units that are capable of relieving issues. The analysis will look at the highest cost unit and begin curtailing that unit first. If the curtailment relieves the violations, no other units will be curtailed if the analysis determines the issue is still present the next highest cost unit will be curtailed, the analysis will continue until all units have been curtailed or violations eliminated. When generating solutions for the analysis each hour will be evaluated independently such that a unique set of generation values will be generated for each hour. The analysis can be setup to either consider or ignore pre-existing conditions. If a feeder is setup to ignore pre-existing conditions, it will discard any congestion or voltage issues that existed before the generation schedules were considered. For example, if a feeder has a flow constraint without any market participant DERs being considered that specific constraint issue will be ignored when the analysis is run. If a feeder is setup to consider pre-existing conditions all violations will be considered such that if anything is made worse by the forecast schedules for the DER units, the units will begin being curtailed to relieve any possible issues.
Economic Dispatch
For Economic Dispatch, Grid DERMS optimizes the dispatch of distributed energy resources (DERs) to minimize total operating costs across the distribution network, while strictly observing network constraints such as voltage and equipment loading limits. The system aggregates DER bids and dynamic pricing information-along with real-time and forecasted network conditions-then runs a multi-interval optimal power flow (OPF) analysis to determine the most cost-effective allocation of real and reactive power among controllable DERs. Economic Dispatch prioritizes the use of lower-cost resources and curtails more expensive units only as needed, ensuring that network safety and reliability are never compromised in pursuit of cost savings.
Peak Shaving
Note: In Flex Operations, Peak Shaving requires the Grid DERMS license (derms) and the Access DERMS Optimization permission. Economic Dispatch and NCA use the same permission. Access Derms Dashboard does not grant optimization access.
For Peak Shaving, Grid DERMS analyzes forecasted load profiles over the next 24 hours to identify periods of anticipated peak demand on the distribution network. The system leverages multi-interval optimal power flow (OPF) to develop an optimized charging and discharging schedule for large-scale battery storage and other controllable distributed energy resources. During identified peak hours, Grid DERMS discharges batteries to reduce system load, thereby mitigating demand peaks and improving system reliability. The solution also strategically manages charging and resource allocation during off-peak periods, ensuring energy storage assets are replenished without causing network overloads or violating operational constraints. By coordinating the dispatch of distributed storage assets in this way, Grid DERMS enables the utility to flatten demand curves, defer infrastructure upgrades, reduce demand charges, and enhance overall distribution network efficiency.