Airflow Requirements
In order to cool the system properly, ensure that adequate airflow travels through
the racks.
 | Caution -
Do not restrict the movement of cool air from the air conditioner to the rack,
or the movement of hot air out of the rear of the rack.
Observe these requirements:
Allow a minimum clearance of 48.5 inches (1232 mm) at the front of the rack, and 36 inches (914 mm) at the rear of the rack for ventilation. There is no airflow requirement for the left and right sides, or the top of the rack.
If the rack is not completely filled with components, cover the empty
sections with filler panels.
Figure 1 Direction of Airflow Is Front to Back
Table 27 SuperCluster M8 Airflow
Single compute server with 3 storage servers
Maximum
Typical
2,082
1,658
Single compute server with 11 storage servers
Maximum
Typical
2,852
2,252
Dual compute server with 6 storage servers
Maximum
Typical
3,773
2,965
Table 28 SuperCluster M7 Airflow
Maximum
Typical
2,010
1,400
Maximum
Typical
2,642
2,141
Dual compute server with 3 storage servers
Maximum
Typical
3,369
2,865
Maximum
Typical
3,605
3,014
Table 29 Expansion Rack Airflow
Expansion rack, EF quarter rack
Maximum
Typical
572
401
Expansion rack, HC quarter rack
Maximum
Typical
533
373
Individual EF storage server
Maximum
Typical
94
66
Individual HC storage server
Maximum
Typical
85
59