Three-Phase PDU Input and Outlet Group Relationship
Figure 6  Three-Phase PDU Input and Outlet Group Relationship
image:Figure showing the relationship between the metering unit inputs                             and the 3-phase PDU outlet groups.
Note -  For three-phase, low-voltage PDUs, each metering unit phase reports current from two outlet groups. Input phase 1 reports a combination of current from outlet groups 0 and 2 (3 and 5, or 6 and 8, depending on which input). Input phase 2 reports a combination of current from outlet groups 1 and 0 (4 and 3, or 7 and 6, depending on which input). Input phase 3 reports a combination of current from outlet groups 2 and 1 (5 and 4, or 8 and 7, depending on which input).
Table 15  Relationship Between Metering Unit Inputs and Outlet Groups on Three-Phase PDUs
PDU Type
Power Input
Lead Number
Input Phase
Outlet Group
15 kVA
0
Phase 1
0, 3
0
Phase 2
1, 4
0
Phase 3
2, 5
24 kVA
0
Phase 1
0
0
Phase 2
1
0
Phase 3
2
1
Phase 1
3
1
Phase 2
4
1
Phase 3
5
37 kVA
0
Phase 1
0
0
Phase 2
1
0
Phase 3
2
1
Phase 1
3
1
Phase 2
4
1
Phase 3
5
2
Phase 1
6
2
Phase 2
7
2
Phase 3
8