5 Powering On Oracle Private Cloud Appliance
Attention:
Before starting the system and applying the initial configuration, read and understand the Oracle Private Cloud Appliance Release Notes. The section Known Limitations and Workarounds provides information that is critical for correctly executing the procedures in this document. Ignoring the release notes may cause you to configure the system incorrectly. Bringing the system back to normal operation may require a complete factory reset.
Power On Task Map
Table 5-1 describes the steps for powering on the Oracle Private Cloud Appliance at your site.
Table 5-1 Steps for Powering On Oracle Private Cloud Appliance
| Step | Description | Links | 
|---|---|---|
| 1 | Review the safety precautions, guidelines, site checklists, and site requirements. | |
| 2 | Perform preliminary checks before connecting the power cords. | |
| 3 | Verify the hardware by visually inspecting the system. | |
| 4 | Connect the appliance public interfaces to the data center network. Also connect a workstation with monitor to the appliance internal management network switch. | |
| 5 | Supply rack power, and perform the power-on self-test device checks. | |
| 6 | Switch on the two power distribution unit (PDU) circuit breakers located on the rear of the main PDU (PDU A). | |
| 7 | Power on the management nodes. | |
| 8 | Wait 5 to 10 minutes and then connect to the Oracle Private Cloud Appliance Dashboard. | 
Before Initial Power On
Before you power on the Oracle Private Cloud Appliance for the first time, ensure that you have made the necessary external network connections.
In addition, you need to connect a workstation with a monitor to the appliance internal management network switch.
- 
                        
                        Connect the workstation to port 48 in the Cisco Nexus 9348GC-FXP Switch 
      Statically configure the workstation IP address to
      192.168.4.254. Start a web browser session in
      order to initially administer your Oracle Private Cloud Appliance using the
      pre-defined IP address (192.168.4.216). For
      more information, see
      Connect the Appliance to the Network.
    
                  
Power On for the First Time
This section provides instructions for each phase of the initial power-on sequence.
Review Safety Guidelines
Before powering on the system or installing any server equipment into the rack, read the Important Safety Information for Oracle's Hardware Systems (7063567) document included with the system.
Before powering on the system, review the following safety precautions. Failure to observe these precautions can result in personal injury, equipment damage, or malfunction.
- 
                           
                           Do not block ventilation openings. 
- 
                           
                           Do not place cables under the equipment or stretch the cables too tightly. 
- 
                           
                           Do not disconnect power cords from the equipment while its power is on. 
- 
                           
                           If you cannot reach the connector lock when disconnecting LAN cables, then press the connector lock with a flathead screwdriver to disconnect the cable. You could damage the system board if you force your fingers into the gap rather than using a flathead screwdriver. 
- 
                           
                           Do not place anything on top of the system or perform any work directly above it. 
- 
                           
                           Do not let the room temperature rise sharply, especially during winter. Sudden temperature changes can cause condensation to form inside the system. Allow for a sufficient warm-up period prior to system operation. 
- 
                           
                           Avoid static electricity at the installation location. Static electricity transferred to the system can cause malfunctions. Static electricity is often generated on carpets. 
- 
                           
                           Confirm that the supply voltage and frequency match the electrical ratings indicated on your Oracle Private Cloud Appliance. 
- 
                           
                           Do not insert anything into any system opening, unless doing so is part of a documented procedure. The system contains high-voltage parts. If a metal object or other electrically-conductive object enters an opening in the system, then it could cause a short circuit. This could result in personal injury, fire, electric shock, and equipment damage. 
Inspect the Appliance
The following procedure describes how to visually inspect your Oracle Private Cloud Appliance after it is physically installed at your site, and prior to power being applied to the system.
- 
                           
                           Check for rack damage. 
- 
                           
                           Check the rack for loose or missing screws. 
- 
                           
                           Check your Oracle Private Cloud Appliance for the ordered configuration. Refer to the Customer Information Sheet (CIS) on the side of the packaging. Note: Oracle Private Cloud Appliance is preconfigured by Oracle as a self-contained system. You should not move any equipment or add any unsupported hardware to the system. 
- 
                           
                           Check that all cable connections are secure and firmly in place as follows: - 
                                 
                                 Check the power cables. Ensure that the correct connectors have been supplied for the data center facility power source. 
- 
                                 
                                 Check the network data cables. 
 
- 
                                 
                                 
- 
                           
                           Check the site location tile arrangement for cable access and airflow. 
- 
                           
                           Check the data center airflow that leads in to the front of the system. For more information, see Ventilation and Cooling Requirements. 
Connect the Power Cords
The following procedure describes how to connect power cords to your Oracle Private Cloud Appliance.
- 
                           
                           Open the rear cabinet door. 
- 
                           
                           Ensure that the correct power connectors have been supplied. 
- 
                           
                           Unfasten the power cord cable ties. The ties are for shipping only and are no longer needed. 
- 
                           
                           Route the power cords to the facility receptacles either above the rack or below the flooring. See Figure 5-1 and Figure 5-2. 
- 
                           
                           Secure the power cords in bundles. See Figure 5-1. Figure 5-1 Power Cord Routing From the Bottom of the Rack  Figure 5-2 Power Cord Routing From the Top of the Rack  
- 
                           
                           Plug the power distribution unit (PDU) power cord connectors into the facility receptacles. Ensure the breaker switches are in the OFF position before connecting the power cables. 
Power On the Appliance
The following procedure describes how to power on your Oracle Private Cloud Appliance.
Note:
You can connect to your Oracle Private Cloud Appliance using a network connection to monitor the system power-on procedure. For instructions, see Connect the Appliance to the Network.
- 
                           
                           Ensure that the three main power cords are connected to a reliable power source. For more information, see Electrical Power Requirements. 
- 
                           
                           Switch on the power distribution unit (PDU) circuit breakers located on the rear of PDU A and B inside the Oracle Private Cloud Appliance. The circuit breakers are on the rear of the system cabinet as shown in Figure 5-3. Press the ON (|) side of the toggle switch. Note: Ensure that the PDU switches have had power applied for approximately two minutes to complete power-on configuration before starting the management nodes. Figure 5-3 PDU Switch Locations  
- 
                           
                           Make sure that the circuit breakers located on the rear left and right side power supplies of the Oracle ZFS Storage Appliance ZS7-2 are in the ON (|) position. Figure 5-4 Oracle ZFS Storage Appliance ZS7-2 Circuit Breakers  
- 
                           
                           Press the Power button located on the front of the first (bottom) management node. See Figure 5-5. The first management node is located in rack unit 5 (U5). The second management node is located in rack unit 6 (U6). It is switched on and configured automatically during the initial power-on sequence. A management nodes take approximately five to ten minutes to power on completely. Once complete, the Power/OK LED illuminates and remains a steady green. Figure 5-5 Oracle Private Cloud Appliance Management Node  Table 5-2 Figure Legend Item Description 1 Power button 2 Power/OK LED 
- 
                           
                           After powering on the first management node, wait while the second management node and all compute nodes are powered on and discovered. Note: After power is applied, the LEDs on all compute nodes and storage server heads will start to blink after approximately two minutes. From the rear of the rack, you can see the green LEDs on the power supply units (PSUs) on the compute nodes turn on instantly after power is applied. In addition, from the rear of the rack, you can see the display on the power distribution units (PDUs) illuminate once power is available. The management nodes will verify all components within the system. The management nodes ensure that the correct networking switches and storage devices are installed in the system, and search for compute nodes to add to the compute fabric. Once compute nodes are located, the management software automatically installs the proper drivers and the Oracle VM Server version on each compute node. Depending on your system configuration, the Oracle Private Cloud Appliance power-on process should take approximately five to ten minutes before the system becomes available for initialization, and up to several hours for the entire configuration to be ready. When initialization is completed, use the Oracle Private Cloud Appliance Dashboard web interface to configure initial system settings (for example: network properties and passwords). For instructions on connecting to the Oracle Private Cloud Appliance and accessing the Dashboard UI, see Connect the Appliance to the Network. 
Connect the Appliance to the Network
For initial access to Oracle Private Cloud Appliance, you must connect a workstation with a monitor to the reserved Ethernet port in the appliance internal management network switch. The Oracle Private Cloud Appliance Dashboard can be reached by means of a web browser.
Note:
You can connect the workstation to the Ethernet port at any time during the system power-on process. However, you should wait approximately two to three minutes after starting the power-on process to allow the IP address to become active. If you connect too soon to the port, you will see an HTTP error code 404 or similar code. If this occurs, wait a few minutes and try to connect again.
You can connect your Oracle Private Cloud Appliance to the network as follows:
- 
                           
                           Ensure that the appliance public interfaces are connected to your data center (public) network. For details, refer to Network Connection Requirements. 
- 
                           
                           Connect a workstation with a web browser directly to the management network using an Ethernet cable connected to the appropriate port: - 
                                 
                                 port 48 in the Cisco Nexus 9348GC-FXP Switch 
 
- 
                                 
                                 
- 
                           
                           Configure the wired network connection of the workstation to use the static IP address 192.168.4.254.
- 
                           
                           Using the web browser on the workstation, connect to the Oracle Private Cloud Appliance Dashboard on the active management node at http://192.168.4.216 . 192.168.4.216is the predefined virtual IP address of the management node cluster for configuring Oracle Private Cloud Appliance. If there is another device on your network that is using this IP address, you should change the conflicting device's IP address prior to connecting to the Oracle Private Cloud Appliance.
- 
                           
                           Log into the Dashboard using the user name adminand the default password, which is provided during the installation process. Contact your Oracle representative if you need the default password.Note: For security reasons, you must set a new password at your earliest convenience. When you have logged in to the Dashboard successfully, the home page is displayed. The central part of the page contains Quick Launch buttons that provide direct access to the key functional areas. Click to open the Hardware View. The Hardware View indicates the status of the appliance as it is being powered on. All the networking and storage should be green. As the compute nodes are discovered, they will change from yellow to green. Wait until all compute nodes have been discovered and provisioned before making configuration changes in the Dashboard interface. 
- 
                           
                           Using the Dashboard, configure the system environment parameters, including domain name, NTP, and DNS servers. Attention: Before reconfiguring the system network settings, ensure that no provisioning or upgrade processes are running. 
- 
                           
                           Go to the Network Environment window and enter the configuration details. Insert the reserved management node IP addresses and environment parameters of your data center network. - 
                                 
                                 In the Management Nodes tab, enter the IP addresses and host names for both management nodes. Note: During the initial configuration of the Oracle Private Cloud Appliance, you change the predefined configuration IP address to the reserved virtual IP address in your data center network. For details, see General Network Configuration. Figure 5-6 Management Nodes Tab  
- 
                                 
                                 In the Data Center Network tab, enter the domain name, netmask, default gateway and NTP server of the network to which the appliance must be connected. If this network is a VLAN, set the slider to active and enter the VLAN ID in the field next to it. Figure 5-7 Data Center Network Tab  
- 
                                 
                                 In the DNS tab, enter at least one and up to three name servers for the network to which the appliance must be connected. Figure 5-8 DNS Tab  
- 
                                 
                                 Enter the Administrator password and click Apply Changes to confirm and apply the configuration parameters you provided. 
 
- 
                                 
                                 
- 
                           
                           Reconnect to the Oracle Private Cloud Appliance Dashboard at the new virtual IP address of the management node cluster: https://<virtual_ip>:7002/dashboard.
For details about the software configuration process, and for advanced configuration and update options, refer to the Oracle Private Cloud Appliance Administrator's Guide.
What's Next?
After powering on your Oracle Private Cloud Appliance and performing the initial system configuration, the environment is ready for virtual machine deployment. Refer to the Oracle Private Cloud Appliance Administrator's Guide for information about working with an operational environment:
- 
                        
                        See Monitoring and Managing Oracle Private Cloud Appliance for instructions to work with the Oracle Private Cloud Appliance Dashboard. 
- 
                        
                        See Managing the Oracle VM Virtual Infrastructure for instructions to work with virtual machines within Oracle VM. 
- 
                        
                        See Upgrading Oracle Private Cloud Appliance for instructions to update the Oracle Private Cloud Appliance controller software. 
- 
                        
                        See Servicing Oracle Private Cloud Appliance Components for instructions to service customer-replaceable components in the Oracle Private Cloud Appliance. 
Note:
Optionally, you can extend Oracle Private Cloud Appliance by adding more compute nodes to the system, by installing extra memory in the compute nodes, or by connecting the appliance to additional external storage. For more information and instructions, refer to the following chapters: