Connecting an Oracle Exadata Storage Expansion Rack to the SPARC SuperCluster T4-4
Three Sun Datacenter InfiniBand Switch 36 switches are needed when cabling racks together. The
SPARC SuperCluster T4-4 and the Oracle Exadata Storage Expansion Half Rack or Oracle Exadata Storage Expansion Full Rack include three
Sun Datacenter InfiniBand Switch 36 switches. Two switches are used as leaf switches, and the third switch is used
as a spine switch. These switches attach to standard Quad Small Form-factor Pluggable
(QSFP) connectors at the end of the InfiniBand cables. The procedures in this section
assume the racks are adjacent to each other. If they are not, then longer cables may be
required for the connections.
InfiniBand Switch Information for the SPARC SuperCluster T4-4
In the SPARC SuperCluster T4-4, the switch at rack unit 1 (U1) is referred to as
the
spine switch. The switches at rack unit 18 (U18) and rack unit 24 (U24)
are referred to as
leaf switches. In a single rack, the two leaf switches are
interconnected using seven connections. In addition, each leaf switch has one
connection to the spine switch. The leaf switches connect to the spine switch as
shown in the following graphic.
InfiniBand Switch Information for the Oracle Exadata Storage Expansion Rack
In the Oracle Exadata Storage Expansion Rack, the switch at rack unit 1 (U1) is referred to as the
spine switch, except for the Oracle Exadata Storage Expansion Quarter Rack which has no spine
switch. The switches at rack unit 20 (U20) and rack unit 24 (U24) are referred to as
leaf switches.
Connecting an Oracle Exadata Storage Expansion Quarter Rack to the SPARC SuperCluster T4-4
These topics describe how to connect an Oracle Exadata Storage Expansion Quarter Rack to your
SPARC SuperCluster T4-4 from Oracle.
Note -
Only one Oracle Exadata Storage Expansion Quarter Rack can be connected to a SPARC SuperCluster T4-4
Half Rack or Full Rack.
The following graphic shows the cable connections from an Oracle Exadata Storage Expansion Quarter Rack to a
SPARC SuperCluster T4-4. The leaf switches within each rack maintain their existing
seven connections. The leaf switches interconnect between the racks with two links
each using the ports reserved for external connectivity.
two or more racks. The following racks can connect to an Oracle Exadata Storage Expansion Quarter Rack:
SPARC SuperCluster T4-4 Half Rack
SPARC SuperCluster T4-4 Full Rack
The racks are interconnected using a fat-tree topology. Each leaf switch in the
Oracle Exadata Storage Expansion Quarter Rack connects to the spine switches in the other Half Racks or Full
Racks with two links each. If there are more than four racks, then use one link
instead of two.
The following terms are used when referring to the two racks:
In addition, because the InfiniBand switches are physically located in different
rack units in the two racks, the following terms are used when referring to the
InfiniBand switches:
InfiniBand 1 (IB1) refers to the spine switch, located in U1 in the
InfiniBand 2 (IB2) refers to the first leaf switch, located in:
InfiniBand 3 (IB3) refers to the second leaf switch, located in U24 in
both racks
The following table shows the cable connections for a single Oracle Exadata Storage Expansion Quarter Rack
to a SPARC SuperCluster T4-4.
Table 89 Leaf Switch Connections for the First Rack in a Two-Rack System
R1-IB3 to Rack 2
R1-IB3-P2A to R2-IB3-P2A
R1-IB3-P2B to R2-IB3-P2B
R1-IB3-P7B to R2-IB2-P7B
R1-IB3-P12A to R2-IB2-P12A
5 meters
R1-IB2 to Rack 2
R1-IB2-P7B to R2-IB3-P7B
R1-IB2-P12A to R2-IB3-P12A
R1-IB2-P2A to R2-IB2-P2A
R1-IB2-P2B to R2-IB2-P2B
5 meters
Connecting an Oracle Exadata Storage Expansion Half Rack or Oracle Exadata Storage Expansion Full Rack to the
These topics describe how to connect an Oracle Exadata Storage Expansion Half Rack or Oracle Exadata Storage Expansion Full Rack to
your SPARC SuperCluster T4-4 from Oracle.
When connecting multiple racks together, remove the seven existing inter-switch
connections between each leaf switches, as well as the two connections between the
leaf switches and the spine switch. From each leaf switch, distribute eight
connections over the spine switches in all racks. In multi-rack environments, the
leaf switches inside a rack are no longer directly interconnected, as shown in the
following graphic.
As shown in the preceding graphic, each leaf switch in rack 1 connects to the
following switches:
The spine switch in rack 1 connects to the following switches:
InfiniBand 1 (IB1) refers to the spine switch, located in U1 in both
racks
both racks
Two-Rack C20abling
The following table shows the cable connections for the first spine switch
(R1-IB1) when cabling two racks together.
Table 90 Leaf Switch Connections for the First Rack in a Two-Rack System
R1-IB3 within Rack 1
R1-IB3-P8A to R1-IB1-P3A
R1-IB3-P8B to R1-IB1-P4A
R1-IB3-P9A to R1-IB1-P5A
R1-IB3-P9B to R1-IB1-P6A
5 meters
R1-IB3 to Rack 2
R1-IB3-P10A to R2-IB1-P7A
R1-IB3-P10B to R2-IB1-P8A
R1-IB3-P11A to R2-IB1-P9A
R1-IB3-P11B to R2-IB1-P10A
5 meters
R1-IB2 within Rack 1
R1-IB2-P8A to R1-IB1-P3B
R1-IB2-P8B to R1-IB1-P4B
R1-IB2-P9A to R1-IB1-P5B
R1-IB2-P9B to R1-IB1-P6B
5 meters
R1-IB2 to Rack 2
R1-IB2-P10A to R2-IB1-P7B
R1-IB2-P10B to R2-IB1-P8B
R1-IB2-P11A to R2-IB1-P9B
R1-IB2-P11B to R2-IB1-P10B
5 meters
The following table shows the cable connections for the second spine switch
(R2-IB1) when cabling two racks together.
Table 91 Leaf Switch Connections for the Second Rack in a Two-Rack System
R2-IB3 within Rack 2
R2-IB3-P8A to R2-IB1-P3A
R2-IB3-P8B to R2-IB1-P4A
R2-IB3-P9A to R2-IB1-P5A
R2-IB3-P9B to R2-IB1-P6A
5 meters
R2-IB3 to Rack 1
R2-IB3-P10A to R1-IB1-P7A
R2-IB3-P10B to R1-IB1-P8A
R2-IB3-P11A to R1-IB1-P9A
R2-IB3-P11B to R1-IB1-P10A
5 meters
R2-IB2 within Rack 2
R2-IB2-P8A to R2-IB1-P3B
R2-IB2-P8B to R2-IB1-P4B
R2-IB2-P9A to R2-IB1-P5B
R2-IB2-P9B to R2-IB1-P6B
5 meters
R2-IB2 to Rack 1
R2-IB2-P10A to R1-IB1-P7B
R2-IB2-P10B to R1-IB1-P8B
R2-IB2-P11A to R1-IB1-P9B
R2-IB2-P11B to R1-IB1-P10B
5 meters
Three-Rack Cabling
(R1-IB1) when cabling three full racks together.
Table 92 Leaf Switch Connections for the First Rack in a Three-Rack System
5 meters
R1-IB3 to Rack 2
R1-IB3-P9B to R2-IB1-P6A
5 meters
R1-IB3 to Rack 3
R1-IB3-P11A to R3-IB1-P9A
R1-IB3-P11B to R3-IB1-P10A
5 meters
5 meters
R1-IB2 to Rack 2
R1-IB2-P9B to R2-IB1-P6B
5 meters
R1-IB2 to Rack 3
R1-IB2-P11A to R3-IB1-P9B
R1-IB2-P11B to R3-IB1-P10B
5 meters
(R2-IB1) when cabling three racks together.
Table 93 Leaf Switch Connections for the Second Rack in a Three-Rack System
5 meters
R2-IB3 to Rack 1
5 meters
R2-IB3 to Rack 3
R2-IB3-P9B to R3-IB1-P6A
R2-IB3-P10A to R3-IB1-P7A
R2-IB3-P10B to R3-IB1-P8A
5 meters
5 meters
R2-IB2 to Rack 1
5 meters
R2-IB2 to Rack 3
R2-IB2-P9B to R3-IB1-P6B
R2-IB2-P10A to R3-IB1-P7B
R2-IB2-P10B to R3-IB1-P8B
5 meters
The following table shows the cable connections for the third spine switch
(R3-IB1) when cabling three full racks together.
Table 94 Leaf Switch Connections for the Third Rack in a Three-Rack System
R3-IB3 within Rack 3
R3-IB3-P8A to R3-IB1-P3A
R3-IB3-P8B to R3-IB1-P4A
R3-IB3-P9A to R3-IB1-P5A
5 meters
R3-IB3 to Rack 1
R3-IB3-P9B to R1-IB1-P6A
R3-IB3-P10A to R1-IB1-P7A
R3-IB3-P10B to R1-IB1-P8A
5 meters
R3-IB3 to Rack 2
R3-IB3-P11A to R2-IB1-P9A
R3-IB3-P11B to R2-IB1-P10A
5 meters
R3-IB2 within Rack 3
R3-IB2-P8A to R3-IB1-P3B
R3-IB2-P8B to R3-IB1-P4B
R3-IB2-P9A to R3-IB1-P5B
5 meters
R3-IB2 to Rack 1
R3-IB2-P9B to R1-IB1-P6B
R3-IB2-P10A to R1-IB1-P7B
R3-IB2-P10B to R1-IB1-P8B
5 meters
R3-IB2 to Rack 2
R3-IB2-P11A to R2-IB1-P9B
R3-IB2-P11B to R2-IB1-P10B
5 meters
Four-Rack Cabling
(R1-IB1) when cabling four full racks together.
Table 95 Leaf Switch Connections for the First Rack in a Four-Rack System
5 meters
R1-IB3 to Rack 2
R1-IB3-P9A to R2-IB1-P5A
5 meters
R1-IB3 to Rack 3
R1-IB3-P10A to R3-IB1-P7A
R1-IB3-P10B to R3-IB1-P8A
5 meters
R1-IB3 to Rack 4
R1-IB3-P11A to R4-IB1-P9A
R1-IB3-P11B to R4-IB1-P10A
10 meters
5 meters
R1-IB2 to Rack 2
R1-IB2-P9A to R2-IB1-P5B
5 meters
R1-IB2 to Rack 3
R1-IB2-P10A to R3-IB1-P7B
R1-IB2-P10B to R3-IB1-P8B
5 meters
R1-IB2 to Rack 4
R1-IB2-P11A to R4-IB1-P9B
R1-IB2-P11B to R4-IB1-P10B
10 meters
(R2-IB1) when cabling four full racks together.
Table 96 Leaf Switch Connections for the Second Rack in a Four-Rack System
5 meters
R2-IB3 to Rack 1
5 meters
R2-IB3 to Rack 3
R2-IB3-P9A to R3-IB1-P5A
5 meters
R2-IB3 to Rack 4
R2-IB3-P10A to R4-IB1-P7A
R2-IB3-P10B to R4-IB1-P8A
5 meters
5 meters
R2-IB2 to Rack 1
5 meters
R2-IB2 to Rack 3
R2-IB2-P9A to R3-IB1-P5B
5 meters
R2-IB2 to Rack 4
R2-IB2-P10A to R4-IB1-P7B
R2-IB2-P10B to R4-IB1-P8B
5 meters
(R3-IB1) when cabling four full racks together.
Table 97 Leaf Switch Connections for the Third Rack in a Four-Rack System
5 meters
R3-IB3 to Rack 1
5 meters
R3-IB3 to Rack 2
5 meters
R3-IB3 to Rack 4
R3-IB3-P9A to R4-IB1-P5A
R3-IB3-P9B to R4-IB1-P6A
5 meters
5 meters
R3-IB2 to Rack 1
5 meters
R3-IB2 to Rack 2
5 meters
R3-IB2 to Rack 4
R3-IB2-P9A to R4-IB1-P5B
R3-IB2-P9B to R4-IB1-P6B
5 meters
The following table shows the cable connections for the fourth spine switch
(R4-IB1) when cabling four full racks together.
Table 98 Leaf Switch Connections for the Fourth Rack in a Four-Rack System
R4-IB3 within Rack 4
R4-IB3-P8A to R4-IB1-P3A
R4-IB3-P8B to R4-IB1-P4A
5 meters
R4-IB3 to Rack 1
R4-IB3-P9A to R1-IB1-P5A
R4-IB3-P9B to R1-IB1-P6A
10 meters
R4-IB3 to Rack 2
R4-IB3-P10A to R2-IB1-P7A
R4-IB3-P10B to R2-IB1-P8A
5 meters
R4-IB3 to Rack 3
R4-IB3-P11A to R3-IB1-P9A
R4-IB3-P11B to R3-IB1-P10A
5 meters
R4-IB2 within Rack 4
R4-IB2-P8A to R4-IB1-P3B
R4-IB2-P8B to R4-IB1-P4B
5 meters
R4-IB2 to Rack 1
R4-IB2-P9A to R1-IB1-P5B
R4-IB2-P9B to R1-IB1-P6B
10 meters
R4-IB2 to Rack 2
R4-IB2-P10A to R2-IB1-P7B
R4-IB2-P10B to R2-IB1-P8B
5 meters
R4-IB2 to Rack 3
R4-IB2-P11A to R3-IB1-P9B
R4-IB2-P11B to R3-IB1-P10B
5 meters
Five-Rack Cabling
(R1-IB1) when cabling five full racks together.
Table 99 Leaf Switch Connections for the First Rack in a Five-Rack System
R1 IB3 within Rack 1
3 meters
R1 IB3 to Rack 2
5 meters
R1 IB3 to Rack 3
5 meters
R1 IB3 to Rack 4
10 meters
R1 IB3 to Rack 5
R1-IB3-P11B to R5-IB1-P10A
10 meters
R1 IB2 within Rack 1
3 meters
R1 IB2 to Rack 2
3 meters
R1 IB2 to Rack 3
5 meters
R1 IB2 to Rack 4
10 meters
R1 IB2 to Rack 5
R1-IB2-P11B to R5-IB1-P10B
10 meters
(R2-IB1) when cabling five full racks together.
Table 100 Leaf Switch Connections for the Second Rack in a Five-Rack System
R2 IB3 within Rack 2
3 meters
R2 IB3 to Rack 1
5 meters
R2 IB3 to Rack 3
5 meters
R2 IB3 to Rack 4
5 meters
R2 IB3 to Rack 5
R2-IB3-P11A to R5-IB1-P9A
10 meters
R2 IB2 within Rack 2
3 meters
R2 IB2 to Rack 1
5 meters
R2 IB2 to Rack 3
5 meters
R2 IB2 to Rack 4
5 meters
R2 IB2 to Rack 5
R2-IB2-P11A to R5-IB1-P9B
10 meters
(R3-IB1) when cabling five full racks together.
Table 101 Leaf Switch Connections for the Third Rack in a Five-Rack System
R3 IB3 within Rack 3
3 meters
R3 IB3 to Rack 1
R3-IB3-P11A to R1-IB1-P9A
5 meters
R3 IB3 to Rack 2
5 meters
R3 IB3 to Rack 4
5 meters
R3 IB3 to Rack 5
R3-IB3-P10A to R5-IB1-P7A
R3-IB3-P10B to R5-IB1-P8A
5 meters
R3 IB2 within Rack 3
3 meters
R3 IB2 to Rack 1
R3-IB2-P11A to R1-IB1-P9B
5 meters
R3 IB2 to Rack 2
5 meters
R3 IB2 to Rack 4
5 meters
R3 IB2 to Rack 5
R3-IB2-P10A to R5-IB1-P7B
R3-IB2-P10B to R5-IB1-P8B
5 meters
(R4-IB1) when cabling five full racks together.
Table 102 Leaf Switch Connections for the Fourth Rack in a Five-Rack System
R4 IB3 within Rack 4
3 meters
R4 IB3 to Rack 1
R4-IB3-P10A to R1-IB1-P7A
R4-IB3-P10B to R1-IB1-P8A
10 meters
R4 IB3 to Rack 2
R4-IB3-P11A to R2-IB1-P9A
5 meters
R4 IB3 to Rack 3
5 meters
R4 IB3 to Rack 5
R4-IB3-P9A to R5-IB1-P5A
R4-IB3-P9B to R5-IB1-P6A
5 meters
R4 IB2 within Rack 4
3 meters
R4 IB2 to Rack 1
R4-IB2-P10A to R1-IB1-P7B
R4-IB2-P10B to R1-IB1-P8B
10 meters
R4 IB2 to Rack 2
R4-IB2-P11A to R2-IB1-P9B
5 meters
R4 IB2 to Rack 3
5 meters
R4 IB2 to Rack 5
R4-IB2-P9A to R5-IB1-P5B
R4-IB2-P9B to R5-IB1-P6B
5 meters
The following table shows the cable connections for the fifth spine switch
(R5-IB1) when cabling five full racks together.
Table 103 Leaf Switch Connections for the Fifth Rack in a Five-Rack System
R5 IB3 within Rack 5
R5-IB3-P8A to R5-IB1-P3A
R5-IB3-P8B to R5-IB1-P4A
3 meters
R5 IB3 to Rack 1
R5-IB3-P9A to R1-IB1-P5A
R5-IB3-P9B to R1-IB1-P6A
10 meters
R5 IB3 to Rack 2
R5-IB3-P10A to R2-IB1-P7A
R5-IB3-P10B to R2-IB1-P8A
10 meters
R5 IB3 to Rack 3
R5-IB3-P11A to R3-IB1-P9A
5 meters
R5 IB3 to Rack 4
R5-IB3-P11B to R4-IB1-P10A
5 meters
R5 IB2 within Rack 5
R5-IB2-P8A to R5-IB1-P3B
R5-IB2-P8B to R5-IB1-P4B
3 meters
R5 IB2 to Rack 1
R5-IB2-P9A to R1-IB1-P5B
R5-IB2-P9B to R1-IB1-P6B
10 meters
R5 IB2 to Rack 2
R5-IB2-P10A to R2-IB1-P7B
R5-IB3-P10B to R2-IB1-P8B
10 meters
R5 IB2 to Rack 3
R5-IB2-P11A to R3-IB1-P9B
5 meters
R5 IB2 to Rack 4
R5-IB2-P11B to R4-IB1-P10B
5 meters
Six-Rack Cabling
(R1-IB1) when cabling six full racks together.
Table 104 Leaf Switch Connections for the First Rack in a Six-Rack System
3 meters
R1 IB3 to Rack 2
5 meters
R1 IB3 to Rack 3
5 meters
R1 IB3 to Rack 4
R1-IB3-P10B to R4-IB1-P8A
10 meters
R1 IB3 to Rack 5
R1-IB3-P11A to R5-IB1-P9A
10 meters
R1 IB3 to Rack 6
R1-IB3-P11B to R6-IB1-P10A
10 meters
3 meters
R1 IB2 to Rack 2
5 meters
R1 IB2 to Rack 3
5 meters
R1 IB2 to Rack 4
R1-IB2-P10B to R4-IB1-P8B
10 meters
R1 IB2 to Rack 5
R1-IB2-P11A to R5-IB1-P9B
10 meters
R1 IB2 to Rack 6
R1-IB2-P11B to R6-IB1-P10B
10 meters
(R2-IB1) when cabling six full racks together.
Table 105 Leaf Switch Connections for the Second Rack in a Six-Rack System
3 meters
R2 IB3 to Rack 1
5 meters
R2 IB3 to Rack 3
5 meters
R2 IB3 to Rack 4
5 meters
R2 IB3 to Rack 5
R2-IB3-P10B to R5-IB1-P8A
10 meters
R2 IB3 to Rack 6
R2-IB3-P11Ato R6-IB1-P9A
10 meters
3 meters
R2 IB2 to Rack 1
5 meters
R2 IB2 to Rack 3
5 meters
R2 IB2 to Rack 4
5 meters
R2 IB2 to Rack 5
R2-IB2-P10B to R5-IB1-P8B
10 meters
R2 IB2 to Rack 6
R2-IB2-P11Ato R6-IB1-P9B
10 meters
(R3-IB1) when cabling six full racks together.
Table 106 Leaf Switch Connections for the Third Rack in a Six-Rack System
3 meters
R3 IB3 to Rack 1
5 meters
R3 IB3 to Rack 2
5 meters
R3 IB3 to Rack 4
5 meters
R3 IB3 to Rack 5
5 meters
R3 IB3 to Rack 6
R3-IB3-P10B to R6-IB1-P8A
5 meters
3 meters
R3 IB2 to Rack 1
5 meters
R3 IB2 to Rack 2
5 meters
R3 IB2 to Rack 4
5 meters
R3 IB2 to Rack 5
5 meters
R3 IB2 to Rack 6
R3-IB2-P10B to R6-IB1-P8B
5 meters
(R4-IB1) when cabling six full racks together.
Table 107 Leaf Switch Connections for the Fourth Rack in a Six-Rack System
3 meters
R4 IB3 to Rack 1
10 meters
R4 IB3 to Rack 2
5 meters
R4 IB3 to Rack 3
5 meters
R4 IB3 to Rack 5
5 meters
R4 IB3 to Rack 6
R4-IB3-P10A to R6-IB1-P7A
5 meters
3 meters
R4 IB2 to Rack 1
10 meters
R4 IB2 to Rack 2
5 meters
R4 IB2 to Rack 3
5 meters
R4 IB2 to Rack 5
5 meters
R4 IB2 to Rack 6
R4-IB2-P10A to R6-IB1-P7B
5 meters
(R5-IB1) when cabling six full racks together.
Table 108 Leaf Switch Connections for the Fifth Rack in a Six-Rack System
3 meters
R5 IB3 to Rack 1
R5-IB3-P10A to R1-IB1-P7A
10 meters
R5 IB3 to Rack 2
10 meters
R5 IB3 to Rack 3
5 meters
R5 IB3 to Rack 4
5 meters
R5 IB3 to Rack 6
R5-IB3-P9A to R6-IB1-P5A
R5-IB3-P9B to R6-IB1-P6A
5 meters
3 meters
R5 IB2 to Rack 1
R5-IB2-P10A to R1-IB1-P7B
10 meters
R5 IB2 to Rack 2
10 meters
R5 IB2 to Rack 3
5 meters
R5 IB2 to Rack 4
5 meters
R5 IB2 to Rack 6
R5-IB2-P9A to R6-IB1-P5B
R5-IB2-P9B to R6-IB1-P6B
5 meters
The following table shows the cable connections for the sixth spine switch
(R6-IB1) when cabling six full racks together.
Table 109 Leaf Switch Connections for the Sixth Rack in a Six-Rack System
R6 IB3 within Rack 6
R6-IB3-P8A to R6-IB1-P3A
R6-IB3-P8B to R6-IB1-P4A
3 meters
R6 IB3 to Rack 1
R6-IB3-P9A to R1-IB1-P5A
R6-IB3-P9B to R1-IB1-P6A
10 meters
R6 IB3 to Rack 2
R6-IB3-P10A to R2-IB1-P7A
10 meters
R6 IB3 to Rack 3
R6-IB3-P10B to R3-IB1-P8A
5 meters
R6 IB3 to Rack 4
R6-IB3-P11A to R4-IB1-P9A
5 meters
R6 IB3 to Rack 5
R6-IB3-P11B to R5-IB1-P10A
5 meters
R6 IB2 within Rack 6
R6-IB2-P8A to R6-IB1-P3B
R6-IB2-P8B to R6-IB1-P4B
3 meters
R6 IB2 to Rack 2
R6-IB3-P10A to R2-IB1-P7B
10 meters
R6 IB2 to Rack 1
R6-IB2-P9A to R1-IB1-P5B
R6-IB2-P9B to R1-IB1-P6B
10 meters
R6 IB2 to Rack 3
R6-IB2-P10B to R3-IB1-P8B
5 meters
R6 IB2 to Rack 4
R6-IB2-P11A to R4-IB1-P9B
5 meters
R6 IB2 to Rack 5
R6-IB2-P11B to R5-IB1-P10B
5 meters
Seven-Rack Cabling
(R1-IB1) when cabling seven full racks together.
Table 110 Leaf Switch Connections for the First Rack in a Seven-Rack System
3 meters
R1 IB3 to Rack 2
5 meters
R1 IB3 to Rack 3
R1-IB3-P9B to R3-IB1-P6A
5 meters
R1 IB3 to Rack 4
R1-IB3-P10A to R4-IB1-P7A
10 meters
R1 IB3 to Rack 5
R1-IB3-P10B to R5-IB1-P8A
10 meters
R1 IB3 to Rack 6
R1-IB3-P11A to R6-IB1-P9A
10 meters
R1 IB3 to Rack 7
R1-IB3-P11B to R7-IB1-P10A
10 meters
3 meters
R1 IB2 to Rack 2
5 meters
R1 IB2 to Rack 3
R1-IB2-P9B to R3-IB1-P6B
5 meters
R1 IB2 to Rack 4
R1-IB2-P10A to R4-IB1-P7B
10 meters
R1 IB2 to Rack 5
R1-IB2-P10B to R5-IB1-P8B
10 meters
R1 IB2 to Rack 6
R1-IB2-P11A to R6-IB1-P9B
10 meters
R1 IB2 to Rack 7
R1-IB2-P11B to R7-IB1-P10B
10 meters
(R2-IB1) when cabling seven full racks together.
Table 111 Leaf Switch Connections for the Second Rack in a Seven-Rack System
3 meters
R2 IB3 to Rack 1
5 meters
R2 IB3 to Rack 3
5 meters
R2 IB3 to Rack 4
R2-IB3-P9B to R4-IB1-P6A
5 meters
R2 IB3 to Rack 5
R2-IB3-P10A to R5-IB1-P7A
10 meters
R2 IB3 to Rack 6
R2-IB3-P10B to R6-IB1-P8A
10 meters
R2 IB3 to Rack 7
R2-IB3-P11A to R7-IB1-P9A
10 meters
3 meters
R2 IB2 to Rack 1
5 meters
R2 IB2 to Rack 3
5 meters
R2 IB2 to Rack 4
R2-IB2-P9B to R4-IB1-P6B
5 meters
R2 IB2 to Rack 5
R2-IB2-P10A to R5-IB1-P7B
10 meters
R2 IB2 to Rack 6
R2-IB2-P10Bto R6-IB1-P8B
10 meters
R2 IB2 to Rack 7
R2-IB2-P11A to R7-IB1-P9B
10 meters
(R3-IB1) when cabling seven full racks together.
Table 112 Leaf Switch Connections for the Third Rack in a Seven-Rack System
3 meters
R3 IB3 to Rack 1
5 meters
R3 IB3 to Rack 2
5 meters
R3 IB3 to Rack 4
5 meters
R3 IB3 to Rack 5
R3-IB3-P9B to R5-IB1-P6A
5 meters
R3 IB3 to Rack 6
R3-IB3-P10A to R6-IB1-P7A
10 meters
R3 IB3 to Rack 7
R3-IB3-P10B to R7-IB1-P8A
10 meters
3 meters
R3 IB2 to Rack 1
5 meters
R3 IB2 to Rack 2
5 meters
R3 IB2 to Rack 4
5 meters
R3 IB2 to Rack 5
R3-IB2-P9B to R5-IB1-P6B
5 meters
R3 IB2 to Rack 6
R3-IB2-P10A to R6-IB1-P7B
10 meters
R3 IB2 to Rack 7
R3-IB2-P10B to R7-IB1-P8B
10 meters
(R4-IB1) when cabling seven full racks together.
Table 113 Leaf Switch Connections for the Fourth Rack in a Seven-Rack System
3 meters
R4 IB3 to Rack 1
10 meters
R4 IB3 to Rack 2
5 meters
R4 IB3 to Rack 3
5 meters
R4 IB3 to Rack 5
5 meters
R4 IB3 to Rack 6
R4-IB3-P9B to R6-IB1-P6A
5 meters
R4 IB3 to Rack 7
R4-IB3-P10A to R7-IB1-P7A
10 meters
3 meters
R4 IB2 to Rack 1
10 meters
R4 IB2 to Rack 2
5 meters
R4 IB2 to Rack 3
5 meters
R4 IB2 to Rack 5
5 meters
R4 IB2 to Rack 6
R4-IB2-P9B to R6-IB1-P6B
5 meters
R4 IB2 to Rack 7
R4-IB2-P10A to R7-IB1-P7B
10 meters
(R5-IB1) when cabling seven full racks together.
Table 114 Leaf Switch Connections for the Fifth Rack in a Seven-Rack System
3 meters
R5 IB3 to Rack 1
10 meters
R5 IB3 to Rack 2
10 meters
R5 IB3 to Rack 3
5 meters
R5 IB3 to Rack 4
5 meters
R5 IB3 to Rack 6
5 meters
R5 IB3 to Rack 7
R5-IB3-P9B to R7-IB1-P6A
5 meters
3 meters
R5 IB2 to Rack 1
10 meters
R5 IB2 to Rack 2
10 meters
R5 IB2 to Rack 3
5 meters
R5 IB2 to Rack 4
5 meters
R5 IB2 to Rack 6
5 meters
R5 IB2 to Rack 7
R5-IB2-P9B to R7-IB1-P6B
5 meters
(R6-IB1) when cabling seven full racks together.
Table 115 Leaf Switch Connections for the Sixth Rack in a Seven-Rack System
3 meters
R6 IB3 to Rack 1
10 meters
R6 IB3 to Rack 2
10 meters
R6 IB3 to Rack 3
5 meters
R6 IB3 to Rack 4
5 meters
R6 IB3 to Rack 5
5 meters
R6 IB3 to Rack 7
R6-IB3-P9A to R7-IB1-P5A
5 meters
3 meters
R6 IB2 to Rack 1
10 meters
R6 IB2 to Rack 2
10 meters
R6 IB2 to Rack 3
5 meters
R6 IB2 to Rack 4
5 meters
R6 IB2 to Rack 5
5 meters
R6 IB2 to Rack 7
R6-IB3-P9A to R7-IB1-P5B
5 meters
The following table shows the cable connections for the seventh spine switch
(R7-IB1) when cabling seven full racks together.
Table 116 Leaf Switch Connections for the Seventh Rack in a Seven-Rack System
R7 IB3 within Rack 7
R7-IB3-P8A to R7-IB1-P3A
R7-IB3-P8B to R7-IB1-P4A
3 meters
R7 IB3 to Rack 1
R7-IB3-P9A to R1-IB1-P5A
10 meters
R7 IB3 to Rack 2
R7-IB3-P9B to R2-IB1-P6A
10 meters
R7 IB3 to Rack 3
R7-IB3-P10A to R3-IB1-P7A
10 meters
R7 IB3 to Rack 4
R7-IB3-P10B to R4-IB1-P8A
10 meters
R7 IB3 to Rack 5
R7-IB3-P11A to R5-IB1-P9A
5 meters
R7 IB3 to Rack 6
R7-IB3-P11B to R6-IB1-P10A
5 meters
R7 IB2 within Rack 7
R7-IB2-P8A to R7-IB1-P3B
R7-IB2-P8B to R7-IB1-P4B
3 meters
R7 IB2 to Rack 1
R7-IB2-P9A to R1-IB1-P5B
10 meters
R7 IB2 to Rack 2
R7-IB3-P9B to R2-IB1-P6B
10 meters
R7 IB2 to Rack 3
R7-IB2-P10A to R3-IB1-P7B
10 meters
R7 IB2 to Rack 4
R7-IB2-P10B to R4-IB1-P8B
10 meters
R7 IB2 to Rack 5
R7-IB2-P11A to R5-IB1-P9B
5 meters
R7 IB2 to Rack 6
R7-IB3-P11B to R6-IB1-P10B
5 meters
Eight-Rack Cabling
(R1-IB1) when cabling eight full racks together.
Table 117 Leaf Switch Connections for the First Rack in an Eight-Rack System
3 meters
R1 IB3 to Rack 2
R1-IB3-P8B to R2-IB1-P4A
5 meters
R1 IB3 to Rack 3
R1-IB3-P9A to R3-IB1-P5A
5 meters
R1 IB3 to Rack 4
R1-IB3-P9B to R4-IB1-P6A
10 meters
R1 IB3 to Rack 5
R1-IB3-P10A to R5-IB1-P7A
10 meters
R1 IB3 to Rack 6
R1-IB3-P10B to R6-IB1-P8A
10 meters
R1 IB3 to Rack 7
R1-IB3-P11A to R7-IB1-P9A
10 meters
R1 IB3 to Rack 8
R1-IB3-P11B to R8-IB1-P10A
10 meters
3 meters
R1 IB2 to Rack 2
R1-IB2-P8B to R2-IB1-P4B
5 meters
R1 IB2 to Rack 3
R1-IB2-P9A to R3-IB1-P5B
5 meters
R1 IB2 to Rack 4
R1-IB2-P9B to R4-IB1-P6B
10 meters
R1 IB2 to Rack 5
R1-IB2-P10A to R5-IB1-P7B
10 meters
R1 IB2 to Rack 6
R1-IB2-P10B to R6-IB1-P8B
10 meters
R1 IB2 to Rack 7
R1-IB2-P11A to R7-IB1-P8B
10 meters
R1 IB2 to Rack 8
R1-IB2-P11B to R8-IB1-P10B
10 meters
(R2-IB1) when cabling eight full racks together.
Table 118 Leaf Switch Connections for the Second Rack in an Eight-Rack System
3 meters
R2 IB3 to Rack 1
5 meters
R2 IB3 to Rack 3
R2-IB3-P8B to R3-IB1-P4A
5 meters
R2 IB3 to Rack 4
R2-IB3-P9A to R4-IB1-P5A
5 meters
R2 IB3 to Rack 5
R2-IB3-P9B to R5-IB1-P6A
10 meters
R2 IB3 to Rack 6
R2-IB3-P10A to R6-IB1-P7A
10 meters
R2 IB3 to Rack 7
R2-IB3-P10B to R7-IB1-P8A
10 meters
R2 IB3 to Rack 8
R2-IB3-P11A to R8-IB1-P9A
10 meters
3 meters
R2 IB2 to Rack 1
5 meters
R2 IB2 to Rack 3
R2-IB2-P8B to R3-IB1-P4B
5 meters
R2 IB2 to Rack 4
R2-IB2-P9A to R4-IB1-P5B
5 meters
R2 IB2 to Rack 5
R2-IB2-P9B to R5-IB1-P6B
10 meters
R2 IB2 to Rack 6
R2-IB2-P10A to R6-IB1-P7B
10 meters
R2 IB2 to Rack 7
R2-IB2-P10B to R7-IB1-P8B
10 meters
R2 IB2 to Rack 8
R2-IB2-P11A to R8-IB1-P9B
10 meters
(R3-IB1) when cabling eight full racks together.
Table 119 Leaf Switch Connections for the Third Rack in an Eight-Rack System
3 meters
R3 IB3 to Rack 1
5 meters
R3 IB3 to Rack 2
5 meters
R3 IB3 to Rack 4
R3-IB3-P8B to R4-IB1-P4A
5 meters
R3 IB3 to Rack 5
R3-IB3-P9A to R5-IB1-P5A
5 meters
R3 IB3 to Rack 6
R3-IB3-P9B to R6-IB1-P6A
5 meters
R3 IB3 to Rack 7
R3-IB3-P10A to R7-IB1-P7A
10 meters
R3 IB3 to Rack 8
R3-IB3-P10B to R8-IB1-P8A
10 meters
3 meters
R3 IB2 to Rack 1
5 meters
R3 IB2 to Rack 2
5 meters
R3 IB2 to Rack 4
R3-IB2-P8B to R4-IB1-P4B
5 meters
R3 IB2 to Rack 5
R3-IB2-P9A to R5-IB1-P5B
5 meters
R3 IB2 to Rack 6
R3-IB2-P9B to R6-IB1-P6B
5 meters
R3 IB2 to Rack 7
R3-IB2-P10A to R7-IB1-P7B
10 meters
R3 IB2 to Rack 8
R3-IB2-P10B to R8-IB1-P8B
10 meters
(R4-IB1) when cabling eight full racks together.
Table 120 Leaf Switch Connections for the Fourth Rack in an Eight-Rack System
3 meters
R4 IB3 to Rack 1
10 meters
R4 IB3 to Rack 2
5 meters
R4 IB3 to Rack 3
5 meters
R4 IB3 to Rack 5
R4-IB3-P8B to R5-IB1-P4A
5 meters
R4 IB3 to Rack 6
R4-IB3-P9A to R6-IB1-P5A
5 meters
R4 IB3 to Rack 7
R4-IB3-P9B to R7-IB1-P6A
10 meters
R4 IB3 to Rack 8
R4-IB3-P10A to R8-IB1-P7A
10 meters
3 meters
R4 IB2 to Rack 1
10 meters
R4 IB2 to Rack 2
5 meters
R4 IB2 to Rack 3
5 meters
R4 IB2 to Rack 5
R4-IB2-P8B to R5-IB1-P4B
5 meters
R4 IB2 to Rack 6
R4-IB2-P9A to R6-IB1-P5B
5 meters
R4 IB2 to Rack 7
R4-IB2-P9B to R7-IB1-P6B
10 meters
R4 IB2 to Rack 8
R4-IB2-P10A to R8-IB1-P7B
10 meters
(R5-IB1) when cabling eight full racks together.
Table 121 Leaf Switch Connections for the Fifth Rack in an Eight-Rack System
3 meters
R5 IB3 to Rack 1
10 meters
R5 IB3 to Rack 2
10 meters
R5 IB3 to Rack 3
5 meters
R5 IB3 to Rack 4
5 meters
R5 IB3 to Rack 6
R5-IB3-P8B to R6-IB1-P4A
5 meters
R5 IB3 to Rack 7
R5-IB3-P9A to R7-IB1-P5A
5 meters
R5 IB3 to Rack 8
R5-IB3-P9B to R8-IB1-P6A
10 meters
3 meters
R5 IB2 to Rack 1
10 meters
R5 IB2 to Rack 2
10 meters
R5 IB2 to Rack 3
5 meters
R5 IB2 to Rack 4
5 meters
R5 IB2 to Rack 6
R5-IB2-P8B to R6-IB1-P4B
5 meters
R5 IB2 to Rack 7
R5-IB2-P9A to R7-IB1-P5B
5 meters
R5 IB2 to Rack 8
R5-IB2-P9B to R8-IB1-P6B
10 meters
(R6-IB1) when cabling eight full racks together.
Table 122 Leaf Switch Connections for the Sixth Rack in an Eight-Rack System
3 meters
R6 IB3 to Rack 1
10 meters
R6 IB3 to Rack 2
10 meters
R6 IB3 to Rack 3
5 meters
R6 IB3 to Rack 4
5 meters
R6 IB3 to Rack 5
5 meters
R6 IB3 to Rack 7
R6-IB3-P8B to R7-IB1-P4A
5 meters
R6 IB3 to Rack 8
R6-IB3-P9A to R8-IB1-P5A
5 meters
3 meters
R6 IB2 to Rack 1
10 meters
R6 IB2 to Rack 2
10 meters
R6 IB2 to Rack 3
5 meters
R6 IB2 to Rack 4
5 meters
R6 IB2 to Rack 5
5 meters
R6 IB2 to Rack 7
R6-IB3-P8B to R7-IB1-P4B
5 meters
R6 IB2 to Rack 8
R6-IB2-P9A to R8-IB1-P5B
5 meters
(R7-IB1) when cabling eight full racks together.
Table 123 Leaf Switch Connections for the Seventh Rack in an Eight-Rack System
3 meters
R7 IB3 to Rack 1
10 meters
R7 IB3 to Rack 2
10 meters
R7 IB3 to Rack 3
10 meters
R7 IB3 to Rack 4
10 meters
R7 IB3 to Rack 5
5 meters
R7 IB3 to Rack 6
5 meters
R7 IB3 to Rack 8
R7-IB3-P8B to R8-IB1-P4A
5 meters
3 meters
R7 IB2 to Rack 1
10 meters
R7 IB2 to Rack 2
10 meters
R7 IB2 to Rack 3
10 meters
R7 IB2 to Rack 4
10 meters
R7 IB2 to Rack 5
5 meters
R7 IB2 to Rack 6
5 meters
R7 IB2 to Rack 8
R7-IB3-P8B to R8-IB1-P4B
5 meters
The following table shows the cable connections for the eighth spine switch
(R8-IB1) when cabling eight full racks together.
Table 124 Leaf Switch Connections for the Eighth Rack in an Eight-Rack System
R8 IB3 within Rack 8
R8-IB3-P8A to R8-IB1-P3A
3 meters
R8 IB3 to Rack 1
R8-IB3-P8B to R1-IB1-P4A
10 meters
R8 IB3 to Rack 2
R8-IB3-P9A to R2-IB1-P5A
10 meters
R8 IB3 to Rack 3
R8-IB3-P9B to R3-IB1-P6A
10 meters
R8 IB3 to Rack 4
R8-IB3-P10A to R4-IB1-P7A
10 meters
R8 IB3 to Rack 5
R8-IB3-P10B to R5-IB1-P8A
5 meters
R8 IB3 to Rack 6
R8-IB3-P11A to R6-IB1-P9A
5 meters
R8 IB3 to Rack 7
R8-IB3-P11B to R7-IB1-P10A
5 meters
R8 IB2 within Rack 8
R8-IB2-P8A to R8-IB1-P3B
3 meters
R8 IB2 to Rack 1
R8-IB2-P8B to R1-IB1-P4B
10 meters
R8 IB2 to Rack 2
R8-IB3-P9A to R2-IB1-P5B
10 meters
R8 IB2 to Rack 3
R8-IB2-P9B to R3-IB1-P6B
10 meters
R8 IB2 to Rack 4
R8-IB2-P10A to R4-IB1-P7B
10 meters
R8 IB2 to Rack 5
R8-IB2-P10B to R5-IB1-P8B
5 meters
R8 IB2 to Rack 6
R8-IB3-P11A to R6-IB1-P9B
5 meters
R8 IB2 to Rack 7
R8-IB3-P1B to R7-IB1-P10B
5 meters