PDU Power
Requirements
When ordering the system you selected one of these options:
Refer to the following tables for Oracle marketing and manufacturing
part numbers.
Note - Each system has two power distribution units (PDUs).
Both PDUs in a rack must be the same type.
Table 6 PDU Choices
Low |
2 |
Low |
3 |
High |
1 |
High |
3 |
Table 7 Low Voltage 2 Phase PDUs
kVA Size |
22 kVA |
Marketing part number |
7100873 |
Manufacturing part number |
7018123 |
Phase |
2 |
No Grounded Neutral provided in input
cords |
Voltage input rating |
3x [2Ph. (2W+ground)] 208 Vac, 50/60
Hz, max. 36.8A per phase |
Can be connected to Ph-Ph input sources
in range of 200V - 240V AC nominal |
Amps per PDU |
110.4A (3 inputs x 36.8A) |
Outlets |
42 C13
6 C19 |
Number of inputs |
3 inputs x50A plug, 2Ph (2W+ground) |
3 inputs/plugs per PDU, or 6 total inputs/plugs
for system |
Input current |
36.8A max. current (per input) |
Data center receptacle |
Hubbell CS8264C |
Outlet groups per PDU |
6 |
Usable PDU power cord length |
2 m (6.6 feet) |
PDU power cords are 4 m long (13 feet),
but sections are used for internal routing in the rack. |
Summary: |
Number of PDUs in Oracle SuperCluster T5-8:
2 |
Number of circuits per PDU:
3 @ 50A 2-phase 208V |
Total number of circuits
required: 6 @ 50A 2-phase 208V (2 per PDU) |
Total number of data center
receptacles required: 6 x Hubbell CS8264C |
Total Amps per PDU: 110.4A
2-phase 208V |
Total Amps for entire Oracle SuperCluster T5-8:
220.8A 2-phase 208V (2 PDUs @ 110.4A 2-phase 208V each) |
Table 8 Low Voltage 3 Phase PDUs
kVA Size |
24 kVA |
6444A |
597-1162-01 |
Phase |
3 |
cords |
2x [3Ph. (3W+ground)] 208 Vac, 50/60
Hz, max. 34.6A per phase |
in range of 190V - 220V AC nominal |
Amps per PDU |
120A (3 x 20A) |
Outlets |
42 C13
6 C19 |
Number of inputs |
2 inputs x 60A plug, 3 ph (3W+GND) |
2 inputs/plugs per PDU,
or 4 total inputs/plugs for system |
Input current |
34.6 A max. per phase |
IEC 309-3P4W-IP67 |
(60A, 250V, AC, 3Ph) |
6 |
2 m (6.6 feet) |
Summary: |
2 |
2 @ 60A 3-phase 208V |
required: 4 @ 60A 3-phase 208V (2 per PDU) |
receptacles required: 4 x IEC 309-3P4W-IP67 |
Total Amps per PDU: 120A
3-phase 208V |
240A 3-phase 208V (2 PDUs @ 120A 3-phase 208V each) |
Table 9 High Voltage 1 Phase PDUs
kVA Size |
22 kVA |
7100874 |
7018124 |
Phase |
1 |
3x [1Ph. (2W+ground)] 230 Vac, 50 Hz,
max. 32A per phase |
Can be connected to Ph-N input sources
in range of 220V - 240V AC nominal |
Amps per PDU |
96A (3 inputs x 32A) |
Outlets |
42 C13
6 C19 |
Number of inputs |
3 inputs x 32A plug, 1Ph (2W+ground) |
or 6 total inputs/plugs for system |
Input current |
32A max. current (per input) |
IEC 309-2P3W-IP44 |
6 |
2 m (6.6 feet) |
Summary: |
2 |
3 @ 32A 1-phase 230V |
required: 6 @ 32A 1-phase 230V (2 per PDU) |
receptacles required: 6 x IEC 309-2P3W-IP44 |
Total Amps per PDU: 96A
1-phase 230V |
192A 1-phase 230V (2 PDUs @ 96A 1-phase 230V each) |
Table 10 High Voltage 3 Phase PDUs
kVA Size |
24 kVA |
6445A |
597-1163-01 |
Phase |
3 |
2x [3Ph. (4W+ground)] 230/400 Vac, 50/60
Hz, max. 18A per phase |
Amps per PDU |
109A (6 inputs x 18.1A) |
Outlets |
42 C13
6 C19 |
Number of inputs |
2 inputs x25A plug, 3 ph (4W+GND) |
Input current |
18 A max. per phase |
IEC 309-4P5W-IP44 |
(32A, 400V, AC, 3Ph) |
6 |
2 m (6.6 feet) |
Summary: |
2 |
2 @ 25A 3-phase 230/400V |
required: 4 @ 25A 3-phase 230/400V (2 per PDU) |
receptacles required: 4 x IEC 309-4P5W-IP44 |
Total Amps per PDU: 109A
3-phase 230/400V |
218A 3-phase 230/400V (2 PDUs @ 109A 3-phase 230/400V each) |