The current Oracle Private Cloud Appliance hardware platform, with factory-installed Controller Software Release 2.4.x, consists of an Oracle Rack Cabinet 1242 base, populated with the hardware components identified in Figure 1.1. Previous generations of hardware components continue to be supported by the latest Controller Software, as described below.
Table 1.1 Figure Legend
| Item | Quantity | Description | 
|---|---|---|
| A | 2 | Oracle ZFS Storage Appliance ZS7-2 controller server | 
| B | 2 | Oracle Server X8-2, used as management nodes | 
| C | 2-25 | Oracle Server X8-2, used as virtualization compute nodes (Due to the power requirements of the Oracle Server X8-2, if the appliance is equipped with 22kVA PDUs, the maximum number of compute nodes is 22. With 15KVA PDUs the maximum is 13 compute nodes.) | 
| D | 2 | Cisco Nexus 9336C-FX2 Switch, used as leaf/data switches | 
| E | 1 | Oracle ZFS Storage Appliance ZS7-2 disk shelf | 
| F | 1 | Cisco Nexus 9348GC-FXP Switch | 
| G | 2 | Cisco Nexus 9336C-FX2 Switch, used as spine switches | 
Support for Previous Generations of Hardware Components
The latest version of the Oracle Private Cloud Appliance Controller Software continues to support all earlier configurations of the hardware platform. These may include the following components:
Table 1.2 Supported Hardware
| Component Type | Component Name and Minimum Software Version | 
|---|---|
| Management Nodes | 
 | 
| Compute Nodes | 
 | 
| Storage Appliance | 
 | 
| InfiniBand Network Hardware | 
 | 
| Internal Management Switch | 
 | 
At the heart of each Oracle Private Cloud Appliance installation is a pair of management nodes. They are installed in rack units 5 and 6 and form a cluster in active/standby configuration for high availability: both servers are capable of running the same services and have equal access to the system configuration, but one operates as the master while the other is ready to take over the master functions in case a failure occurs. The master management node runs the full set of services required, while the standby management node runs a subset of services until it is promoted to the master role. The master role is determined at boot through OCFS2 Distributed Lock Management on an iSCSI LUN, which both management nodes share on the ZFS Storage Appliance installed inside the rack. Because rack units are numbered from the bottom up, and the bottom four are occupied by components of the ZFS Storage Appliance, the master management node is typically the server in rack unit 5. It is the only server that must be powered on by the administrator in the entire process to bring the appliance online.
For details about how high availability is achieved with Oracle Private Cloud Appliance, refer to Section 1.5, “High Availability”.
When you power on the Oracle Private Cloud Appliance for the first time, you can change the factory default IP configuration of the management node cluster, so that it can be easily reached from your data center network. The management nodes share a Virtual IP, where the management web interface can be accessed. This virtual IP is assigned to whichever server has the master role at any given time. During system initialization, after the management cluster is set up successfully, the master management node loads a number of Oracle Linux services, in addition to Oracle VM and its associated MySQL database – including network, sshd, ntpd, iscsi initiator, dhcpd – to orchestrate the provisioning of all system components. During provisioning, all networking and storage is configured, and all compute nodes are discovered, installed and added to an Oracle VM server pool. All provisioning configurations are preloaded at the factory and should not be modified by the customer.
For details about the provisioning process, refer to Section 1.4, “Provisioning and Orchestration”.
The compute nodes in the Oracle Private Cloud Appliance constitute the virtualization platform. The compute nodes provide the processing power and memory capacity for the virtual servers they host. The entire provisioning process is orchestrated by the management nodes: compute nodes are installed with Oracle VM Server 3.4.x and additional packages for Software Defined Networking. When provisioning is complete, the Oracle Private Cloud Appliance Controller Software expects all compute nodes in the same rack to be part of the same Oracle VM server pool.
For hardware configuration details of the compute nodes, refer to Server Components in the Oracle Private Cloud Appliance Installation Guide.
The Oracle Private Cloud Appliance Dashboard allows the administrator to monitor the health and status of the compute nodes, as well as all other rack components, and perform certain system operations. The virtual infrastructure is configured and managed with Oracle VM Manager.
The Oracle Private Cloud Appliance offers modular compute capacity that can be increased according to business needs. The minimum configuration of the base rack contains just two compute nodes, but it can be expanded by one node at a time up to 25 compute nodes. Apart from the hardware installation, adding compute nodes requires no intervention by the administrator. New nodes are discovered, powered on, installed and provisioned automatically by the master management node. The additional compute nodes are integrated into the existing configuration and, as a result, the Oracle VM server pool offers increased capacity for more or larger virtual machines.
As a further expansion option, the Oracle Server X8-2 compute nodes can be ordered with pre-installed fibre channel cards, or equipped with fibre channel cards after installation. Once these compute nodes are integrated in the Oracle Private Cloud Appliance environment, the fibre channel HBAs can connect to standard FC switches and storage hardware in your data center. External FC storage configuration is managed through Oracle VM Manager. For more information, refer to the Fibre Channel Storage Attached Network section of the Oracle VM Concepts Guide.
When using expansion nodes containing fibre channel cards in a system with InfiniBand-based network architecture, the vHBAs must be disabled on those compute nodes.
Because of the diversity of possible virtualization scenarios it is difficult to quantify the compute capacity as a number of virtual machines. For sizing guidelines, refer to the chapter entitled Configuration Maximums in the Oracle Private Cloud Appliance Release Notes.
The Oracle Private Cloud Appliance Controller Software continues to provide support for previous generations of the ZFS Storage Appliance installed in the base rack. However, there are functional differences between the Oracle ZFS Storage Appliance ZS7-2, which is part of systems with an Ethernet-based network architecture, and the previous models of the ZFS Storage Appliance, which are part of systems with an InfiniBand-based network architecture. For clarity, this section describes the different storage appliances separately.
The Oracle ZFS Storage Appliance ZS7-2, which consists of two controller servers installed at the bottom of the appliance rack and disk shelf about halfway up, fulfills the role of 'system disk' for the entire appliance. It is crucial in providing storage space for the Oracle Private Cloud Appliance software.
A portion of the disk space, 3TB by default, is made available for customer use and is sufficient for an Oracle VM storage repository with several virtual machines, templates and assemblies. The remaining part of approximately 100TB in total disk space can also be configured as a storage repository for virtual machine resources. Further capacity extension with external storage is also possible.
The hardware configuration of the Oracle ZFS Storage Appliance ZS7-2 is as follows:
- Two clustered storage heads with two 14TB hard disks each 
- One fully populated disk chassis with twenty 14TB hard disks 
- Four cache disks installed in the disk shelf: 2x 200GB SSD and 2x 7.68TB SSD 
- RAID-1 configuration, for optimum data protection, with a total usable space of approximately 100TB 
          The storage appliance is connected to the management subnet
          (192.168.4.0/24) and the
          storage subnet
          (192.168.40.0/24). Both heads
          form a cluster in active-passive configuration to guarantee
          continuation of service in the event that one storage head
          should fail. The storage heads share a single IP in the
          storage subnet, but both have an individual management IP
          address for convenient maintenance access. The RAID-1 storage
          pool contains two projects, named
          OVCA and
          OVM .
        
          The OVCA project contains all
          LUNs and file systems used by the Oracle Private Cloud Appliance software:
        
- LUNs - Locks(12GB) – to be used exclusively for cluster locking on the two management nodes
- Manager(200GB) – to be used exclusively as an additional file system on both management nodes
 
- File systems: - MGMT_ROOT– to be used for storage of all files specific to the Oracle Private Cloud Appliance
- Database– placeholder file system for databases
- Incoming(20GB) – to be used for FTP file transfers, primarily for Oracle Private Cloud Appliance component backups
- Templates– placeholder file system for future use
- User– placeholder file system for future use
- Yum– to be used for system package updates
 
          The OVM project contains all
          LUNs and file systems used by Oracle VM:
        
- LUNs - iscsi_repository1(3TB) – to be used as Oracle VM storage repository
- iscsi_serverpool1(12GB) – to be used as server pool file system for the Oracle VM clustered server pool
 
- File systems: - nfs_repository1(3TB) – used by- kdump; not available for customer use
- nfs_serverpool1(12GB) – to be used as server pool file system for the Oracle VM clustered server pool in case NFS is preferred over iSCSI
 
If the internal ZFS Storage Appliance contains customer-created LUNs, make sure they are not mapped to the default initiator group. See Customer Created LUNs Are Mapped to the Wrong Initiator Group in the Oracle Private Cloud Appliance Release Notes.
In addition to offering storage, the ZFS storage appliance also runs the xinetd and tftpd services. These complement the Oracle Linux services on the master management node in order to orchestrate the provisioning of all Oracle Private Cloud Appliance system components.
The Oracle ZFS Storage Appliance ZS5-ES installed at the bottom of the appliance rack should be considered a 'system disk' for the entire appliance. Its main purpose is to provide storage space for the Oracle Private Cloud Appliance software. A portion of the disk space is made available for customer use and is sufficient for an Oracle VM storage repository with a limited number of virtual machines, templates and assemblies.
The hardware configuration of the Oracle ZFS Storage Appliance ZS5-ES is as follows:
- Two clustered storage heads with two 3.2TB SSDs each, used exclusively for cache 
- One fully populated disk chassis with twenty 1.2TB 10000 RPM SAS hard disks 
- RAID-Z2 configuration, for best balance between performance and data protection, with a total usable space of approximately 15TB 
Oracle Private Cloud Appliance base racks shipped prior to software release 2.3.3 use a Sun ZFS Storage Appliance 7320 or Oracle ZFS Storage Appliance ZS3-ES. Those systems may be upgraded to a newer software stack, which continues to provide support for each Oracle Private Cloud Appliance storage configuration. The newer storage appliance offers the same functionality and configuration, with modernized hardware and thus better performance.
          The storage appliance is connected to the management subnet (
          192.168.4.0/24 ) and the
          InfiniBand (IPoIB) storage subnet (
          192.168.40.0/24 ). Both heads
          form a cluster in active-passive configuration to guarantee
          continuation of service in the event that one storage head
          should fail. The storage heads share a single IP in the
          storage subnet, but both have an individual management IP
          address for convenient maintenance access. The RAID-Z2 storage
          pool contains two projects, named
          OVCA and
          OVM .
        
          The OVCA project contains all
          LUNs and file systems used by the Oracle Private Cloud Appliance software:
        
- LUNs - Locks(12GB) – to be used exclusively for cluster locking on the two management nodes
- Manager(200GB) – to be used exclusively as an additional file system on both management nodes
 
- File systems: - MGMT_ROOT– to be used for storage of all files specific to the Oracle Private Cloud Appliance
- Database– placeholder file system for databases
- Incoming(20GB) – to be used for FTP file transfers, primarily for Oracle Private Cloud Appliance component backups
- Templates– placeholder file system for future use
- User– placeholder file system for future use
- Yum– to be used for system package updates
 
          The OVM project contains all
          LUNs and file systems used by Oracle VM:
        
- LUNs - iscsi_repository1(300GB) – to be used as Oracle VM storage repository
- iscsi_serverpool1(12GB) – to be used as server pool file system for the Oracle VM clustered server pool
 
- File systems: - nfs_repository1(300GB) – to be used as Oracle VM storage repository in case NFS is preferred over iSCSI
- nfs_serverpool1(12GB) – to be used as server pool file system for the Oracle VM clustered server pool in case NFS is preferred over iSCSI
 
If the internal ZFS Storage Appliance contains customer-created LUNs, make sure they are not mapped to the default initiator group. See Customer Created LUNs Are Mapped to the Wrong Initiator Group in the Oracle Private Cloud Appliance Release Notes.
In addition to offering storage, the ZFS storage appliance also runs the xinetd and tftpd services. These complement the Oracle Linux services on the master management node in order to orchestrate the provisioning of all Oracle Private Cloud Appliance system components.
For network connectivity, Oracle Private Cloud Appliance relies on a physical layer that provides the necessary high-availability, bandwidth and speed. On top of this, several different virtual networks are optimally configured for different types of data traffic. Only the internal administration network is truly physical; the appliance data connectivity uses Software Defined Networking (SDN). The appliance rack contains redundant network hardware components, which are pre-cabled at the factory to help ensure continuity of service in case a failure should occur.
Depending on the exact hardware configuration of your appliance, the physical network layer is either high-speed Ethernet or InfiniBand. In this section, both network architectures are described separately in more detail.
Oracle Private Cloud Appliance with Ethernet-based network architecture relies on redundant physical high-speed Ethernet connectivity.
Administration Network
          The administration network provides internal access to the
          management interfaces of all appliance components. These have
          Ethernet connections to the Cisco Nexus 9348GC-FXP Switch, and all have a
          predefined IP address in the
          192.168.4.0/24 range. In
          addition, all management and compute nodes have a second IP
          address in this range, which is used for Oracle Integrated Lights Out Manager (ILOM)
          connectivity.
        
          While the appliance is initializing, the data network is not
          accessible, which means that the internal administration
          network is temporarily the only way to connect to the system.
          Therefore, the administrator should connect a workstation to
          the reserved Ethernet port 48 in the Cisco Nexus 9348GC-FXP Switch, and
          assign the fixed IP address
          192.168.4.254 to the
          workstation. From this workstation, the administrator opens a
          browser connection to the web server on the master management
          node at https://192.168.4.216
          , in order to monitor the initialization process and perform
          the initial configuration steps when the appliance is powered
          on for the first time.
        
Data Network
The appliance data connectivity is built on redundant Cisco Nexus 9336C-FX2 Switches in a leaf-spine design. In this two-layer design, the leaf switches interconnect the rack hardware components, while the spine switches form the backbone of the network and perform routing tasks. Each leaf switch is connected to all the spine switches, which are also interconnected. The main benefits of this network architecture are extensibility and path optimization. An Oracle Private Cloud Appliance rack contains two leaf and two spine switches.
          The Cisco Nexus 9336C-FX2 Switch offers a maximum throughput of 100Gbit
          per port. The spine switches use 5 interlinks (500Gbit); the
          leaf switches use 2 interlinks (200Gbit) and 2x2 crosslinks to
          the spines. Each compute node is connected to both leaf
          switches in the rack, through the bond1
          interface that consists of two 100Gbit Ethernet ports in link
          aggregation mode. The two storage controllers are connected to
          the spine switches using 4x40Gbit connections.
        
For external connectivity, 5 ports are reserved on each spine switch. Four ports are available for custom network configurations; one port is required for the default uplink. This default external uplink requires that port 5 on both spine switches is split using a QSFP+-to-SFP+ four way splitter or breakout cable. Two of those four 10GbE SFP+ breakout ports per spine switch, ports 5/1 and 5/2, must be connected to a pair of next-level data center switches, also called top-of-rack or ToR switches.
Software Defined Networking
While the physical data network described above allows the data packets to be transferred, the true connectivity is implemented through Software Defined Networking (SDN). Using VxLAN encapsulation and VLAN tagging, thousands of virtual networks can be deployed, providing segregated data exchange. Traffic can be internal between resources within the appliance environment, or external to network storage, applications, or other resources in the data center or on the internet. SDN maintains the traffic separation of hard-wired connections, and adds better performance and dynamic (re-)allocation. From the perspective of the customer network, the use of VxLANs in Oracle Private Cloud Appliance is transparent: encapsulation and de-encapsulation take place internally, without modifying inbound or outbound data packets. In other words, this design extends customer networking, tagged or untagged, into the virtualized environment hosted by the appliance.
During the initialization process of the Oracle Private Cloud Appliance, several essential default networks are configured:
- The Internal Storage Network is a redundant 40Gbit Ethernet connection from the spine switches to the ZFS storage appliance. All four storage controller interfaces are bonded using LACP into one datalink. Management and compute nodes can reach the internal storage over the - 192.168.40.0/21subnet on VLAN 3093. This network also fulfills the heartbeat function for the clustered Oracle VM server pool.
- The Internal Management Network provides connectivity between the management nodes and compute nodes in the subnet - 192.168.32.0/21on VLAN 3092. It is used for all network traffic inherent to Oracle VM Manager, Oracle VM Server and the Oracle VM Agents.
- The Internal Underlay Network provides the infrastructure layer for data traffic between compute nodes. It uses the subnet - 192.168.64.0/21on VLAN 3091. On top of the internal underlay network, internal VxLAN overlay networks are built to enable virtual machine connectivity where only internal access is required.- One such internal VxLAN is configured in advance: the default internal VM network, to which all compute nodes are connected with their - vx2interface. Untagged traffic is supported by default over this network. Customers can add VLANs of their choice to the Oracle VM network configuration, and define the subnet(s) appropriate for IP address assignment at the virtual machine level.
- The External Underlay Network provides the infrastructure layer for data traffic between Oracle Private Cloud Appliance and the data center network. It uses the subnet - 192.168.72.0/21on VLAN 3090. On top of the external underlay network, VxLAN overlay networks with external access are built to enable public connectivity for the physical nodes and all the virtual machines they host.- One such public VxLAN is configured in advance: the default external network, to which all compute nodes and management nodes are connected with their - vx13040interface. Both tagged and untagged traffic are supported by default over this network. Customers can add VLANs of their choice to the Oracle VM network configuration, and define the subnet(s) appropriate for IP address assignment at the virtual machine level.- The default external network also provides access to the management nodes from the data center network and allows the management nodes to run a number of system services. The management node external network settings are configurable through the Network Settings tab in the Oracle Private Cloud Appliance Dashboard. If this network is a VLAN, its ID or tag must be configured in the Network Setup tab of the Dashboard. 
For the appliance default networking to be configured successfully, the default external uplink must be in place before the initialization of the appliance begins. At the end of the initialization process, the administrator assigns three reserved IP addresses from the data center (public) network range to the management node cluster of the Oracle Private Cloud Appliance: one for each management node, and an additional Virtual IP shared by the clustered nodes. From this point forward, the Virtual IP is used to connect to the master management node's web server, which hosts both the Oracle Private Cloud Appliance Dashboard and the Oracle VM Manager web interface.
It is critical that both spine Cisco Nexus 9336C-FX2 Switches have two 10GbE connections each to a pair of next-level data center switches. For this purpose, a 4-way breakout cable must be attached to port 5 of each spine switch, and 10GbE breakout ports 5/1 and 5/2 must be used as uplinks. Note that ports 5/3 and 5/4 remain unused.
This outbound cabling between the spine switches and the data center network should be crossed or meshed, to ensure optimal continuity of service.
Oracle Private Cloud Appliance with InfiniBand-based network architecture relies on a physical InfiniBand network fabric, with additional Ethernet connectivity for internal management communication.
Ethernet
          The Ethernet network relies on two interconnected Oracle Switch ES1-24
          switches, to which all other rack components are connected
          with CAT6 Ethernet cables. This network serves as the
          appliance management network, in which every component has a
          predefined IP address in the
          192.168.4.0/24 range. In
          addition, all management and compute nodes have a second IP
          address in this range, which is used for Oracle Integrated Lights Out Manager (ILOM)
          connectivity.
        
          While the appliance is initializing, the InfiniBand fabric is
          not accessible, which means that the management network is the
          only way to connect to the system. Therefore, the
          administrator should connect a workstation to the available
          Ethernet port 19 in one of the Oracle Switch ES1-24 switches, and
          assign the fixed IP address
          192.168.4.254 to the
          workstation. From this workstation, the administrator opens a
          browser connection to the web server on the master management
          node at http://192.168.4.216
          , in order to monitor the initialization process and perform
          the initial configuration steps when the appliance is powered
          on for the first time.
        
InfiniBand
The Oracle Private Cloud Appliance rack contains two NM2-36P Sun Datacenter InfiniBand Expansion Switches. These redundant switches have redundant cable connections to both InfiniBand ports in each management node, compute node and storage head. Both InfiniBand switches, in turn, have redundant cable connections to both Fabric Interconnects in the rack. All these components combine to form a physical InfiniBand backplane with a 40Gbit (Quad Data Rate) bandwidth.
When the appliance initialization is complete, all necessary Oracle Private Cloud Appliance software packages, including host drivers and InfiniBand kernel modules, have been installed and configured on each component. At this point, the system is capable of using software defined networking (SDN) configured on top of the physical InfiniBand fabric. SDN is implemented through the Fabric Interconnects.
Fabric Interconnect
All Oracle Private Cloud Appliance network connectivity is managed through the Fabric Interconnects. Data is transferred across the physical InfiniBand fabric, but connectivity is implemented in the form of Software Defined Networks (SDN), which are sometimes referred to as 'clouds'. The physical InfiniBand backplane is capable of hosting thousands of virtual networks. These Private Virtual Interconnects (PVI) dynamically connect virtual machines and bare metal servers to networks, storage and other virtual machines, while maintaining the traffic separation of hard-wired connections and surpassing their performance.
During the initialization process of the Oracle Private Cloud Appliance, five essential networks, four of which are SDNs, are configured: a storage network, an Oracle VM management network, a management Ethernet network, and two virtual machine networks. Tagged and untagged virtual machine traffic is supported. VLANs can be constructed using virtual interfaces on top of the existing bond interfaces of the compute nodes.
- The storage network, technically not software-defined, is a bonded IPoIB connection between the management nodes and the ZFS storage appliance, and uses the - 192.168.40.0/24subnet. This network also fulfills the heartbeat function for the clustered Oracle VM server pool. DHCP ensures that compute nodes are assigned an IP address in this subnet.
- The Oracle VM management network is a PVI that connects the management nodes and compute nodes in the - 192.168.140.0/24subnet. It is used for all network traffic inherent to Oracle VM Manager, Oracle VM Server and the Oracle VM Agents.
- The management Ethernet network is a bonded Ethernet connection between the management nodes. The primary function of this network is to provide access to the management nodes from the data center network, and enable the management nodes to run a number of system services. Since all compute nodes are also connected to this network, Oracle VM can use it for virtual machine connectivity, with access to and from the data center network. The management node external network settings are configurable through the Network Settings tab in the Oracle Private Cloud Appliance Dashboard. If this network is a VLAN, its ID or tag must be configured in the Network Setup tab of the Dashboard. 
- The public virtual machine network is a bonded Ethernet connection between the compute nodes. Oracle VM uses this network for virtual machine connectivity, where external access is required. Untagged traffic is supported by default over this network. Customers can add their own VLANs to the Oracle VM network configuration, and define the subnet(s) appropriate for IP address assignment at the virtual machine level. For external connectivity, the next-level data center switches must be configured to accept your tagged VLAN traffic. 
- The private virtual machine network is a bonded Ethernet connection between the compute nodes. Oracle VM uses this network for virtual machine connectivity, where only internal access is required. Untagged traffic is supported by default over this network. Customers can add VLANs of their choice to the Oracle VM network configuration, and define the subnet(s) appropriate for IP address assignment at the virtual machine level. 
Finally, the Fabric Interconnects also manage the physical public network connectivity of the Oracle Private Cloud Appliance. Two 10GbE ports on each Fabric Interconnect must be connected to redundant next-level data center switches. At the end of the initialization process, the administrator assigns three reserved IP addresses from the data center (public) network range to the management node cluster of the Oracle Private Cloud Appliance: one for each management node, and an additional Virtual IP shared by the clustered nodes. From this point forward, the Virtual IP is used to connect to the master management node's web server, which hosts both the Oracle Private Cloud Appliance Dashboard and the Oracle VM Manager web interface.
It is critical that both Fabric Interconnects have two 10GbE connections each to a pair of next-level data center switches. This configuration with four cable connections provides redundancy and load splitting at the level of the Fabric Interconnects, the 10GbE ports and the data center switches. This outbound cabling should not be crossed or meshed, because the internal connections to the pair of Fabric Interconnects are already configured that way. The cabling pattern plays a key role in the continuation of service during failover scenarios involving Fabric Interconnect outages and other components.