Monitor the Enhanced PDU (HTML Interface)
Using the metering unit's HTML interface, you can monitor how much power,
energy, and current the equipment attached to the PDU uses, as well as the
voltage level powering the equipment. The reported voltage for 3ph PDUs is L-N
for HV PDUs and L-G for LV PDUs. The reported voltage for 1ph PDUs is L-N for HV
PDUs and L-L for LV PDUs. You can see how the current and voltage readings
relate to the threshold parameters you set in Set Threshold Parameter Values (Enhanced PDU).
Access the PDU metering unit from a system on the network.
See Access a Metering Unit on the Network (Enhanced PDU). After accessing the
PDU, the Metering Overview page displays.
View the Metering Overview page.
The following figure shows an example
Metering Overview page for a 24kVA PDU, which has two inputs
with three phases each. See Understanding the Relationship Between Inputs and Outlet Groups for a description of PDU inputs.
The following figure displays the details of the current measurement of an
example single PDU input.
1
2
Phase number
3
State
4
Graph displaying the amps of current being
used per phase
5
Number of amps of current being used per phase
6
Voltage level applied per phase
7
Amount of active power being used per phase
8
Amount of apparent power being used per phase
9
Energy level being used per phase
The black vertical bar indicates the current used by the attached
equipment. The color behind the line is determined by the threshold
parameter values. If you set voltage threshold parameter values, the
background of the voltage color indicates the state of the voltage powering
the equipment. For more information on threshold limits, see Set Threshold Parameter Values (Enhanced PDU).
Note -
The Enhanced PDU supports both, 10/100 Full Duplex and 10/100 Half
Duplex as well as auto-negotiation as defined in IEEE802.3u. If the
switch port supports auto-negotiation the Enhanced PDU will configure
itself to the fastest speed supported by the switch. If a specific mode
of operation is needed the switch port needs to be configured to the
specific mode of operation.
Blue
Measured current is below Info threshold.
Attached equipment is using less current
than expected.
Green
Measured current is between the Info and Warning
thresholds.
Attached equipment is using the expected amount of
current.
Yellow
Measured current is above the Warning threshold, but
below the Alarm threshold.
Attached equipment is using more current than
expected.
Red
Measured current is above the Alarm
threshold.
Attached equipment is using a critical amount of
current and requires immediate attention.
Flashing bar with red text
Out of Balance threshold. Also, a blinking
red “Out of Balance” message displays above
the input graph.
The equipment attached to one phase is using more
current than the other phases on the input. The PDU and
attached equipment require immediate attention.
![Caution Caution](graphics/hot.gif) | Caution -
If the PDU is out of balance, the PDU and the attached equipment might
heat up and cause serious damage to the equipment, PDU, and the rack.
Power off the equipment and the PDU immediately.
If you set voltage thresholds parameter values, the background of the
voltage color indicates the state of the voltage powering the equipment. See
the following table for a description of these colors.
Green
Measured Voltage is above Warning threshold.
Attached equipment is operating with an expected
voltage level.
Yellow
Measured Voltage is between Warning and Alarm
threshold.
Attached equipment is operating at an allowable
voltage level.
Red
Measured Voltage is below Alarm
threshold.
Attached equipment might not operate as
expected.
![Caution Caution](graphics/caution.gif) | Caution -
If the PDU input voltage is below the Alarm level, the attached
equipment (and PDU) might be damaged. Power off the equipment and PDU
immediately.