In most cases, replacement of a faulty DIMM is detected when the SPM is power cycled. In those cases, the fault is automatically cleared from the server. If show faulty still displays the fault, the set command clears it.
-> set /SYS/MB/CMP0/MCU0/CH0/D0 requested_config_state=Enabled
-> set /HOST keyswitch_state=Diag Set 'keyswitch_state' to 'Diag'
-> stop /System Are you sure you want to stop /System (y/n)? y Stopping /System -> start /System Are you sure you want to start /System (y/n)? y Starting /System
Allow approximately one minute before performing this step. Type the show /HOST command. When the host is powered off, the console displays status=Powered Off.
Watch the POST output for possible fault messages. This output indicates that POST did not detect any faults:
-> start /HOST/console ... 0:0:0>INFO: 0:0:0> POST Passed all devices. 0:0:0>POST: Return to VBSC. 0:0:0>Master set ACK for vbsc runpost command and spin...
-> set /HOST keyswitch_state=Normal Set 'keyswitch_state' to 'Normal'
# fmadm faulty
If any faults are reported, refer to the diagnostics instructions described in Identify Faulted Components.
-> show faulty Target | Property | Value --------------------+------------------------+------------------------------- /SP/faultmgmt/0 | fru | /SYS/CMP0/MCU0/CH0/D0 /SP/faultmgmt/0 | timestamp | Mar 18 16:02:56 /SP/faultmgmt/0/ | sunw-msg-id | SPSUN4V-8001-OJ faults/0 | | /SP/faultmgmt/0/ | uuid | 2782ad0c-91cb-c780-9663-807f0bf806df faults/0 | | /SP/faultmgmt/0/ | timestamp | Mar 18 16:02:56 faults/0 | |
If this command reports a fault with a UUID go to Step 6. If show faulty does not report a fault with a UUID, you are done with the verification process.
Use the same UUID that was displayed from the output of the Oracle ILOM show faulty command. For example, type:
# fmadm repair 7c7efb20-3333-e2d7-b8ea-986b3e9dbaa9
