Go to main content
Sun Rack II Power Distribution Units User's Guide
Exit Print View
Updated: December 2016
Standard PDU Electrical Specifications
The following tables describe the PDU electrical specifications, including the number and type of connectors and receptacles.
Table 3  Specifications for North and South America, Japan, and Taiwan Low-Voltage PDUs
Specification
5 kVA
10 kVA
15 kVA, 1ph
15 kVA, 3ph
24 kVA
37 kVA
Number of Inputs
1 x 30A 1ph
2 x 30A 1ph
3 x 30A 1ph
1 x 60A 3ph
2 x 60A 3ph
3 x 60A 3ph
Voltage
200 - 240 VAC
200 - 240 VAC
200 - 240 VAC
200 - 208 VAC 3ph
200 - 208 VAC 3ph
200 - 208 VAC 3ph
Frequency
50/60 Hz
50/60 Hz
50/60 Hz
50/60 Hz
50/60 Hz
50/60 Hz
Current
24A max.
24A max. per input
24A max. per input
40A max. per phase
34.6A max. per phase
Power Rating
5 kVA
10 kVA
15 kVA
14.4 kVA
25.0 kVA
37.5 kVA
Output Current
24A
48A (2 x 24A)
72A (3 x 24A)
69A (3 x 23A)
120A (6 x 20A)
180A (9 x 20A)
Outlets
42 x C13 6 x C19
42 x C13 6 x C19
42 x C13 6 x C19
42 x C13 6 x C19
42 x C13 6 x C19
45 x C13 9 x C19
Outlet Groups
6
6
6
6
6
9
Group Protection
UL489 2-pole circuit breaker.
20A
20A
20A
20A
20A
20A
Data Center Receptacle
NEMA L6-30
NEMA L6-30
NEMA L6-30
IEC309 60A 4 PIN 250VAC 3ph IP67
Table 4  Specifications for EMEA and APAC High-Voltage PDUs
Specification
5 kVA
10 kVA
15 kVA, 1ph
15 kVA, 3ph
22 kVA
24 kVA
37 kVA
Number of Inputs
1 x 25A 1ph
2 x 25A 1ph
3 x 25A 1ph
1 x 25A 3ph
3x32A 1ph
2 x 25A 3ph
3 x 25A 3ph
Voltage
220 - 240 VAC
220 - 240V AC
220 - 240 VAC
220/380 – 240/415 VAC 3ph
220 - 240 VAC
Frequency
50/60 Hz
50/60 Hz
50/60 Hz
50/60 Hz
50/60 Hz
50/60 Hz
50/60 Hz
Current
25A max.
25A max. per input
25A max. per input
25A max. per phase
32A max per input
18A max. per phase
18A max. per phase
Power Rating
5 kVA
10 kVA
15 kVA
14.4 kVA
22 kVA
25.0 kVA
37.5 kVA
Output Current
24A
48A (2 x 24A)
72A (3 x 24A)
62.7A (3 x 20.9A)
96A
(3x32A)
109A (6 x 18.1A)
163A (9 x 18.1A)
Outlets
42 x C13 6 x C19
42 x C13 6 x C19
42 x C13 6 x C19
42 x C13 6 x C19
42 x C13 6 x C19
42 x C13 6 x C19
45 x C13 9 x C19
Outlet Groups
6
6
6
6
6
6
9
Group Protection
UL489 1-pole circuit breaker.
20A
20A
20A
20A
20A
20A
20A
IEC309 32A 3 PIN 250 VAC IP44
IEC309 32A 5 PIN 230/400V 3ph IP44