Go to main content
oracle home
Oracle
SuperCluster M8 and SuperCluster M7 Installation Guide
Exit Print View
Search Term
Search Scope:
This Document
Entire Library
Documentation Home
Oracle SuperCluster M8 and SuperCluster M7 ...
Oracle
SuperCluster M8 and ...
Preparing the Site
Reviewing Power Requirements
Reviewing PDU Thresholds
PDU Thresholds (Dual-Server Model With 6 ...
Updated: January 2019
Oracle
Document Information
Using This Documentation
Product Documentation Library
Feedback
Installing SuperCluster M8 and SuperCluster M7 Systems
Hardware Installation Task Overview
Hardware Installation Documents
Single-Server Hardware Overview
Dual-Server Hardware Overview
Spares Kit
Preparing the Site
Prepare the Site
Physical Specifications (SuperCluster M8 and Expansion Rack)
Physical Specifications (SuperCluster M7 and Expansion Rack)
Power Consumption
Facility Power Requirements
Grounding Requirements
SuperCluster M8 and SuperCluster M7 PDU Power Specifications
Expansion Rack PDU Power Specifications
Circuit Breaker Requirements
Grounding Guidelines
PDU Thresholds (Single- and Dual-Server Models With 3 Storage Servers)
PDU Thresholds (Single-Server Model With 11 Storage Servers)
PDU Thresholds (Dual-Server Model With 6 Storage Servers)
Preparing for Cooling
Heat Dissipation Specifications
Airflow Requirements
Perforated Floor Tiles
Environmental Specifications
Preparing the Networks
Network Topology
Network Infrastructure Requirements
Installing Optional Fibre Channel PCIe Cards
Fibre Channel PCIe Card Overview
Install Optional Fibre Channel PCIe Cards
Prepare DNS
Cabling SuperCluster
SuperCluster Rack Components
Connect SuperCluster to the Facility Networks
Compute Server Cabled Components
Storage Server Cabled Components
X6-2L Storage Server (SuperCluster M7)
X7-2L Storage Server (SuperCluster M8)
Power Cabling (Single Phase)
Power Cabling (Three Phase)
Leaf Switch Cabling (Single Server)
Leaf Switch Cabling (Dual Servers)
IB Switch-to-Switch Cabling Reference
Ethernet Management Switch Cabling Reference
ZFS Storage Appliance Cabling
ZS3-ES Cabling Reference (SuperCluster M7)
ZS5-ES Cabling Reference (SuperCluster M8)
Connecting Multiple SuperCluster M8 or SuperCluster M7 Systems
Multirack Cabling Overview
Connect Additional SuperCluster M8 or SuperCluster M7 Racks
Two-Rack Cabling
Three-Rack Cabling
Four-Rack Cabling
Five-Rack Cabling
Six-Rack Cabling
Seven-Rack Cabling
Eight-Rack Cabling
Connecting Expansion Racks
Expansion Rack Overview
Expansion Rack Components
Install Expansion Racks
Cabling Multiple Expansion Racks
One Expansion Rack Cabling
Two Expansion Racks Cabling
Three Expansion Racks Cabling
Four Expansion Racks Cabling
Five Expansion Racks Cabling
Six Expansion Racks Cabling
Seven Expansion Racks Cabling
Expansion Rack Default IP Addresses
Glossary
Index
Index A
Index C
Index D
Index E
Index F
Index G
Index H
Index I
Index M
Index N
Index O
Index P
Index S
Index T
Index Z
Language:
English
Table 22
22 kVA Single-Phase PDUs
Low Voltage
Low Voltage
High Voltage
High Voltage
PDU A
PDU B
Warning (Amps)
Alarm (Amps)
Warning (Amps)
Alarm (Amps)
M1-3
M1-1
28
36
26
32
M1-2
M1-2
27
35
25
32
M1-1
M1-3
29
36
26
32
Table 23
24 kVA 3-Phase PDUs
Low Voltage
Low Voltage
High Voltage
High Voltage
PDU A
PDU B
Warning (Amps)
Alarm (Amps)
Warning (Amps)
Alarm (Amps)
M2-3
M1-3
25
31
13
17
M2-2
M1-2
25
32
13
17
M2-1
M1-1
25
32
14
18
M1-3
M2-3
24
31
13
16
M1-2
M2-2
24
30
13
17
M1-1
M2-1
23
30
12
16