SuperCluster M8 and SuperCluster M7 PDU Power Specifications
When ordering SuperCluster M8 or SuperCluster M7, you must provide two
specifications for the racks:
Use one of these tables to identify the PDU power specifications for your type of
rack.
Table 10 Low-Voltage, Single-Phase PDUs
Voltage
200 to 240 VAC
Frequency
50/60 Hz
Current
35.4A max. per input
Power rating
22 kVA
Output current
120A (6 x 20A)
Outlets
42 x C13, 6 x C19
Outlet groups
6
Group protection (UL489 2-pole circuit breaker)
20A
Datacenter receptacle
Hubbell CS8264C
Number of inputs
3 x 50A 1ph
Table 11 Low-Voltage, Three-Phase PDUs
Voltage
200 to 208 VAC 3ph
Frequency
50/60 Hz
Current
34.6A max. per phase
Power rating
25 kVA
Output current
120A (6 x 20A)
Outlets
42 x C13, 6 x C19
Outlet groups
6
20A
IEC309 60A 4-pin 250VAC 3ph IP67
Number of inputs
2 x 60A 3ph
Table 12 High-Voltage, Single-Phase PDUs
Voltage
220 to 240 VAC
Frequency
50/60 Hz
Current
32A maximum per input
Power rating
22 kVA
Output current
96A (3 x 32A)
Outlets
42 x C13, 6 x C19
Outlet groups
6
Group protection (UL489 1-pole circuit breaker)
20A
IEC 60309 32A with 3-pin 250 VAC IP44
Number of inputs
3x32A 1ph
Table 13 High-Voltage, Three-Phase PDUs
Voltage
220/380 to 240/415 VAC 3ph
Frequency
50/60 Hz
Current
18A maximum per input
Power rating
25 kVA
Output current
109A (6 x 18.1A)
Outlets
42 x C13, 6 x C19
Outlet groups
6
20A
IEC309 32A 5-pin 230/400V 3ph IP44
Number of inputs
2 x 25A 3ph