You can set the PDU to send system log ( syslog) messages to up to four systems on the network. syslog is the standard UNIX system logging utility, which monitors critical system events and configuration changes. These syslog messages are sent to the systems using user datagram protocol (UDP) port 514.
For more information about syslog, refer to the Oracle Solaris documentation and the syslogd(1M) and syslog.conf(4) man pages.
Lines IN0: L1: 0.96kW 0.96kVA 8.02A 120.0V L2: 0.47kW 0.56kVA 4.65A 121.6V L3: 0.50kW 0.56kVA 4.66A 121.1V Lines IN1: L1: 0.93kW 0.93kVA 7.75A 120.0V L2: 0.47kW 0.55kVA 4.59A 121.6V L3: 0.47kW 0.53kVA 4.44A 121.1V Inputs: IN0: 1.93kW IN1: 1.88kW PDU: 3.82kW
In the example, Lines IN0: L1: 0.96kW 0.96kVA 8.02A 120.0V, is a message for Input 0, Phase 1. The PDU is consuming 8.02A, 0.96 kVA, and 0.96kW with 120.0V applied.
Inputs: IN0: 1.93kW, displays the message of the power consumed by Input 0.PDU: 3.82kW, displays the message of the power consumed by the PDU.
See Login Information.
For example, if you set the duration for 12 hours, the PDU sends syslog messages every 12 hours.
If checked , and if you set threshold parameter values (see Set Threshold Parameter Values (Enhanced PDU)), the metering unit sends alarm messages when threshold parameter values are reached.
Possible syslog alarm messages are shown in Enabling and Configuring SNMP (Enhanced PDU).